[TRNSYS-users] (no subject)
David BRADLEY
d.bradley at tess-inc.com
Mon May 21 07:46:28 PDT 2018
First, the heating type in TRNBuild is quite separate from the energy
delivered by a radiant floor. If you have defined and are feeding hot
water to a radiant floor then you should turn off the heating type in
that zone. If you don't then the heating type will automatically keep
the zone at the desired setpoint and your radiant floor will not have
anything to do.
Second, you have to decide how you want to define the energy delivered
to the radiant floor. If you compute q = m Cp (Tin - Tout) on the liquid
side of the radiant floor then you are looking at the amount of energy
that was delivered to the radiant floor from the liquid loop. You'll
need to look through the Type56 outputs for the liquid outlet
temperature for your radiant floor. All the other variables (m, Cp, and
Tin) will come from the component upstream of the radiant floor.
If, on the other hand, you want to see how much energy was delivered
from the radiant floor to the zone then you'll need to look at the
Type56 QCOMI output. The different between the two (QCOMI and the energy
delivered from the loop to the floor) is the amount of energy that is
being stored in the floor for the current time step.
kind regards,
David
On 05/21/2018 01:32, berkane ahlem via TRNSYS-users wrote:
>
> Hello sirs,
> How can i define energy delivered by a radiant floor in heating
> type(heating power) .I define an active layer in the floor of building
> in TRNBuild)
> Thank you
>
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20180521/8e58909f/attachment.htm>
More information about the TRNSYS-users
mailing list