[Equest-users] Airflow Schedule based on Occupancy - switch statements and symbol values
Bishop, Bill via Equest-users
equest-users at lists.onebuilding.org
Wed Oct 26 07:12:39 PDT 2016
I retained the case numbers from the default DOE-2 expression for MIN-FLOW-RATIO below. The switch statement is based on symbol values according to the symbol table for system TYPE. The symbol tables are found in a file called BDLKEY.OUT which, for eQUEST 3-65, is found in Documents -> eQUEST 3-65 Data -> DOE-2.
A short cut to determining which case numbers to use with switch statements is to enter a user expression for an appropriate keyword. For system TYPE, you could enter, “#SV(#P("TYPE"))” as a user expression for a zone keyword such as MIN-FLOW/AREA to see which symbol value matches the zone’s system type.
~Bill
From: Daric Adair [mailto:Daric.Adair at hei-eng.com]
Sent: Tuesday, October 25, 2016 4:23 PM
To: Bishop, Bill <bbishop at pathfinder-ea.com>; Darryl Kasun <darryl.kasun at gmail.com>
Subject: RE: [Equest-users] Airflow Schedule based on Occupancy
Bill;
Can you expand/explain where the “case #” / “case ##” elements come from/are defined (help files, manual?). I can’t seem to place my finger on where they are….thanks!
Thanks,
DARIC R. ADAIR PE, C.E.M.
Henderson Engineers, Inc. | Mechanical Engineer, Energy Analyst
dir 913 742 5530 tel 913 742 5000 fax 913 742 5001 tx id #F-001236 email daric.adair at hei-eng.com www.hei-eng.com<http://www.hei-eng.com/>
Licensed in KS.
From: Bishop, Bill via Equest-users [mailto:equest-users at lists.onebuilding.org]
Sent: Tuesday, October 25, 2016 1:41 PM
To: Darryl Kasun <darryl.kasun at gmail.com<mailto:darryl.kasun at gmail.com>>
Cc: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: Re: [Equest-users] Airflow Schedule based on Occupancy
Hi Darryl,
First, I would use a user expression for ZONE: MIN-FLOW-RATIO for any zones that you want to control to 6 ACH minimum. Then I would create and apply a ZONE: MIN-FLOW-SCH with values of 1.0 during occupied hours and -999 for unoccupied hours. The expression below for MIN-FLOW-RATIO should give you 6 ACH . It will give you an error if a value is entered for ASSIGNED-FLOW that is less than 6 ACH.
Regards,
~Bill
/* This expression for ZONE:MIN-FLOW-RATIO calculates and enters
a value based on a desired minimum ACH. */
if (#P("MIN-CFM-RATIO") == unused)
then unused
else switch #SV(#P("TYPE"))
case 2 : unused
case 17 : unused
case 19 : unused
case 26 : unused
case 27 : unused
case 28 : unused
case 29 : unused
default : if (#RV(#L("AIR-CHANGES/HR")) == 0
.AND. #L("AIR-CHANGES/HR") = 6) then 1 $ 6 ACH
else if (#RV(#L("ASSIGNED-FLOW")) == 0) then
6*#LR("SPACE","HEIGHT")*#LR("SPACE","AREA")/60/#L("ASSIGNED-FLOW")
else no_default endif
endif
endswitch
endif
William Bishop, PE, BEMP, BEAP, CEM, LEED AP | Pathfinder Engineers & Architects LLP
Senior Energy Engineer
[cid:image002.jpg at 01D22F71.7FB76120] [cid:image004.jpg at 01D22F71.7FB76120]
134 South Fitzhugh Street Rochester, NY 14608
T: (585) 698-1956 F: (585) 325-6005
bbishop at pathfinder-ea.com<mailto:wbishop at pathfinder-ea.com> www.pathfinder-ea.com<http://www.pathfinder-ea.com/>
[http://png-5.findicons.com/files/icons/977/rrze/720/globe.png]Carbon Fee and Dividend - simple, effective, and market-based.
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Darryl Kasun via Equest-users
Sent: Tuesday, October 25, 2016 1:54 PM
To: equest <equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>>
Subject: [Equest-users] Airflow Schedule based on Occupancy
Hi everyone,
I have a zone that is served by a VAV system. The controls for the zone state that when the zone is occupied, the VAV box should be fully opened and when unoccupied, the zone supply air be reduced to 6 ACH. There are multiple zones controlled in this manner.
To model this I am thinking of creating a min airflow schedule that matches occupancy schedule. The minimum hourly fraction within the min airflow schedule would be equivalent to the airflow fraction of 6 ACH.
In other words, if there are hourly fractions in the min airflow schedule (which is a copy of the occupancy schedule) that are below the equivalent fraction of 6 ACH, those hours would be changed to the 6 ACH fraction.
Hopefully that makes sense to you.
This method seems fine to me but a bit tedious as it will require developing multiple min airflow schedules.
Any thoughts?
________________________________
This email and any files transmitted with it are confidential and are intended solely for the use of the individual or entity to whom they are addressed. This communication represents the originator's personal views and opinions, which do not necessarily reflect those of Henderson Engineers, Inc. If you are not the original recipient or the person responsible for delivering the email to the intended recipient, be advised that you have received this email in error, and that any use, dissemination, forwarding, printing, or copying of this email is strictly prohibited. If you received this email in error, please immediately notify administrator at hei-eng.com<mailto:administrator at hei-eng.com>.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20161026/641d4e3c/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.jpg
Type: image/jpeg
Size: 1400 bytes
Desc: image002.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20161026/641d4e3c/attachment.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.jpg
Type: image/jpeg
Size: 1509 bytes
Desc: image004.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20161026/641d4e3c/attachment-0001.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image006.png
Type: image/png
Size: 4178 bytes
Desc: image006.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20161026/641d4e3c/attachment.png>
More information about the Equest-users
mailing list