[Equest-users] Fw: Composite wall of frame and cavity insulation
Nicholas Caton via Equest-users
equest-users at lists.onebuilding.org
Mon Apr 3 08:19:20 PDT 2017
It would be nice quality-of-life feature to someday add a “framing + insulation” calculator to the detailed interface, but in the interim it’s not too bad to look up:
With 90.1-2007 open/at-hand:
· Table A9.2B details effective R-values for a layer of steel studs + batt layer, for a variety of spacing & framing dimensions.
· For wood framing, a parallel path calc can reference:
o R-1.25/in for two-by wood framing (See Table A9.4D if you are uncertain of actual lumber depth dimensions), and
o Table A9.4C to look up effective batt insulation when compressed into wood stud cavities for various dimensions.
I would expect these to line up very closely with the insulation+ framing layer the wizards generate. Opening a second instance of eQUEST to leverage the wizard dropdowns is an option I suppose, though I’m not sure if it will save you much time relative to tabbing a copy of 90.1.
~Nick
[cid:image001.png at 01D2AC60.A65DF8E0]
Nick Caton, P.E., BEMP
Senior Energy Engineer
Regional Energy Engineering Manager
Energy and Sustainability Services
Schneider Electric
D 913.564.6361
M 785.410.3317
F 913.564.6380
E nicholas.caton at schneider-electric.com<mailto:nicholas.caton at schneider-electric.com>
15200 Santa Fe Trail Drive
Suite 204
Lenexa, KS 66219
United States
[cid:image002.png at 01D2AC60.A65DF8E0]
From: John Aulbach [mailto:jra_sac at yahoo.com]
Sent: Sunday, April 02, 2017 10:28 PM
To: Nicholas Caton <Nicholas.Caton at schneider-electric.com>
Cc: 'equest-users' <equest-users at lists.onebuilding.org>
Subject: Re: RE: [Equest-users] Fw: Composite wall of frame and cavity insulation
Hi Nick:
You just keep doing what you are doing. You do this forum a great service.
Back before you were born, I recall a California Energy Commission manual that gave equivalent U-Values for framing plus insulation - whole tables, and am currently trying to find them.
When you input a frame (wood or metal) with a certain batt insulation R-value, the resulting code in the .INP file (or in the Detail Edit wall composition), it comes out like the attached (E1 EWall Cons Mat 2 (6)). I cannot find this reference in any eQuest or DOE-2 documentation.
But it MEANS something !! Change the framing and its spacing at the R value and the code changes.
THAT is the coding i am seeking.
Thanks.
John
On Friday, March 31, 2017, 6:25:37 AM PDT, Nicholas Caton <Nicholas.Caton at schneider-electric.com<mailto:Nicholas.Caton at schneider-electric.com>> wrote:
I’ll keep working on getting myself older and learned… I’m at least accomplishing one of those things day by day!
Are you looking specifically for framing + insulation layer properties for a MATERIAL? I’m not aware if those exist in any current eQUEST library as distributed, but you can look up various combinations for wood/steel framing in 90.1 Appendix A (two separate tables).
There are some (though not a ton) of library LAYERS describing different interior/exterior constructions with attributed ASHRAE codes, but I’m not very clear on what list of constructions these labels are supposed to reference. Presumably something in Fundamentals of a specific year/vintage, I would guess.
Regards,
~Nick
[cid:image001.png at 01D2AC60.A65DF8E0]
Nick Caton, P.E., BEMP
Senior Energy Engineer
Regional Energy Engineering Manager
Energy and Sustainability Services
Schneider Electric
D 913.564.6361
M 785.410.3317
F 913.564.6380
E nicholas.caton at schneider-electric.com<mailto:nicholas.caton at schneider-electric.com>
15200 Santa Fe Trail Drive
Suite 204
Lenexa, KS 66219
United States
[cid:image002.png at 01D2AC60.A65DF8E0]
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of John Aulbach via Equest-users
Sent: Friday, March 31, 2017 11:57 AM
To: Equest-users <equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>>
Subject: [Equest-users] Fw: Composite wall of frame and cavity insulation
Cant seem to get this message through. Will try again.
----- Forwarded Message -----
From: John Aulbach <jra_sac at yahoo.com<mailto:jra_sac at yahoo.com>>
To: Equest-users <equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>>
Sent: Friday, March 31, 2017, 2:29:30 AM PDT
Subject: Composite wall of frame and cavity insulation
This is probably something for older learned types (or Nick Caton).
I seem to remember somewhere in the cobwebs of DOE-2 having a particular steel (or wood) framing size and spacing and having different insulating R-values added in the air space between A wall section code fell out, thus being able to be put into a DETAIL Edit construction.
Is the answer to make a dummy Wizard run, create the steel frame spacing, add the insulation, then go to the tree diagram and determine the wall "code" it invented.
This stuff doesn't appear to exist in the wall library.
Thanks
John
______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
______________________________________________________________________
______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
______________________________________________________________________
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170403/3b4dcb9d/attachment-0005.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 255 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170403/3b4dcb9d/attachment-0010.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.png
Type: image/png
Size: 8477 bytes
Desc: image002.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170403/3b4dcb9d/attachment-0011.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: oledata.mso
Type: application/octet-stream
Size: 7133 bytes
Desc: oledata.mso
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170403/3b4dcb9d/attachment-0005.obj>
More information about the Equest-users
mailing list