[Equest-users] Tank less DWH
David Eldridge via Equest-users
equest-users at lists.onebuilding.org
Tue Jun 20 08:48:57 PDT 2017
I think there are two separate issues. The vendor is comparing their system as a retrofit to an older and inefficient system. For Appendix G modeling purposes you wouldn’t compare against that existing hot water system, the baseline would be the code minimum new system as selected by your building’s characteristics.
So even if the system did save 30% to 40% against existing storage systems, it won’t likely do that against an Appendix G baseline.
Arriving at the 30% to 40% figure for existing building retrofits is a whole different can of worms – tank losses could be reduced for sure. The thermal efficiency is shown to be very high. There are many other losses in the existing system that may also come into play though, so the rule of thumb savings figure is difficult without saying “percentage of what” – it wouldn’t affect the flow rates as you mention which is an additional opportunity, and if the system is recirculating it will have losses from that activity.
Looks like a good product though, definitely some energy reduction potential for sites that fit the capacity and venting requirements.
David
David S. Eldridge, Jr., P.E., LEED AP BD+C, BEMP, BEAP, HBDP
Grumman/Butkus Associates
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Morteza Kasmai via Equest-users
Sent: Tuesday, June 20, 2017 9:42 AM
To: Nicholas Caton <Nicholas.Caton at schneider-electric.com>
Cc: equest-users <equest-users at lists.onebuilding.org>
Subject: Re: [Equest-users] Tank less DWH
Nick,
Thank you for your guidance, as always your suggestions is very helpful.
I am agreeing with you that serious energy savings related to service hot water serving is through low flow fixtures, however the manufacturer provided some engineering data, including thermal efficiency, of the water heater (page 8 of the attach file) that I thought can be helpful to achieve more savings.
I wanted to be sure on selecting the correct system for the base model. As I understand from your suggestions, since this is storage less heater in the proposed design, for the baseline model, I have to select “Gas instantaneous water heater” in Table 7.8 and there are no any other options, is this correct?
I truly appreciate your help,
Morteza
[https://lh6.googleusercontent.com/Uuukta80GuFfvKouzA0mdSvUXqml7MtSwSiw-evuGMU=w147-h43-p-no]
On Mon, Jun 19, 2017 at 5:05 PM, Nicholas Caton <Nicholas.Caton at schneider-electric.com<mailto:Nicholas.Caton at schneider-electric.com>> wrote:
I don’t believe I’ve ever documented 30-40% Service Hot Water savings on unitary heating equipment alone. Either your designer/manufacturer must also be counting on serious reductions with low flow fixtures, or somebody is trying to sell something...
The Appendix G Table G3.1 will direct you back towards the table at the end of the Service Water Heating section in 90.1 for direct guidance on what the baseline case should reflect in relation to your proposed case instantaneous heaters. Looks like for your make/model you’ll be needing to address both thermal combustion efficiency AND determine standby losses based upon the capacity of the unit cited.
I’d advise caution before immediately entering “n/a” for proposed case standby losses in your LEED documentation. Consider whether in fact there is a storage tank somewhere, or other opportunities outside of combustion and piping distributions for heat to leave the system.
For the proposed case side, I might poke the manufacturer (time allowing) to provide you a thermal efficiency (combustion + condensate recovery) at a sampling of firing rates for a given delta (ground water --> delivery temp), and use that data to evaluate whether the library curves eQUEST assigns for instantaneous gas boilers is in alignment or otherwise needs tweaking. If you don’t have time to dive this far I’d simply be mindful to ensure baseline + proposed case curves are at least matching.
Hope that helps!
~Nick
[cid:image001.png at 01D2E9B1.54BC3770]
Nick Caton, P.E., BEMP
Senior Energy Engineer
Regional Energy Engineering Manager
Energy and Sustainability Services
Schneider Electric
D 913.564.6361<tel:(913)%20564-6361>
M 785.410.3317<tel:(785)%20410-3317>
F 913.564.6380<tel:(913)%20564-6380>
E nicholas.caton at schneider-electric.com<mailto:nicholas.caton at schneider-electric.com>
15200 Santa Fe Trail Drive
Suite 204
Lenexa, KS 66219
United States
[cid:image002.png at 01D2E9B1.54BC3770]
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org<mailto:equest-users-bounces at lists.onebuilding.org>] On Behalf Of Morteza Kasmai via Equest-users
Sent: Monday, June 19, 2017 10:54 AM
To: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: [Equest-users] Tank less DWH
Hello, everyone
I am trying to model a new DWH (Intelli-hot system Gen-II-iQ1501) for a mid-rise residential building. This is a high-output, on-demand water heater, which eliminates storage tank, standby losses, and mixing valves. Per the manufacturers and the project’s engineer notes, expected savings on hot water for this type of WH compare to a regular storage tank WH is 30% to 40%. I am wondering what type of WH should I select for the Baseline Case in order to comply with ASHRAE/LEED energy modeling protocol.
Your thoughts and suggestions would be highly appreciated,
Morteza
[https://lh6.googleusercontent.com/Uuukta80GuFfvKouzA0mdSvUXqml7MtSwSiw-evuGMU=w147-h43-p-no]
______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
______________________________________________________________________
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170620/a833d027/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 255 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170620/a833d027/attachment-0004.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.png
Type: image/png
Size: 8477 bytes
Desc: image002.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170620/a833d027/attachment-0005.png>
More information about the Equest-users
mailing list