[Bldg-sim] HVAC Engineering Calculation

Pedro Nunes pmnunes at gmail.com
Mon Mar 15 09:00:24 PDT 2010


Hi,

If I right understood, besides the characteristics of the flows, you have to
know the efficiency of the fan coil. Then,

air_fow*T_dif_air*cp_air=efficiency*water_flow*T_dif_water*cp_water <=>

T_dif_air=efficiency*(water_flow*T_dif_water*cp_water)/(air_flow*cp_air)

Regards.

On Mon, Mar 15, 2010 at 2:17 PM, Kimball, Matthew <
Matthew.Kimball at jacobs.com> wrote:

>  I have an interesting problem and wonder if it can be solved
> theoretically.  It is just a simple hot water heating coil with constant
> water flow rate and constant air flow with constant incoming temp. and
> humidity.  If current conditions are given, is there a way to calculate the
> temperature drop in the delivered air based on lowering the temperature of
> the incoming hot water?
>
> Thanks,
> Matt
>
>
> NOTICE - This communication may contain confidential and privileged
> information that is for the sole use of the intended recipient. Any viewing,
> copying or distribution of, or reliance on this message by unintended
> recipients is strictly prohibited. If you have received this message in
> error, please notify us immediately by replying to the message and deleting
> it from your computer.
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send  a blank message to
> BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20100315/a512bcc7/attachment.htm>


More information about the Bldg-sim mailing list