[Bldg-sim] LEED project - maximum limit allowed to simplified wall azimuth.
Vikram Sami via Bldg-sim
bldg-sim at lists.onebuilding.org
Thu Dec 15 12:10:29 PST 2016
Nick,
I think the relative impact of the degree of simplification would probably depend on a number of factors. Three that immediately come to mind are:
· Calculation method for transmitted solar radiation - does the software incorporate natural incident angle dependent transmittance values that are a part of how glass behaves? I know there's a big difference between using the simplified method in eQUEST and actually using the detailed input (either the LBNL window way or just picking an actual glass from the library).
· Type of building - if it's a more skin dominant load, then you will see a greater impact from the simplification.
· Orientation (I'm guessing some orientations are more sensitive to this).
From: Bldg-sim [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Nicholas Caton via Bldg-sim
Sent: Thursday, December 15, 2016 10:25 AM
To: Leonard Sciarra <leonard_sciarra at gensler.com>; julien.dutel at mern.gouv.qc.ca
Cc: bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] LEED project - maximum limit allowed to simplified wall azimuth.
Put another way:
If you have a perfectly circular floorplate, ASHRAE wants you to model an octagon, with respect to a minimum number of facets.
This specific query reminds me: There was a pretty interesting thought-study presented at ASHRAE's energy conference in 2015 where someone tested this logic, by asking the question (paraphrasing) "how few facets can we get away with and still accurately represent a perfect circle?" I don't recall exactly the answer but the results surprised me with how far you could go in simplifying the shape & still maintain relative accuracy. I believe a 4 sided square (corrected geometrically for volume) in fact performed very closely to the baseline.
If you're sincerely & specifically interested in modeling an octagon as a square, I think you'll find that could actually be pretty accurate so long as you are correcting for conditioned volume / exposed area. I'd seek out that actual paper/presentation while you're at it ;-).
~Nick
[cid:image001.png at 01D256C5.382C0240]
Nick Caton, P.E., BEMP
Senior Energy Engineer
Energy and Sustainability Services
Schneider Electric
D 913.564.6361
M 785.410.3317
E nicholas.caton at schneider-electric.com<mailto:nicholas.caton at schneider-electric.com>
F 913.564.6380
15200 Santa Fe Trail Drive
Suite 204
Lenexa, KS 66219
United States
[cid:image001.png at 01D189AB.58634A10]
From: Bldg-sim [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Leonard Sciarra via Bldg-sim
Sent: Thursday, December 15, 2016 12:05 PM
To: bldg-sim at lists.onebuilding.org<mailto:bldg-sim at lists.onebuilding.org>
Subject: Re: [Bldg-sim] LEED project - maximum limit allowed to simplified wall azimuth.
Julian -
The text is written to include 45 degrees. So if they are 45 degrees, then you can make it a square, although the exception was intended for curved surfaces.
Hope this helps.
Leonard Sciarra, AIA, ASHRAE, LEED ap+
Senior Associate
+1 312.577.6580 Direct
+1 312.456.0123 Main
+1 847.345.5619 Mobile
Gensler
11 East Madison Street
Suite 300
Chicago, Illinois 60602
USA
Gensler.com<http://www.gensler.com/> | Blog<http://www.gensleron.com/> | Facebook<http://www.facebook.com/GenslerDesign> | Twitter<http://www.twitter.com/GenslerOnCities> | YouTube<http://www.youtube.com/GenslerTV>
What's ahead for design and our clients?
Find out here: Gensler Design Forecast 2016<http://www.gensler.com/doc/gensler-design-forecast-2016>
From: Bldg-sim [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of via Bldg-sim
Sent: Thursday, December 15, 2016 11:17 AM
To: bldg-sim at lists.onebuilding.org<mailto:bldg-sim at lists.onebuilding.org>
Subject: [Bldg-sim] LEED project - maximum limit allowed to simplified wall azimuth.
Hello,
Does anyone know how to interpret "no more than 45 degrees" of exception 5.b - table G3.1 (90.1-2007/2010/2013) ? :
5. Building Envelope
All components of the building envelope in the proposed design shall be modeled as shown on architectural drawings or as built for existing building envelopes.
Exceptions:
b. Exterior surfaces whose azimuth orientation and tilt differ by no more than 45 degrees and are otherwise the same may be described as either a single surface or by using multipliers.
Because "no more than 45 degree" include 45 degree, does the exception still apply if the azimuth of two walls is exactly 45 degrees?
In other words, considering a LEED project, can a perfect octagonal building shape be modeled as a square building (as long as they have the same floor area and the 8 walls have a similar construction) ?
Thanks
Julien
____________________________________________________________________
Julien Dutel, ing., CEM, CMVP.
Direction des secteurs résidentiel, institutionnel et des affaires
Bureau de l'efficacité et de l'innovation énergétiques
Ministère de l'Énergie et des Ressources naturelles
5700, 4e Avenue Ouest, B-406
Québec (Québec) G1H 6R1
Téléphone : 418 627-6379, poste 8060
Téléphone sans frais : 1 877 727-6655
Télécopieur : 418 643-5828
julien.dutel at mern.gouv.qc.ca<mailto:julien.dutel at mern.gouv.qc.ca>
mern.gouv.qc.ca
______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
______________________________________________________________________
______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
______________________________________________________________________
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20161215/9fa7666c/attachment-0001.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 255 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20161215/9fa7666c/attachment-0006.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.png
Type: image/png
Size: 7893 bytes
Desc: image002.png
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20161215/9fa7666c/attachment-0007.png>
More information about the Bldg-sim
mailing list