[Bldg-sim] Modeling only the Common Areas in a Building
Sheila Sagerer
ssagerer at comcast.net
Thu Feb 10 14:16:43 PST 2022
Good afternoon, Ahmad.
When I need to separate consumptions from different buildings, I set up different utility meters and assign all loads for the areas in question to the new meters. The PS-F gives monthly data for each meter individually.
A couple things to be aware of:
If a boiler or chiller serves both residential and common, the plant cannot be split to two meters. I’ve gotten around this by setting up separate meters for the plant and then manually apportioning the plant energy to each of the separate areas based on proportions; one example of determining might be sum of capacities of coils assigned to each area compared to sum of all coils.
Or, another possibility might be to set up two supply loops off the boiler or chiller - one dedicated to each portion of the building. Then the PV-A report would give you loop capacity for each loop which can be used to split the boiler or chiller consumption.
Good luck!
Sheila
Sent from my iPhone
On Feb 10, 2022, at 3:57 PM, Ahmad Fraij via Bldg-sim <bldg-sim at lists.onebuilding.org> wrote:
Hello Guys,
I am modeling a residential apartments building and I have the energy consumption only for the common areas of this building. I need to calibrate the eQUEST model to this common areas monthly energy consumption data so, what will be the best solution? I am thinking about the below two solutions:
Can I connect all the common areas systems (HVAC, lighting...etc) to one meter and use the data of this meter to calibrate the model to the actual energy consumption? If yes, then in which simulation report can I find the monthly readings of this meter?
The other option I can do is to not assign any HVAC, lighting...etc to the residential apartments and I only assign these systems to the common areas and then run the simulation.
So, did anybody encounter this before? which option of the above is the best? Or may be you can help me with another better solution?
Thanking you guys for any help
Regards
Ahmad
_______________________________________________
Bldg-sim mailing list
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
To unsubscribe from this mailing list send a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20220210/23830f26/attachment-0002.html>
More information about the Bldg-sim
mailing list