Hello Hamza:</div>
<div style="font-family: Calibri, Arial, Helvetica, sans-serif; font-size: 12pt; color: rgb(0, 0, 0);" class="elementToProof">
<br>
</div>
<div style="font-family: Calibri, Arial, Helvetica, sans-serif; font-size: 12pt; color: rgb(0, 0, 0);" class="elementToProof">
John's right, check the DOE-2 Reference Manuals, Part 2, which has a complete explanation between LS-D, SS-D and SV-A...as there's a big difference in the values being reported (LA-7890-M, LBL-8706 Rev.1). There is also useful information in the DOE-2 Basics
 manual. </div>
<div style="font-family: Calibri, Arial, Helvetica, sans-serif; font-size: 12pt; color: rgb(0, 0, 0);" class="elementToProof">
<br>
</div>
<div style="font-family: Calibri, Arial, Helvetica, sans-serif; font-size: 12pt; color: rgb(0, 0, 0);" class="elementToProof">
In general, anything to do with LOADS is the simulation run at a constant indoor temperature, as well as other oddities that DOE-2 had in LOADS. So, SS-D would be coming from SYSTEMS, where the actual space temperature was determined by weighting factors, and
 the load change accordingly. This would include thermostat setbacks, etc.</div>
<div style="font-family: Calibri, Arial, Helvetica, sans-serif; font-size: 12pt; color: rgb(0, 0, 0);" class="elementToProof">
<br>
</div>
<div style="font-family: Calibri, Arial, Helvetica, sans-serif; font-size: 12pt; color: rgb(0, 0, 0);" class="elementToProof">
The SV-A report is not really a simulation result, but rather a verification of what you put into the simulation since much of what's in a DOE-2 input file is "hidden" in the defaults, only to be seen in the LV, SV, PV outputs.</div>
<div style="font-family: Calibri, Arial, Helvetica, sans-serif; font-size: 12pt; color: rgb(0, 0, 0);" class="elementToProof">
<br>
</div>
<div style="font-family: Calibri, Arial, Helvetica, sans-serif; font-size: 12pt; color: rgb(0, 0, 0);" class="elementToProof">
To complicate things, EQUEST has slightly different outputs than does DOE2.1e, but follows it pretty closely.</div>
<div style="font-family: Calibri, Arial, Helvetica, sans-serif; font-size: 12pt; color: rgb(0, 0, 0);" class="elementToProof">
<br>
</div>
<div style="font-family: Calibri, Arial, Helvetica, sans-serif; font-size: 12pt; color: rgb(0, 0, 0);" class="elementToProof">
Hope this helps. If you can't get your hands on the manuals let me know. I should be able to put a copy on the TAMU google drive for you.</div>
<div style="font-family: Calibri, Arial, Helvetica, sans-serif; font-size: 12pt; color: rgb(0, 0, 0);" class="elementToProof">
<br>
</div>
<div style="font-family: Calibri, Arial, Helvetica, sans-serif; font-size: 12pt; color: rgb(0, 0, 0);" class="elementToProof">
Jeff</div>
<div class="elementToProof">
<div style="font-family: Calibri, Arial, Helvetica, sans-serif; font-size: 12pt; color: rgb(0, 0, 0);">
<br>
</div>
<div id="Signature">
<div>
<div name="divtagdefaultwrapper" style="margin:0px; font-family:Calibri,Arial,Helvetica,sans-serif">
</div>
<div name="divtagdefaultwrapper" style="margin:0px; font-family:Calibri,Arial,Helvetica,sans-serif">
<p>Jeff S. Haberl, Ph.D., P.E.inactive, FASHRAE,FIBPSA               We are like fluttering leaves on the branches of trees</p>
<p>Department of Architecture                                                       in the forests of the landscape that surrounds us.</p>
<p>Texas A&M University                                                                  If we could, for just a moment, flutter together,</p>
<p>College Station, TX 77845-3581                                                 We could lift the earth up to be a better place.  JSH 2022</p>
<p>Office: 979-845-6507, Lab: 979-845-6065</p>
<p>Fax 979-862-2457</p>
<p><a tabindex="0" href="mailto:jhaberl@tamu.edu,www.esl.tamu.edu">jhaberl@tamu.edu,www.esl.tamu.edu</a></p>
</div>
</div>
</div>
</div>
<div id="appendonsend"></div>
<hr style="display:inline-block;width:98%" tabindex="-1">
<div id="divRplyFwdMsg" dir="ltr"><font face="Calibri, sans-serif" style="font-size:11pt" color="#000000"><b>From:</b> Bldg-sim <bldg-sim-bounces@lists.onebuilding.org> on behalf of John Aulbach via Bldg-sim <bldg-sim@lists.onebuilding.org><br>
<b>Sent:</b> Tuesday, May 16, 2023 11:33 AM<br>
<b>To:</b> bldg-sim@lists.onebuilding.org <bldg-sim@lists.onebuilding.org>; Hamza Sohail <hamzasohail054@gmail.com><br>
<b>Subject:</b> Re: [Bldg-sim] LS-D vs SS-D vs SV-A reports in equest</font>
