[Bldg-sim] climate zone Rome
Jim Dirkes
jim at buildingperformanceteam.com
Wed Feb 3 07:53:56 PST 2016
Thanks, Joe. I appreciate the additional insights. I suspect that LEED
reviewers don't know as much background as you do and are inclined to
follow the 90.1 table.
Francesco, if it's beneficial for your client to use Climate Zone #3, I
think you could make a case for that based on Joe's insights and
information. If your project is registered with USGBC, you can ask
questions in advance of a formal submission of the modeling results - that
might be worth doing to settle the question before defining the model.
On Wed, Feb 3, 2016 at 10:42 AM, Joe Huang <yjhuang at whiteboxtechnologies.com
> wrote:
> I beg to differ on this. ASHRAE Climate Zones are very simply defined
> based of degree days, plus what I consider a faulty use of precipitation
> to differentiate "wet" from "dry" climates. When a EPW stat file gives the
> ASHRAE Climate Zone as 3, it's simply reporting the number of degree days
> in the file, and in that sense, absolutely correct. The reason for the
> discrepancy is that ASHRAE 90.1, or actually ASHRAE Standard 169 (Climate
> Data for Building Design Standards), did their climate zone mapping, they
> came up with a degree day value that put Rome in Climate Zone 4. The
> problem in this case is that all 3 weather files for Rome that I've looked
> into (IWEC, IWEC2, IGDG - the one used by Francesco) show HDD from 1440 to
> 1514, much below the 2000 HDD to fall into Climate Zone 4. I have a good
> idea how Standard 169 derived its degree days, but am waiting for
> confirmation lest I misspeak.
>
> In the meanwhile, I would also recommend using the climate zone shown in
> 90.1 to set the reference building, but only because that's what listed,
> not because it's technically better.
>
> Joe
>
> Joe Huang
> White Box Technologies, Inc.
> 346 Rheem Blvd., Suite 205A
> Moraga CA 94556yjhuang at whiteboxtechnologies.comhttp://weather.whiteboxtechnologies.com for simulation-ready weather data
> (o) (925)388-0265
> (c) (510)928-2683
> "building energy simulations at your fingertips"
>
> On 2/3/2016 6:43 AM, Jim Dirkes wrote:
>
> Francesco,
> As I recall, the E+ weather files derive the climate zone based on various
> attributes of the weather data. In fact, I think there is a qualifying
> statement within the .EPW files which says the climate zone may not be
> "perfect"
> For that reason, I would use the climate zone referenced in 90.1
>
> On Wed, Feb 3, 2016 at 9:15 AM, Francesco Passerini <
> <fpasserini.tn at gmail.com>fpasserini.tn at gmail.com> wrote:
>
>> In order to understand what thermal transmittances I shall impose in a
>> baseline model for LEED, I have to understand in what climate zone I shall
>> consider Rome.
>> In TABLE B-3 "International Climate Zones" of ASHRAE 90.1-2010,
>> "Roma/Fiumicion" is zone 4, while in the weather file zone 3C is indicated.
>> The weather file for Fiumicino is available here:
>>
>> https://energyplus.net/weather-location/europe_wmo_region_6/ITA//ITA_Roma-Fiumicino.162420_IGDG
>> If you see the .stat file, HDD18°C = 1514, which respects the thermal
>> criteria for zone 3C (see Table B-4).
>> Is TABLE B-3 based on other weather data?
>> Best Regards
>> Francesco
>>
>> _______________________________________________
>> Bldg-sim mailing list
>> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
>> To unsubscribe from this mailing list send a blank message to
>> BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>>
>>
>
>
> --
>
> James V Dirkes II, PE, BEMP, LEED AP
> CEO/President
> The Building Performance Team Inc.
> 1631 Acacia Dr, GR, Mi 49504
>
> Direct: 616.450.8653
> <jim at buildingperformanceteam.com>jim at buildingperformanceteam.com
>
> Website <http://buildingperformanceteamcom>l LinkedIn
> <https://www.linkedin.com/pub/jim-dirkes/7/444/413>
>
> Fail faster!
>
>
> _______________________________________________
> Bldg-sim mailing listhttp://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
--
James V Dirkes II, PE, BEMP, LEED AP
CEO/President
The Building Performance Team Inc.
1631 Acacia Dr, GR, Mi 49504
Direct: 616.450.8653
jim at buildingperformanceteam.com
Website <http://buildingperformanceteamcom>l LinkedIn
<https://www.linkedin.com/pub/jim-dirkes/7/444/413>
Fail faster!