[Bldg-sim] Thermal Blocks in Multifamily Residential Buildings
Jim Dirkes
jim at buildingperformanceteam.com
Sun Oct 25 15:39:52 PDT 2015
If an apartment has a single thermostat, then it makes no sense to model it
as more than one zone - because it IS a single zone.
On Sun, Oct 25, 2015 at 6:06 PM, Julien Marrec <julien.marrec at gmail.com>
wrote:
> Is this a LEED project?
>
> Long story short, no I don't think this is a reasonable comment.
> One block per apartment is common practice, and you can merge block if
> their share a similar orientation.
>
> Julien
>
> Envoyé de mon iPhone
>
> Le 25 oct. 2015 à 13:01, Sherif Farag <sherif.sabr at gmail.com> a écrit :
>
> Dear Modellers;
>
> I am modelled a multifamily residential building with thermal blocks
> following ASHRAE 90.1:2007 Table G3.1 *item 9*. but I received a comment
> from the reviewer asking me to follow Table G3.1 *item 7a* and justified
> the comment because the living areas and bedroom areas having different
> occupancy profiles, he also suggested that (to simplify the profiles) the
> occupants are in the living space from 1800hrs to 2400hrs and in the
> bedroom spaces 0000hrs to 0800hrs.
>
> Is this a reasonable comment?
> Did anybody here had a similar experience?
>
> I will appreciate your feedback & recommendations.
>
> Thanks & Regards;
>
>
> *Sherif Farag*
>
> *Sustainability Consultant*
>
> P.O. Box: 127842
>
> Abu Dhabi, UAE
>
> M: +971 55 199 0022 | E: sherif.sabr at gmail.com | Skype ID: sherif.farag9
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
--
James V Dirkes II, PE, BEMP, LEED AP
CEO/President
The Building Performance Team Inc.
1631 Acacia Dr, GR, Mi 49504
Direct: 616.450.8653
jim at buildingperformanceteam.com
Website <http://buildingperformanceteamcom>l LinkedIn
<https://www.linkedin.com/pub/jim-dirkes/7/444/413>
“…happiness is the joy produced in us by truth. To be truly happy means
coming to know how things really are, experiencing …reality in its ultimate
root…
What matters more to one’s happiness than getting more freedom and power is
the end toward which we order whatever freedom and power we have. Unless we
order ourselves to the truth, more freedom and more power will bring only
more unhappiness, examples of which abound.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20151025/06a65616/attachment-0001.html>
More information about the Bldg-sim
mailing list