[Equest-users] [Bldg-sim] Heat Pump Efficiencies
Mehta, Gaurav
Gaurav.Mehta at stantec.com
Wed May 12 16:04:49 PDT 2010
Heating EIR = (1/(COP*3.413)-0.012167)/((1/3.413)-0.012167)
and
Heating EIR = (1/((HSPF*0.28+1.13)*3.413)-0.012167)/((1/3.413)-0.012167)
Gaurav Mehta, LEED® AP
Sustainable Building Analyst
Stantec
1932 First Avenue Suite 307
Seattle WA 98101
Ph: (206) 770-7779
Fx: (206) 770-5941
Gaurav.Mehta at stantec.com
stantec.com <http://www.stantec.com>
The content of this email is the confidential property of Stantec and should not be copied, modified, retransmitted, or used for any purpose except with Stantec's written authorization. If you are not the intended recipient, please delete all copies and notify us immediately.
ü Please consider the environment before printing this email.
From: bldg-sim-bounces at lists.onebuilding.org [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Demba Ndiaye
Sent: Wednesday, May 12, 2010 12:27 PM
To: equest-users at lists.onebuilding.org; bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] [Equest-users] Heat Pump Efficiencies
The formulas below were shared sometimes ago. Does anyone know the corresponding formulas for the COP and HSPF?
_______________
Demba NDIAYE
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Bishop, Bill
Sent: Wednesday, March 24, 2010 2:39 PM
To: Carol Gardner; Bassam Yammine
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Heat Pump Efficiencies
Carol,
I got the attachment from an eQUEST training CD. Marlin Addison is listed as the author.
Regards,
Bill
William Bishop, EIT, BEMP, LEED® AP | Pathfinder Engineers & Architects LLP
Mechanical Engineer
134 South Fitzhugh Street
Rochester, NY 14608
T: (585) 325-6004 Ext. 114
F: (585) 325-6005
wbishop at pathfinder-ea.com
www.pathfinder-ea.com
P Please strive to live sustainably.
________________________________
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Carol Gardner
Sent: Wednesday, March 24, 2010 12:12 PM
To: Bassam Yammine
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Heat Pump Efficiencies
I also found some formulas when tooling around in the archives the other day and could love to get comments, if any about their utlity:
EIR=(1/EER-0.012167)/((1/3.413)+0.012167)
and
EIR=((1/SEER*0.778+1.4)-0.012167)/((1/3.413)+0.012167)
Anyone remember these that knows the source and utility? Is there one for HSPF?
Carol
On Wed, Mar 24, 2010 at 7:50 AM, Bassam Yammine <byammine at flowgroup.ca> wrote:
Hi Michael, to modify the EIR (which is in Btu/Btu) in the detailed mode, click on the Air-Side HVAC icon at the top of your screen, then double click on the heat pump. Under the cooling and heating tabs you will find a Unitary Power tab where you can change your EIR.
Regards,
Bassam
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of M. Shields
Sent: Wednesday, March 24, 2010 6:59 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Heat Pump Efficiencies
Hi All,
I am still fairly new to equest and I am having a bit of trouble with setting up my HVAC. I created a building model using the equest wizard and now I have made a number of changes within the detailed DOE2 interface. The building uses air source heat pumps for the HVAC and I would like to change the EER/COP values without going back to the wizard, but I cannot figure where these values are stored. Is there an easy way to make changes like that within DOE2?
Thanks,
Michael Shields
____________________________
Michael Shields
Facility Strategies Group
2222 Gold Hill Road, Suite 5
Fort Mill, SC 29708
Phone: 803-493-4507
Fax: 803-548-2511
Email: mshields at fstrategies.com
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100512/8d9a85f0/attachment.htm>
More information about the Equest-users
mailing list