[TRNSYS-users] Problem of temperature decrease

Augustin CUQ augustin.cuq at gmail.com
Tue May 24 01:14:57 PDT 2011


Dear trnsys-users,

I have made a simple model, with a two rooms building. The regulation device
is as simple as the model: when the temperature is lower than the
instruction one , the heating signal is put to 1; else, it remains equal to
0.
When the heating signal is put to 1, the temperature of the concerned room
increases logically. When the signal becomes equal to 0, temperature go down
very fast during two time steps. Then, a little increase of the temperature
can be observed (but there is no reason why...).
The little increase I previously mentioned can be observed changing the
heating device by the TRNSys Building heating type manager (after the same
number of time step).

I tried to modify the time step, the radiative part of the heating device,
the power of the heating device, the walls composition but nothing has
changed...

Can anyone explain to me why those phenomenons are observed?

Thanks in advance.

Please find attached some results of the simulation... It can, for instance,
be observed between the simulation times 14.75hr and 18.75hr
-- 
Augustin CUQ
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20110524/1f52121a/attachment-0005.htm>
-------------- next part --------------
  TIME                     	 Top_Room1                	 Top_Room2                	 Text                      	 Heat_Sign_Room1       	 Heat_Sign_Room2       	 Tcons_1                   	 Tcons_2                   	 Total Power for Room1 	 Total Power for Room2 		Temp_diff 1	Temp_diff 2
1	19.13	19.21	-5.4	 -     	 -     	16	16	 -     	 -     		3.13	3.21
1.25	19.16	19.17	-5.4	 -     	 -     	16	16	 -     	 -     		3.16	3.17
1.5	19.15	19.18	-5.4	 -     	 -     	16	16	 -     	 -     		3.15	3.18
1.75	19.14	19.16	-5.9	 -     	 -     	16	16	 -     	 -     		3.14	3.16
2	18.88	18.93	-5.9	 -     	 -     	16	16	 -     	 -     		2.88	2.93
2.25	18.79	18.85	-5.9	 -     	 -     	16	16	 -     	 -     		2.79	2.85
2.5	18.81	18.87	-5.9	 -     	 -     	16	16	 -     	 -     		2.81	2.87
2.75	18.8	18.86	-6.1	 -     	 -     	16	16	 -     	 -     		2.8	2.86
3	18.59	18.67	-6.1	 -     	 -     	16	16	 -     	 -     		2.59	2.67
3.25	18.51	18.6	-6.1	 -     	 -     	16	16	 -     	 -     		2.51	2.6
3.5	18.53	18.62	-6.1	 -     	 -     	16	16	 -     	 -     		2.53	2.62
3.75	18.52	18.61	-6.3	 -     	 -     	16	16	 -     	 -     		2.52	2.61
4	18.32	18.42	-6.3	 -     	 -     	16	16	 -     	 -     		2.32	2.42
4.25	18.24	18.36	-6.3	 -     	 -     	16	16	 -     	 -     		2.24	2.36
4.5	18.26	18.38	-6.3	 -     	 -     	16	16	 -     	 -     		2.26	2.38
4.75	18.25	18.37	-6.4	 -     	 -     	16	16	 -     	 -     		2.25	2.37
5	18.05	18.18	-6.4	 -     	 -     	16	16	 -     	 -     		2.05	2.18
5.25	17.98	18.12	-6.4	 -     	 -     	16	16	 -     	 -     		1.98	2.12
5.5	17.99	18.14	-6.4	 -     	 -     	16	16	 -     	 -     		1.99	2.14
5.75	17.97	18.11	-7	 -     	 -     	16	16	 -     	 -     		1.97	2.11
6	17.76	17.92	-7	 -     	 -     	16	16	 -     	 -     		1.76	1.92
6.25	17.69	17.85	-7	 -     	 -     	16	16	 -     	 -     		1.69	1.85
6.5	17.7	17.87	-7	 -     	 -     	16	16	 -     	 -     		1.7	1.87
6.75	17.65	17.82	-8.4	 -     	 -     	16	16	 -     	 -     		1.65	1.82
7	17.42	17.61	-8.4	 -     	 -     	16	16	 -     	 -     		1.42	1.61
7.25	17.35	17.55	-8.4	 -     	 -     	16	16	 -     	 -     		1.35	1.55
7.5	17.37	17.56	-8.4	 -     	 -     	16	16	 -     	 -     		1.37	1.56
7.75	17.28	17.47	-10.9	 -     	 -     	16	16	 -     	 -     		1.28	1.47
8	17.03	17.24	-10.9	 -     	 -     	16	16	 -     	 -     		1.03	1.24
8.25	17.09	20.42	-10.9	 -     	1	16	19	 -     	32 046.67		1.09	1.42
8.5	17.05	18.81	-10.9	 -     	 -     	16	19	 -     	 -     		1.05	-0.19
8.75	17.1	20.05	-10.3	 -     	1	16	19	 -     	32 046.67		1.1	1.05
9	16.94	19.39	-10.3	 -     	 -     	16	19	 -     	 -     		0.94	0.39
9.25	16.86	17.45	-10.3	 -     	 -     	16	19	 -     	 -     		0.86	-1.55
9.5	16.98	21.19	-10.3	 -     	1	16	19	 -     	32 046.67		0.98	2.19
9.75	17.03	19.48	-7.6	 -     	 -     	16	19	 -     	 -     		1.03	0.48
10	16.87	17.75	-7.6	 -     	 -     	16	19	 -     	 -     		0.87	-1.25
10.25	16.86	21.51	-7.6	 -     	1	16	19	 -     	32 046.67		0.86	2.51
10.5	16.84	19.69	-7.6	 -     	 -     	16	19	 -     	 -     		0.84	0.69
10.75	16.85	17.83	-6.1	 -     	 -     	16	19	 -     	 -     		0.85	-1.17
11	16.81	21.66	-6.1	 -     	1	16	19	 -     	32 046.67		0.81	2.66
11.25	16.72	19.88	-6.1	 -     	 -     	16	19	 -     	 -     		0.72	0.88
11.5	16.69	17.96	-6.1	 -     	 -     	16	19	 -     	 -     		0.69	-1.04
11.75	16.78	21.71	-5.7	 -     	1	16	19	 -     	32 046.67		0.78	2.71
12	16.65	20.31	-5.7	 -     	 -     	16	19	 -     	 -     		0.65	1.31
12.25	16.57	18.54	-5.7	 -     	 -     	16	19	 -     	 -     		0.57	-0.46
12.5	16.67	22.23	-5.7	 -     	1	16	19	 -     	32 046.67		0.67	3.23
12.75	16.67	20.47	-4.8	 -     	 -     	16	19	 -     	 -     		0.67	1.47
13	16.53	18.69	-4.8	 -     	 -     	16	19	 -     	 -     		0.53	-0.31
13.25	16.55	22.45	-4.8	 -     	1	16	19	 -     	32 046.67		0.55	3.45
13.5	16.52	20.62	-4.8	 -     	 -     	16	19	 -     	 -     		0.52	1.62
13.75	16.5	18.73	-4.1	 -     	 -     	16	19	 -     	 -     		0.5	-0.27
14	16.5	22.55	-4.1	 -     	1	16	19	 -     	32 046.67		0.5	3.55
14.25	20.01	20.79	-4.1	1	 -     	19	16	32 046.67	 -     		1.01	4.79
14.5	18.32	18.8	-4.1	 -     	 -     	19	16	 -     	 -     		-0.68	2.8
14.75	19.68	19.38	-4.2	1	 -     	19	16	32 046.67	 -     		0.68	3.38
15	19.14	19.34	-4.2	 -     	 -     	19	16	 -     	 -     		0.14	3.34
15.25	17.16	19.39	-4.2	 -     	 -     	19	16	 -     	 -     		-1.84	3.39
15.5	21.13	19.45	-4.2	1	 -     	19	16	32 046.67	 -     		2.13	3.45
15.75	19.3	19.4	-4.7	 -     	 -     	19	16	 -     	 -     		0.3	3.4
16	17.44	19.12	-4.7	 -     	 -     	19	16	 -     	 -     		-1.56	3.12
16.25	21.49	19.12	-4.7	1	 -     	19	16	32 046.67	 -     		2.49	3.12
16.5	19.68	19.11	-4.7	 -     	 -     	19	16	 -     	 -     		0.68	3.11
16.75	18.45	19.24	-6.4	 -     	 -     	19	16	 -     	 -     		-0.55	3.24
17	21.81	18.91	-6.4	1	 -     	19	16	32 046.67	 -     		2.81	2.91
17.25	19.62	18.7	-6.4	 -     	 -     	19	16	 -     	 -     		0.62	2.7
17.5	17.55	18.7	-6.4	 -     	 -     	19	16	 -     	 -     		-1.45	2.7
17.75	21.47	18.74	-7.2	1	 -     	19	16	32 046.67	 -     		2.47	2.74
18	20.07	18.51	-7.2	 -     	 -     	19	16	 -     	 -     		1.07	2.51
18.25	18.05	18.4	-7.2	 -     	 -     	16	16	 -     	 -     		2.05	2.4
18.5	18.46	18.42	-7.2	 -     	 -     	16	16	 -     	 -     		2.46	2.42
18.75	18.38	18.42	-7.2	 -     	 -     	16	16	 -     	 -     		2.38	2.42
19	18.11	18.2	-7.2	 -     	 -     	16	16	 -     	 -     		2.11	2.2
19.25	18	18.12	-7.2	 -     	 -     	16	16	 -     	 -     		2	2.12
19.5	18.02	18.14	-7.2	 -     	 -     	16	16	 -     	 -     		2.02	2.14
19.75	18.07	18.19	-5.7	 -     	 -     	16	16	 -     	 -     		2.07	2.19
20	17.84	18.01	-5.7	 -     	 -     	16	16	 -     	 -     		1.84	2.01
20.25	17.73	17.93	-5.7	 -     	 -     	16	16	 -     	 -     		1.73	1.93
20.5	17.75	17.95	-5.7	 -     	 -     	16	16	 -     	 -     		1.75	1.95
20.75	17.76	17.96	-5.3	 -     	 -     	16	16	 -     	 -     		1.76	1.96
21	17.55	17.78	-5.3	 -     	 -     	16	16	 -     	 -     		1.55	1.78
21.25	17.46	17.71	-5.3	 -     	 -     	16	16	 -     	 -     		1.46	1.71
21.5	17.48	17.73	-5.3	 -     	 -     	16	16	 -     	 -     		1.48	1.73
21.75	17.49	17.74	-4.9	 -     	 -     	16	16	 -     	 -     		1.49	1.74
22	17.29	17.57	-4.9	 -     	 -     	16	16	 -     	 -     		1.29	1.57
22.25	17.22	17.5	-4.9	 -     	 -     	16	16	 -     	 -     		1.22	1.5
22.5	17.23	17.52	-4.9	 -     	 -     	16	16	 -     	 -     		1.23	1.52
22.75	17.24	17.53	-4.6	 -     	 -     	16	16	 -     	 -     		1.24	1.53
23	17.05	17.36	-4.6	 -     	 -     	16	16	 -     	 -     		1.05	1.36
23.25	16.98	17.3	-4.6	 -     	 -     	16	16	 -     	 -     		0.98	1.3
23.5	17	17.32	-4.6	 -     	 -     	16	16	 -     	 -     		1	1.32
23.75	16.98	17.31	-4.8	 -     	 -     	16	16	 -     	 -     		0.98	1.31
24	16.8	17.14	-4.8	 -     	 -     	16	16	 -     	 -     		0.8	1.14
24.25	16.73	17.08	-4.8	 -     	 -     	16	16	 -     	 -     		0.73	1.08
24.5	16.74	17.1	-4.8	 -     	 -     	16	16	 -     	 -     		0.74	1.1
24.75	16.73	17.08	-5	 -     	 -     	16	16	 -     	 -     		0.73	1.08
25	16.55	16.92	-5	 -     	 -     	16	16	 -     	 -     		0.55	0.92
25.25	16.49	16.86	-5	 -     	 -     	16	16	 -     	 -     		0.49	0.86
25.5	16.5	16.88	-5	 -     	 -     	16	16	 -     	 -     		0.5	0.88
25.75	16.5	16.88	-4.9	 -     	 -     	16	16	 -     	 -     		0.5	0.88
26	16.33	16.72	-4.9	 -     	 -     	16	16	 -     	 -     		0.33	0.72
26.25	16.26	16.66	-4.9	 -     	 -     	16	16	 -     	 -     		0.26	0.66
26.5	16.28	16.67	-4.9	 -     	 -     	16	16	 -     	 -     		0.28	0.67
26.75	16.28	16.68	-4.7	 -     	 -     	16	16	 -     	 -     		0.28	0.68
27	16.12	16.52	-4.7	 -     	 -     	16	16	 -     	 -     		0.12	0.52
27.25	16.05	16.47	-4.7	 -     	 -     	16	16	 -     	 -     		0.05	0.47
27.5	16.07	16.48	-4.7	 -     	 -     	16	16	 -     	 -     		0.07	0.48
27.75	16.05	16.47	-5	 -     	 -     	16	16	 -     	 -     		0.05	0.47
28	15.88	16.31	-5	 -     	 -     	16	16	 -     	 -     		-0.12	0.31
28.25	19.32	16.33	-5	1	 -     	16	16	32 046.67	 -     		3.32	0.33
28.5	17.62	16.31	-5	 -     	 -     	16	16	 -     	 -     		1.62	0.31
28.75	15.44	16.26	-5	 -     	 -     	16	16	 -     	 -     		-0.56	0.26
29	19.64	16.21	-5	1	 -     	16	16	32 046.67	 -     		3.64	0.21
29.25	17.9	16.13	-5	 -     	 -     	16	16	 -     	 -     		1.9	0.13
29.5	15.73	16.09	-5	 -     	 -     	16	16	 -     	 -     		-0.27	0.09
29.75	19.68	16.15	-5.6	1	 -     	16	16	32 046.67	 -     		3.68	0.15
30	18.36	15.99	-5.6	 -     	 -     	16	16	 -     	 -     		2.36	-0.01
30.25	16.47	19.09	-5.6	 -     	1	16	16	 -     	32 046.67		0.47	3.09
30.5	16.86	17.45	-5.6	 -     	 -     	16	16	 -     	 -     		0.86	1.45
30.75	16.72	15.49	-5.7	 -     	 -     	16	16	 -     	 -     		0.72	-0.51
31	16.61	19.39	-5.7	 -     	1	16	16	 -     	32 046.67		0.61	3.39
31.25	16.49	17.64	-5.7	 -     	 -     	16	16	 -     	 -     		0.49	1.64
31.5	16.46	15.71	-5.7	 -     	 -     	16	16	 -     	 -     		0.46	-0.29
31.75	16.55	19.44	-5.5	 -     	1	16	16	 -     	32 046.67		0.55	3.44
32	16.33	18.05	-5.5	 -     	 -     	16	16	 -     	 -     		0.33	2.05
32.25	16.34	19.54	-5.5	 -     	1	16	19	 -     	32 046.67		0.34	0.54
32.5	16.31	18.41	-5.5	 -     	 -     	16	19	 -     	 -     		0.31	-0.59
32.75	16.36	19.53	-4.7	 -     	1	16	19	 -     	32 046.67		0.36	0.53
33	16.21	18.9	-4.7	 -     	 -     	16	19	 -     	 -     		0.21	-0.1
33.25	16.2	20.12	-4.7	 -     	1	16	19	 -     	32 046.67		0.2	1.12
33.5	16.19	19.02	-4.7	 -     	 -     	16	19	 -     	 -     		0.19	0.02
33.75	16.14	16.9	-5	 -     	 -     	16	19	 -     	 -     		0.14	-2.1
34	16.09	20.81	-5	 -     	1	16	19	 -     	32 046.67		0.09	1.81
34.25	16.02	19.04	-5	 -     	 -     	16	19	 -     	 -     		0.02	0.04
34.5	15.99	17.12	-5	 -     	 -     	16	19	 -     	 -     		-0.01	-1.88
34.75	19.58	20.94	-4.6	1	1	16	19	32 046.67	32 046.67		3.58	1.94
35	18.07	19.52	-4.6	 -     	 -     	16	19	 -     	 -     		2.07	0.52
35.25	15.92	17.7	-4.6	 -     	 -     	16	19	 -     	 -     		-0.08	-1.3
35.5	19.95	21.46	-4.6	1	1	16	19	32 046.67	32 046.67		3.95	2.46
35.75	18.11	19.64	-4.2	 -     	 -     	16	19	 -     	 -     		2.11	0.64
36	16.2	17.82	-4.2	 -     	 -     	16	19	 -     	 -     		0.2	-1.18
36.25	16.85	21.6	-4.2	 -     	1	16	19	 -     	32 046.67		0.85	2.6
36.5	16.69	19.77	-4.2	 -     	 -     	16	19	 -     	 -     		0.69	0.77
36.75	16.66	17.85	-4.8	 -     	 -     	16	19	 -     	 -     		0.66	-1.15
37	16.51	21.63	-4.8	 -     	1	16	19	 -     	32 046.67		0.51	2.63
37.25	16.39	19.85	-4.8	 -     	 -     	16	19	 -     	 -     		0.39	0.85
37.5	16.35	17.91	-4.8	 -     	 -     	16	19	 -     	 -     		0.35	-1.09
37.75	16.42	21.63	-5.1	 -     	1	16	19	 -     	32 046.67		0.42	2.63
38	16.25	20.21	-5.1	 -     	 -     	16	19	 -     	 -     		0.25	1.21
38.25	19.69	18.45	-5.1	1	 -     	19	16	32 046.67	 -     		0.69	2.45
38.5	18.01	18.87	-5.1	 -     	 -     	19	16	 -     	 -     		-0.99	2.87
38.75	19.32	18.77	-5.2	1	 -     	19	16	32 046.67	 -     		0.32	2.77
39	18.63	18.55	-5.2	 -     	 -     	19	16	 -     	 -     		-0.37	2.55
39.25	20.05	18.49	-5.2	1	 -     	19	16	32 046.67	 -     		1.05	2.49
