Nick and Grammy,
Thanks a lot.
I was confused by SD input that only allows maximum 2 HVAC system.
Lisa Li
--- On Wed, 1/12/11, Nick Caton <ncaton at smithboucher.com> wrote:
From: Nick Caton <ncaton at smithboucher.com>
Subject: RE: [Equest-users] Maximum HVAC Systems
To: "Grammy" <grammy.hkust at gmail.com>, "Lisa Li" <li.lisa at ymail.com>
Cc: "equest-users" <equest-users at lists.onebuilding.org>
Date: Wednesday, January 12, 2011, 3:13 PM
Lisa,
I believe the upper limit on # of unique systems follows the
upper limit on # of zones, which is something higher than 1,000 but I’m
not certain where the sidewalk ends in the current version 3.64. If you
should have more than 1,000 zones or systems to include in one building, you might
need to use multiple models.
A more probable limit for most situations is the number of zones
actually defined – and this relates to Grammy’s point about 1
system per zone: If you only have 15 zones, you can’t complete a
simulation with more than 15 systems. It follows that you need a minimum
of 15 spaces to define 15 zones. The important point to take away here is
that you really must, at a minimum, define at least one distinct space to
correspond to each system when you are considering and creating your building
geometries.
The building design you’re describing thus far sounds
perfectly do-able within eQuest.
~Nick
NICK CATON, E.I.T.
PROJECT ENGINEER
Smith & Boucher Engineers
25501 west valley parkway
olathe ks 66061
direct 913 344.0036
fax 913 345.0617
www.smithboucher.com
From:
equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Grammy
Sent: Wednesday, January 12, 2011 4:49 AM
To: Lisa Li
Cc: equest-users
Subject: Re: [Equest-users] Maximum HVAC Systems
Hi, Lisa,
I am not clear what's your point, but I can state that one
zone have only one system assigned (exception only baseboard). And one building
can have more than one system to condition different zones: condition or
ventilation only, or uncontidtion.
On Wed, Jan 12, 2011 at 9:52 AM, Lisa Li <li.lisa at ymail.com> wrote:
Dear All,
How many HVAC systems can be created to model a building with multi-zones?
I am doing energy consumption modeling for an existing club house building.
There are rooftop units with gas heating, split AC units, split heat pumps
and gas furnace with split DX coils, etc. All the units have different
capacity and EER too.
Regards,
Lisa Li
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110112/cc9ca7e3/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110112/cc9ca7e3/attachment.jpeg>
More information about the Equest-users
mailing list