[Bldg-sim] Thermal Blocks in Multifamily Residential Buildings
Julien Marrec
julien.marrec at gmail.com
Sun Oct 25 15:06:39 PDT 2015
Is this a LEED project?
Long story short, no I don't think this is a reasonable comment.
One block per apartment is common practice, and you can merge block if their share a similar orientation.
Julien
Envoyé de mon iPhone
> Le 25 oct. 2015 à 13:01, Sherif Farag <sherif.sabr at gmail.com> a écrit :
>
> Dear Modellers;
>
> I am modelled a multifamily residential building with thermal blocks following ASHRAE 90.1:2007 Table G3.1 item 9. but I received a comment from the reviewer asking me to follow Table G3.1 item 7a and justified the comment because the living areas and bedroom areas having different occupancy profiles, he also suggested that (to simplify the profiles) the occupants are in the living space from 1800hrs to 2400hrs and in the bedroom spaces 0000hrs to 0800hrs.
>
> Is this a reasonable comment?
> Did anybody here had a similar experience?
>
> I will appreciate your feedback & recommendations.
>
> Thanks & Regards;
>
> Sherif Farag
>
> Sustainability Consultant
>
> P.O. Box: 127842
>
> Abu Dhabi, UAE
>
> M: +971 55 199 0022 | E: sherif.sabr at gmail.com | Skype ID: sherif.farag9
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20151025/bdcae3f5/attachment-0001.html>
More information about the Bldg-sim
mailing list