39.5	18.79	18.48	-5.2	 -     	 -     	19	16	 -     	 -     		-0.21	2.48
39.75	19.99	18.48	-5.6	1	 -     	19	16	32 046.67	 -     		0.99	2.48
40	19.27	18.24	-5.6	 -     	 -     	19	16	 -     	 -     		0.27	2.24
40.25	17.18	18.12	-5.6	 -     	 -     	19	16	 -     	 -     		-1.82	2.12
40.5	21.12	18.22	-5.6	1	 -     	19	16	32 046.67	 -     		2.12	2.22
40.75	19.29	18.15	-6.1	 -     	 -     	19	16	 -     	 -     		0.29	2.15
41	17.27	17.9	-6.1	 -     	 -     	19	16	 -     	 -     		-1.73	1.9
41.25	21.29	17.91	-6.1	1	 -     	19	16	32 046.67	 -     		2.29	1.91
41.5	19.47	17.89	-6.1	 -     	 -     	19	16	 -     	 -     		0.47	1.89
41.75	17.32	17.84	-6.1	 -     	 -     	19	16	 -     	 -     		-1.68	1.84
42	21.36	17.73	-6.1	1	 -     	19	16	32 046.67	 -     		2.36	1.73
42.25	19.54	17.63	-6.1	 -     	 -     	16	16	 -     	 -     		3.54	1.63
42.5	17.36	17.6	-6.1	 -     	 -     	16	16	 -     	 -     		1.36	1.6
42.75	17.83	17.6	-6.1	 -     	 -     	16	16	 -     	 -     		1.83	1.6
43	17.83	17.42	-6.1	 -     	 -     	16	16	 -     	 -     		1.83	1.42
43.25	17.89	17.35	-6.1	 -     	 -     	16	16	 -     	 -     		1.89	1.35
43.5	17.87	17.37	-6.1	 -     	 -     	16	16	 -     	 -     		1.87	1.37
43.75	17.88	17.37	-5.9	 -     	 -     	16	16	 -     	 -     		1.88	1.37
44	17.6	17.19	-5.9	 -     	 -     	16	16	 -     	 -     		1.6	1.19
44.25	17.49	17.12	-5.9	 -     	 -     	16	16	 -     	 -     		1.49	1.12
44.5	17.51	17.14	-5.9	 -     	 -     	16	16	 -     	 -     		1.51	1.14
44.75	17.51	17.13	-5.8	 -     	 -     	16	16	 -     	 -     		1.51	1.13
45	17.28	16.95	-5.8	 -     	 -     	16	16	 -     	 -     		1.28	0.95
45.25	17.19	16.89	-5.8	 -     	 -     	16	16	 -     	 -     		1.19	0.89
45.5	17.21	16.91	-5.8	 -     	 -     	16	16	 -     	 -     		1.21	0.91
45.75	17.22	16.92	-5.4	 -     	 -     	16	16	 -     	 -     		1.22	0.92
46	17.01	16.75	-5.4	 -     	 -     	16	16	 -     	 -     		1.01	0.75
46.25	16.93	16.69	-5.4	 -     	 -     	16	16	 -     	 -     		0.93	0.69
46.5	16.95	16.7	-5.4	 -     	 -     	16	16	 -     	 -     		0.95	0.7
46.75	16.95	16.71	-5.2	 -     	 -     	16	16	 -     	 -     		0.95	0.71
47	16.76	16.54	-5.2	 -     	 -     	16	16	 -     	 -     		0.76	0.54
47.25	16.68	16.48	-5.2	 -     	 -     	16	16	 -     	 -     		0.68	0.48
47.5	16.7	16.5	-5.2	 -     	 -     	16	16	 -     	 -     		0.7	0.5
47.75	16.7	16.5	-5	 -     	 -     	16	16	 -     	 -     		0.7	0.5
48	16.51	16.34	-5	 -     	 -     	16	16	 -     	 -     		0.51	0.34
48.25	16.44	16.28	-5	 -     	 -     	16	16	 -     	 -     		0.44	0.28
48.5	16.46	16.3	-5	 -     	 -     	16	16	 -     	 -     		0.46	0.3
48.75	16.46	16.31	-4.7	 -     	 -     	16	16	 -     	 -     		0.46	0.31
49	16.29	16.15	-4.7	 -     	 -     	16	16	 -     	 -     		0.29	0.15
49.25	16.22	16.1	-4.7	 -     	 -     	16	16	 -     	 -     		0.22	0.1
49.5	16.23	16.11	-4.7	 -     	 -     	16	16	 -     	 -     		0.23	0.11
49.75	16.24	16.12	-4.4	 -     	 -     	16	16	 -     	 -     		0.24	0.12
50	16.07	15.97	-4.4	 -     	 -     	16	16	 -     	 -     		0.07	-0.03
50.25	16.08	19.11	-4.4	 -     	1	16	16	 -     	32 046.67		0.08	3.11
50.5	16.06	17.46	-4.4	 -     	 -     	16	16	 -     	 -     		0.06	1.46
50.75	16.01	15.5	-4.4	 -     	 -     	16	16	 -     	 -     		0.01	-0.5
51	15.94	19.41	-4.4	 -     	1	16	16	 -     	32 046.67		-0.06	3.41
51.25	19.35	17.74	-4.4	1	 -     	16	16	32 046.67	 -     		3.35	1.74
51.5	17.61	15.77	-4.4	 -     	 -     	16	16	 -     	 -     		1.61	-0.23
51.75	15.51	19.46	-4.3	 -     	1	16	16	 -     	32 046.67		-0.49	3.46
52	19.7	18.18	-4.3	1	 -     	16	16	32 046.67	 -     		3.7	2.18
52.25	17.94	16.38	-4.3	 -     	 -     	16	16	 -     	 -     		1.94	0.38
52.5	15.77	16.83	-4.3	 -     	 -     	16	16	 -     	 -     		-0.23	0.83
52.75	19.75	16.78	-4.1	1	 -     	16	16	32 046.67	 -     		3.75	0.78
53	18.43	16.6	-4.1	 -     	 -     	16	16	 -     	 -     		2.43	0.6
53.25	16.47	16.48	-4.1	 -     	 -     	16	16	 -     	 -     		0.47	0.48
53.5	16.89	16.51	-4.1	 -     	 -     	16	16	 -     	 -     		0.89	0.51
53.75	16.8	16.5	-4.1	 -     	 -     	16	16	 -     	 -     		0.8	0.5
54	16.59	16.31	-4.1	 -     	 -     	16	16	 -     	 -     		0.59	0.31
54.25	16.5	16.24	-4.1	 -     	 -     	16	16	 -     	 -     		0.5	0.24
54.5	16.52	16.26	-4.1	 -     	 -     	16	16	 -     	 -     		0.52	0.26
54.75	16.52	16.26	-4	 -     	 -     	16	16	 -     	 -     		0.52	0.26
55	16.31	16.09	-4	 -     	 -     	16	16	 -     	 -     		0.31	0.09
55.25	16.24	16.04	-4	 -     	 -     	16	16	 -     	 -     		0.24	0.04
55.5	16.26	16.05	-4	 -     	 -     	16	16	 -     	 -     		0.26	0.05
55.75	16.26	16.05	-3.9	 -     	 -     	16	16	 -     	 -     		0.26	0.05
56	16.08	15.9	-3.9	 -     	 -     	16	16	 -     	 -     		0.08	-0.1
56.25	16.14	19.1	-3.9	 -     	1	16	19	 -     	32 046.67		0.14	0.1
56.5	16.1	17.48	-3.9	 -     	 -     	16	19	 -     	 -     		0.1	-1.52
56.75	16.12	18.72	-3.8	 -     	1	16	19	 -     	32 046.67		0.12	-0.28
57	16.06	21.29	-3.8	 -     	1	16	19	 -     	32 046.67		0.06	2.29
57.25	15.95	17.68	-3.8	 -     	 -     	16	19	 -     	 -     		-0.05	-1.32
57.5	19.51	19.56	-3.8	1	1	16	19	32 046.67	32 046.67		3.51	0.56
57.75	17.76	18.25	-3.6	 -     	 -     	16	19	 -     	 -     		1.76	-0.75
58	15.93	19.89	-3.6	 -     	1	16	19	 -     	32 046.67		-0.07	0.89
58.25	19.98	19.07	-3.6	1	 -     	16	19	32 046.67	 -     		3.98	0.07
58.5	18.08	16.87	-3.6	 -     	 -     	16	19	 -     	 -     		2.08	-2.13
58.75	16.05	20.64	-3.4	 -     	1	16	19	 -     	32 046.67		0.05	1.64
59	16.68	19.17	-3.4	 -     	 -     	16	19	 -     	 -     		0.68	0.17
59.25	16.6	17.38	-3.4	 -     	 -     	16	19	 -     	 -     		0.6	-1.62
59.5	16.69	21.08	-3.4	 -     	1	16	19	 -     	32 046.67		0.69	2.08
59.75	16.67	19.29	-3.1	 -     	 -     	16	19	 -     	 -     		0.67	0.29
60	16.45	17.52	-3.1	 -     	 -     	16	19	 -     	 -     		0.45	-1.48
60.25	16.47	21.29	-3.1	 -     	1	16	19	 -     	32 046.67		0.47	2.29
60.5	16.45	19.47	-3.1	 -     	 -     	16	19	 -     	 -     		0.45	0.47
60.75	16.4	17.55	-2.8	 -     	 -     	16	19	 -     	 -     		0.4	-1.45
61	16.35	21.38	-2.8	 -     	1	16	19	 -     	32 046.67		0.35	2.38
61.25	16.27	19.6	-2.8	 -     	 -     	16	19	 -     	 -     		0.27	0.6
61.5	16.24	17.68	-2.8	 -     	 -     	16	19	 -     	 -     		0.24	-1.32
61.75	16.34	21.43	-2.3	 -     	1	16	19	 -     	32 046.67		0.34	2.43
62	16.23	20.04	-2.3	 -     	 -     	16	19	 -     	 -     		0.23	1.04
62.25	19.7	18.29	-2.3	1	 -     	19	16	32 046.67	 -     		0.7	2.29
62.5	18.04	18.72	-2.3	 -     	 -     	19	16	 -     	 -     		-0.96	2.72
62.75	19.42	18.63	-2.2	1	 -     	19	16	32 046.67	 -     		0.42	2.63
63	18.81	18.46	-2.2	 -     	 -     	19	16	 -     	 -     		-0.19	2.46
63.25	20.24	18.41	-2.2	1	 -     	19	16	32 046.67	 -     		1.24	2.41
63.5	18.95	18.39	-2.2	 -     	 -     	19	16	 -     	 -     		-0.05	2.39
63.75	20.14	18.39	-2.5	1	 -     	19	16	32 046.67	 -     		1.14	2.39
64	19.49	18.19	-2.5	 -     	 -     	19	16	 -     	 -     		0.49	2.19
64.25	17.42	18.08	-2.5	 -     	 -     	19	16	 -     	 -     		-1.58	2.08
64.5	21.35	18.17	-2.5	1	 -     	19	16	32 046.67	 -     		2.35	2.17
64.75	19.5	18.1	-3.1	 -     	 -     	19	16	 -     	 -     		0.5	2.1
65	17.47	17.86	-3.1	 -     	 -     	19	16	 -     	 -     		-1.53	1.86
65.25	21.5	17.88	-3.1	1	 -     	19	16	32 046.67	 -     		2.5	1.88
65.5	19.66	17.86	-3.1	 -     	 -     	19	16	 -     	 -     		0.66	1.86
65.75	17.52	17.8	-3.2	 -     	 -     	19	16	 -     	 -     		-1.48	1.8
66	21.58	17.71	-3.2	1	 -     	19	16	32 046.67	 -     		2.58	1.71
66.25	19.75	17.62	-3.2	 -     	 -     	16	16	 -     	 -     		3.75	1.62
66.5	17.58	17.59	-3.2	 -     	 -     	16	16	 -     	 -     		1.58	1.59
66.75	18.05	17.59	-3.2	 -     	 -     	16	16	 -     	 -     		2.05	1.59
67	18.07	17.43	-3.2	 -     	 -     	16	16	 -     	 -     		2.07	1.43
67.25	18.13	17.38	-3.2	 -     	 -     	16	16	 -     	 -     		2.13	1.38
67.5	18.12	17.39	-3.2	 -     	 -     	16	16	 -     	 -     		2.12	1.39
67.75	18.13	17.4	-2.9	 -     	 -     	16	16	 -     	 -     		2.13	1.4
68	17.87	17.23	-2.9	 -     	 -     	16	16	 -     	 -     		1.87	1.23
68.25	17.76	17.17	-2.9	 -     	 -     	16	16	 -     	 -     		1.76	1.17
68.5	17.79	17.19	-2.9	 -     	 -     	16	16	 -     	 -     		1.79	1.19
68.75	17.81	17.21	-2.1	 -     	 -     	16	16	 -     	 -     		1.81	1.21
69	17.61	17.07	-2.1	 -     	 -     	16	16	 -     	 -     		1.61	1.07
69.25	17.53	17.01	-2.1	 -     	 -     	16	16	 -     	 -     		1.53	1.01
69.5	17.55	17.02	-2.1	 -     	 -     	16	16	 -     	 -     		1.55	1.02
69.75	17.56	17.03	-1.6	 -     	 -     	16	16	 -     	 -     		1.56	1.03
70	17.38	16.9	-1.6	 -     	 -     	16	16	 -     	 -     		1.38	0.9
70.25	17.31	16.84	-1.6	 -     	 -     	16	16	 -     	 -     		1.31	0.84
70.5	17.32	16.86	-1.6	 -     	 -     	16	16	 -     	 -     		1.32	0.86
70.75	17.33	16.86	-1.3	 -     	 -     	16	16	 -     	 -     		1.33	0.86
71	17.16	16.73	-1.3	 -     	 -     	16	16	 -     	 -     		1.16	0.73
71.25	17.1	16.68	-1.3	 -     	 -     	16	16	 -     	 -     		1.1	0.68
71.5	17.11	16.69	-1.3	 -     	 -     	16	16	 -     	 -     		1.11	0.69
71.75	17.12	16.7	-1	 -     	 -     	16	16	 -     	 -     		1.12	0.7
72	16.96	16.57	-1	 -     	 -     	16	16	 -     	 -     		0.96	0.57
72.25	16.9	16.52	-1	 -     	 -     	16	16	 -     	 -     		0.9	0.52
72.5	16.91	16.53	-1	 -     	 -     	16	16	 -     	 -     		0.91	0.53
72.75	16.9	16.52	-1.2	 -     	 -     	16	16	 -     	 -     		0.9	0.52
73	16.74	16.39	-1.2	 -     	 -     	16	16	 -     	 -     		0.74	0.39
73.25	16.69	16.35	-1.2	 -     	 -     	16	16	 -     	 -     		0.69	0.35
73.5	16.7	16.36	-1.2	 -     	 -     	16	16	 -     	 -     		0.7	0.36
73.75	16.71	16.37	-0.7	 -     	 -     	16	16	 -     	 -     		0.71	0.37
74	16.57	16.25	-0.7	 -     	 -     	16	16	 -     	 -     		0.57	0.25
74.25	16.51	16.2	-0.7	 -     	 -     	16	16	 -     	 -     		0.51	0.2
74.5	16.52	16.22	-0.7	 -     	 -     	16	16	 -     	 -     		0.52	0.22
74.75	16.53	16.22	-0.5	 -     	 -     	16	16	 -     	 -     		0.53	0.22
75	16.39	16.1	-0.5	 -     	 -     	16	16	 -     	 -     		0.39	0.1
75.25	16.33	16.06	-0.5	 -     	 -     	16	16	 -     	 -     		0.33	0.06
75.5	16.35	16.07	-0.5	 -     	 -     	16	16	 -     	 -     		0.35	0.07
75.75	16.34	16.06	-0.6	 -     	 -     	16	16	 -     	 -     		0.34	0.06
76	16.2	15.94	-0.6	 -     	 -     	16	16	 -     	 -     		0.2	-0.06
76.25	16.22	19.1	-0.6	 -     	1	16	16	 -     	32 046.67		0.22	3.1
76.5	16.2	17.45	-0.6	 -     	 -     	16	16	 -     	 -     		0.2	1.45
76.75	16.14	15.47	-1	 -     	 -     	16	16	 -     	 -     		0.14	-0.53
77	16.1	19.42	-1	 -     	1	16	16	 -     	32 046.67		0.1	3.42
77.25	16.02	17.68	-1	 -     	 -     	16	16	 -     	 -     		0.02	1.68
77.5	15.99	15.74	-1	 -     	 -     	16	16	 -     	 -     		-0.01	-0.26
77.75	19.56	19.55	-1.3	1	1	16	16	32 046.67	32 046.67		3.56	3.55
78	18.04	18.16	-1.3	 -     	 -     	16	16	 -     	 -     		2.04	2.16
78.25	15.9	16.36	-1.3	 -     	 -     	16	16	 -     	 -     		-0.1	0.36
78.5	19.86	16.93	-1.3	1	 -     	16	16	32 046.67	 -     		3.86	0.93
78.75	18.01	16.72	-2.7	 -     	 -     	16	16	 -     	 -     		2.01	0.72
79	16.09	16.52	-2.7	 -     	 -     	16	16	 -     	 -     		0.09	0.52
79.25	16.66	16.46	-2.7	 -     	 -     	16	16	 -     	 -     		0.66	0.46
79.5	16.53	16.48	-2.7	 -     	 -     	16	16	 -     	 -     		0.53	0.48
79.75	16.55	16.46	-3.1	 -     	 -     	16	16	 -     	 -     		0.55	0.46
80	16.33	16.28	-3.1	 -     	 -     	16	16	 -     	 -     		0.33	0.28
80.25	16.39	19.49	-3.1	 -     	1	16	19	 -     	32 046.67		0.39	0.49
80.5	16.36	17.88	-3.1	 -     	 -     	16	19	 -     	 -     		0.36	-1.12
80.75	16.42	19.14	-2	 -     	1	16	19	 -     	32 046.67		0.42	0.14
81	16.32	18.54	-2	 -     	 -     	16	19	 -     	 -     		0.32	-0.46
81.25	16.31	19.79	-2	 -     	1	16	19	 -     	32 046.67		0.31	0.79
81.5	16.29	18.68	-2	 -     	 -     	16	19	 -     	 -     		0.29	-0.32
81.75	16.35	19.8	-0.9	 -     	1	16	19	 -     	32 046.67		0.35	0.8
82	16.26	19.21	-0.9	 -     	 -     	16	19	 -     	 -     		0.26	0.21
82.25	16.18	17.25	-0.9	 -     	 -     	16	19	 -     	 -     		0.18	-1.75
82.5	16.26	21	-0.9	 -     	1	16	19	 -     	32 046.67		0.26	2
82.75	16.24	19.2	-0.5	 -     	 -     	16	19	 -     	 -     		0.24	0.2
83	16.12	17.46	-0.5	 -     	 -     	16	19	 -     	 -     		0.12	-1.54
83.25	16.17	21.26	-0.5	 -     	1	16	19	 -     	32 046.67		0.17	2.26
