[Bldg-sim] climate zone Rome
Joe Huang
yjhuang at whiteboxtechnologies.com
Wed Feb 3 07:42:38 PST 2016
I beg to differ on this. ASHRAE Climate Zones are very simply defined based of degree
days, plus what I consider a faulty use of precipitation to differentiate "wet" from
"dry" climates. When a EPW stat file gives the ASHRAE Climate Zone as 3, it's simply
reporting the number of degree days in the file, and in that sense, absolutely correct.
The reason for the discrepancy is that ASHRAE 90.1, or actually ASHRAE Standard 169
(Climate Data for Building Design Standards), did their climate zone mapping, they came up
with a degree day value that put Rome in Climate Zone 4. The problem in this case is that
all 3 weather files for Rome that I've looked into (IWEC, IWEC2, IGDG - the one used by
Francesco) show HDD from 1440 to 1514, much below the 2000 HDD to fall into Climate Zone
4. I have a good idea how Standard 169 derived its degree days, but am waiting for
confirmation lest I misspeak.
In the meanwhile, I would also recommend using the climate zone shown in 90.1 to set the
reference building, but only because that's what listed, not because it's technically better.
Joe
Joe Huang
White Box Technologies, Inc.
346 Rheem Blvd., Suite 205A
Moraga CA 94556
yjhuang at whiteboxtechnologies.com
http://weather.whiteboxtechnologies.com for simulation-ready weather data
(o) (925)388-0265
(c) (510)928-2683
"building energy simulations at your fingertips"
On 2/3/2016 6:43 AM, Jim Dirkes wrote:
> Francesco,
> As I recall, the E+ weather files derive the climate zone based on various attributes of
> the weather data. In fact, I think there is a qualifying statement within the .EPW
> files which says the climate zone may not be "perfect"
> For that reason, I would use the climate zone referenced in 90.1
>
> On Wed, Feb 3, 2016 at 9:15 AM, Francesco Passerini <fpasserini.tn at gmail.com
> <mailto:fpasserini.tn at gmail.com>> wrote:
>
> In order to understand what thermal transmittances I shall impose in a baseline
> model for LEED, I have to understand in what climate zone I shall consider Rome.
> In TABLE B-3 "International Climate Zones" of ASHRAE 90.1-2010, "Roma/Fiumicion" is
> zone 4, while in the weather file zone 3C is indicated.
> The weather file for Fiumicino is available here:
> https://energyplus.net/weather-location/europe_wmo_region_6/ITA//ITA_Roma-Fiumicino.162420_IGDG
> If you see the .stat file, HDD18°C = 1514, which respects the thermal criteria for
> zone 3C (see Table B-4).
> Is TABLE B-3 based on other weather data?
> Best Regards
> Francesco
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG <mailto:BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG>
>
>
>
>
> --
>
> James V Dirkes II, PE, BEMP, LEED AP
> CEO/President
> The Building Performance Team Inc.
> 1631 Acacia Dr, GR, Mi 49504
>
> Direct: 616.450.8653
> jim at buildingperformanceteam.com <mailto:jim at buildingperformanceteam.com>
>
> Website <http://buildingperformanceteamcom>l LinkedIn
> <https://www.linkedin.com/pub/jim-dirkes/7/444/413>
>
> *//*
>
> Fail faster!
>
>
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20160203/3515b887/attachment-0001.html>
More information about the Bldg-sim
mailing list