Hi Chris,
Thanks for your response. It would make sense if the Reference Building were also a WLHP but based on AHRI definitions I think a WHLP is pretty clearly not:
a. an “air-cooled unitary <http://www.ahrinet.org/Certification/AHRI-Certification-Programs/Unitary-Air-Conditioner-Equipment> ” product,
b. a packaged terminal air conditioner <http://www.ahrinet.org/Certification/AHRI-Certification-Programs/Packaged-Terminal-Air-Conditioners> or heat pump <http://www.ahrinet.org/Certification/AHRI-Certification-Programs/Packaged-Terminal-Heat-Pumps> , or
c. a fan coil.
A WLHP is water-cooled unitary product.
If they simply said “unitary” or “air-cooled or water-cooled unitary” then it would makes sense to me that you model an identical system but they specifically state “air-cooled unitary”.
Aaron
Aaron Smith, P.Eng
Principal, Mechanical Engineer
LEED® AP BD+C, BEMP, BEAP, CGD
M&R Engineering Ltd.
From: Chris Hadlock [mailto:cjhadlock at gmail.com]
Sent: February-18-19 11:27 AM
To: Aaron Smith <asmith at mreng.ca>
Cc: bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] NECB - MURB Reference Heating Type
Hi Aaron,
The way I would interpret it is the Reference system will be identical to your Proposed system (i.e. WLHP connected to fossil fuel boiler). If you had a air-source, water-source (i.e. river, lake) or ground-source, then you would have to worry about auxiliary heating (per Section 8.4.4.13.2). The "through-the-wall" system only applies in the otherwise case (i.e. when your system is not one of the ones listed).
This is my interpretation - I'd be interested to hear others.
Chris
On Sun, Feb 17, 2019 at 10:10 PM Aaron Smith via Bldg-sim <bldg-sim at lists.onebuilding.org <mailto:bldg-sim at lists.onebuilding.org> > wrote:
Hello,
I’ve got a question about the NECB Reference Building heating system type for Multi-Unit Residential Buildings. Specifically what should it be when you have water-loop heat pumps connected to a fossil fuel boiler?
Table 8.4.4.7.-A of the 2015 NECB states that Reference Building HVAC systems for Multi-Unit Residential areas are:
“Where the proposed building or space is heated as well as being cooled with an air-cooled unitary, packaged terminal or room air conditioner (or heat pumps), or fan coils, the reference building or space's HVAC system shall be modeled as being identical to that of the proposed building or space; otherwise, the reference building or space shall use through-the-wall systems.”
I’d consider water-loop heat pumps to be in the “through-the-wall systems” category so the cooling would be air-cooled DX. It doesn’t describe the heating source for “through-the-wall systems” but 8.4.4.9.4 says that the energy type of the reference building’s heating system shall be identical to the energy type of the proposed building’s heating system. The code considers heat pump to be an energy type so I think it should be an air-source heat pump. I’m just not sure about the auxiliary heat – electric resistance or hot water?
I tried running this in CAN-QUEST but got some errors. When I run a 4-storey office building with WLHP, the reference building is coming out as air-source heat pump with electric resistance heat so I’m leaning toward using that. I can see there being an argument for hot water auxiliary heat though based on the proposed building having a fuel-fired boiler (to avoid fuel switching).
Thanks,
Aaron
Aaron Smith, P.Eng
Principal, Mechanical Engineer
LEED® AP BD+C, BEMP, BEAP, CGD
t: (902) 422-7393
f: (902) 423-4945
e: <mailto:asmith at mreng.ca> asmith at mreng.ca
www.mreng.ca <http://www.mreng.ca/>
The electronic message contained herein is private and confidential, intended only for the recipient(s) specified. If you have received this message in error, please delete it and notify us immediately. Any accompanying files are supplied as a matter of courtesy only. The data are without warranty of any kind. Any person or business making use of the data is responsible for confirming its accuracy and completeness. M&R Engineering Ltd. is not responsible for edited or produced versions of this digital information.
_______________________________________________
Bldg-sim mailing list
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
To unsubscribe from this mailing list send a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG <mailto:BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20190218/c73a7ded/attachment-0002.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 1849 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20190218/c73a7ded/attachment-0004.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.jpg
Type: image/jpeg
Size: 1432 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20190218/c73a7ded/attachment-0005.jpg>
More information about the Bldg-sim
mailing list