83.5	16.15	19.43	-0.5	 -     	 -     	16	19	 -     	 -     		0.15	0.43
83.75	16.15	17.55	0.6	 -     	 -     	16	19	 -     	 -     		0.15	-1.45
84	16.18	21.43	0.6	 -     	1	16	19	 -     	32 046.67		0.18	2.43
84.25	16.13	19.66	0.6	 -     	 -     	16	19	 -     	 -     		0.13	0.66
84.5	16.11	17.73	0.6	 -     	 -     	16	19	 -     	 -     		0.11	-1.27
84.75	16.2	21.48	0.7	 -     	1	16	19	 -     	32 046.67		0.2	2.48
85	16.15	20.13	0.7	 -     	 -     	16	19	 -     	 -     		0.15	1.13
85.25	16.1	18.36	0.7	 -     	 -     	16	19	 -     	 -     		0.1	-0.64
85.5	16.19	22.05	0.7	 -     	1	16	19	 -     	32 046.67		0.19	3.05
85.75	16.18	20.25	0.5	 -     	 -     	16	19	 -     	 -     		0.18	1.25
86	16.12	18.49	0.5	 -     	 -     	16	19	 -     	 -     		0.12	-0.51
86.25	19.68	19.1	0.5	1	 -     	19	16	32 046.67	 -     		0.68	3.1
86.5	18	18.87	0.5	 -     	 -     	19	16	 -     	 -     		-1	2.87
86.75	19.33	18.94	0.3	1	 -     	19	16	32 046.67	 -     		0.33	2.94
87	18.77	18.7	0.3	 -     	 -     	19	16	 -     	 -     		-0.23	2.7
87.25	20.21	18.66	0.3	1	 -     	19	16	32 046.67	 -     		1.21	2.66
87.5	18.87	18.63	0.3	 -     	 -     	19	16	 -     	 -     		-0.13	2.63
87.75	20.08	18.64	-0.1	1	 -     	19	16	32 046.67	 -     		1.08	2.64
88	19.5	18.47	-0.1	 -     	 -     	19	16	 -     	 -     		0.5	2.47
88.25	17.45	18.38	-0.1	 -     	 -     	19	16	 -     	 -     		-1.55	2.38
88.5	21.4	18.47	-0.1	1	 -     	19	16	32 046.67	 -     		2.4	2.47
88.75	19.66	18.43	-0.4	 -     	 -     	19	16	 -     	 -     		0.66	2.43
89	17.55	18.19	-0.4	 -     	 -     	19	16	 -     	 -     		-1.45	2.19
89.25	21.54	18.2	-0.4	1	 -     	19	16	32 046.67	 -     		2.54	2.2
89.5	19.72	18.18	-0.4	 -     	 -     	19	16	 -     	 -     		0.72	2.18
89.75	17.57	18.14	-0.3	 -     	 -     	19	16	 -     	 -     		-1.43	2.14
90	21.66	18.07	-0.3	1	 -     	19	16	32 046.67	 -     		2.66	2.07
90.25	19.85	17.97	-0.3	 -     	 -     	16	16	 -     	 -     		3.85	1.97
90.5	17.65	17.94	-0.3	 -     	 -     	16	16	 -     	 -     		1.65	1.94
90.75	18.13	17.94	-0.3	 -     	 -     	16	16	 -     	 -     		2.13	1.94
91	18.17	17.8	-0.3	 -     	 -     	16	16	 -     	 -     		2.17	1.8
91.25	18.24	17.75	-0.3	 -     	 -     	16	16	 -     	 -     		2.24	1.75
91.5	18.23	17.77	-0.3	 -     	 -     	16	16	 -     	 -     		2.23	1.77
91.75	18.22	17.76	-0.5	 -     	 -     	16	16	 -     	 -     		2.22	1.76
92	17.97	17.6	-0.5	 -     	 -     	16	16	 -     	 -     		1.97	1.6
92.25	17.87	17.55	-0.5	 -     	 -     	16	16	 -     	 -     		1.87	1.55
92.5	17.89	17.56	-0.5	 -     	 -     	16	16	 -     	 -     		1.89	1.56
92.75	17.9	17.56	-0.3	 -     	 -     	16	16	 -     	 -     		1.9	1.56
93	17.71	17.42	-0.3	 -     	 -     	16	16	 -     	 -     		1.71	1.42
93.25	17.63	17.37	-0.3	 -     	 -     	16	16	 -     	 -     		1.63	1.37
93.5	17.65	17.38	-0.3	 -     	 -     	16	16	 -     	 -     		1.65	1.38
93.75	17.64	17.38	-0.3	 -     	 -     	16	16	 -     	 -     		1.64	1.38
94	17.47	17.24	-0.3	 -     	 -     	16	16	 -     	 -     		1.47	1.24
94.25	17.4	17.19	-0.3	 -     	 -     	16	16	 -     	 -     		1.4	1.19
94.5	17.41	17.21	-0.3	 -     	 -     	16	16	 -     	 -     		1.41	1.21
94.75	17.41	17.21	-0.2	 -     	 -     	16	16	 -     	 -     		1.41	1.21
95	17.25	17.07	-0.2	 -     	 -     	16	16	 -     	 -     		1.25	1.07
95.25	17.19	17.03	-0.2	 -     	 -     	16	16	 -     	 -     		1.19	1.03
95.5	17.2	17.04	-0.2	 -     	 -     	16	16	 -     	 -     		1.2	1.04
95.75	17.2	17.03	-0.3	 -     	 -     	16	16	 -     	 -     		1.2	1.03
96	17.04	16.9	-0.3	 -     	 -     	16	16	 -     	 -     		1.04	0.9
96.25	16.98	16.86	-0.3	 -     	 -     	16	16	 -     	 -     		0.98	0.86
96.5	16.99	16.87	-0.3	 -     	 -     	16	16	 -     	 -     		0.99	0.87
96.75	16.99	16.86	-0.3	 -     	 -     	16	16	 -     	 -     		0.99	0.86
97	16.84	16.74	-0.3	 -     	 -     	16	16	 -     	 -     		0.84	0.74
97.25	16.78	16.69	-0.3	 -     	 -     	16	16	 -     	 -     		0.78	0.69
97.5	16.79	16.7	-0.3	 -     	 -     	16	16	 -     	 -     		0.79	0.7
97.75	16.77	16.68	-1	 -     	 -     	16	16	 -     	 -     		0.77	0.68
98	16.61	16.54	-1	 -     	 -     	16	16	 -     	 -     		0.61	0.54
98.25	16.56	16.5	-1	 -     	 -     	16	16	 -     	 -     		0.56	0.5
98.5	16.57	16.51	-1	 -     	 -     	16	16	 -     	 -     		0.57	0.51
98.75	16.57	16.51	-1	 -     	 -     	16	16	 -     	 -     		0.57	0.51
99	16.42	16.38	-1	 -     	 -     	16	16	 -     	 -     		0.42	0.38
99.25	16.37	16.34	-1	 -     	 -     	16	16	 -     	 -     		0.37	0.34
99.5	16.38	16.35	-1	 -     	 -     	16	16	 -     	 -     		0.38	0.35
99.75	16.36	16.33	-1.5	 -     	 -     	16	16	 -     	 -     		0.36	0.33
100	16.21	16.2	-1.5	 -     	 -     	16	16	 -     	 -     		0.21	0.2
100.25	16.16	16.15	-1.5	 -     	 -     	16	16	 -     	 -     		0.16	0.15
100.5	16.17	16.16	-1.5	 -     	 -     	16	16	 -     	 -     		0.17	0.16
100.75	16.15	16.14	-2.2	 -     	 -     	16	16	 -     	 -     		0.15	0.14
101	15.99	16	-2.2	 -     	 -     	16	16	 -     	 -     		-0.01	0
101.25	19.45	16.04	-2.2	1	 -     	16	16	32 046.67	 -     		3.45	0.04
101.5	17.74	16.01	-2.2	 -     	 -     	16	16	 -     	 -     		1.74	0.01
101.75	15.56	15.96	-2.4	 -     	 -     	16	16	 -     	 -     		-0.44	-0.04
102	19.84	19.12	-2.4	1	1	16	16	32 046.67	32 046.67		3.84	3.12
102.25	18.08	17.39	-2.4	 -     	 -     	16	16	 -     	 -     		2.08	1.39
102.5	15.86	15.39	-2.4	 -     	 -     	16	16	 -     	 -     		-0.14	-0.61
102.75	19.91	19.21	-2.6	1	1	16	16	32 046.67	32 046.67		3.91	3.21
103	18.61	17.88	-2.6	 -     	 -     	16	16	 -     	 -     		2.61	1.88
103.25	16.62	16.1	-2.6	 -     	 -     	16	16	 -     	 -     		0.62	0.1
103.5	17.05	16.59	-2.6	 -     	 -     	16	16	 -     	 -     		1.05	0.59
103.75	16.96	16.46	-2.6	 -     	 -     	16	16	 -     	 -     		0.96	0.46
104	16.82	16.32	-2.6	 -     	 -     	16	16	 -     	 -     		0.82	0.32
104.25	16.86	19.51	-2.6	 -     	1	16	19	 -     	32 046.67		0.86	0.51
104.5	16.87	17.91	-2.6	 -     	 -     	16	19	 -     	 -     		0.87	-1.09
104.75	16.87	19.13	-2.7	 -     	1	16	19	 -     	32 046.67		0.87	0.13
105	16.7	18.49	-2.7	 -     	 -     	16	19	 -     	 -     		0.7	-0.51
105.25	16.67	19.74	-2.7	 -     	1	16	19	 -     	32 046.67		0.67	0.74
105.5	16.64	18.63	-2.7	 -     	 -     	16	19	 -     	 -     		0.64	-0.37
105.75	16.7	19.74	-1.9	 -     	1	16	19	 -     	32 046.67		0.7	0.74
106	16.56	19.13	-1.9	 -     	 -     	16	19	 -     	 -     		0.56	0.13
106.25	16.47	17.16	-1.9	 -     	 -     	16	19	 -     	 -     		0.47	-1.84
106.5	16.56	20.92	-1.9	 -     	1	16	19	 -     	32 046.67		0.56	1.92
106.75	16.56	19.13	-1	 -     	 -     	16	19	 -     	 -     		0.56	0.13
107	16.41	17.38	-1	 -     	 -     	16	19	 -     	 -     		0.41	-1.62
107.25	16.46	21.18	-1	 -     	1	16	19	 -     	32 046.67		0.46	2.18
107.5	16.45	19.37	-1	 -     	 -     	16	19	 -     	 -     		0.45	0.37
107.75	16.44	17.47	-0.6	 -     	 -     	16	19	 -     	 -     		0.44	-1.53
108	16.45	21.33	-0.6	 -     	1	16	19	 -     	32 046.67		0.45	2.33
108.25	16.39	19.57	-0.6	 -     	 -     	16	19	 -     	 -     		0.39	0.57
108.5	16.37	17.64	-0.6	 -     	 -     	16	19	 -     	 -     		0.37	-1.36
108.75	16.47	21.4	 -     	 -     	1	16	19	 -     	32 046.67		0.47	2.4
109	16.4	20.04	 -     	 -     	 -     	16	19	 -     	 -     		0.4	1.04
109.25	16.33	18.27	 -     	 -     	 -     	16	19	 -     	 -     		0.33	-0.73
109.5	16.41	21.96	 -     	 -     	1	16	19	 -     	32 046.67		0.41	2.96
109.75	16.37	20.16	0.2	 -     	 -     	16	19	 -     	 -     		0.37	1.16
110	16.26	18.4	0.2	 -     	 -     	16	19	 -     	 -     		0.26	-0.6
110.25	19.78	19.01	0.2	1	 -     	19	16	32 046.67	 -     		0.78	3.01
110.5	18.09	18.77	0.2	 -     	 -     	19	16	 -     	 -     		-0.91	2.77
110.75	19.45	18.86	0.5	1	 -     	19	16	32 046.67	 -     		0.45	2.86
111	18.88	18.62	0.5	 -     	 -     	19	16	 -     	 -     		-0.12	2.62
111.25	20.4	18.6	0.5	1	 -     	19	16	32 046.67	 -     		1.4	2.6
111.5	19.21	18.6	0.5	 -     	 -     	19	16	 -     	 -     		0.21	2.6
111.75	16.96	18.54	0.2	 -     	 -     	19	16	 -     	 -     		-2.04	2.54
112	21.29	18.48	0.2	1	 -     	19	16	32 046.67	 -     		2.29	2.48
112.25	19.58	18.39	0.2	 -     	 -     	19	16	 -     	 -     		0.58	2.39
112.5	17.41	18.36	0.2	 -     	 -     	19	16	 -     	 -     		-1.59	2.36
112.75	21.53	18.47	 -     	1	 -     	19	16	32 046.67	 -     		2.53	2.47
113	19.97	18.22	 -     	 -     	 -     	19	16	 -     	 -     		0.97	2.22
113.25	17.89	18.1	 -     	 -     	 -     	19	16	 -     	 -     		-1.11	2.1
113.5	21.84	18.2	 -     	1	 -     	19	16	32 046.67	 -     		2.84	2.2
113.75	20.03	18.16	-0.1	 -     	 -     	19	16	 -     	 -     		1.03	2.16
114	18.04	17.96	-0.1	 -     	 -     	19	16	 -     	 -     		-0.96	1.96
114.25	18.53	17.92	-0.1	 -     	 -     	16	16	 -     	 -     		2.53	1.92
114.5	18.39	17.93	-0.1	 -     	 -     	16	16	 -     	 -     		2.39	1.93
114.75	18.42	17.93	-0.1	 -     	 -     	16	16	 -     	 -     		2.42	1.93
115	18.13	17.76	-0.1	 -     	 -     	16	16	 -     	 -     		2.13	1.76
115.25	18.03	17.7	-0.1	 -     	 -     	16	16	 -     	 -     		2.03	1.7
115.5	18.05	17.72	-0.1	 -     	 -     	16	16	 -     	 -     		2.05	1.72
115.75	18.04	17.71	-0.3	 -     	 -     	16	16	 -     	 -     		2.04	1.71
116	17.84	17.56	-0.3	 -     	 -     	16	16	 -     	 -     		1.84	1.56
116.25	17.76	17.5	-0.3	 -     	 -     	16	16	 -     	 -     		1.76	1.5
116.5	17.78	17.52	-0.3	 -     	 -     	16	16	 -     	 -     		1.78	1.52
116.75	17.77	17.52	-0.3	 -     	 -     	16	16	 -     	 -     		1.77	1.52
117	17.59	17.37	-0.3	 -     	 -     	16	16	 -     	 -     		1.59	1.37
117.25	17.52	17.32	-0.3	 -     	 -     	16	16	 -     	 -     		1.52	1.32
117.5	17.54	17.34	-0.3	 -     	 -     	16	16	 -     	 -     		1.54	1.34
117.75	17.53	17.33	-0.4	 -     	 -     	16	16	 -     	 -     		1.53	1.33
118	17.36	17.19	-0.4	 -     	 -     	16	16	 -     	 -     		1.36	1.19
118.25	17.29	17.14	-0.4	 -     	 -     	16	16	 -     	 -     		1.29	1.14
118.5	17.31	17.15	-0.4	 -     	 -     	16	16	 -     	 -     		1.31	1.15
118.75	17.3	17.15	-0.5	 -     	 -     	16	16	 -     	 -     		1.3	1.15
119	17.14	17.01	-0.5	 -     	 -     	16	16	 -     	 -     		1.14	1.01
119.25	17.08	16.96	-0.5	 -     	 -     	16	16	 -     	 -     		1.08	0.96
119.5	17.09	16.98	-0.5	 -     	 -     	16	16	 -     	 -     		1.09	0.98
119.75	17.09	16.97	-0.5	 -     	 -     	16	16	 -     	 -     		1.09	0.97
120	16.93	16.84	-0.5	 -     	 -     	16	16	 -     	 -     		0.93	0.84
120.25	16.88	16.79	-0.5	 -     	 -     	16	16	 -     	 -     		0.88	0.79
120.5	16.89	16.81	-0.5	 -     	 -     	16	16	 -     	 -     		0.89	0.81
120.75	16.89	16.81	-0.4	 -     	 -     	16	16	 -     	 -     		0.89	0.81
121	16.74	16.68	-0.4	 -     	 -     	16	16	 -     	 -     		0.74	0.68
121.25	16.69	16.63	-0.4	 -     	 -     	16	16	 -     	 -     		0.69	0.63
121.5	16.7	16.65	-0.4	 -     	 -     	16	16	 -     	 -     		0.7	0.65
121.75	16.69	16.64	-0.5	 -     	 -     	16	16	 -     	 -     		0.69	0.64
122	16.55	16.51	-0.5	 -     	 -     	16	16	 -     	 -     		0.55	0.51
122.25	16.49	16.47	-0.5	 -     	 -     	16	16	 -     	 -     		0.49	0.47
122.5	16.51	16.48	-0.5	 -     	 -     	16	16	 -     	 -     		0.51	0.48
122.75	16.51	16.48	-0.4	 -     	 -     	16	16	 -     	 -     		0.51	0.48
123	16.37	16.36	-0.4	 -     	 -     	16	16	 -     	 -     		0.37	0.36
123.25	16.32	16.31	-0.4	 -     	 -     	16	16	 -     	 -     		0.32	0.31
123.5	16.33	16.33	-0.4	 -     	 -     	16	16	 -     	 -     		0.33	0.33
123.75	16.32	16.32	-0.6	 -     	 -     	16	16	 -     	 -     		0.32	0.32
124	16.18	16.19	-0.6	 -     	 -     	16	16	 -     	 -     		0.18	0.19
124.25	16.13	16.15	-0.6	 -     	 -     	16	16	 -     	 -     		0.13	0.15
124.5	16.14	16.16	-0.6	 -     	 -     	16	16	 -     	 -     		0.14	0.16
124.75	16.13	16.15	-0.8	 -     	 -     	16	16	 -     	 -     		0.13	0.15
125	15.99	16.03	-0.8	 -     	 -     	16	16	 -     	 -     		-0.01	0.03
125.25	19.45	16.06	-0.8	1	 -     	16	16	32 046.67	 -     		3.45	0.06
125.5	17.75	16.04	-0.8	 -     	 -     	16	16	 -     	 -     		1.75	0.04
125.75	15.58	16	-0.4	 -     	 -     	16	16	 -     	 -     		-0.42	0
126	19.82	15.99	-0.4	1	 -     	16	16	32 046.67	 -     		3.82	-0.01
126.25	18.17	19.12	-0.4	 -     	1	16	16	 -     	32 046.67		2.17	3.12
126.5	15.95	17.42	-0.4	 -     	 -     	16	16	 -     	 -     		-0.05	1.42
126.75	19.89	15.53	-0.4	1	 -     	16	16	32 046.67	 -     		3.89	-0.47
127	18.71	19.49	-0.4	 -     	1	16	16	 -     	32 046.67		2.71	3.49