<div> </div>
</div>
<div>
<div style="display:none!important; display:none; visibility:hidden; font-size:1px; color:#ffffff; line-height:1px; height:0px; max-height:0px; opacity:0; overflow:hidden">
Try checking in Volume 4 Libraries and Reports of the online DOE-2 help menu within the program. It would be the absolute best source. John R Aulbach, PE On Tuesday, May 16, 2023 at 09: 26: 34 AM PDT, Hamza Sohail via Bldg-sim <bldg-sim@ lists. onebuilding. org>
</div>
<div style="display:none!important; display:none; visibility:hidden; font-size:1px; color:#ffffff; line-height:1px; height:0px; max-height:0px; opacity:0; overflow:hidden">
ZjQcmQRYFpfptBannerStart</div>
<div dir="ltr" id="x_pfptBanner4p6wzcd" style="display:block!important; text-align:left!important; margin:16px 0px 16px 0px!important; padding:8px 16px 8px 16px!important; border-radius:4px!important; min-width:200px!important; background-color:#D0D8DC!important; background-color:#D0D8DC; border-top:4px solid #90a4ae!important; border-top:4px solid #90a4ae">
<div id="x_pfptBanner4p6wzcd" style="float:left!important; display:block!important; margin:0px 0px 1px 0px!important; max-width:600px!important">
<div id="x_pfptBanner4p6wzcd" style="display:block!important; visibility:visible!important; background-color:#D0D8DC!important; color:#000000!important; color:#000000; font-family:'Arial',sans-serif!important; font-family:'Arial',sans-serif; font-weight:bold!important; font-weight:bold; font-size:14px!important; line-height:18px!important; line-height:18px">
This Message Is From an External Sender </div>
<div id="x_pfptBanner4p6wzcd" style="display:block!important; visibility:visible!important; background-color:#D0D8DC!important; color:#000000!important; color:#000000; font-weight:normal; font-family:'Arial',sans-serif!important; font-family:'Arial',sans-serif; font-size:12px!important; line-height:18px!important; line-height:18px; margin-top:2px!important">
This message came from outside your organization. </div>
</div>
<div style="clear:both!important; display:block!important; visibility:hidden!important; line-height:0!important; font-size:0.01px!important; height:0px">
 </div>
</div>
<div style="display:none!important; display:none; visibility:hidden; font-size:1px; color:#ffffff; line-height:1px; height:0px; max-height:0px; opacity:0; overflow:hidden">
ZjQcmQRYFpfptBannerEnd</div>
<style>
<!--
#x_pfptBanner4p6wzcd
        {display:block!important;
        visibility:visible!important;
        opacity:1!important;
        background-color:#D0D8DC!important;
        max-width:none!important;
        max-height:none!important}
-->
</style>
<div class="x_ydpac4059a8yahoo-style-wrap" style="font-family:verdana,helvetica,sans-serif; font-size:16px">
<div></div>
<div dir="ltr" data-setdir="false">Try checking in Volume 4 Libraries and Reports of the online DOE-2 help menu within the program. It would be the absolute best source.</div>
<div dir="ltr" data-setdir="false"><br>
</div>
<div dir="ltr" data-setdir="false">John R Aulbach, PE</div>
<div><br>
</div>
</div>
<div id="x_yahoo_quoted_4335208156" class="x_yahoo_quoted">
<div style="font-family:'Helvetica Neue',Helvetica,Arial,sans-serif; font-size:13px; color:#26282a">
<div>On Tuesday, May 16, 2023 at 09:26:34 AM PDT, Hamza Sohail via Bldg-sim <bldg-sim@lists.onebuilding.org> wrote:
</div>
<div><br>
</div>
<div><br>
</div>
<div>
<div id="x_yiv9523099023">
<div dir="ltr"><span style="color:rgb(75,75,75); font-family:Arial; font-size:14px">hi, can some one explain me difference between LS-D(building monthly load summary) and SS-D(building hvac load summary and SV-A(system design parameters) reports in eQuest as
 i am confused because in each report it shows different "Maximum Cooling Load kBTU/hr" value.</span><br>
</div>
</div>
_______________________________________________<br>
Bldg-sim mailing list<br>
<a href="https://urldefense.com/v3/__http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org__;!!KwNVnqRv!FMzNUVAgMKi0UOevhbMobGN1tDjQ6IzkzwF4gSw2bxaIgvRHl6gVqdQFghaB3MKl-dAShqRJ-OVoW6qOEhL_lvs3QO4$" target="_blank">http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org</a><br>
To unsubscribe from this mailing list send  a blank message to <a href="mailto:BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG">
BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
</div>
</div>
</div>
</div>
</body>
</html>