[Equest-users] Coil Flow and Pressure Drop
Darryl Kasun via Equest-users
equest-users at lists.onebuilding.org
Tue Aug 30 11:28:22 PDT 2016
Hi everyone,
I am looking for confirmation I understand what eQUEST is doing with inputs
for VAV boxes with HW reheat coils.
On the water side for each. reheat coil, I know design flow, design delta
T, design heat gain and design pressure drop.
Based on the below inputs, I am assuming eQUEST will calculate the design
flow ~ 1.9 GPM; [9,625 Btu/hr / 500 / 10 degF = 1.9 GPM].
[image: Inline image 5]
On the air side, I also know the design flow and delta T. For this
example, it is 270 CFM and 25 degF:
[image: Inline image 4]
Will eQUEST use the max airflow (270 CFM) and subsequently calculate the
max heat gain across the coil (~7,290 Btu/hr); [1.08 * 270 CFM * 25 degF =
7,290 Btu/hr].
If so, does eQUEST adjust the HW flow rate through coil to match this heat
gain (~1.46 GPM); [7,290 Btu/hr / 500 / 10 degF = 1.46 GPM]
Am I correct in how eQUEST is using these inputs?
Also. how does eQUEST calculate the PD through the coils, both on the
water-side and air-side?
Thanks
Darryl
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20160830/a1a1709d/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image.png
Type: image/png
Size: 29685 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20160830/a1a1709d/attachment-0002.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image.png
Type: image/png
Size: 18890 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20160830/a1a1709d/attachment-0003.png>
More information about the Equest-users
mailing list