    I think there's such a large difference in computational intensity
    (?) between DOE-2 (or any simulation program that models a thermal
    zone as a single node) and CFD that coupling the two together does
    not make sense to me, even if it could be done.  I think you're much
    better off looking into coupling DOE-2 to a multi-zone air-flow
    program like CONTAM or COMIS.  Even then, you have to exchange data
    back and forth at each time step, since air flows and zone air
    temperatures are so interconnected.  I spent more than a year in
    coupling EnergyPlus to COMIS back in 200-2002.<br>
    It would probably be easier to do in DOE-2 SYSTEMS, but would still
    require changes to the source code to call the airflow program at
    each time step.  Not trivial and not a "work around".  Thoughts from
    others would be welcomed.<br>
    <br>
    Joe<br>
    <pre class="moz-signature" cols="90">Joe Huang
White Box Technologies, Inc.
346 Rheem Blvd., Suite 205A
Moraga CA 94556
<a class="moz-txt-link-abbreviated" href="mailto:yjhuang@whiteboxtechnologies.com">yjhuang@whiteboxtechnologies.com</a>
<a class="moz-txt-link-freetext" href="http://weather.whiteboxtechnologies.com">http://weather.whiteboxtechnologies.com</a> for simulation-ready weather data
(o) (925)388-0265
(c) (510)928-2683
"building energy simulations at your fingertips"
</pre>
    <div class="moz-cite-prefix">On 2/29/2016 7:52 AM, 冷面寒枪 wrote:<br>
    </div>
    <blockquote cite="mid:tencent_62FA03311CDE8C2D2F434227@qq.com"
      type="cite">
      <div>
        <p style="margin: 0px 0px 14px; padding: 0px 5px 5px 0px;
          border: none; line-height: 1.4; color: rgb(75, 75, 75);
          font-family: Arial;">Hi,everyone</p>
        <p style="margin: 0px 0px 14px; padding: 0px 5px 5px 0px;
          border: none; line-height: 1.4; color: rgb(75, 75, 75);
          font-family: Arial;">I want to invesitigate nature
          ventiation's impaction on building energy.However,nature
          ventilation feature has many restrictions in eQUEST.So I
          consider coupling DOE2 with CFD software such as fluent to
          analysis the energy saving potential of nature ventilation.Any
          suggestion?</p>
        <p style="margin: 0px 0px 14px; padding: 0px 5px 5px 0px;
          border: none; line-height: 1.4; color: rgb(75, 75, 75);
          font-family: Arial;">Thanks you!</p>
      </div>
      <div><br>
      </div>
      <div>
        <div style="color:#909090;font-family:Arial
          Narrow;font-size:12px">------------------</div>
        <div style="font-size:14px;font-family:Verdana;color:#000;">
          <div>
            <div><font color="#3366ff" size="2"><strong>Yongqing Zhao</strong></font></div>
            <div><font size="2"><strong><font color="#006600">Changsha
                    Green Building & Energy Saving Technology
                    CO.,LTD<br>
                  </font></strong><font color="#3366ff">NO.438,Shaoshan
                  Road,Changsha,Hunan,China<br>
                  Telephone:13574805636</font></font></div>
            <div><font color="#3366ff" size="2"><a class="moz-txt-link-abbreviated" href="mailto:Email:zhaoyongqing1987@126.com">Email:zhaoyongqing1987@126.com</a></font></div>
            <div><font size="2">         <span><a class="moz-txt-link-abbreviated" href="mailto:503271081@qq.com">503271081@qq.com</a></span></font> </div>
          </div>
        </div>
      </div>
      <div> </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
Equest-users mailing list
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a>
To unsubscribe from this mailing list send  a blank message to <a class="moz-txt-link-abbreviated" href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a>
</pre>
    </blockquote>
    <br>
  </body>
</html>