[Bldg-sim] Regulated vs. Unregulated Energy in Appendix G
Michael Shannon
mshannon at epinc.com
Thu Aug 7 09:40:12 PDT 2025
BLDG-SIM!
I'm trying to sort out some atypical loads and whether they should be treated as Regulated vs. Unregulated. Since this drives the PCI_t for the project, it's pretty critical where each of these falls.
Load Type
Regulated or Unregulated?
Indoor Pool Heating
Regulated
Outdoor Pool Heating
Regulated
Spa Pool (110F) Heating
Regulated
Indoor Pool Pumps
Unregulated
Outdoor Pool Pumps
Unregulated
Spa Pool Pumps
Unregulated
Exterior Sports Court Lighting
Unregulated
Exterior Parking and Building Lighting
Regulated
Dryer Exhaust Fans
Regulated
Thoughts? Pool pumps have time switch control requirements, except in the case where public health standards require 24-hour pump operation, which is the case here.
Any insight is appreciated!
Join us on Sept. 18th for our Fishin' Up North Open House! RSVP HERE<https://www.eventbrite.com/e/emanuelson-podas-fishin-up-north-open-house-2025-tickets-1497425523049?aff=oddtdtcreator>.
Michael Shannon, PE, LEED AP BD+C
Senior Building Performance Engineer
Emanuelson-Podas, Inc.
7705 Bush Lake Road
Edina, MN 55439
Cell: (763) 744-6186
Direct: (952) 540-4019
Office: (952) 930-0050
www.epinc.com<https://linkprotect.cudasvc.com/url?a=http%3a%2f%2fwww.epinc.com&c=E,1,6xuFSnICzD0kigyCITUBWmplFKIf4XlEAlsLJDamsuDRAE3CNTWErAmFwPfSnnhaIf0ptkARCf8aNXeRD8f97WMslHXrb4j_yPYa8IUulClgG-XmpEC9CSquVw,,&typo=1>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20250807/a8ac8d64/attachment.htm>
More information about the Bldg-sim
mailing list