127.25	16.72	17.72	-0.4	 -     	 -     	16	16	 -     	 -     		0.72	1.72
127.5	17.1	15.78	-0.4	 -     	 -     	16	16	 -     	 -     		1.1	-0.22
127.75	17.09	19.53	-0.3	 -     	1	16	16	 -     	32 046.67		1.09	3.53
128	16.91	18.17	-0.3	 -     	 -     	16	16	 -     	 -     		0.91	2.17
128.25	16.81	16.41	-0.3	 -     	 -     	16	16	 -     	 -     		0.81	0.41
128.5	16.83	16.9	-0.3	 -     	 -     	16	16	 -     	 -     		0.83	0.9
128.75	16.84	16.77	-0.1	 -     	 -     	16	16	 -     	 -     		0.84	0.77
129	16.66	16.63	-0.1	 -     	 -     	16	16	 -     	 -     		0.66	0.63
129.25	16.6	16.56	-0.1	 -     	 -     	16	16	 -     	 -     		0.6	0.56
129.5	16.62	16.59	-0.1	 -     	 -     	16	16	 -     	 -     		0.62	0.59
129.75	16.63	16.59	-0.1	 -     	 -     	16	16	 -     	 -     		0.63	0.59
130	16.5	16.46	-0.1	 -     	 -     	16	16	 -     	 -     		0.5	0.46
130.25	16.45	16.41	-0.1	 -     	 -     	16	16	 -     	 -     		0.45	0.41
130.5	16.48	16.44	-0.1	 -     	 -     	16	16	 -     	 -     		0.48	0.44
130.75	16.46	16.42	-0.5	 -     	 -     	16	16	 -     	 -     		0.46	0.42
131	16.34	16.3	-0.5	 -     	 -     	16	16	 -     	 -     		0.34	0.3
131.25	16.31	16.27	-0.5	 -     	 -     	16	16	 -     	 -     		0.31	0.27
131.5	16.33	16.29	-0.5	 -     	 -     	16	16	 -     	 -     		0.33	0.29
131.75	16.37	16.32	0.2	 -     	 -     	16	16	 -     	 -     		0.37	0.32
132	16.29	16.24	0.2	 -     	 -     	16	16	 -     	 -     		0.29	0.24
132.25	16.27	16.2	0.2	 -     	 -     	16	16	 -     	 -     		0.27	0.2
132.5	16.3	16.22	0.2	 -     	 -     	16	16	 -     	 -     		0.3	0.22
132.75	16.38	16.24	1	 -     	 -     	16	16	 -     	 -     		0.38	0.24
133	16.38	16.18	1	 -     	 -     	16	16	 -     	 -     		0.38	0.18
133.25	16.41	16.16	1	 -     	 -     	16	16	 -     	 -     		0.41	0.16
133.5	16.52	16.18	1	 -     	 -     	16	16	 -     	 -     		0.52	0.18
133.75	16.57	16.16	0.3	 -     	 -     	16	16	 -     	 -     		0.57	0.16
134	16.66	16.1	0.3	 -     	 -     	16	16	 -     	 -     		0.66	0.1
134.25	16.72	16.08	0.3	 -     	 -     	16	16	 -     	 -     		0.72	0.08
134.5	16.73	16.09	0.3	 -     	 -     	16	16	 -     	 -     		0.73	0.09
134.75	16.7	16.07	 -     	 -     	 -     	16	16	 -     	 -     		0.7	0.07
135	16.75	16	 -     	 -     	 -     	16	16	 -     	 -     		0.75	0
135.25	16.76	15.98	 -     	 -     	 -     	16	16	 -     	 -     		0.76	-0.02
135.5	16.8	19.18	 -     	 -     	1	16	16	 -     	32 046.67		0.8	3.18
135.75	16.7	17.46	-1.3	 -     	 -     	16	16	 -     	 -     		0.7	1.46
136	16.66	15.75	-1.3	 -     	 -     	16	16	 -     	 -     		0.66	-0.25
136.25	16.7	19.58	-1.3	 -     	1	16	16	 -     	32 046.67		0.7	3.58
136.5	16.57	17.72	-1.3	 -     	 -     	16	16	 -     	 -     		0.57	1.72
136.75	16.53	15.78	-2.1	 -     	 -     	16	16	 -     	 -     		0.53	-0.22
137	16.32	19.6	-2.1	 -     	1	16	16	 -     	32 046.67		0.32	3.6
137.25	16.18	17.83	-2.1	 -     	 -     	16	16	 -     	 -     		0.18	1.83
137.5	16.16	15.9	-2.1	 -     	 -     	16	16	 -     	 -     		0.16	-0.1
137.75	16.17	19.57	-4	 -     	1	16	16	 -     	32 046.67		0.17	3.57
138	15.97	18.13	-4	 -     	 -     	16	16	 -     	 -     		-0.03	2.13
138.25	19.38	16.45	-4	1	 -     	16	16	32 046.67	 -     		3.38	0.45
138.5	17.67	16.92	-4	 -     	 -     	16	16	 -     	 -     		1.67	0.92
138.75	15.5	16.74	-4	 -     	 -     	16	16	 -     	 -     		-0.5	0.74
139	19.68	16.66	-4	1	 -     	16	16	32 046.67	 -     		3.68	0.66
139.25	17.93	16.54	-4	 -     	 -     	16	16	 -     	 -     		1.93	0.54
139.5	15.78	16.52	-4	 -     	 -     	16	16	 -     	 -     		-0.22	0.52
139.75	19.7	16.55	-5.4	1	 -     	16	16	32 046.67	 -     		3.7	0.55
140	18.34	16.33	-5.4	 -     	 -     	16	16	 -     	 -     		2.34	0.33
140.25	16.38	16.23	-5.4	 -     	 -     	16	16	 -     	 -     		0.38	0.23
140.5	16.82	16.25	-5.4	 -     	 -     	16	16	 -     	 -     		0.82	0.25
140.75	16.74	16.26	-4.9	 -     	 -     	16	16	 -     	 -     		0.74	0.26
141	16.54	16.09	-4.9	 -     	 -     	16	16	 -     	 -     		0.54	0.09
141.25	16.44	16.02	-4.9	 -     	 -     	16	16	 -     	 -     		0.44	0.02
141.5	16.46	16.04	-4.9	 -     	 -     	16	16	 -     	 -     		0.46	0.04
141.75	16.49	16.07	-3.8	 -     	 -     	16	16	 -     	 -     		0.49	0.07
142	16.3	15.92	-3.8	 -     	 -     	16	16	 -     	 -     		0.3	-0.08
142.25	16.29	19.05	-3.8	 -     	1	16	16	 -     	32 046.67		0.29	3.05
142.5	16.28	17.41	-3.8	 -     	 -     	16	16	 -     	 -     		0.28	1.41
142.75	16.25	15.46	-3.2	 -     	 -     	16	16	 -     	 -     		0.25	-0.54
143	16.18	19.39	-3.2	 -     	1	16	16	 -     	32 046.67		0.18	3.39
143.25	16.08	17.63	-3.2	 -     	 -     	16	16	 -     	 -     		0.08	1.63
143.5	16.05	15.7	-3.2	 -     	 -     	16	16	 -     	 -     		0.05	-0.3
143.75	16.13	19.44	-3	 -     	1	16	16	 -     	32 046.67		0.13	3.44
144	15.97	18.06	-3	 -     	 -     	16	16	 -     	 -     		-0.03	2.06
144.25	19.37	16.37	-3	1	 -     	16	16	32 046.67	 -     		3.37	0.37
144.5	17.68	16.82	-3	 -     	 -     	16	16	 -     	 -     		1.68	0.82
144.75	15.51	16.65	-2.6	 -     	 -     	16	16	 -     	 -     		-0.49	0.65
145	19.71	16.59	-2.6	1	 -     	16	16	32 046.67	 -     		3.71	0.59
145.25	17.98	16.48	-2.6	 -     	 -     	16	16	 -     	 -     		1.98	0.48
145.5	15.8	16.45	-2.6	 -     	 -     	16	16	 -     	 -     		-0.2	0.45
145.75	19.79	16.54	-2.1	1	 -     	16	16	32 046.67	 -     		3.79	0.54
146	18.5	16.37	-2.1	 -     	 -     	16	16	 -     	 -     		2.5	0.37
146.25	16.53	16.27	-2.1	 -     	 -     	16	16	 -     	 -     		0.53	0.27
146.5	16.96	16.29	-2.1	 -     	 -     	16	16	 -     	 -     		0.96	0.29
146.75	16.86	16.28	-2.2	 -     	 -     	16	16	 -     	 -     		0.86	0.28
147	16.66	16.12	-2.2	 -     	 -     	16	16	 -     	 -     		0.66	0.12
147.25	16.58	16.06	-2.2	 -     	 -     	16	16	 -     	 -     		0.58	0.06
147.5	16.6	16.08	-2.2	 -     	 -     	16	16	 -     	 -     		0.6	0.08
147.75	16.59	16.07	-2.4	 -     	 -     	16	16	 -     	 -     		0.59	0.07
148	16.39	15.92	-2.4	 -     	 -     	16	16	 -     	 -     		0.39	-0.08
148.25	16.39	19.06	-2.4	 -     	1	16	16	 -     	32 046.67		0.39	3.06
148.5	16.37	17.41	-2.4	 -     	 -     	16	16	 -     	 -     		0.37	1.41
148.75	16.31	15.43	-2.8	 -     	 -     	16	16	 -     	 -     		0.31	-0.57
149	16.23	19.35	-2.8	 -     	1	16	16	 -     	32 046.67		0.23	3.35
149.25	16.14	17.61	-2.8	 -     	 -     	16	16	 -     	 -     		0.14	1.61
149.5	16.1	15.67	-2.8	 -     	 -     	16	16	 -     	 -     		0.1	-0.33
149.75	16.17	19.39	-3.1	 -     	1	16	16	 -     	32 046.67		0.17	3.39
150	16	18.01	-3.1	 -     	 -     	16	16	 -     	 -     		0	2.01
150.25	19.4	16.32	-3.1	1	 -     	16	16	32 046.67	 -     		3.4	0.32
150.5	17.71	16.77	-3.1	 -     	 -     	16	16	 -     	 -     		1.71	0.77
150.75	15.52	16.59	-3.2	 -     	 -     	16	16	 -     	 -     		-0.48	0.59
151	19.71	16.52	-3.2	1	 -     	16	16	32 046.67	 -     		3.71	0.52
151.25	17.98	16.41	-3.2	 -     	 -     	16	16	 -     	 -     		1.98	0.41
151.5	15.81	16.38	-3.2	 -     	 -     	16	16	 -     	 -     		-0.19	0.38
151.75	19.78	16.46	-3.2	1	 -     	16	16	32 046.67	 -     		3.78	0.46
152	18.64	16.3	-3.2	 -     	 -     	16	16	 -     	 -     		2.64	0.3
152.25	16.73	16.22	-3.2	 -     	 -     	16	16	 -     	 -     		0.73	0.22
152.5	17.15	16.25	-3.2	 -     	 -     	16	16	 -     	 -     		1.15	0.25
152.75	17.03	16.24	-3.3	 -     	 -     	16	16	 -     	 -     		1.03	0.24
153	16.88	16.1	-3.3	 -     	 -     	16	16	 -     	 -     		0.88	0.1
153.25	16.79	16.05	-3.3	 -     	 -     	16	16	 -     	 -     		0.79	0.05
153.5	16.8	16.07	-3.3	 -     	 -     	16	16	 -     	 -     		0.8	0.07
153.75	16.79	16.07	-3.3	 -     	 -     	16	16	 -     	 -     		0.79	0.07
154	16.6	15.93	-3.3	 -     	 -     	16	16	 -     	 -     		0.6	-0.07
154.25	16.6	19.08	-3.3	 -     	1	16	16	 -     	32 046.67		0.6	3.08
154.5	16.58	17.43	-3.3	 -     	 -     	16	16	 -     	 -     		0.58	1.43
154.75	16.53	15.48	-3.1	 -     	 -     	16	16	 -     	 -     		0.53	-0.52
155	16.48	19.43	-3.1	 -     	1	16	16	 -     	32 046.67		0.48	3.43
155.25	16.41	17.7	-3.1	 -     	 -     	16	16	 -     	 -     		0.41	1.7
155.5	16.37	15.75	-3.1	 -     	 -     	16	16	 -     	 -     		0.37	-0.25
155.75	16.45	19.49	-2.9	 -     	1	16	16	 -     	32 046.67		0.45	3.49
156	16.32	18.14	-2.9	 -     	 -     	16	16	 -     	 -     		0.32	2.14
156.25	16.23	16.38	-2.9	 -     	 -     	16	16	 -     	 -     		0.23	0.38
156.5	16.24	16.88	-2.9	 -     	 -     	16	16	 -     	 -     		0.24	0.88
156.75	16.24	16.74	-2.8	 -     	 -     	16	16	 -     	 -     		0.24	0.74
157	16.11	16.6	-2.8	 -     	 -     	16	16	 -     	 -     		0.11	0.6
157.25	16.06	16.53	-2.8	 -     	 -     	16	16	 -     	 -     		0.06	0.53
157.5	16.07	16.55	-2.8	 -     	 -     	16	16	 -     	 -     		0.07	0.55
157.75	16.08	16.56	-2.3	 -     	 -     	16	16	 -     	 -     		0.08	0.56
158	15.96	16.41	-2.3	 -     	 -     	16	16	 -     	 -     		-0.04	0.41
158.25	19.41	16.42	-2.3	1	 -     	16	16	32 046.67	 -     		3.41	0.42
158.5	17.7	16.4	-2.3	 -     	 -     	16	16	 -     	 -     		1.7	0.4
158.75	15.53	16.35	-2.1	 -     	 -     	16	16	 -     	 -     		-0.47	0.35
159	19.77	16.31	-2.1	1	 -     	16	16	32 046.67	 -     		3.77	0.31
159.25	18.04	16.23	-2.1	 -     	 -     	16	16	 -     	 -     		2.04	0.23
159.5	15.89	16.19	-2.1	 -     	 -     	16	16	 -     	 -     		-0.11	0.19
159.75	19.87	16.27	-2.1	1	 -     	16	16	32 046.67	 -     		3.87	0.27
160	18.6	16.13	-2.1	 -     	 -     	16	16	 -     	 -     		2.6	0.13
160.25	16.66	16.05	-2.1	 -     	 -     	16	16	 -     	 -     		0.66	0.05
160.5	17.09	16.06	-2.1	 -     	 -     	16	16	 -     	 -     		1.09	0.06
160.75	16.96	16.04	-2.3	 -     	 -     	16	16	 -     	 -     		0.96	0.04
161	16.73	15.88	-2.3	 -     	 -     	16	16	 -     	 -     		0.73	-0.12
161.25	16.71	19.02	-2.3	 -     	1	16	16	 -     	32 046.67		0.71	3.02
161.5	16.7	17.37	-2.3	 -     	 -     	16	16	 -     	 -     		0.7	1.37
161.75	16.65	15.41	-2.3	 -     	 -     	16	16	 -     	 -     		0.65	-0.59
162	16.54	19.33	-2.3	 -     	1	16	16	 -     	32 046.67		0.54	3.33
162.25	16.44	17.58	-2.3	 -     	 -     	16	16	 -     	 -     		0.44	1.58
162.5	16.41	15.64	-2.3	 -     	 -     	16	16	 -     	 -     		0.41	-0.36
162.75	16.49	19.38	-2.3	 -     	1	16	16	 -     	32 046.67		0.49	3.38
163	16.31	18	-2.3	 -     	 -     	16	16	 -     	 -     		0.31	2
163.25	16.21	16.24	-2.3	 -     	 -     	16	16	 -     	 -     		0.21	0.24
163.5	16.23	16.73	-2.3	 -     	 -     	16	16	 -     	 -     		0.23	0.73
163.75	16.22	16.59	-2.4	 -     	 -     	16	16	 -     	 -     		0.22	0.59
164	16.05	16.42	-2.4	 -     	 -     	16	16	 -     	 -     		0.05	0.42
164.25	15.98	16.34	-2.4	 -     	 -     	16	16	 -     	 -     		-0.02	0.34
164.5	19.5	16.44	-2.4	1	 -     	16	16	32 046.67	 -     		3.5	0.44
164.75	17.78	16.39	-2.5	 -     	 -     	16	16	 -     	 -     		1.78	0.39
165	15.84	16.19	-2.5	 -     	 -     	16	16	 -     	 -     		-0.16	0.19
165.25	19.9	16.21	-2.5	1	 -     	16	16	32 046.67	 -     		3.9	0.21
165.5	18.07	16.19	-2.5	 -     	 -     	16	16	 -     	 -     		2.07	0.19
165.75	15.91	16.14	-2.6	 -     	 -     	16	16	 -     	 -     		-0.09	0.14
166	20.04	16.08	-2.6	1	 -     	16	16	32 046.67	 -     		4.04	0.08
166.25	18.28	15.99	-2.6	 -     	 -     	16	16	 -     	 -     		2.28	-0.01
166.5	16.19	19.15	-2.6	 -     	1	16	16	 -     	32 046.67		0.19	3.15
166.75	16.63	17.5	-2.5	 -     	 -     	16	16	 -     	 -     		0.63	1.5
167	16.66	15.75	-2.5	 -     	 -     	16	16	 -     	 -     		0.66	-0.25
167.25	16.83	19.56	-2.5	 -     	1	16	16	 -     	32 046.67		0.83	3.56
167.5	16.78	17.73	-2.5	 -     	 -     	16	16	 -     	 -     		0.78	1.73
167.75	16.74	15.81	-2.6	 -     	 -     	16	16	 -     	 -     		0.74	-0.19
168	16.59	19.65	-2.6	 -     	1	16	16	 -     	32 046.67		0.59	3.65
168.25	16.48	17.88	-2.6	 -     	 -     	16	16	 -     	 -     		0.48	1.88
168.5	16.45	15.95	-2.6	 -     	 -     	16	16	 -     	 -     		0.45	-0.05
168.75	16.52	19.68	-2.6	 -     	1	16	16	 -     	32 046.67		0.52	3.68
169	16.34	18.29	-2.6	 -     	 -     	16	16	 -     	 -     		0.34	2.29
169.25	16.23	16.51	-2.6	 -     	 -     	16	16	 -     	 -     		0.23	0.51
169.5	16.25	17.01	-2.6	 -     	 -     	16	16	 -     	 -     		0.25	1.01
169.75	16.24	16.86	-3	 -     	 -     	16	16	 -     	 -     		0.24	0.86
170	16.05	16.67	-3	 -     	 -     	16	16	 -     	 -     		0.05	0.67
170.25	15.99	16.58	-3	 -     	 -     	16	16	 -     	 -     		-0.01	0.58
170.5	19.5	16.68	-3	1	 -     	16	16	32 046.67	 -     		3.5	0.68
