[Equest-users] Maximum HVAC Systems

Nick Caton ncaton at smithboucher.com
Wed Jan 12 07:13:06 PST 2011


Lisa, 

 

I believe the upper limit on # of unique systems follows the upper limit
on # of zones, which is something higher than 1,000 but I'm not certain
where the sidewalk ends in the current version 3.64.  If you should have
more than 1,000 zones or systems to include in one building, you might
need to use multiple models.

 

A more probable limit for most situations is the number of zones
actually defined - and this relates to Grammy's point about 1 system per
zone:  If you only have 15 zones, you can't complete a simulation with
more than 15 systems.  It follows that you need a minimum of 15 spaces
to define 15 zones.  The important point to take away here is that you
really must, at a minimum, define at least one distinct space to
correspond to each system when you are considering and creating your
building geometries.  

 

The building design you're describing thus far sounds perfectly do-able
within eQuest.

 

~Nick

  

 

 

 

NICK CATON, E.I.T.

PROJECT ENGINEER

Smith & Boucher Engineers

25501 west valley parkway

olathe ks 66061

direct 913 344.0036

fax 913 345.0617

www.smithboucher.com 

 

From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Grammy
Sent: Wednesday, January 12, 2011 4:49 AM
To: Lisa Li
Cc: equest-users
Subject: Re: [Equest-users] Maximum HVAC Systems

 

Hi, Lisa,

 

I am not clear what's your point, but I can state that one zone have
only one system assigned (exception only baseboard). And one building
can have more than one system to condition different zones: condition or
ventilation only, or uncontidtion. 

 

 

On Wed, Jan 12, 2011 at 9:52 AM, Lisa Li <li.lisa at ymail.com> wrote:

Dear All,
How many HVAC systems can be created to model a building with
multi-zones?
I am doing energy consumption modeling for an existing club house
building. There are rooftop units with gas heating, split AC units,
split heat pumps and gas furnace with split DX coils, etc. All the units
have different capacity and EER too.
Regards,
Lisa Li



_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send  a blank message to 
EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG

 

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110112/55ddb139/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110112/55ddb139/attachment.jpeg>


More information about the Equest-users mailing list