[Equest-users] DD "Exterior Windows"
Pasha Korber-Gonzalez
pasha.pkconsulting at gmail.com
Thu Jun 24 01:25:22 PDT 2010
You probably need to adjust the sill height of your template window as well
as the width and height. You should find these inputs to the left of your %
input boxes for each orientation. By resizing the template window dimension
appropriately it will allow DOE-2 to evenly place the correct amount of
template windows on your wall to get as close to your coverage % that you
want.
If you can't get this to work for you, then you should use the custom window
placement button at the bottom of your wizard screen and place the quantity
and dimensions for each window specifically.
pkg
2010/6/23 Ju-Yeon Julie Shin <juyeon519 at hotmail.com>
> Hello all,
>
> I have a question regarding to the "Exterior Windows".
>
> I calculated window-wall ratio for each orientatioin and floor.
>
> So on the first floor, I have the following window-wall ratio: S-88%,
> N-69%, E-96%, W-94%, and NE-69%
>
> When I put these inputs, however, it keeps giving me a warning saying
> "Range Check Error: Value being checked=88. Percent Glass value exceeds
> maximum (based on the window height and the sizes & positions of other
> windows).
>
> Could you please tell me how I can fix this issue? Is my calculation method
> wrong? Plesae provide me some advice.
>
> Thank you so much.
>
> Joo Yun Julie Shin
>
> ------------------------------
> Hotmail: Trusted email with powerful SPAM protection. Sign up now.<https://signup.live.com/signup.aspx?id=60969>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100624/095f1ec9/attachment.htm>
More information about the Equest-users
mailing list