170.75	17.77	16.62	-3.6	 -     	 -     	16	16	 -     	 -     		1.77	0.62
171	15.81	16.4	-3.6	 -     	 -     	16	16	 -     	 -     		-0.19	0.4
171.25	19.87	16.42	-3.6	1	 -     	16	16	32 046.67	 -     		3.87	0.42
171.5	18.04	16.4	-3.6	 -     	 -     	16	16	 -     	 -     		2.04	0.4
171.75	15.88	16.35	-3.6	 -     	 -     	16	16	 -     	 -     		-0.12	0.35
172	20	16.27	-3.6	1	 -     	16	16	32 046.67	 -     		4	0.27
172.25	18.24	16.18	-3.6	 -     	 -     	16	16	 -     	 -     		2.24	0.18
172.5	16.08	16.15	-3.6	 -     	 -     	16	16	 -     	 -     		0.08	0.15
172.75	16.55	16.16	-3.5	 -     	 -     	16	16	 -     	 -     		0.55	0.16
173	16.61	16.01	-3.5	 -     	 -     	16	16	 -     	 -     		0.61	0.01
173.25	16.68	15.96	-3.5	 -     	 -     	16	16	 -     	 -     		0.68	-0.04
173.5	16.74	19.17	-3.5	 -     	1	16	16	 -     	32 046.67		0.74	3.17
173.75	16.71	17.5	-3.5	 -     	 -     	16	16	 -     	 -     		0.71	1.5
174	16.44	15.72	-3.5	 -     	 -     	16	16	 -     	 -     		0.44	-0.28
174.25	16.44	19.53	-3.5	 -     	1	16	16	 -     	32 046.67		0.44	3.53
174.5	16.42	17.7	-3.5	 -     	 -     	16	16	 -     	 -     		0.42	1.7
174.75	16.37	15.78	-3.6	 -     	 -     	16	16	 -     	 -     		0.37	-0.22
175	16.27	19.62	-3.6	 -     	1	16	16	 -     	32 046.67		0.27	3.62
175.25	16.17	17.85	-3.6	 -     	 -     	16	16	 -     	 -     		0.17	1.85
175.5	16.14	15.92	-3.6	 -     	 -     	16	16	 -     	 -     		0.14	-0.08
175.75	16.23	19.66	-3.3	 -     	1	16	16	 -     	32 046.67		0.23	3.66
176	16.06	18.27	-3.3	 -     	 -     	16	16	 -     	 -     		0.06	2.27
176.25	16.11	19.76	-3.3	 -     	1	16	19	 -     	32 046.67		0.11	0.76
176.5	16.06	18.63	-3.3	 -     	 -     	16	19	 -     	 -     		0.06	-0.37
176.75	16.12	19.73	-3	 -     	1	16	19	 -     	32 046.67		0.12	0.73
177	16.05	19.1	-3	 -     	 -     	16	19	 -     	 -     		0.05	0.1
177.25	16	17.14	-3	 -     	 -     	16	19	 -     	 -     		0	-1.86
177.5	19.61	20.97	-3	1	1	16	19	32 046.67	32 046.67		3.61	1.97
177.75	17.88	19.14	-2.5	 -     	 -     	16	19	 -     	 -     		1.88	0.14
178	15.97	17.35	-2.5	 -     	 -     	16	19	 -     	 -     		-0.03	-1.65
178.25	20.14	21.22	-2.5	1	1	16	19	32 046.67	32 046.67		4.14	2.22
178.5	18.23	19.36	-2.5	 -     	 -     	16	19	 -     	 -     		2.23	0.36
178.75	16.05	17.43	-1.7	 -     	 -     	16	19	 -     	 -     		0.05	-1.57
179	16.84	21.3	-1.7	 -     	1	16	19	 -     	32 046.67		0.84	2.3
179.25	16.79	19.53	-1.7	 -     	 -     	16	19	 -     	 -     		0.79	0.53
179.5	16.75	17.6	-1.7	 -     	 -     	16	19	 -     	 -     		0.75	-1.4
179.75	16.86	21.37	-0.7	 -     	1	16	19	 -     	32 046.67		0.86	2.37
180	16.71	20.02	-0.7	 -     	 -     	16	19	 -     	 -     		0.71	1.02
180.25	16.62	18.25	-0.7	 -     	 -     	16	19	 -     	 -     		0.62	-0.75
180.5	16.7	21.94	-0.7	 -     	1	16	19	 -     	32 046.67		0.7	2.94
180.75	16.67	20.15	-0.3	 -     	 -     	16	19	 -     	 -     		0.67	1.15
181	16.53	18.39	-0.3	 -     	 -     	16	19	 -     	 -     		0.53	-0.61
181.25	16.56	22.17	-0.3	 -     	1	16	19	 -     	32 046.67		0.56	3.17
181.5	16.53	20.33	-0.3	 -     	 -     	16	19	 -     	 -     		0.53	1.33
181.75	16.47	18.41	-0.3	 -     	 -     	16	19	 -     	 -     		0.47	-0.59
182	16.45	22.24	-0.3	 -     	1	16	19	 -     	32 046.67		0.45	3.24
182.25	19.92	20.48	-0.3	1	 -     	19	16	32 046.67	 -     		0.92	4.48
182.5	18.19	18.48	-0.3	 -     	 -     	19	16	 -     	 -     		-0.81	2.48
182.75	19.5	19.05	-0.3	1	 -     	19	16	32 046.67	 -     		0.5	3.05
183	18.87	19	-0.3	 -     	 -     	19	16	 -     	 -     		-0.13	3
183.25	20.32	19.12	-0.3	1	 -     	19	16	32 046.67	 -     		1.32	3.12
183.5	19.04	19.06	-0.3	 -     	 -     	19	16	 -     	 -     		0.04	3.06
183.75	16.76	19.01	-0.2	 -     	 -     	19	16	 -     	 -     		-2.24	3.01
184	20.98	18.87	-0.2	1	 -     	19	16	32 046.67	 -     		1.98	2.87
184.25	19.24	18.75	-0.2	 -     	 -     	19	16	 -     	 -     		0.24	2.75
184.5	17.08	18.73	-0.2	 -     	 -     	19	16	 -     	 -     		-1.92	2.73
184.75	21.05	18.8	 -     	1	 -     	19	16	32 046.67	 -     		2.05	2.8
185	19.72	18.6	 -     	 -     	 -     	19	16	 -     	 -     		0.72	2.6
185.25	17.74	18.5	 -     	 -     	 -     	19	16	 -     	 -     		-1.26	2.5
185.5	21.68	18.6	 -     	1	 -     	19	16	32 046.67	 -     		2.68	2.6
185.75	19.89	18.57	0.6	 -     	 -     	19	16	 -     	 -     		0.89	2.57
186	17.92	18.38	0.6	 -     	 -     	19	16	 -     	 -     		-1.08	2.38
186.25	18.42	18.33	0.6	 -     	 -     	16	16	 -     	 -     		2.42	2.33
186.5	18.27	18.34	0.6	 -     	 -     	16	16	 -     	 -     		2.27	2.34
186.75	18.3	18.34	0.6	 -     	 -     	16	16	 -     	 -     		2.3	2.34
187	18.03	18.17	0.6	 -     	 -     	16	16	 -     	 -     		2.03	2.17
187.25	17.93	18.11	0.6	 -     	 -     	16	16	 -     	 -     		1.93	2.11
187.5	17.95	18.13	0.6	 -     	 -     	16	16	 -     	 -     		1.95	2.13
187.75	17.94	18.12	0.5	 -     	 -     	16	16	 -     	 -     		1.94	2.12
188	17.75	17.96	0.5	 -     	 -     	16	16	 -     	 -     		1.75	1.96
188.25	17.68	17.91	0.5	 -     	 -     	16	16	 -     	 -     		1.68	1.91
188.5	17.69	17.92	0.5	 -     	 -     	16	16	 -     	 -     		1.69	1.92
188.75	17.68	17.91	0.3	 -     	 -     	16	16	 -     	 -     		1.68	1.91
189	17.51	17.76	0.3	 -     	 -     	16	16	 -     	 -     		1.51	1.76
189.25	17.44	17.71	0.3	 -     	 -     	16	16	 -     	 -     		1.44	1.71
189.5	17.45	17.73	0.3	 -     	 -     	16	16	 -     	 -     		1.45	1.73
189.75	17.45	17.72	0.3	 -     	 -     	16	16	 -     	 -     		1.45	1.72
190	17.29	17.58	0.3	 -     	 -     	16	16	 -     	 -     		1.29	1.58
190.25	17.22	17.53	0.3	 -     	 -     	16	16	 -     	 -     		1.22	1.53
190.5	17.24	17.54	0.3	 -     	 -     	16	16	 -     	 -     		1.24	1.54
190.75	17.24	17.54	0.5	 -     	 -     	16	16	 -     	 -     		1.24	1.54
191	17.09	17.41	0.5	 -     	 -     	16	16	 -     	 -     		1.09	1.41
191.25	17.03	17.36	0.5	 -     	 -     	16	16	 -     	 -     		1.03	1.36
191.5	17.04	17.37	0.5	 -     	 -     	16	16	 -     	 -     		1.04	1.37
191.75	17.04	17.37	0.6	 -     	 -     	16	16	 -     	 -     		1.04	1.37
192	16.9	17.24	0.6	 -     	 -     	16	16	 -     	 -     		0.9	1.24
192.25	16.84	17.19	0.6	 -     	 -     	16	16	 -     	 -     		0.84	1.19
192.5	16.85	17.21	0.6	 -     	 -     	16	16	 -     	 -     		0.85	1.21
192.75	16.85	17.2	0.5	 -     	 -     	16	16	 -     	 -     		0.85	1.2
193	16.7	17.07	0.5	 -     	 -     	16	16	 -     	 -     		0.7	1.07
193.25	16.65	17.02	0.5	 -     	 -     	16	16	 -     	 -     		0.65	1.02
193.5	16.66	17.03	0.5	 -     	 -     	16	16	 -     	 -     		0.66	1.03
193.75	16.66	17.03	0.5	 -     	 -     	16	16	 -     	 -     		0.66	1.03
194	16.52	16.9	0.5	 -     	 -     	16	16	 -     	 -     		0.52	0.9
194.25	16.47	16.86	0.5	 -     	 -     	16	16	 -     	 -     		0.47	0.86
194.5	16.48	16.87	0.5	 -     	 -     	16	16	 -     	 -     		0.48	0.87
194.75	16.48	16.87	0.5	 -     	 -     	16	16	 -     	 -     		0.48	0.87
195	16.34	16.74	0.5	 -     	 -     	16	16	 -     	 -     		0.34	0.74
195.25	16.29	16.69	0.5	 -     	 -     	16	16	 -     	 -     		0.29	0.69
195.5	16.3	16.71	0.5	 -     	 -     	16	16	 -     	 -     		0.3	0.71
195.75	16.3	16.7	0.5	 -     	 -     	16	16	 -     	 -     		0.3	0.7
196	16.17	16.58	0.5	 -     	 -     	16	16	 -     	 -     		0.17	0.58
196.25	16.12	16.54	0.5	 -     	 -     	16	16	 -     	 -     		0.12	0.54
196.5	16.13	16.55	0.5	 -     	 -     	16	16	 -     	 -     		0.13	0.55
196.75	16.13	16.54	0.4	 -     	 -     	16	16	 -     	 -     		0.13	0.54
197	16	16.42	0.4	 -     	 -     	16	16	 -     	 -     		0	0.42
197.25	19.46	16.45	0.4	1	 -     	16	16	32 046.67	 -     		3.46	0.45
197.5	17.75	16.43	0.4	 -     	 -     	16	16	 -     	 -     		1.75	0.43
197.75	15.57	16.38	0.5	 -     	 -     	16	16	 -     	 -     		-0.43	0.38
198	19.82	16.36	0.5	1	 -     	16	16	32 046.67	 -     		3.82	0.36
198.25	18.09	16.29	0.5	 -     	 -     	16	16	 -     	 -     		2.09	0.29
198.5	15.91	16.26	0.5	 -     	 -     	16	16	 -     	 -     		-0.09	0.26
198.75	19.89	16.34	0.5	1	 -     	16	16	32 046.67	 -     		3.89	0.34
199	18.62	16.21	0.5	 -     	 -     	16	16	 -     	 -     		2.62	0.21
199.25	16.66	16.14	0.5	 -     	 -     	16	16	 -     	 -     		0.66	0.14
199.5	17.08	16.15	0.5	 -     	 -     	16	16	 -     	 -     		1.08	0.15
199.75	16.99	16.15	0.5	 -     	 -     	16	16	 -     	 -     		0.99	0.15
200	16.85	16.04	0.5	 -     	 -     	16	16	 -     	 -     		0.85	0.04
200.25	16.93	19.28	0.5	 -     	1	16	19	 -     	32 046.67		0.93	0.28
200.5	16.9	17.67	0.5	 -     	 -     	16	19	 -     	 -     		0.9	-1.33
200.75	16.93	18.9	0.7	 -     	1	16	19	 -     	32 046.67		0.93	-0.1
201	16.9	21.53	0.7	 -     	1	16	19	 -     	32 046.67		0.9	2.53
201.25	16.81	17.94	0.7	 -     	 -     	16	19	 -     	 -     		0.81	-1.06
201.5	16.86	19.72	0.7	 -     	1	16	19	 -     	32 046.67		0.86	0.72
201.75	16.8	18.46	0.8	 -     	 -     	16	19	 -     	 -     		0.8	-0.54
202	16.73	20.14	0.8	 -     	1	16	19	 -     	32 046.67		0.73	1.14
202.25	16.67	19.25	0.8	 -     	 -     	16	19	 -     	 -     		0.67	0.25
202.5	16.62	17.07	0.8	 -     	 -     	16	19	 -     	 -     		0.62	-1.93
202.75	16.72	20.9	1.6	 -     	1	16	19	 -     	32 046.67		0.72	1.9
203	16.61	19.47	1.6	 -     	 -     	16	19	 -     	 -     		0.61	0.47
203.25	16.53	17.68	1.6	 -     	 -     	16	19	 -     	 -     		0.53	-1.32
203.5	16.62	21.38	1.6	 -     	1	16	19	 -     	32 046.67		0.62	2.38
203.75	16.59	19.6	1.7	 -     	 -     	16	19	 -     	 -     		0.59	0.6
204	16.47	17.84	1.7	 -     	 -     	16	19	 -     	 -     		0.47	-1.16
204.25	16.51	21.64	1.7	 -     	1	16	19	 -     	32 046.67		0.51	2.64
204.5	16.49	19.82	1.7	 -     	 -     	16	19	 -     	 -     		0.49	0.82
204.75	16.45	17.9	2.2	 -     	 -     	16	19	 -     	 -     		0.45	-1.1
205	16.46	21.77	2.2	 -     	1	16	19	 -     	32 046.67		0.46	2.77
205.25	16.4	20.01	2.2	 -     	 -     	16	19	 -     	 -     		0.4	1.01
205.5	16.37	18.07	2.2	 -     	 -     	16	19	 -     	 -     		0.37	-0.93
205.75	16.45	21.82	2.3	 -     	1	16	19	 -     	32 046.67		0.45	2.82
206	16.35	20.44	2.3	 -     	 -     	16	19	 -     	 -     		0.35	1.44
206.25	19.83	18.69	2.3	1	 -     	19	16	32 046.67	 -     		0.83	2.69
206.5	18.14	19.1	2.3	 -     	 -     	19	16	 -     	 -     		-0.86	3.1
206.75	19.47	19.01	2.4	1	 -     	19	16	32 046.67	 -     		0.47	3.01
207	18.85	18.85	2.4	 -     	 -     	19	16	 -     	 -     		-0.15	2.85
207.25	20.3	18.81	2.4	1	 -     	19	16	32 046.67	 -     		1.3	2.81
207.5	19.02	18.79	2.4	 -     	 -     	19	16	 -     	 -     		0.02	2.79
207.75	16.73	18.73	2.5	 -     	 -     	19	16	 -     	 -     		-2.27	2.73
208	20.98	18.64	2.5	1	 -     	19	16	32 046.67	 -     		1.98	2.64
208.25	19.24	18.54	2.5	 -     	 -     	19	16	 -     	 -     		0.24	2.54
208.5	17.05	18.51	2.5	 -     	 -     	19	16	 -     	 -     		-1.95	2.51
208.75	21.02	18.57	2.1	1	 -     	19	16	32 046.67	 -     		2.02	2.57
209	19.71	18.39	2.1	 -     	 -     	19	16	 -     	 -     		0.71	2.39
209.25	17.74	18.3	2.1	 -     	 -     	19	16	 -     	 -     		-1.26	2.3
209.5	21.68	18.39	2.1	1	 -     	19	16	32 046.67	 -     		2.68	2.39
209.75	19.86	18.34	1.5	 -     	 -     	19	16	 -     	 -     		0.86	2.34
210	17.88	18.14	1.5	 -     	 -     	19	16	 -     	 -     		-1.12	2.14
210.25	18.38	18.1	1.5	 -     	 -     	16	16	 -     	 -     		2.38	2.1
210.5	18.24	18.11	1.5	 -     	 -     	16	16	 -     	 -     		2.24	2.11
210.75	18.27	18.11	1.5	 -     	 -     	16	16	 -     	 -     		2.27	2.11
211	18.01	17.95	1.5	 -     	 -     	16	16	 -     	 -     		2.01	1.95
211.25	17.91	17.9	1.5	 -     	 -     	16	16	 -     	 -     		1.91	1.9
211.5	17.93	17.91	1.5	 -     	 -     	16	16	 -     	 -     		1.93	1.91
211.75	17.92	17.91	1.4	 -     	 -     	16	16	 -     	 -     		1.92	1.91
212	17.74	17.76	1.4	 -     	 -     	16	16	 -     	 -     		1.74	1.76
212.25	17.67	17.71	1.4	 -     	 -     	16	16	 -     	 -     		1.67	1.71
212.5	17.68	17.72	1.4	 -     	 -     	16	16	 -     	 -     		1.68	1.72
212.75	17.68	17.72	1.4	 -     	 -     	16	16	 -     	 -     		1.68	1.72
213	17.51	17.58	1.4	 -     	 -     	16	16	 -     	 -     		1.51	1.58
213.25	17.45	17.53	1.4	 -     	 -     	16	16	 -     	 -     		1.45	1.53
213.5	17.46	17.55	1.4	 -     	 -     	16	16	 -     	 -     		1.46	1.55
213.75	17.45	17.54	1.2	 -     	 -     	16	16	 -     	 -     		1.45	1.54
214	17.29	17.4	1.2	 -     	 -     	16	16	 -     	 -     		1.29	1.4
214.25	17.23	17.36	1.2	 -     	 -     	16	16	 -     	 -     		1.23	1.36
