[Bldg-sim] Modeling zones that are conditioned but not controlled
Peter Simmonds
psimmonds11 at gmail.com
Fri Feb 23 11:40:43 PST 2018
One should also point out that a corridor is a transient space and is
therefore not critical.
Peter Simmonds, Ph.D., FASHRAE, FIBPSA, FFTI
Mobile USA: +1-310-383-9911
Mobile HKG: +852-9227-1640
Mobile UK: +44 7470461689
www.petersimmonds.com
On Fri, Feb 23, 2018 at 8:29 AM, Bishop, Bill via Bldg-sim <
bldg-sim at lists.onebuilding.org> wrote:
> Christopher,
>
> I agree with Jim.
>
> I typically model all *conditioned spaces* including *semiheated *spaces
> with heating and cooling thermostat schedules, except for heating-only
> zones that meet the criteria for Systems 9/10 in Appendix G, for which I
> leave the cooling thermostat schedule undefined. I may enter relaxed design
> conditions for zones that aren’t intended to have tight temperature control
> (using DESIGN-COOL-T and DESIGN-HEAT-T in DOE-2/eQUEST), and use
> correspondingly relaxed thermostat schedules for those zones. If there are
> unmet hours in the proposed design that I can’t address by relaxing the
> thermostat schedules even further, than I might leave the heating and/or
> cooling thermostat schedules undefined to represent floating with no
> thermostat control (which results in no reported unmet loads to have to
> explain). I keep all design conditions and thermostat schedules identical
> in the baseline as required by Appendix G.
>
> Regards,
>
> ~Bill
>
>
>
> *William Bishop, PE, BEMP, BEAP, CEM, LEED AP **|** Pathfinder Engineers
> & Architects LLP*
>
> *Senior Energy Engineer*
>
>
>
>
>
> 134 South Fitzhugh Street Rochester, NY 14608
>
> *T: (585) 698-1956* F: (585) 325-6005
>
> bbishop at pathfinder-ea.com <wbishop at pathfinder-ea.com>
> www.pathfinder-ea.com
>
> [image: http://png-5.findicons.com/files/icons/977/rrze/720/globe.png]Carbon
> Fee and Dividend - simple, effective, and market-based.
>
>
>
> *From:* Bldg-sim [mailto:bldg-sim-bounces at lists.onebuilding.org] *On
> Behalf Of *Jones, Christopher via Bldg-sim
> *Sent:* Friday, February 23, 2018 11:21 AM
> *To:* Jim Dirkes <jim at buildingperformanceteam.com>
>
> *Cc:* bldg-sim at lists.onebuilding.org
> *Subject:* Re: [Bldg-sim] Modeling zones that are conditioned but not
> controlled
>
>
>
> Thanks Jim,
>
> Your suggested approaches are in line with how I have been handing the
> issue.
>
>
>
>
>
> *Christopher R. Jones*, P.Eng.
>
> Technical Specialist
>
> Sustainability & Energy
>
>
>
> T +1 416-644-0252
>
>
>
> 2300 Yonge Street, Suite 2300
>
> Toronto, ON M4P 1E4 Canada
>
> wsp.com
>
>
>
>
>
> *Please consider the environment before printing...*
>
>
>
>
>
> *From:* Jim Dirkes [mailto:jim at buildingperformanceteam.com
> <jim at buildingperformanceteam.com>]
> *Sent:* Friday, February 23, 2018 11:18 AM
> *To:* Jones, Christopher <Christopher.r.Jones at wsp.com>
> *Cc:* bldg-sim at lists.onebuilding.org
> *Subject:* Re: [Bldg-sim] Modeling zones that are conditioned but not
> controlled
>
>
>
> My opinion:
>
> If there is no thermostat, the design essentially says that a wide
> temperature variation is acceptable. You might consider arguing that those
> zones *cannot *have unmet load hours because the design does not attempt
> to control temperature.
>
>
>
> For your own peace of mind (if your software allows it), you might also
> report hourly temperatures in the zone to confirm that temps don't go crazy
> unexpectedly during occupied hours.
>
>
>
>
>
> On Fri, Feb 23, 2018 at 10:47 AM, Jones, Christopher via Bldg-sim <
> bldg-sim at lists.onebuilding.org> wrote:
>
> I am wondering what others do for building zones that are conditioned but
> have no direct HVAC control. For example, a typical school will have a DOAS
> with perimeter radiation in exterior zones. There will be temperature and
> CO2 DCV in these occupied zones. The corridor will have transfer air and
> may have a couple of small supply diffusers from the DOAS but there is no
> thermostat to control the temperature in that corridor.
