[Equest-users] DD "Exterior Windows"
Sami, Vikram
Vikram.Sami at perkinswill.com
Thu Jun 24 07:42:05 PDT 2010
What is the height you've specified? If your height is not enough (the default is 5 ft I think), then you cannot get to the percentages you are specifying without your window being wider than the wall it sits in.
On a side note - that's a LOT of glass :-). If you're doing an ASHRAE comparison your baseline is only going to have 40%.
Vikram Sami, LEED AP
Sustainable Design Analyst
1382 Peachtree St. NE, Atlanta, GA 30309
t: 404-443-7462 f: 404.892.5823 e: vikram.sami at perkinswill.com www.perkinswill.com<http://www.perkinswill.com/>
Perkins+Will. Ideas + buildings that honor the broader goals of society
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Ju-Yeon Julie Shin
Sent: Thursday, June 24, 2010 1:25 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] DD "Exterior Windows"
Hello all,
I have a question regarding to the "Exterior Windows".
I calculated window-wall ratio for each orientatioin and floor.
So on the first floor, I have the following window-wall ratio: S-88%, N-69%, E-96%, W-94%, and NE-69%
When I put these inputs, however, it keeps giving me a warning saying "Range Check Error: Value being checked=88. Percent Glass value exceeds maximum (based on the window height and the sizes & positions of other windows).
Could you please tell me how I can fix this issue? Is my calculation method wrong? Plesae provide me some advice.
Thank you so much.
Joo Yun Julie Shin
________________________________
Hotmail: Trusted email with powerful SPAM protection. Sign up now.<https://signup.live.com/signup.aspx?id=60969>
This email and any files transmitted with it are confidential and intended solely for the addressee. If you are not the named addressee you should not disseminate, distribute, copy, or alter this email.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100624/6fb1aadf/attachment.htm>
More information about the Equest-users
mailing list