[Bldg-sim] LS-D vs SS-D vs SV-A reports in equest
Haberl, Jeff
jhaberl at tamu.edu
Tue May 16 10:00:10 PDT 2023
Hello Hamza:
John's right, check the DOE-2 Reference Manuals, Part 2, which has a complete explanation between LS-D, SS-D and SV-A...as there's a big difference in the values being reported (LA-7890-M, LBL-8706 Rev.1). There is also useful information in the DOE-2 Basics manual.
In general, anything to do with LOADS is the simulation run at a constant indoor temperature, as well as other oddities that DOE-2 had in LOADS. So, SS-D would be coming from SYSTEMS, where the actual space temperature was determined by weighting factors, and the load change accordingly. This would include thermostat setbacks, etc.
The SV-A report is not really a simulation result, but rather a verification of what you put into the simulation since much of what's in a DOE-2 input file is "hidden" in the defaults, only to be seen in the LV, SV, PV outputs.
To complicate things, EQUEST has slightly different outputs than does DOE2.1e, but follows it pretty closely.
Hope this helps. If you can't get your hands on the manuals let me know. I should be able to put a copy on the TAMU google drive for you.
Jeff
Jeff S. Haberl, Ph.D., P.E.inactive, FASHRAE,FIBPSA We are like fluttering leaves on the branches of trees
Department of Architecture in the forests of the landscape that surrounds us.
Texas A&M University If we could, for just a moment, flutter together,
College Station, TX 77845-3581 We could lift the earth up to be a better place. JSH 2022
Office: 979-845-6507, Lab: 979-845-6065
Fax 979-862-2457
jhaberl at tamu.edu,www.esl.tamu.edu<mailto:jhaberl at tamu.edu,www.esl.tamu.edu>
________________________________
From: Bldg-sim <bldg-sim-bounces at lists.onebuilding.org> on behalf of John Aulbach via Bldg-sim <bldg-sim at lists.onebuilding.org>
Sent: Tuesday, May 16, 2023 11:33 AM
To: bldg-sim at lists.onebuilding.org <bldg-sim at lists.onebuilding.org>; Hamza Sohail <hamzasohail054 at gmail.com>
Subject: Re: [Bldg-sim] LS-D vs SS-D vs SV-A reports in equest
Try checking in Volume 4 Libraries and Reports of the online DOE-2 help menu within the program. It would be the absolute best source. John R Aulbach, PE On Tuesday, May 16, 2023 at 09: 26: 34 AM PDT, Hamza Sohail via Bldg-sim <bldg-sim@ lists. onebuilding. org>
ZjQcmQRYFpfptBannerStart
This Message Is From an External Sender
This message came from outside your organization.
ZjQcmQRYFpfptBannerEnd
Try checking in Volume 4 Libraries and Reports of the online DOE-2 help menu within the program. It would be the absolute best source.
John R Aulbach, PE
On Tuesday, May 16, 2023 at 09:26:34 AM PDT, Hamza Sohail via Bldg-sim <bldg-sim at lists.onebuilding.org> wrote:
hi, can some one explain me difference between LS-D(building monthly load summary) and SS-D(building hvac load summary and SV-A(system design parameters) reports in eQuest as i am confused because in each report it shows different "Maximum Cooling Load kBTU/hr" value.
_______________________________________________
Bldg-sim mailing list
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org<https://urldefense.com/v3/__http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org__;!!KwNVnqRv!FMzNUVAgMKi0UOevhbMobGN1tDjQ6IzkzwF4gSw2bxaIgvRHl6gVqdQFghaB3MKl-dAShqRJ-OVoW6qOEhL_lvs3QO4$>
To unsubscribe from this mailing list send a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20230516/1ef17a7c/attachment.htm>
More information about the Bldg-sim
mailing list