214.5	17.25	17.37	1.2	 -     	 -     	16	16	 -     	 -     		1.25	1.37
214.75	17.24	17.36	1.2	 -     	 -     	16	16	 -     	 -     		1.24	1.36
215	17.09	17.24	1.2	 -     	 -     	16	16	 -     	 -     		1.09	1.24
215.25	17.04	17.19	1.2	 -     	 -     	16	16	 -     	 -     		1.04	1.19
215.5	17.05	17.2	1.2	 -     	 -     	16	16	 -     	 -     		1.05	1.2
215.75	17.04	17.19	1	 -     	 -     	16	16	 -     	 -     		1.04	1.19
216	16.89	17.06	1	 -     	 -     	16	16	 -     	 -     		0.89	1.06
216.25	16.84	17.02	1	 -     	 -     	16	16	 -     	 -     		0.84	1.02
216.5	16.85	17.03	1	 -     	 -     	16	16	 -     	 -     		0.85	1.03
216.75	16.85	17.03	1	 -     	 -     	16	16	 -     	 -     		0.85	1.03
217	16.71	16.9	1	 -     	 -     	16	16	 -     	 -     		0.71	0.9
217.25	16.66	16.86	1	 -     	 -     	16	16	 -     	 -     		0.66	0.86
217.5	16.67	16.87	1	 -     	 -     	16	16	 -     	 -     		0.67	0.87
217.75	16.66	16.86	0.9	 -     	 -     	16	16	 -     	 -     		0.66	0.86
218	16.53	16.74	0.9	 -     	 -     	16	16	 -     	 -     		0.53	0.74
218.25	16.48	16.7	0.9	 -     	 -     	16	16	 -     	 -     		0.48	0.7
218.5	16.49	16.71	0.9	 -     	 -     	16	16	 -     	 -     		0.49	0.71
218.75	16.48	16.7	0.7	 -     	 -     	16	16	 -     	 -     		0.48	0.7
219	16.34	16.57	0.7	 -     	 -     	16	16	 -     	 -     		0.34	0.57
219.25	16.29	16.53	0.7	 -     	 -     	16	16	 -     	 -     		0.29	0.53
219.5	16.3	16.54	0.7	 -     	 -     	16	16	 -     	 -     		0.3	0.54
219.75	16.3	16.54	0.7	 -     	 -     	16	16	 -     	 -     		0.3	0.54
220	16.17	16.42	0.7	 -     	 -     	16	16	 -     	 -     		0.17	0.42
220.25	16.12	16.38	0.7	 -     	 -     	16	16	 -     	 -     		0.12	0.38
220.5	16.13	16.39	0.7	 -     	 -     	16	16	 -     	 -     		0.13	0.39
220.75	16.14	16.39	1	 -     	 -     	16	16	 -     	 -     		0.14	0.39
221	16.02	16.28	1	 -     	 -     	16	16	 -     	 -     		0.02	0.28
221.25	15.97	16.24	1	 -     	 -     	16	16	 -     	 -     		-0.03	0.24
221.5	19.5	16.32	1	1	 -     	16	16	32 046.67	 -     		3.5	0.32
221.75	17.78	16.29	1.2	 -     	 -     	16	16	 -     	 -     		1.78	0.29
222	15.88	16.16	1.2	 -     	 -     	16	16	 -     	 -     		-0.12	0.16
222.25	19.96	16.2	1.2	1	 -     	16	16	32 046.67	 -     		3.96	0.2
222.5	18.12	16.18	1.2	 -     	 -     	16	16	 -     	 -     		2.12	0.18
222.75	15.97	16.14	1.5	 -     	 -     	16	16	 -     	 -     		-0.03	0.14
223	20.15	16.13	1.5	1	 -     	16	16	32 046.67	 -     		4.15	0.13
223.25	18.41	16.06	1.5	 -     	 -     	16	16	 -     	 -     		2.41	0.06
223.5	16.23	16.02	1.5	 -     	 -     	16	16	 -     	 -     		0.23	0.02
223.75	16.71	16.03	1.8	 -     	 -     	16	16	 -     	 -     		0.71	0.03
224	16.83	15.95	1.8	 -     	 -     	16	16	 -     	 -     		0.83	-0.05
224.25	17.05	19.19	1.8	 -     	1	16	19	 -     	32 046.67		1.05	0.19
224.5	16.98	17.57	1.8	 -     	 -     	16	19	 -     	 -     		0.98	-1.43
224.75	17.02	18.81	2	 -     	1	16	19	 -     	32 046.67		1.02	-0.19
225	16.96	21.44	2	 -     	1	16	19	 -     	32 046.67		0.96	2.44
225.25	16.86	17.85	2	 -     	 -     	16	19	 -     	 -     		0.86	-1.15
225.5	16.93	19.64	2	 -     	1	16	19	 -     	32 046.67		0.93	0.64
225.75	16.9	18.38	2.2	 -     	 -     	16	19	 -     	 -     		0.9	-0.62
226	16.84	20.08	2.2	 -     	1	16	19	 -     	32 046.67		0.84	1.08
226.25	16.77	19.19	2.2	 -     	 -     	16	19	 -     	 -     		0.77	0.19
226.5	16.72	17.01	2.2	 -     	 -     	16	19	 -     	 -     		0.72	-1.99
226.75	16.82	20.84	2.5	 -     	1	16	19	 -     	32 046.67		0.82	1.84
227	16.71	19.42	2.5	 -     	 -     	16	19	 -     	 -     		0.71	0.42
227.25	16.63	17.64	2.5	 -     	 -     	16	19	 -     	 -     		0.63	-1.36
227.5	16.7	21.32	2.5	 -     	1	16	19	 -     	32 046.67		0.7	2.32
227.75	16.69	19.54	3	 -     	 -     	16	19	 -     	 -     		0.69	0.54
228	16.58	17.81	3	 -     	 -     	16	19	 -     	 -     		0.58	-1.19
228.25	16.63	21.61	3	 -     	1	16	19	 -     	32 046.67		0.63	2.61
228.5	16.59	19.77	3	 -     	 -     	16	19	 -     	 -     		0.59	0.77
228.75	16.54	17.84	2.8	 -     	 -     	16	19	 -     	 -     		0.54	-1.16
229	16.55	21.72	2.8	 -     	1	16	19	 -     	32 046.67		0.55	2.72
229.25	16.51	19.96	2.8	 -     	 -     	16	19	 -     	 -     		0.51	0.96
229.5	16.49	18.03	2.8	 -     	 -     	16	19	 -     	 -     		0.49	-0.97
229.75	16.57	21.78	2.9	 -     	1	16	19	 -     	32 046.67		0.57	2.78
230	16.5	20.42	2.9	 -     	 -     	16	19	 -     	 -     		0.5	1.42
230.25	19.98	18.67	2.9	1	 -     	19	16	32 046.67	 -     		0.98	2.67
230.5	18.28	19.08	2.9	 -     	 -     	19	16	 -     	 -     		-0.72	3.08
230.75	19.59	18.97	2.8	1	 -     	19	16	32 046.67	 -     		0.59	2.97
231	18.98	18.81	2.8	 -     	 -     	19	16	 -     	 -     		-0.02	2.81
231.25	20.43	18.77	2.8	1	 -     	19	16	32 046.67	 -     		1.43	2.77
231.5	19.14	18.75	2.8	 -     	 -     	19	16	 -     	 -     		0.14	2.75
231.75	16.84	18.68	2.4	 -     	 -     	19	16	 -     	 -     		-2.16	2.68
232	21.09	18.59	2.4	1	 -     	19	16	32 046.67	 -     		2.09	2.59
232.25	19.37	18.5	2.4	 -     	 -     	19	16	 -     	 -     		0.37	2.5
232.5	17.19	18.47	2.4	 -     	 -     	19	16	 -     	 -     		-1.81	2.47
232.75	21.15	18.52	2.1	1	 -     	19	16	32 046.67	 -     		2.15	2.52
233	19.83	18.34	2.1	 -     	 -     	19	16	 -     	 -     		0.83	2.34
233.25	17.86	18.25	2.1	 -     	 -     	19	16	 -     	 -     		-1.14	2.25
233.5	21.79	18.35	2.1	1	 -     	19	16	32 046.67	 -     		2.79	2.35
233.75	19.99	18.31	2.2	 -     	 -     	19	16	 -     	 -     		0.99	2.31
234	18.02	18.13	2.2	 -     	 -     	19	16	 -     	 -     		-0.98	2.13
234.25	18.52	18.09	2.2	 -     	 -     	16	16	 -     	 -     		2.52	2.09
234.5	18.38	18.1	2.2	 -     	 -     	16	16	 -     	 -     		2.38	2.1
234.75	18.41	18.09	2.2	 -     	 -     	16	16	 -     	 -     		2.41	2.09
235	18.15	17.94	2.2	 -     	 -     	16	16	 -     	 -     		2.15	1.94
235.25	18.05	17.89	2.2	 -     	 -     	16	16	 -     	 -     		2.05	1.89
235.5	18.07	17.9	2.2	 -     	 -     	16	16	 -     	 -     		2.07	1.9
235.75	18.05	17.88	1.5	 -     	 -     	16	16	 -     	 -     		2.05	1.88
236	17.85	17.73	1.5	 -     	 -     	16	16	 -     	 -     		1.85	1.73
236.25	17.79	17.68	1.5	 -     	 -     	16	16	 -     	 -     		1.79	1.68
236.5	17.8	17.7	1.5	 -     	 -     	16	16	 -     	 -     		1.8	1.7
236.75	17.79	17.69	1.3	 -     	 -     	16	16	 -     	 -     		1.79	1.69
237	17.62	17.55	1.3	 -     	 -     	16	16	 -     	 -     		1.62	1.55
237.25	17.56	17.5	1.3	 -     	 -     	16	16	 -     	 -     		1.56	1.5
237.5	17.57	17.51	1.3	 -     	 -     	16	16	 -     	 -     		1.57	1.51
237.75	17.57	17.51	1.5	 -     	 -     	16	16	 -     	 -     		1.57	1.51
238	17.42	17.39	1.5	 -     	 -     	16	16	 -     	 -     		1.42	1.39
238.25	17.36	17.34	1.5	 -     	 -     	16	16	 -     	 -     		1.36	1.34
238.5	17.37	17.35	1.5	 -     	 -     	16	16	 -     	 -     		1.37	1.35
238.75	17.37	17.35	1.6	 -     	 -     	16	16	 -     	 -     		1.37	1.35
239	17.22	17.22	1.6	 -     	 -     	16	16	 -     	 -     		1.22	1.22
239.25	17.17	17.18	1.6	 -     	 -     	16	16	 -     	 -     		1.17	1.18
239.5	17.18	17.19	1.6	 -     	 -     	16	16	 -     	 -     		1.18	1.19
239.75	17.18	17.19	1.6	 -     	 -     	16	16	 -     	 -     		1.18	1.19
240	17.04	17.06	1.6	 -     	 -     	16	16	 -     	 -     		1.04	1.06
240.25	16.98	17.02	1.6	 -     	 -     	16	16	 -     	 -     		0.98	1.02
240.5	16.99	17.03	1.6	 -     	 -     	16	16	 -     	 -     		0.99	1.03
240.75	16.99	17.03	1.5	 -     	 -     	16	16	 -     	 -     		0.99	1.03
241	16.85	16.9	1.5	 -     	 -     	16	16	 -     	 -     		0.85	0.9
241.25	16.8	16.86	1.5	 -     	 -     	16	16	 -     	 -     		0.8	0.86
241.5	16.81	16.87	1.5	 -     	 -     	16	16	 -     	 -     		0.81	0.87
241.75	16.8	16.86	1.3	 -     	 -     	16	16	 -     	 -     		0.8	0.86
242	16.66	16.74	1.3	 -     	 -     	16	16	 -     	 -     		0.66	0.74
242.25	16.61	16.7	1.3	 -     	 -     	16	16	 -     	 -     		0.61	0.7
242.5	16.62	16.71	1.3	 -     	 -     	16	16	 -     	 -     		0.62	0.71
242.75	16.62	16.7	1.2	 -     	 -     	16	16	 -     	 -     		0.62	0.7
243	16.49	16.58	1.2	 -     	 -     	16	16	 -     	 -     		0.49	0.58
243.25	16.44	16.54	1.2	 -     	 -     	16	16	 -     	 -     		0.44	0.54
243.5	16.45	16.55	1.2	 -     	 -     	16	16	 -     	 -     		0.45	0.55
243.75	16.44	16.55	1.1	 -     	 -     	16	16	 -     	 -     		0.44	0.55
244	16.31	16.43	1.1	 -     	 -     	16	16	 -     	 -     		0.31	0.43
244.25	16.26	16.39	1.1	 -     	 -     	16	16	 -     	 -     		0.26	0.39
244.5	16.27	16.4	1.1	 -     	 -     	16	16	 -     	 -     		0.27	0.4
244.75	16.27	16.4	1.1	 -     	 -     	16	16	 -     	 -     		0.27	0.4
245	16.14	16.28	1.1	 -     	 -     	16	16	 -     	 -     		0.14	0.28
245.25	16.1	16.24	1.1	 -     	 -     	16	16	 -     	 -     		0.1	0.24
245.5	16.11	16.25	1.1	 -     	 -     	16	16	 -     	 -     		0.11	0.25
245.75	16.1	16.24	1	 -     	 -     	16	16	 -     	 -     		0.1	0.24
246	15.98	16.13	1	 -     	 -     	16	16	 -     	 -     		-0.02	0.13
246.25	19.44	16.16	1	1	 -     	16	16	32 046.67	 -     		3.44	0.16
246.5	17.74	16.14	1	 -     	 -     	16	16	 -     	 -     		1.74	0.14
246.75	15.54	16.08	0.8	 -     	 -     	16	16	 -     	 -     		-0.46	0.08
247	19.79	16.07	0.8	1	 -     	16	16	32 046.67	 -     		3.79	0.07
247.25	18.07	16	0.8	 -     	 -     	16	16	 -     	 -     		2.07	0
247.5	15.88	15.96	0.8	 -     	 -     	16	16	 -     	 -     		-0.12	-0.04
247.75	19.94	19.24	0.6	1	1	16	16	32 046.67	32 046.67		3.94	3.24
248	18.72	17.76	0.6	 -     	 -     	16	16	 -     	 -     		2.72	1.76
248.25	16.84	19.1	0.6	 -     	1	16	19	 -     	32 046.67		0.84	0.1
248.5	17.25	18.01	0.6	 -     	 -     	16	19	 -     	 -     		1.25	-0.99
248.75	17.18	19.1	0.8	 -     	1	16	19	 -     	32 046.67		1.18	0.1
249	17.05	18.56	0.8	 -     	 -     	16	19	 -     	 -     		1.05	-0.44
249.25	17.02	19.82	0.8	 -     	1	16	19	 -     	32 046.67		1.02	0.82
249.5	17	18.7	0.8	 -     	 -     	16	19	 -     	 -     		1	-0.3
249.75	17.03	19.79	0.8	 -     	1	16	19	 -     	32 046.67		1.03	0.79
250	16.88	19.19	0.8	 -     	 -     	16	19	 -     	 -     		0.88	0.19
250.25	16.8	17.23	0.8	 -     	 -     	16	19	 -     	 -     		0.8	-1.77
250.5	16.88	20.98	0.8	 -     	1	16	19	 -     	32 046.67		0.88	1.98
250.75	16.85	19.17	0.8	 -     	 -     	16	19	 -     	 -     		0.85	0.17
251	16.7	17.43	0.8	 -     	 -     	16	19	 -     	 -     		0.7	-1.57
251.25	16.74	21.23	0.8	 -     	1	16	19	 -     	32 046.67		0.74	2.23
251.5	16.72	19.4	0.8	 -     	 -     	16	19	 -     	 -     		0.72	0.4
251.75	16.67	17.48	0.6	 -     	 -     	16	19	 -     	 -     		0.67	-1.52
252	16.65	21.34	0.6	 -     	1	16	19	 -     	32 046.67		0.65	2.34
252.25	16.58	19.58	0.6	 -     	 -     	16	19	 -     	 -     		0.58	0.58
252.5	16.55	17.64	0.6	 -     	 -     	16	19	 -     	 -     		0.55	-1.36
252.75	16.64	21.39	0.8	 -     	1	16	19	 -     	32 046.67		0.64	2.39
253	16.56	20.03	0.8	 -     	 -     	16	19	 -     	 -     		0.56	1.03
253.25	16.52	18.27	0.8	 -     	 -     	16	19	 -     	 -     		0.52	-0.73
253.5	16.63	21.97	0.8	 -     	1	16	19	 -     	32 046.67		0.63	2.97
253.75	16.66	20.19	0.9	 -     	 -     	16	19	 -     	 -     		0.66	1.19
254	16.61	18.44	0.9	 -     	 -     	16	19	 -     	 -     		0.61	-0.56
254.25	20.18	19.06	0.9	1	 -     	19	16	32 046.67	 -     		1.18	3.06
254.5	18.56	18.83	0.9	 -     	 -     	19	16	 -     	 -     		-0.44	2.83
254.75	19.91	18.91	0.5	1	 -     	19	16	32 046.67	 -     		0.91	2.91
255	19.42	18.69	0.5	 -     	 -     	19	16	 -     	 -     		0.42	2.69
255.25	17.43	18.59	0.5	 -     	 -     	19	16	 -     	 -     		-1.57	2.59
255.5	21.38	18.68	0.5	1	 -     	19	16	32 046.67	 -     		2.38	2.68
255.75	19.54	18.62	0.2	 -     	 -     	19	16	 -     	 -     		0.54	2.62
256	17.76	18.45	0.2	 -     	 -     	19	16	 -     	 -     		-1.24	2.45
256.25	21.85	18.48	0.2	1	 -     	19	16	32 046.67	 -     		2.85	2.48
256.5	19.93	18.44	0.2	 -     	 -     	19	16	 -     	 -     		0.93	2.44
256.75	17.73	18.35	-0.5	 -     	 -     	19	16	 -     	 -     		-1.27	2.35
257	21.7	18.23	-0.5	1	 -     	19	16	32 046.67	 -     		2.7	2.23
257.25	19.9	18.13	-0.5	 -     	 -     	19	16	 -     	 -     		0.9	2.13
257.5	17.74	18.1	-0.5	 -     	 -     	19	16	 -     	 -     		-1.26	2.1
257.75	21.69	18.16	-1.1	1	 -     	19	16	32 046.67	 -     		2.69	2.16
258	20.34	17.98	-1.1	 -     	 -     	19	16	 -     	 -     		1.34	1.98
258.25	18.32	17.88	-1.1	 -     	 -     	16	16	 -     	 -     		2.32	1.88