>
>
>
> If there is no thermostat, there is no setpoint so how does one determine
> if the corridor has unmet loads? How would one model the corridor zone in
> the baseline case for Appendix G?
>
>
>
>
>
> *Christopher R. Jones*, P.Eng.
>
> Technical Specialist
>
> Sustainability & Energy
>
>
>
> T +1 416-644-0252 <(416)%20644-0252>
>
>
>
> 2300 Yonge Street, Suite 2300
>
> Toronto, ON M4P 1E4 Canada
>
> wsp.com
>
>
>
>
>
> *Please consider the environment before printing...*
>
>
>
>
>
>
> ------------------------------
>
>
>
> NOTICE: This communication and any attachments ("this message") may
> contain information which is privileged, confidential, proprietary or
> otherwise subject to restricted disclosure under applicable law. This
> message is for the sole use of the intended recipient(s). Any unauthorized
> use, disclosure, viewing, copying, alteration, dissemination or
> distribution of, or reliance on, this message is strictly prohibited. If
> you have received this message in error, or you are not an authorized or
> intended recipient, please notify the sender immediately by replying to
> this message, delete this message and all copies from your e-mail system
> and destroy any printed copies. You are receiving this communication
> because you are listed as a current WSP contact. Should you have any
> questions regarding WSP's electronic communications policy, please consult
> our Anti-Spam Commitment at www.wsp.com/casl. For any concern or if you
> believe you should not be receiving this message, please forward this
> message to caslcompliance at wsp.com so that we can promptly address your
> request. Note that not all messages sent by WSP qualify as commercial
> electronic messages.
>
> AVIS : Ce message, incluant tout fichier l'accompagnant (« le message »),
> peut contenir des renseignements ou de l'information privilégiés,
> confidentiels, propriétaires ou à divulgation restreinte en vertu de la
> loi. Ce message est destiné à l'usage exclusif du/des destinataire(s)
> voulu(s). Toute utilisation non permise, divulgation, lecture,
> reproduction, modification, diffusion ou distribution est interdite. Si
> vous avez reçu ce message par erreur, ou que vous n'êtes pas un
> destinataire autorisé ou voulu, veuillez en aviser l'expéditeur
> immédiatement et détruire le message et toute copie électronique ou
> imprimée. Vous recevez cette communication car vous faites partie des
> contacts de WSP. Si vous avez des questions concernant la politique de
> communications électroniques de WSP, veuillez consulter notre Engagement
> anti-pourriel au www.wsp.com/lcap. Pour toute question ou si vous croyez
> que vous ne devriez pas recevoir ce message, prière de le transférer au
> conformitelcap at wsp.com afin que nous puissions rapidement traiter votre
> demande. Notez que ce ne sont pas tous les messages transmis par WSP qui
> constituent des messages electroniques commerciaux.
>
>
>
> -LAEmHhHzdJzBlTWfa4Hgs7pbKl
>
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
>
>
>
> --
>
> James V Dirkes II, CEO / President
> The Building Performance Team Inc.
> 1631 Acacia Dr, Grand Rapids, MI 49504
>
>
>
> (alphabet soup of efforts for greater understanding: PE, BEMP, BCxP, LEED
> AP)
>
> Direct / Mobile: 616.450.8653
> jim at buildingperformanceteam.com
>
> Website <http://buildingperformanceteam.com>l LinkedIn
> <https://www.linkedin.com/pub/jim-dirkes/7/444/413>
>
> *Coffee conversation:*
>
> The first idea is the worst, but it is the most important because it
> starts discussion and becomes the building block for other ideas.
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20180223/9dfc0dc7/attachment-0002.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image009.png
Type: image/png
Size: 25844 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20180223/9dfc0dc7/attachment-0004.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image010.jpg
Type: image/jpeg
Size: 1647 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20180223/9dfc0dc7/attachment-0004.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image011.png
Type: image/png
Size: 3859 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20180223/9dfc0dc7/attachment-0005.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 1517 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20180223/9dfc0dc7/attachment-0005.jpg>
More information about the Bldg-sim
mailing list