<br>Hi,<br><br>If I right understood, besides the characteristics of the flows, you have to know the efficiency of the fan coil. Then,<br><br>air_fow*T_dif_air*cp_air=efficiency*water_flow*T_dif_water*cp_water <=><br>

<br>T_dif_air=efficiency*(water_flow*T_dif_water*cp_water)/(air_flow*cp_air)<br><br>Regards.<br><br><div class="gmail_quote">On Mon, Mar 15, 2010 at 2:17 PM, Kimball, Matthew <span dir="ltr"><<a href="mailto:Matthew.Kimball@jacobs.com">Matthew.Kimball@jacobs.com</a>></span> wrote:<br>

<blockquote class="gmail_quote" style="border-left: 1px solid rgb(204, 204, 204); margin: 0pt 0pt 0pt 0.8ex; padding-left: 1ex;">





<div vlink="purple" link="blue" name="Compose message area" lang="EN-US">
<div dir="ltr" align="left"><font size="2" color="#0000ff" face="Arial"><span>I have an interesting problem and wonder if it can be 
solved theoretically.  It is just a simple hot water heating coil with 
constant water flow rate and constant air flow with constant incoming temp. 
and humidity.  If current conditions are given, is there a way to calculate 
the temperature drop in the delivered air based on lowering the 
temperature of the incoming hot water?</span></font></div>
<div dir="ltr" align="left"><font size="2" color="#0000ff" face="Arial"><span></span></font> </div>
<div dir="ltr" align="left"><font size="2" color="#0000ff" face="Arial"><span>Thanks,</span></font></div>
<div dir="ltr" align="left"><font size="2" color="#0000ff" face="Arial"><span>Matt</span></font></div><div> </div><br>NOTICE - This communication may contain confidential and privileged information that is for the sole use of the intended recipient. Any viewing, copying or distribution of, or reliance on this message by unintended recipients is strictly prohibited. If you have received this message in error, please notify us immediately by replying to the message and deleting it from your computer.</div>