[Equest-users] Converting Heat Pump COP to EIR

Ana N. ananeddav at hotmail.com
Mon Jan 3 08:25:48 PST 2011



 
You can use this link to access discussion on this topic.
 
http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/2010-May/004407.html
 
 
Heating EIR = (1/(COP*3.413)-0.012167)/((1/3.413)-0.012167)
and
Heating EIR = (1/((HSPF*0.28+1.13)*3.413)-0.012167)/((1/3.413)-0.012167)
 
Hope this helps, 
 
Ana
 



Date: Mon, 3 Jan 2011 08:12:26 -0800
From: kathryn.kerns at bceengineers.com
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Converting Heat Pump COP to EIR



Everyone, is there a relationship written down somewhere that removes fan energy from a heat pump COP value to develop a heating EIR?  Something like the DX cooling EER equation that removes fan energy from EIR  cooling values? It looks like the eQuest wizard is doing something like that when a heat pump heating COP is entered, but I am not sure what.
_______________________________________________ Equest-users mailing list http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG 		 	   		  