258.5	18.72	17.9	-1.1	 -     	 -     	16	16	 -     	 -     		2.72	1.9
258.75	18.64	17.9	-1.1	 -     	 -     	16	16	 -     	 -     		2.64	1.9
259	18.41	17.73	-1.1	 -     	 -     	16	16	 -     	 -     		2.41	1.73
259.25	18.31	17.67	-1.1	 -     	 -     	16	16	 -     	 -     		2.31	1.67
259.5	18.33	17.69	-1.1	 -     	 -     	16	16	 -     	 -     		2.33	1.69
259.75	18.32	17.68	-1.3	 -     	 -     	16	16	 -     	 -     		2.32	1.68
260	18.09	17.52	-1.3	 -     	 -     	16	16	 -     	 -     		2.09	1.52
260.25	18.01	17.47	-1.3	 -     	 -     	16	16	 -     	 -     		2.01	1.47
260.5	18.03	17.48	-1.3	 -     	 -     	16	16	 -     	 -     		2.03	1.48
260.75	18.02	17.48	-1.2	 -     	 -     	16	16	 -     	 -     		2.02	1.48
261	17.83	17.33	-1.2	 -     	 -     	16	16	 -     	 -     		1.83	1.33
261.25	17.76	17.28	-1.2	 -     	 -     	16	16	 -     	 -     		1.76	1.28
261.5	17.77	17.29	-1.2	 -     	 -     	16	16	 -     	 -     		1.77	1.29
261.75	17.77	17.29	-1.3	 -     	 -     	16	16	 -     	 -     		1.77	1.29
262	17.58	17.14	-1.3	 -     	 -     	16	16	 -     	 -     		1.58	1.14
262.25	17.51	17.09	-1.3	 -     	 -     	16	16	 -     	 -     		1.51	1.09
262.5	17.53	17.1	-1.3	 -     	 -     	16	16	 -     	 -     		1.53	1.1
262.75	17.52	17.09	-1.6	 -     	 -     	16	16	 -     	 -     		1.52	1.09
263	17.34	16.95	-1.6	 -     	 -     	16	16	 -     	 -     		1.34	0.95
263.25	17.27	16.9	-1.6	 -     	 -     	16	16	 -     	 -     		1.27	0.9
263.5	17.29	16.91	-1.6	 -     	 -     	16	16	 -     	 -     		1.29	0.91
263.75	17.28	16.9	-1.9	 -     	 -     	16	16	 -     	 -     		1.28	0.9
264	17.1	16.76	-1.9	 -     	 -     	16	16	 -     	 -     		1.1	0.76
264.25	17.04	16.71	-1.9	 -     	 -     	16	16	 -     	 -     		1.04	0.71
264.5	17.06	16.72	-1.9	 -     	 -     	16	16	 -     	 -     		1.06	0.72
264.75	17.04	16.71	-2.2	 -     	 -     	16	16	 -     	 -     		1.04	0.71
265	16.88	16.57	-2.2	 -     	 -     	16	16	 -     	 -     		0.88	0.57
265.25	16.82	16.52	-2.2	 -     	 -     	16	16	 -     	 -     		0.82	0.52
265.5	16.83	16.53	-2.2	 -     	 -     	16	16	 -     	 -     		0.83	0.53
265.75	16.83	16.53	-2.2	 -     	 -     	16	16	 -     	 -     		0.83	0.53
266	16.67	16.39	-2.2	 -     	 -     	16	16	 -     	 -     		0.67	0.39
266.25	16.61	16.34	-2.2	 -     	 -     	16	16	 -     	 -     		0.61	0.34
266.5	16.62	16.36	-2.2	 -     	 -     	16	16	 -     	 -     		0.62	0.36
266.75	16.62	16.35	-2.2	 -     	 -     	16	16	 -     	 -     		0.62	0.35
267	16.46	16.22	-2.2	 -     	 -     	16	16	 -     	 -     		0.46	0.22
267.25	16.4	16.17	-2.2	 -     	 -     	16	16	 -     	 -     		0.4	0.17
267.5	16.42	16.18	-2.2	 -     	 -     	16	16	 -     	 -     		0.42	0.18
267.75	16.41	16.18	-2.3	 -     	 -     	16	16	 -     	 -     		0.41	0.18
268	16.26	16.04	-2.3	 -     	 -     	16	16	 -     	 -     		0.26	0.04
268.25	16.2	16	-2.3	 -     	 -     	16	16	 -     	 -     		0.2	0
268.5	16.29	19.21	-2.3	 -     	1	16	16	 -     	32 046.67		0.29	3.21
268.75	16.25	17.54	-2.4	 -     	 -     	16	16	 -     	 -     		0.25	1.54
269	16.08	15.79	-2.4	 -     	 -     	16	16	 -     	 -     		0.08	-0.21
269.25	16.11	19.61	-2.4	 -     	1	16	16	 -     	32 046.67		0.11	3.61
269.5	16.08	17.77	-2.4	 -     	 -     	16	16	 -     	 -     		0.08	1.77
269.75	16.04	15.86	-2.4	 -     	 -     	16	16	 -     	 -     		0.04	-0.14
270	15.99	19.72	-2.4	 -     	1	16	16	 -     	32 046.67		-0.01	3.72
270.25	19.41	18.03	-2.4	1	 -     	16	16	32 046.67	 -     		3.41	2.03
270.5	17.66	16.06	-2.4	 -     	 -     	16	16	 -     	 -     		1.66	0.06
270.75	15.48	16.56	-2.4	 -     	 -     	16	16	 -     	 -     		-0.52	0.56
271	19.72	16.65	-2.4	1	 -     	16	16	32 046.67	 -     		3.72	0.65
271.25	18	16.71	-2.4	 -     	 -     	16	16	 -     	 -     		2	0.71
271.5	15.82	16.64	-2.4	 -     	 -     	16	16	 -     	 -     		-0.18	0.64
271.75	19.79	16.72	-2.7	1	 -     	16	16	32 046.67	 -     		3.79	0.72
272	18.55	16.52	-2.7	 -     	 -     	16	16	 -     	 -     		2.55	0.52
272.25	16.71	19.68	-2.7	 -     	1	16	19	 -     	32 046.67		0.71	0.68
272.5	17.1	18.08	-2.7	 -     	 -     	16	19	 -     	 -     		1.1	-0.92
272.75	17.02	19.3	-2.8	 -     	1	16	19	 -     	32 046.67		1.02	0.3
273	16.87	18.67	-2.8	 -     	 -     	16	19	 -     	 -     		0.87	-0.33
273.25	16.85	19.92	-2.8	 -     	1	16	19	 -     	32 046.67		0.85	0.92
273.5	16.83	18.81	-2.8	 -     	 -     	16	19	 -     	 -     		0.83	-0.19
273.75	16.86	19.9	-2.6	 -     	1	16	19	 -     	32 046.67		0.86	0.9
274	16.7	19.29	-2.6	 -     	 -     	16	19	 -     	 -     		0.7	0.29
274.25	16.61	17.32	-2.6	 -     	 -     	16	19	 -     	 -     		0.61	-1.68
274.5	16.69	21.07	-2.6	 -     	1	16	19	 -     	32 046.67		0.69	2.07
274.75	16.67	19.26	-2.3	 -     	 -     	16	19	 -     	 -     		0.67	0.26
275	16.5	17.5	-2.3	 -     	 -     	16	19	 -     	 -     		0.5	-1.5
275.25	16.54	21.29	-2.3	 -     	1	16	19	 -     	32 046.67		0.54	2.29
275.5	16.51	19.46	-2.3	 -     	 -     	16	19	 -     	 -     		0.51	0.46
275.75	16.47	17.55	-2.1	 -     	 -     	16	19	 -     	 -     		0.47	-1.45
276	16.44	21.39	-2.1	 -     	1	16	19	 -     	32 046.67		0.44	2.39
276.25	16.37	19.62	-2.1	 -     	 -     	16	19	 -     	 -     		0.37	0.62
276.5	16.34	17.69	-2.1	 -     	 -     	16	19	 -     	 -     		0.34	-1.31
276.75	16.42	21.43	-2	 -     	1	16	19	 -     	32 046.67		0.42	2.43
277	16.3	20.05	-2	 -     	 -     	16	19	 -     	 -     		0.3	1.05
277.25	16.23	18.28	-2	 -     	 -     	16	19	 -     	 -     		0.23	-0.72
277.5	16.31	21.97	-2	 -     	1	16	19	 -     	32 046.67		0.31	2.97
277.75	16.28	20.17	-1.9	 -     	 -     	16	19	 -     	 -     		0.28	1.17
278	16.14	18.39	-1.9	 -     	 -     	16	19	 -     	 -     		0.14	-0.61
278.25	19.64	18.99	-1.9	1	 -     	19	16	32 046.67	 -     		0.64	2.99
278.5	17.96	18.75	-1.9	 -     	 -     	19	16	 -     	 -     		-1.04	2.75
278.75	19.27	18.83	-2	1	 -     	19	16	32 046.67	 -     		0.27	2.83
279	18.63	18.56	-2	 -     	 -     	19	16	 -     	 -     		-0.37	2.56
279.25	20.08	18.52	-2	1	 -     	19	16	32 046.67	 -     		1.08	2.52
279.5	18.81	18.5	-2	 -     	 -     	19	16	 -     	 -     		-0.19	2.5
279.75	20.03	18.52	-2	1	 -     	19	16	32 046.67	 -     		1.03	2.52
280	19.38	18.33	-2	 -     	 -     	19	16	 -     	 -     		0.38	2.33
280.25	17.31	18.23	-2	 -     	 -     	19	16	 -     	 -     		-1.69	2.23
280.5	21.24	18.32	-2	1	 -     	19	16	32 046.67	 -     		2.24	2.32
280.75	19.39	18.25	-2.3	 -     	 -     	19	16	 -     	 -     		0.39	2.25
281	17.4	18.03	-2.3	 -     	 -     	19	16	 -     	 -     		-1.6	2.03
281.25	21.44	18.05	-2.3	1	 -     	19	16	32 046.67	 -     		2.44	2.05
281.5	19.61	18.03	-2.3	 -     	 -     	19	16	 -     	 -     		0.61	2.03
281.75	17.45	17.97	-2.6	 -     	 -     	19	16	 -     	 -     		-1.55	1.97
282	21.52	17.88	-2.6	1	 -     	19	16	32 046.67	 -     		2.52	1.88
282.25	19.71	17.79	-2.6	 -     	 -     	16	16	 -     	 -     		3.71	1.79
282.5	17.52	17.76	-2.6	 -     	 -     	16	16	 -     	 -     		1.52	1.76
282.75	17.99	17.76	-2.6	 -     	 -     	16	16	 -     	 -     		1.99	1.76
283	18.02	17.6	-2.6	 -     	 -     	16	16	 -     	 -     		2.02	1.6
283.25	18.09	17.55	-2.6	 -     	 -     	16	16	 -     	 -     		2.09	1.55
283.5	18.07	17.56	-2.6	 -     	 -     	16	16	 -     	 -     		2.07	1.56
283.75	18.07	17.55	-2.9	 -     	 -     	16	16	 -     	 -     		2.07	1.55
284	17.8	17.38	-2.9	 -     	 -     	16	16	 -     	 -     		1.8	1.38
284.25	17.7	17.32	-2.9	 -     	 -     	16	16	 -     	 -     		1.7	1.32
284.5	17.72	17.33	-2.9	 -     	 -     	16	16	 -     	 -     		1.72	1.33
284.75	17.71	17.33	-3	 -     	 -     	16	16	 -     	 -     		1.71	1.33
285	17.5	17.16	-3	 -     	 -     	16	16	 -     	 -     		1.5	1.16
285.25	17.42	17.11	-3	 -     	 -     	16	16	 -     	 -     		1.42	1.11
285.5	17.43	17.12	-3	 -     	 -     	16	16	 -     	 -     		1.43	1.12
285.75	17.43	17.12	-3.1	 -     	 -     	16	16	 -     	 -     		1.43	1.12
286	17.23	16.96	-3.1	 -     	 -     	16	16	 -     	 -     		1.23	0.96
286.25	17.16	16.9	-3.1	 -     	 -     	16	16	 -     	 -     		1.16	0.9
286.5	17.18	16.92	-3.1	 -     	 -     	16	16	 -     	 -     		1.18	0.92
286.75	17.17	16.92	-3.1	 -     	 -     	16	16	 -     	 -     		1.17	0.92
287	16.99	16.77	-3.1	 -     	 -     	16	16	 -     	 -     		0.99	0.77
287.25	16.92	16.71	-3.1	 -     	 -     	16	16	 -     	 -     		0.92	0.71
287.5	16.94	16.73	-3.1	 -     	 -     	16	16	 -     	 -     		0.94	0.73
287.75	16.93	16.72	-3.3	 -     	 -     	16	16	 -     	 -     		0.93	0.72
288	16.75	16.57	-3.3	 -     	 -     	16	16	 -     	 -     		0.75	0.57
288.25	16.68	16.51	-3.3	 -     	 -     	16	16	 -     	 -     		0.68	0.51
288.5	16.7	16.53	-3.3	 -     	 -     	16	16	 -     	 -     		0.7	0.53
288.75	16.69	16.52	-3.3	 -     	 -     	16	16	 -     	 -     		0.69	0.52
289	16.52	16.38	-3.3	 -     	 -     	16	16	 -     	 -     		0.52	0.38
289.25	16.46	16.33	-3.3	 -     	 -     	16	16	 -     	 -     		0.46	0.33
289.5	16.47	16.34	-3.3	 -     	 -     	16	16	 -     	 -     		0.47	0.34
289.75	16.47	16.34	-3.2	 -     	 -     	16	16	 -     	 -     		0.47	0.34
290	16.31	16.2	-3.2	 -     	 -     	16	16	 -     	 -     		0.31	0.2
290.25	16.25	16.15	-3.2	 -     	 -     	16	16	 -     	 -     		0.25	0.15
290.5	16.26	16.16	-3.2	 -     	 -     	16	16	 -     	 -     		0.26	0.16
290.75	16.27	16.17	-3	 -     	 -     	16	16	 -     	 -     		0.27	0.17
291	16.11	16.03	-3	 -     	 -     	16	16	 -     	 -     		0.11	0.03
291.25	16.05	15.98	-3	 -     	 -     	16	16	 -     	 -     		0.05	-0.02
291.5	16.14	19.19	-3	 -     	1	16	16	 -     	32 046.67		0.14	3.19
291.75	16.11	17.53	-2.9	 -     	 -     	16	16	 -     	 -     		0.11	1.53
292	15.93	15.77	-2.9	 -     	 -     	16	16	 -     	 -     		-0.07	-0.23
292.25	19.47	19.67	-2.9	1	1	16	16	32 046.67	32 046.67		3.47	3.67
292.5	17.73	17.8	-2.9	 -     	 -     	16	16	 -     	 -     		1.73	1.8
292.75	15.5	15.84	-2.9	 -     	 -     	16	16	 -     	 -     		-0.5	-0.16
293	19.81	19.8	-2.9	1	1	16	16	32 046.67	32 046.67		3.81	3.8
293.25	18.05	18	-2.9	 -     	 -     	16	16	 -     	 -     		2.05	2
293.5	15.83	16.02	-2.9	 -     	 -     	16	16	 -     	 -     		-0.17	0.02
293.75	19.81	16.65	-2.9	1	 -     	16	16	32 046.67	 -     		3.81	0.65
294	18.53	16.63	-2.9	 -     	 -     	16	16	 -     	 -     		2.53	0.63
294.25	16.57	16.69	-2.9	 -     	 -     	16	16	 -     	 -     		0.57	0.69
294.5	17	16.66	-2.9	 -     	 -     	16	16	 -     	 -     		1	0.66
294.75	16.9	16.67	-3.1	 -     	 -     	16	16	 -     	 -     		0.9	0.67
295	16.7	16.45	-3.1	 -     	 -     	16	16	 -     	 -     		0.7	0.45
295.25	16.61	16.37	-3.1	 -     	 -     	16	16	 -     	 -     		0.61	0.37
295.5	16.63	16.39	-3.1	 -     	 -     	16	16	 -     	 -     		0.63	0.39
295.75	16.62	16.38	-3.2	 -     	 -     	16	16	 -     	 -     		0.62	0.38
296	16.52	16.23	-3.2	 -     	 -     	16	16	 -     	 -     		0.52	0.23
296.25	16.49	16.19	-3.2	 -     	 -     	16	16	 -     	 -     		0.49	0.19
296.5	16.51	16.21	-3.2	 -     	 -     	16	16	 -     	 -     		0.51	0.21
296.75	16.5	16.21	-3.2	 -     	 -     	16	16	 -     	 -     		0.5	0.21
297	16.36	16.08	-3.2	 -     	 -     	16	16	 -     	 -     		0.36	0.08
297.25	16.3	16.04	-3.2	 -     	 -     	16	16	 -     	 -     		0.3	0.04
297.5	16.32	16.06	-3.2	 -     	 -     	16	16	 -     	 -     		0.32	0.06
297.75	16.34	16.07	-2.9	 -     	 -     	16	16	 -     	 -     		0.34	0.07
298	16.22	15.96	-2.9	 -     	 -     	16	16	 -     	 -     		0.22	-0.04
298.25	16.25	19.12	-2.9	 -     	1	16	16	 -     	32 046.67		0.25	3.12
298.5	16.23	17.47	-2.9	 -     	 -     	16	16	 -     	 -     		0.23	1.47
298.75	16.2	15.52	-2.7	 -     	 -     	16	16	 -     	 -     		0.2	-0.48
299	16.22	19.5	-2.7	 -     	1	16	16	 -     	32 046.67		0.22	3.5
299.25	16.18	17.77	-2.7	 -     	 -     	16	16	 -     	 -     		0.18	1.77
299.5	16.2	15.84	-2.7	 -     	 -     	16	16	 -     	 -     		0.2	-0.16
299.75	16.34	19.59	-2.4	 -     	1	16	16	 -     	32 046.67		0.34	3.59
300	16.38	18.27	-2.4	 -     	 -     	16	16	 -     	 -     		0.38	2.27
300.25	16.43	16.53	-2.4	 -     	 -     	16	16	 -     	 -     		0.43	0.53
300.5	16.56	17.02	-2.4	 -     	 -     	16	16	 -     	 -     		0.56	1.02
300.75	16.69	16.91	-1.8	 -     	 -     	16	16	 -     	 -     		0.69	0.91
301	16.85	16.81	-1.8	 -     	 -     	16	16	 -     	 -     		0.85	0.81
301.25	16.94	16.75	-1.8	 -     	 -     	16	16	 -     	 -     		0.94	0.75
301.5	16.99	16.78	-1.8	 -     	 -     	16	16	 -     	 -     		0.99	0.78
301.75	17.04	16.8	-1.2	 -     	 -     	16	16	 -     	 -     		1.04	0.8
