Heat recovery from chillers is a little tricky in eQUEST. In order to
recover heat, the condenser loop supply temperature must be higher than
the heating loop return temperature. Doing that typically increases the
lift on the chiller increasing the electrical input energy.
You stated you couldn't recover to your reheat loop -- is it a secondary
loop? Unfortunately no primary equipment can be attached to secondary
loops.
On 09/02/2016 10:39 AM, Bikesh Dahal wrote:
>
> Hi Everyone,
>
> I am working on a project where I have a heat recovery chiller that is
> recovering heat from IT room units in a hospital and then providing
> heat to VAV reheat systems for other spaces. I am trying to model this
> in equest and not getting the desired result.
>
> eQuest is not letting me connect to reheat loop. And when I connect it
> to my steam loop, I see no heating savings whereas I see increased
> cooling use.
>
> Anyone has any ideas on how to model this properly?
>
> *Bikesh Dahal, BEMP*
>
> *Associate*
>
> *//*
>
> cid:image003.png at 01D06C70.35E5BD50
>
> 159 West 25th Street
>
> New York, NY 10001
>
> tel: 212-529-5969, ext. 318
>
> fax: 212-529-6023
>
> bdahal at emegroup.com <mailto:bdahal at emegroup.com>
>
> www.emegroup.com <http://www.emegroup.com>
>
> NY ▪ Albany ▪ Philadelphia ▪ Denver
>
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20160209/aa955d28/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 8763 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20160209/aa955d28/attachment-0002.png>
More information about the Equest-users
mailing list