[Equest-users] Heat Recovery Chiller

Bikesh Dahal BDahal at EMEGroup.com
Tue Feb 9 07:55:30 PST 2016


Unfortunately it is. So, how is this normally done. Use excel spreadsheet to calculate savings? Or is there a work around to it.

From: Brian Fountain [mailto:bfountain at greensim.com]
Sent: Tuesday, February 09, 2016 10:47 AM
To: Bikesh Dahal; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Heat Recovery Chiller

Heat recovery from chillers is a little tricky in eQUEST.  In order to recover heat, the condenser loop supply temperature must be higher than the heating loop return temperature.  Doing that typically increases the lift on the chiller increasing the electrical input energy.

You stated you couldn't recover to your reheat loop -- is it a secondary loop?  Unfortunately no primary equipment can be attached to secondary loops.
On 09/02/2016 10:39 AM, Bikesh Dahal wrote:
Hi Everyone,
I am working on a project where I have a heat recovery chiller that is recovering heat from IT room units in a hospital and then providing heat to VAV reheat systems for other spaces. I am trying to model this in  equest and not getting the desired result.

eQuest is not letting me connect to reheat loop. And when I connect it to my steam loop, I see no heating savings whereas I see increased cooling use.
Anyone has any ideas on how to model this properly?

Bikesh Dahal, BEMP
Associate

[cid:image003.png at 01D06C70.35E5BD50]
159 West 25th Street
New York, NY  10001
tel:  212-529-5969, ext. 318
fax: 212-529-6023
bdahal at emegroup.com<mailto:bdahal at emegroup.com>
www.emegroup.com<http://www.emegroup.com>
NY ▪ Albany ▪ Philadelphia ▪ Denver





_______________________________________________

Equest-users mailing list

http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org

To unsubscribe from this mailing list send  a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20160209/5009b7ea/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 8763 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20160209/5009b7ea/attachment-0002.png>


More information about the Equest-users mailing list