<div dir="ltr">Hi everyone,<div><br></div><div>I am looking for confirmation I understand what eQUEST is doing with inputs for VAV boxes with HW reheat coils.  </div><div><br></div><div>On the water side for each. reheat coil, I know design flow, design delta T, design heat gain and design pressure drop.  </div><div><br></div><div>Based on the below inputs, I am assuming eQUEST will calculate the design flow ~ 1.9 GPM;  [9,625 Btu/hr / 500 / 10 degF = 1.9 GPM].<br></div><div><br></div><div><img src="cid:ii_156dca7670435b1e" alt="Inline image 5" width="454" height="255"><br></div><div><br></div><div>On the air side, I also know the design flow and delta T.  For this example, it is 270 CFM and 25 degF:</div><div><br></div><div><img src="cid:ii_156dca6cf66cbaf4" alt="Inline image 4" width="454" height="152"><br></div><div><br></div><div>Will eQUEST use the max airflow (270 CFM) and subsequently calculate the max heat gain across the coil (~7,290 Btu/hr); [1.08 * 270 CFM * 25 degF = 7,290 Btu/hr].</div><div><br></div><div>If so, does eQUEST adjust the HW flow rate through coil to match this heat gain (~1.46 GPM); [7,290 Btu/hr / 500 / 10 degF = 1.46 GPM]  </div><div><br></div><div>Am I correct in how eQUEST is using these inputs?</div><div><br></div><div>Also. how does eQUEST calculate the PD through the coils, both on the water-side and air-side?</div><div><br></div><div>Thanks</div><div>Darryl</div></div>