Alastair McDowell alastair.mcdowell at energyae.com
Mon May 2 01:39:07 PDT 2016


Hi Adnan,

Use Ntype 20, QCOMO for ‘energy to the outside surface incl. conv to the air and l-wave radiation to the other surfaces or Tsky’.

Note the definition of this energy flow means for a positive heatloss, QCOMO will be a negative value.

After you have selected QCOMO, double click on it to select the particular wall surface you want to know heat loss/gain for.
Kind regards,
Alastair McDowell
Engineering Consultant
Energy Analysis & Engineering – Enabling innovation for a sustainable future
T: +61 450 600 842
E: alastair.mcdowell at energyae.com<mailto:alastair.mcdowell at energyae.com>
608 Harris St Sydney NSW 2007 Australia | http://www.energyae.com<http://www.energyae.com/>

From: TRNSYS-users [mailto:trnsys-users-bounces at lists.onebuilding.org] On Behalf Of Adnan Upm Spain
Sent: Thursday, April 28, 2016 11:55 PM
To: TRNSYS users mailing list at OneBuilding. org <trnsys-users at lists.onebuilding.org>
Subject: [TRNSYS-users] NTYPE


Hello everyone,

I want to get convective + radiative ( longwave radiation) heat loss through one external wall i am using type56 and building model is made in TRNSBuild. Which NType can give me this output among these

Ntype 19 - Qcomo
Ntype 20 - Qcomi
Ntype 77 - Qsky
Ntype.      - Qheat
NType2.   - Qsens

BEST Regards
Adnan