Chris Hadlock
cjhadlock at gmail.com
Mon Feb 18 07:27:21 PST 2019
Hi Aaron,
The way I would interpret it is the Reference system will be identical to
your Proposed system (i.e. WLHP connected to fossil fuel boiler). If you
had a air-source, water-source (i.e. river, lake) or ground-source, then
you would have to worry about auxiliary heating (per Section 8.4.4.13.2).
The "through-the-wall" system only applies in the otherwise case (i.e. when
your system is not one of the ones listed).
This is my interpretation - I'd be interested to hear others.
Chris
On Sun, Feb 17, 2019 at 10:10 PM Aaron Smith via Bldg-sim <
bldg-sim at lists.onebuilding.org> wrote:
> Hello,
>
>
>
> I’ve got a question about the NECB Reference Building heating system type
> for Multi-Unit Residential Buildings. Specifically what should it be when
> you have water-loop heat pumps connected to a fossil fuel boiler?
>
>
>
> Table 8.4.4.7.-A of the 2015 NECB states that Reference Building HVAC
> systems for Multi-Unit Residential areas are:
>
>
>
> “Where the proposed building or space is heated as well as being cooled
> with an air-cooled unitary, packaged terminal or room air conditioner (or
> heat pumps), or fan coils, the reference building or space's HVAC system
> shall be modeled as being identical to that of the proposed building or
> space; otherwise, the reference building or space shall use
> through-the-wall systems.”
>
>
>
> I’d consider water-loop heat pumps to be in the “through-the-wall systems”
> category so the cooling would be air-cooled DX. It doesn’t describe the
> heating source for “through-the-wall systems” but 8.4.4.9.4 says that the
> energy type of the reference building’s heating system shall be identical
> to the energy type of the proposed building’s heating system. The code
> considers heat pump to be an energy type so I think it should be an
> air-source heat pump. I’m just not sure about the auxiliary heat –
> electric resistance or hot water?
>
>
>
> I tried running this in CAN-QUEST but got some errors. When I run a
> 4-storey office building with WLHP, the reference building is coming out as
> air-source heat pump with electric resistance heat so I’m leaning toward
> using that. I can see there being an argument for hot water auxiliary heat
> though based on the proposed building having a fuel-fired boiler (to avoid
> fuel switching).
>
>
>
> Thanks,
>
> Aaron
>
>
>
> * Aaron Smith, **P.Eng*
>
> * Principal, Mechanical Engineer*
>
>
>
> *LEED® AP BD+C, BEMP, BEAP, CGD*
>
> [image: cid:image004.jpg at 01D045E5.C57CEB70] [image:
> webCertified_logo_colorRGB72DPI]
>
> t: (902) 422-7393
>
> f: (902) 423-4945
>
> e: asmith at mreng.ca
>
> *www.mreng.ca <http://www.mreng.ca/> *
>
>
>
> The electronic message contained herein is private and confidential,
> intended only for the recipient(s) specified. If you have received this
> message in error, please delete it and notify us immediately.
> Any accompanying files are supplied as a matter of courtesy only. The data
> are without warranty of any kind. Any person or business making use of the
> data is responsible for confirming its accuracy and completeness. M&R
> Engineering Ltd. is not responsible for edited or produced versions of this
> digital information.
>
>
>
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20190218/95785511/attachment-0002.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 1849 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20190218/95785511/attachment-0004.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.jpg
Type: image/jpeg
Size: 1453 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20190218/95785511/attachment-0005.jpg>
More information about the Bldg-sim
mailing list