[Bldg-sim] Regulated vs. Unregulated Energy in Appendix G

Bill Bishop William.J.Bishop at imegcorp.com
Thu Aug 7 11:22:57 PDT 2025


Hi Michael,

I agree with your assessment per the table you shared, based on 90.1-2016 and -2019. I don't know if the newest versions have added or clarified requirements.

Your list reminds me of another specific load - snow melt. There are controls requirements for freeze protection and snow melt systems per 90.1-2016 and -2019, 6.4.3.7, but there are no heating efficiency requirements.

Thanks,
~Bill

William Bishop, PE, CEM, LEED AP, ASHRAE (BEMP, BEAP, CDP)
Associate Principal | Project Executive | Sustainability & Energy
[now IMEG]<https://www.imegcorp.com/>
IMEG | formerly Pathfinder                                                 (585) 698-1956 | phone
134 South Fitzhugh Street | Rochester, NY 14608               (315) 879-1122 | mobile
William.J.Bishop at imegcorp.com<mailto:William.J.Bishop at imegcorp.com>  website<https://imegcorp.com/> | vCard<https://dynasend.com/signatures/vcard/William.J.Bishop-at-imegcorp.com.vcf> | map<https://www.google.com/maps/place/Pathfinder+Engineers+%26+Architects+LLP/@43.1504815,-77.6145058,17z/data=!3m1!4b1!4m6!3m5!1s0x89d6b4fe9e48aab1:0x6991ae3d559d5aee!8m2!3d43.1504776!4d-77.6119309!16s%2Fg%2F1tcw955j?hl=en&entry=ttu>          [Twitter] <https://merlin.allaboutbirds.org/>   [Facebook] <https://fossilfreefunds.org/>   [LinkedIn] <https://www.linkedin.com/company/imeg-corp>
Learn more<https://www.imegcorp.com/about/our-story/> about us and the IMEG story!   Ride your bike!  [A person on a motorcycle  Description automatically generated]

From: Bldg-sim <bldg-sim-bounces at lists.onebuilding.org> On Behalf Of Michael Shannon via Bldg-sim
Sent: Thursday, August 7, 2025 12:40 PM
To: BLDG SIM <bldg-sim at lists.onebuilding.org>
Subject: [Bldg-sim] Regulated vs. Unregulated Energy in Appendix G

External Email: Treat links and attachments with caution.
BLDG-SIM!

I'm trying to sort out some atypical loads and whether they should be treated as Regulated vs. Unregulated. Since this drives the PCI_t for the project, it's pretty critical where each of these falls.

Load Type
Regulated or Unregulated?
Indoor Pool Heating
Regulated
Outdoor Pool Heating
Regulated
Spa Pool (110F) Heating
Regulated
Indoor Pool Pumps
Unregulated
Outdoor Pool Pumps
Unregulated
Spa Pool Pumps
Unregulated
Exterior Sports Court Lighting
Unregulated
Exterior Parking and Building Lighting
Regulated
Dryer Exhaust Fans
Regulated

Thoughts? Pool pumps have time switch control requirements, except in the case where public health standards require 24-hour pump operation, which is the case here.

Any insight is appreciated!

Join us on Sept. 18th for our Fishin' Up North Open House! RSVP HERE<https://www.eventbrite.com/e/emanuelson-podas-fishin-up-north-open-house-2025-tickets-1497425523049?aff=oddtdtcreator>.

Michael Shannon, PE, LEED AP BD+C
Senior Building Performance Engineer

Emanuelson-Podas, Inc.
7705 Bush Lake Road
Edina, MN 55439
Cell:    (763) 744-6186
Direct: (952) 540-4019
Office: (952) 930-0050
www.epinc.com<https://linkprotect.cudasvc.com/url?a=http%3a%2f%2fwww.epinc.com&c=E,1,6xuFSnICzD0kigyCITUBWmplFKIf4XlEAlsLJDamsuDRAE3CNTWErAmFwPfSnnhaIf0ptkARCf8aNXeRD8f97WMslHXrb4j_yPYa8IUulClgG-XmpEC9CSquVw,,&typo=1>


-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20250807/e9cf31d4/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 5138 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20250807/e9cf31d4/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.png
Type: image/png
Size: 420 bytes
Desc: image002.png
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20250807/e9cf31d4/attachment-0001.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.png
Type: image/png
Size: 342 bytes
Desc: image003.png
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20250807/e9cf31d4/attachment-0002.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.png
Type: image/png
Size: 387 bytes
Desc: image004.png
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20250807/e9cf31d4/attachment-0003.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image005.png
Type: image/png
Size: 2724 bytes
Desc: image005.png
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20250807/e9cf31d4/attachment-0004.png>


More information about the Bldg-sim mailing list