<div>You probably need to adjust the sill height of your template window as well as the width and height. You should find these inputs to the left of your % input boxes for each orientation. By resizing the template window dimension appropriately it will allow DOE-2 to evenly place the correct amount of template windows on your wall to get as close to your coverage % that you want.</div>
<div> </div>
<div>If you can't get this to work for you, then you should use the custom window placement button at the bottom of your wizard screen and place the quantity and dimensions for each window specifically.</div>
<div> </div>
<div>pkg<br><br></div>
<div class="gmail_quote">2010/6/23 Ju-Yeon Julie Shin <span dir="ltr"><<a href="mailto:juyeon519@hotmail.com">juyeon519@hotmail.com</a>></span><br>
<blockquote style="BORDER-LEFT: #ccc 1px solid; MARGIN: 0px 0px 0px 0.8ex; PADDING-LEFT: 1ex" class="gmail_quote">
<div>Hello all,<br> <br>I have a question regarding to the "Exterior Windows".<br> <br>I calculated window-wall ratio for each orientatioin and floor.<br> <br>So on the first floor, I have the following window-wall ratio: S-88%, N-69%, E-96%, W-94%, and NE-69%<br>
<br>When I put these inputs, however, it keeps giving me a warning saying "Range Check Error: Value being checked=88. Percent Glass value exceeds maximum (based on the window height and the sizes & positions of other windows).<br>
<br>Could you please tell me how I can fix this issue? Is my calculation method wrong? Plesae provide me some advice.<br> <br>Thank you so much.<br> <br>Joo Yun Julie Shin<br>
<div class="hm"><br>
<hr>
Hotmail: Trusted email with powerful SPAM protection. <a href="https://signup.live.com/signup.aspx?id=60969" target="_blank">Sign up now.</a></div></div><br>_______________________________________________<br>Equest-users mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>To unsubscribe from this mailing list send a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>