I think there's such a large difference in computational intensity (?) between DOE-2 (or
any simulation program that models a thermal zone as a single node) and CFD that coupling
the two together does not make sense to me, even if it could be done. I think you're much
better off looking into coupling DOE-2 to a multi-zone air-flow program like CONTAM or
COMIS. Even then, you have to exchange data back and forth at each time step, since air
flows and zone air temperatures are so interconnected. I spent more than a year in
coupling EnergyPlus to COMIS back in 200-2002.
It would probably be easier to do in DOE-2 SYSTEMS, but would still require changes to the
source code to call the airflow program at each time step. Not trivial and not a "work
around". Thoughts from others would be welcomed.
Joe
Joe Huang
White Box Technologies, Inc.
346 Rheem Blvd., Suite 205A
Moraga CA 94556
yjhuang at whiteboxtechnologies.com
http://weather.whiteboxtechnologies.com for simulation-ready weather data
(o) (925)388-0265
(c) (510)928-2683
"building energy simulations at your fingertips"
On 2/29/2016 7:52 AM, 冷面寒枪 wrote:
>
> Hi,everyone
>
> I want to invesitigate nature ventiation's impaction on building energy.However,nature
> ventilation feature has many restrictions in eQUEST.So I consider coupling DOE2 with CFD
> software such as fluent to analysis the energy saving potential of nature
> ventilation.Any suggestion?
>
> Thanks you!
>
>
> ------------------
> *Yongqing Zhao*
> *Changsha Green Building & Energy Saving Technology CO.,LTD
> *NO.438,Shaoshan Road,Changsha,Hunan,China
> Telephone:13574805636
> Email:zhaoyongqing1987 at 126.com
> 503271081 at qq.com
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20160229/478c1370/attachment-0002.htm>
More information about the Equest-users
mailing list