[Equest-users] Airflow Schedule based on Occupancy
Bishop, Bill via Equest-users
equest-users at lists.onebuilding.org
Tue Oct 25 11:41:21 PDT 2016
Hi Darryl,
First, I would use a user expression for ZONE: MIN-FLOW-RATIO for any zones that you want to control to 6 ACH minimum. Then I would create and apply a ZONE: MIN-FLOW-SCH with values of 1.0 during occupied hours and -999 for unoccupied hours. The expression below for MIN-FLOW-RATIO should give you 6 ACH . It will give you an error if a value is entered for ASSIGNED-FLOW that is less than 6 ACH.
Regards,
~Bill
/* This expression for ZONE:MIN-FLOW-RATIO calculates and enters
a value based on a desired minimum ACH. */
if (#P("MIN-CFM-RATIO") == unused)
then unused
else switch #SV(#P("TYPE"))
case 2 : unused
case 17 : unused
case 19 : unused
case 26 : unused
case 27 : unused
case 28 : unused
case 29 : unused
default : if (#RV(#L("AIR-CHANGES/HR")) == 0
.AND. #L("AIR-CHANGES/HR") = 6) then 1 $ 6 ACH
else if (#RV(#L("ASSIGNED-FLOW")) == 0) then
6*#LR("SPACE","HEIGHT")*#LR("SPACE","AREA")/60/#L("ASSIGNED-FLOW")
else no_default endif
endif
endswitch
endif
William Bishop, PE, BEMP, BEAP, CEM, LEED AP | Pathfinder Engineers & Architects LLP
Senior Energy Engineer
[cid:image007.jpg at 01D22ECD.DEB59060] [cid:image008.jpg at 01D22ECD.DEB59060]
134 South Fitzhugh Street Rochester, NY 14608
T: (585) 698-1956 F: (585) 325-6005
bbishop at pathfinder-ea.com<mailto:wbishop at pathfinder-ea.com> www.pathfinder-ea.com<http://www.pathfinder-ea.com/>
[http://png-5.findicons.com/files/icons/977/rrze/720/globe.png]Carbon Fee and Dividend - simple, effective, and market-based.
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Darryl Kasun via Equest-users
Sent: Tuesday, October 25, 2016 1:54 PM
To: equest <equest-users at lists.onebuilding.org>
Subject: [Equest-users] Airflow Schedule based on Occupancy
Hi everyone,
I have a zone that is served by a VAV system. The controls for the zone state that when the zone is occupied, the VAV box should be fully opened and when unoccupied, the zone supply air be reduced to 6 ACH. There are multiple zones controlled in this manner.
To model this I am thinking of creating a min airflow schedule that matches occupancy schedule. The minimum hourly fraction within the min airflow schedule would be equivalent to the airflow fraction of 6 ACH.
In other words, if there are hourly fractions in the min airflow schedule (which is a copy of the occupancy schedule) that are below the equivalent fraction of 6 ACH, those hours would be changed to the 6 ACH fraction.
Hopefully that makes sense to you.
This method seems fine to me but a bit tedious as it will require developing multiple min airflow schedules.
Any thoughts?
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20161025/33361a31/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image007.jpg
Type: image/jpeg
Size: 1517 bytes
Desc: image007.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20161025/33361a31/attachment-0004.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image008.jpg
Type: image/jpeg
Size: 1647 bytes
Desc: image008.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20161025/33361a31/attachment-0005.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image009.png
Type: image/png
Size: 3859 bytes
Desc: image009.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20161025/33361a31/attachment-0002.png>
More information about the Equest-users
mailing list