    First, the heating type in TRNBuild is quite separate from the
    energy delivered by a radiant floor. If you have defined and are
    feeding hot water to a radiant floor then you should turn off the
    heating type in that zone. If you don't then the heating type will
    automatically keep the zone at the desired setpoint and your radiant
    floor will not have anything to do.<br>
    <br>
    Second, you have to decide how you want to define the energy
    delivered to the radiant floor. If you compute q = m Cp (Tin - Tout)
    on the liquid side of the radiant floor then you are looking at the
    amount of energy that was delivered to the radiant floor from the
    liquid loop. You'll need to look through the Type56 outputs for the
    liquid outlet temperature for your radiant floor. All the other
    variables (m, Cp, and Tin) will come from the component upstream of
    the radiant floor. <br>
    <br>
    If, on the other hand, you want to see how much energy was delivered
    from the radiant floor to the zone then you'll need to look at the
    Type56 QCOMI output. The different between the two (QCOMI and the
    energy delivered from the loop to the floor) is the amount of energy
    that is being stored in the floor for the current time step.<br>
    kind regards,<br>
     David<br>
    <br>
    <br>
    <div class="moz-cite-prefix">On 05/21/2018 01:32, berkane ahlem via
      TRNSYS-users wrote:<br>
    </div>
    <blockquote type="cite"
cite="mid:CACC+vA7nr7UXKxT3SwyW26Sf-pAxMQ-u32-vydVfLTEvSiPJtA@mail.gmail.com">
      <p dir="ltr">Hello sirs,<br>
        How can i define energy  delivered by a radiant floor in heating
        type(heating power) .I define an active layer in the floor of
        building in TRNBuild)<br>
        Thank you<br>
      </p>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@lists.onebuilding.org">TRNSYS-users@lists.onebuilding.org</a>
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a>
</pre>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>