[Equest-users] Converting Heat Pump COP to EIR

Walson, Kristy kristy.walson at tlc-eng.com
Mon Jan 3 08:17:39 PST 2011


Hi Kathryn,

This is what we use:

EER adjusted = EER/(0.9585-0.01217*EER)

The conversion for EER to COP is:  COP = EER/3.412.

Kristy Walson, PE, LEED AP
Mechanical Engineer / Sustainable Design

From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Kathryn Kerns
Sent: Monday, January 03, 2011 11:12 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Converting Heat Pump COP to EIR

Everyone, is there a relationship written down somewhere that removes fan energy from a heat pump COP value to develop a heating EIR?  Something like the DX cooling EER equation that removes fan energy from EIR  cooling values? It looks like the eQuest wizard is doing something like that when a heat pump heating COP is entered, but I am not sure what.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110103/80ac624a/attachment.htm>


More information about the Equest-users mailing list