302	17.25	16.7	-1.2	 -     	 -     	16	16	 -     	 -     		1.25	0.7
302.25	17.31	16.67	-1.2	 -     	 -     	16	16	 -     	 -     		1.31	0.67
302.5	17.28	16.68	-1.2	 -     	 -     	16	16	 -     	 -     		1.28	0.68
302.75	17.23	16.66	-1.6	 -     	 -     	16	16	 -     	 -     		1.23	0.66
303	17.35	16.57	-1.6	 -     	 -     	16	16	 -     	 -     		1.35	0.57
303.25	17.37	16.54	-1.6	 -     	 -     	16	16	 -     	 -     		1.37	0.54
303.5	17.29	16.54	-1.6	 -     	 -     	16	16	 -     	 -     		1.29	0.54
303.75	17.24	16.54	-1.2	 -     	 -     	16	16	 -     	 -     		1.24	0.54
304	17.29	16.46	-1.2	 -     	 -     	16	16	 -     	 -     		1.29	0.46
304.25	17.25	16.42	-1.2	 -     	 -     	16	16	 -     	 -     		1.25	0.42
304.5	17.11	16.39	-1.2	 -     	 -     	16	16	 -     	 -     		1.11	0.39
304.75	16.98	16.33	-2.5	 -     	 -     	16	16	 -     	 -     		0.98	0.33
305	16.66	16.13	-2.5	 -     	 -     	16	16	 -     	 -     		0.66	0.13
305.25	16.57	16.08	-2.5	 -     	 -     	16	16	 -     	 -     		0.57	0.08
305.5	16.59	16.09	-2.5	 -     	 -     	16	16	 -     	 -     		0.59	0.09
305.75	16.53	16.04	-4.1	 -     	 -     	16	16	 -     	 -     		0.53	0.04
306	16.31	15.86	-4.1	 -     	 -     	16	16	 -     	 -     		0.31	-0.14
306.25	16.31	19	-4.1	 -     	1	16	16	 -     	32 046.67		0.31	3
306.5	16.29	17.35	-4.1	 -     	 -     	16	16	 -     	 -     		0.29	1.35
306.75	16.24	15.39	-4.1	 -     	 -     	16	16	 -     	 -     		0.24	-0.61
307	16.16	19.31	-4.1	 -     	1	16	16	 -     	32 046.67		0.16	3.31
307.25	16.06	17.55	-4.1	 -     	 -     	16	16	 -     	 -     		0.06	1.55
307.5	16.03	15.62	-4.1	 -     	 -     	16	16	 -     	 -     		0.03	-0.38
307.75	16.1	19.35	-4.3	 -     	1	16	16	 -     	32 046.67		0.1	3.35
308	15.92	17.96	-4.3	 -     	 -     	16	16	 -     	 -     		-0.08	1.96
308.25	19.32	16.26	-4.3	1	 -     	16	16	32 046.67	 -     		3.32	0.26
308.5	17.63	16.72	-4.3	 -     	 -     	16	16	 -     	 -     		1.63	0.72
308.75	15.45	16.54	-4.2	 -     	 -     	16	16	 -     	 -     		-0.55	0.54
309	19.63	16.47	-4.2	1	 -     	16	16	32 046.67	 -     		3.63	0.47
309.25	17.88	16.35	-4.2	 -     	 -     	16	16	 -     	 -     		1.88	0.35
309.5	15.73	16.33	-4.2	 -     	 -     	16	16	 -     	 -     		-0.27	0.33
309.75	19.69	16.4	-4.5	1	 -     	16	16	32 046.67	 -     		3.69	0.4
310	18.35	16.2	-4.5	 -     	 -     	16	16	 -     	 -     		2.35	0.2
310.25	16.38	16.1	-4.5	 -     	 -     	16	16	 -     	 -     		0.38	0.1
310.5	16.82	16.12	-4.5	 -     	 -     	16	16	 -     	 -     		0.82	0.12
310.75	16.72	16.1	-4.8	 -     	 -     	16	16	 -     	 -     		0.72	0.1
311	16.5	15.92	-4.8	 -     	 -     	16	16	 -     	 -     		0.5	-0.08
311.25	16.48	19.05	-4.8	 -     	1	16	16	 -     	32 046.67		0.48	3.05
311.5	16.46	17.39	-4.8	 -     	 -     	16	16	 -     	 -     		0.46	1.39
311.75	16.41	15.43	-4.9	 -     	 -     	16	16	 -     	 -     		0.41	-0.57
312	16.29	19.34	-4.9	 -     	1	16	16	 -     	32 046.67		0.29	3.34
312.25	16.18	17.56	-4.9	 -     	 -     	16	16	 -     	 -     		0.18	1.56
312.5	16.16	15.63	-4.9	 -     	 -     	16	16	 -     	 -     		0.16	-0.37
312.75	16.23	19.38	-5	 -     	1	16	16	 -     	32 046.67		0.23	3.38
313	16.03	17.95	-5	 -     	 -     	16	16	 -     	 -     		0.03	1.95
313.25	15.93	16.18	-5	 -     	 -     	16	16	 -     	 -     		-0.07	0.18
313.5	19.44	16.77	-5	1	 -     	16	16	32 046.67	 -     		3.44	0.77
313.75	17.71	16.59	-5.2	 -     	 -     	16	16	 -     	 -     		1.71	0.59
314	15.75	16.37	-5.2	 -     	 -     	16	16	 -     	 -     		-0.25	0.37
314.25	19.8	16.37	-5.2	1	 -     	16	16	32 046.67	 -     		3.8	0.37
314.5	17.95	16.36	-5.2	 -     	 -     	16	16	 -     	 -     		1.95	0.36
314.75	15.81	16.3	-5.3	 -     	 -     	16	16	 -     	 -     		-0.19	0.3
315	19.91	16.2	-5.3	1	 -     	16	16	32 046.67	 -     		3.91	0.2
315.25	18.13	16.09	-5.3	 -     	 -     	16	16	 -     	 -     		2.13	0.09
315.5	15.98	16.07	-5.3	 -     	 -     	16	16	 -     	 -     		-0.02	0.07
315.75	19.94	16.13	-5.6	1	 -     	16	16	32 046.67	 -     		3.94	0.13
316	18.57	15.94	-5.6	 -     	 -     	16	16	 -     	 -     		2.57	-0.06
316.25	16.67	19.04	-5.6	 -     	1	16	16	 -     	32 046.67		0.67	3.04
316.5	17.08	17.38	-5.6	 -     	 -     	16	16	 -     	 -     		1.08	1.38
316.75	16.94	15.42	-5.8	 -     	 -     	16	16	 -     	 -     		0.94	-0.58
317	16.8	19.31	-5.8	 -     	1	16	16	 -     	32 046.67		0.8	3.31
317.25	16.67	17.54	-5.8	 -     	 -     	16	16	 -     	 -     		0.67	1.54
317.5	16.65	15.61	-5.8	 -     	 -     	16	16	 -     	 -     		0.65	-0.39
317.75	16.7	19.34	-6.3	 -     	1	16	16	 -     	32 046.67		0.7	3.34
318	16.46	17.9	-6.3	 -     	 -     	16	16	 -     	 -     		0.46	1.9
318.25	16.34	16.13	-6.3	 -     	 -     	16	16	 -     	 -     		0.34	0.13
318.5	16.36	16.63	-6.3	 -     	 -     	16	16	 -     	 -     		0.36	0.63
318.75	16.34	16.48	-6.7	 -     	 -     	16	16	 -     	 -     		0.34	0.48
319	16.12	16.28	-6.7	 -     	 -     	16	16	 -     	 -     		0.12	0.28
319.25	16.04	16.18	-6.7	 -     	 -     	16	16	 -     	 -     		0.04	0.18
319.5	16.06	16.21	-6.7	 -     	 -     	16	16	 -     	 -     		0.06	0.21
319.75	16.05	16.2	-6.9	 -     	 -     	16	16	 -     	 -     		0.05	0.2
320	16.01	16.01	-6.9	 -     	 -     	16	16	 -     	 -     		0.01	0.01
320.25	15.99	15.96	-6.9	 -     	 -     	16	16	 -     	 -     		-0.01	-0.04
320.5	19.55	19.25	-6.9	1	1	16	16	32 046.67	32 046.67		3.55	3.25
320.75	17.83	17.56	-6.3	 -     	 -     	16	16	 -     	 -     		1.83	1.56
321	15.95	15.79	-6.3	 -     	 -     	16	16	 -     	 -     		-0.05	-0.21
321.25	20.12	19.69	-6.3	1	1	16	16	32 046.67	32 046.67		4.12	3.69
321.5	18.29	17.84	-6.3	 -     	 -     	16	16	 -     	 -     		2.29	1.84
321.75	16.14	15.9	-6.2	 -     	 -     	16	16	 -     	 -     		0.14	-0.1
322	16.98	19.78	-6.2	 -     	1	16	16	 -     	32 046.67		0.98	3.78
322.25	16.98	18.03	-6.2	 -     	 -     	16	16	 -     	 -     		0.98	2.03
322.5	16.98	16.11	-6.2	 -     	 -     	16	16	 -     	 -     		0.98	0.11
322.75	17.05	16.67	-5.8	 -     	 -     	16	16	 -     	 -     		1.05	0.67
323	17.05	16.68	-5.8	 -     	 -     	16	16	 -     	 -     		1.05	0.68
323.25	17.11	16.78	-5.8	 -     	 -     	16	16	 -     	 -     		1.11	0.78
323.5	17.2	16.75	-5.8	 -     	 -     	16	16	 -     	 -     		1.2	0.75
323.75	17.31	16.78	-4.9	 -     	 -     	16	16	 -     	 -     		1.31	0.78
324	17.45	16.61	-4.9	 -     	 -     	16	16	 -     	 -     		1.45	0.61
324.25	17.53	16.53	-4.9	 -     	 -     	16	16	 -     	 -     		1.53	0.53
324.5	17.58	16.55	-4.9	 -     	 -     	16	16	 -     	 -     		1.58	0.55
324.75	17.66	16.59	-3.4	 -     	 -     	16	16	 -     	 -     		1.66	0.59
325	17.88	16.49	-3.4	 -     	 -     	16	16	 -     	 -     		1.88	0.49
325.25	17.94	16.45	-3.4	 -     	 -     	16	16	 -     	 -     		1.94	0.45
325.5	17.92	16.47	-3.4	 -     	 -     	16	16	 -     	 -     		1.92	0.47
325.75	17.94	16.5	-2.7	 -     	 -     	16	16	 -     	 -     		1.94	0.5
326	18.14	16.43	-2.7	 -     	 -     	16	16	 -     	 -     		2.14	0.43
326.25	18.2	16.4	-2.7	 -     	 -     	16	16	 -     	 -     		2.2	0.4
326.5	18.17	16.41	-2.7	 -     	 -     	16	16	 -     	 -     		2.17	0.41
326.75	18.15	16.44	-1.8	 -     	 -     	16	16	 -     	 -     		2.15	0.44
327	18.28	16.37	-1.8	 -     	 -     	16	16	 -     	 -     		2.28	0.37
327.25	18.27	16.34	-1.8	 -     	 -     	16	16	 -     	 -     		2.27	0.34
327.5	18.19	16.34	-1.8	 -     	 -     	16	16	 -     	 -     		2.19	0.34
327.75	18.14	16.34	-1.5	 -     	 -     	16	16	 -     	 -     		2.14	0.34
328	18.16	16.26	-1.5	 -     	 -     	16	16	 -     	 -     		2.16	0.26
328.25	18.11	16.22	-1.5	 -     	 -     	16	16	 -     	 -     		2.11	0.22
328.5	17.96	16.2	-1.5	 -     	 -     	16	16	 -     	 -     		1.96	0.2
328.75	17.86	16.16	-1.8	 -     	 -     	16	16	 -     	 -     		1.86	0.16
329	17.53	15.98	-1.8	 -     	 -     	16	16	 -     	 -     		1.53	-0.02
329.25	17.49	19.12	-1.8	 -     	1	16	16	 -     	32 046.67		1.49	3.12
329.5	17.48	17.47	-1.8	 -     	 -     	16	16	 -     	 -     		1.48	1.47
329.75	17.36	15.44	-3.9	 -     	 -     	16	16	 -     	 -     		1.36	-0.56
330	17.21	19.33	-3.9	 -     	1	16	16	 -     	32 046.67		1.21	3.33
330.25	17.11	17.59	-3.9	 -     	 -     	16	16	 -     	 -     		1.11	1.59
330.5	17.08	15.65	-3.9	 -     	 -     	16	16	 -     	 -     		1.08	-0.35
330.75	17.16	19.38	-3.9	 -     	1	16	16	 -     	32 046.67		1.16	3.38
331	16.95	17.99	-3.9	 -     	 -     	16	16	 -     	 -     		0.95	1.99
331.25	16.84	16.22	-3.9	 -     	 -     	16	16	 -     	 -     		0.84	0.22
331.5	16.86	16.72	-3.9	 -     	 -     	16	16	 -     	 -     		0.86	0.72
331.75	16.84	16.56	-4.4	 -     	 -     	16	16	 -     	 -     		0.84	0.56
332	16.63	16.38	-4.4	 -     	 -     	16	16	 -     	 -     		0.63	0.38
332.25	16.56	16.29	-4.4	 -     	 -     	16	16	 -     	 -     		0.56	0.29
332.5	16.58	16.32	-4.4	 -     	 -     	16	16	 -     	 -     		0.58	0.32
332.75	16.55	16.29	-5	 -     	 -     	16	16	 -     	 -     		0.55	0.29
333	16.35	16.09	-5	 -     	 -     	16	16	 -     	 -     		0.35	0.09
333.25	16.28	16.02	-5	 -     	 -     	16	16	 -     	 -     		0.28	0.02
333.5	16.3	16.04	-5	 -     	 -     	16	16	 -     	 -     		0.3	0.04
333.75	16.28	16.02	-5.4	 -     	 -     	16	16	 -     	 -     		0.28	0.02
334	16.08	15.83	-5.4	 -     	 -     	16	16	 -     	 -     		0.08	-0.17
334.25	16.09	18.96	-5.4	 -     	1	16	16	 -     	32 046.67		0.09	2.96
334.5	16.07	17.32	-5.4	 -     	 -     	16	16	 -     	 -     		0.07	1.32
334.75	16.01	15.34	-5.8	 -     	 -     	16	16	 -     	 -     		0.01	-0.66
335	15.92	19.23	-5.8	 -     	1	16	16	 -     	32 046.67		-0.08	3.23
335.25	19.32	17.55	-5.8	1	 -     	16	16	32 046.67	 -     		3.32	1.55
335.5	17.57	15.58	-5.8	 -     	 -     	16	16	 -     	 -     		1.57	-0.42
335.75	15.47	19.26	-5.9	 -     	1	16	16	 -     	32 046.67		-0.53	3.26
336	19.64	17.95	-5.9	1	 -     	16	16	32 046.67	 -     		3.64	1.95
336.25	17.87	16.15	-5.9	 -     	 -     	16	16	 -     	 -     		1.87	0.15
336.5	15.71	16.6	-5.9	 -     	 -     	16	16	 -     	 -     		-0.29	0.6
336.75	19.66	16.53	-6.2	1	 -     	16	16	32 046.67	 -     		3.66	0.53
337	18.32	16.33	-6.2	 -     	 -     	16	16	 -     	 -     		2.32	0.33
337.25	16.35	16.21	-6.2	 -     	 -     	16	16	 -     	 -     		0.35	0.21
337.5	16.78	16.23	-6.2	 -     	 -     	16	16	 -     	 -     		0.78	0.23
337.75	16.68	16.22	-6.4	 -     	 -     	16	16	 -     	 -     		0.68	0.22
338	16.45	16	-6.4	 -     	 -     	16	16	 -     	 -     		0.45	0
338.25	16.35	15.93	-6.4	 -     	 -     	16	16	 -     	 -     		0.35	-0.07
338.5	16.45	19.14	-6.4	 -     	1	16	16	 -     	32 046.67		0.45	3.14
338.75	16.4	17.46	-6.7	 -     	 -     	16	16	 -     	 -     		0.4	1.46
339	16.14	15.65	-6.7	 -     	 -     	16	16	 -     	 -     		0.14	-0.35
339.25	16.14	19.44	-6.7	 -     	1	16	16	 -     	32 046.67		0.14	3.44
339.5	16.12	17.6	-6.7	 -     	 -     	16	16	 -     	 -     		0.12	1.6
339.75	16.07	15.68	-6.9	 -     	 -     	16	16	 -     	 -     		0.07	-0.32
340	15.95	19.48	-6.9	 -     	1	16	16	 -     	32 046.67		-0.05	3.48
340.25	19.34	17.77	-6.9	1	 -     	16	16	32 046.67	 -     		3.34	1.77
340.5	17.58	15.82	-6.9	 -     	 -     	16	16	 -     	 -     		1.58	-0.18
340.75	15.5	19.51	-6.7	 -     	1	16	16	 -     	32 046.67		-0.5	3.51
341	19.66	18.17	-6.7	1	 -     	16	16	32 046.67	 -     		3.66	2.17
341.25	17.87	16.37	-6.7	 -     	 -     	16	16	 -     	 -     		1.87	0.37
341.5	15.7	16.82	-6.7	 -     	 -     	16	16	 -     	 -     		-0.3	0.82
341.75	19.69	16.77	-6.6	1	 -     	16	16	32 046.67	 -     		3.69	0.77
342	18.33	16.55	-6.6	 -     	 -     	16	16	 -     	 -     		2.33	0.55
342.25	16.35	16.42	-6.6	 -     	 -     	16	16	 -     	 -     		0.35	0.42
342.5	16.79	16.45	-6.6	 -     	 -     	16	16	 -     	 -     		0.79	0.45
342.75	16.69	16.44	-6.8	 -     	 -     	16	16	 -     	 -     		0.69	0.44
343	16.45	16.21	-6.8	 -     	 -     	16	16	 -     	 -     		0.45	0.21
343.25	16.35	16.13	-6.8	 -     	 -     	16	16	 -     	 -     		0.35	0.13
343.5	16.37	16.15	-6.8	 -     	 -     	16	16	 -     	 -     		0.37	0.15
343.75	16.38	16.16	-6.5	 -     	 -     	16	16	 -     	 -     		0.38	0.16
344	16.48	16.02	-6.5	 -     	 -     	16	16	 -     	 -     		0.48	0.02
344.25	16.58	19.22	-6.5	 -     	1	16	19	 -     	32 046.67		0.58	0.22
344.5	16.43	17.59	-6.5	 -     	 -     	16	19	 -     	 -     		0.43	-1.41
344.75	16.52	18.85	-6.1	 -     	1	16	19	 -     	32 046.67		0.52	-0.15
345	16.64	21.43	-6.1	 -     	1	16	19	 -     	32 046.67		0.64	2.43
345.25	16.62	17.83	-6.1	 -     	 -     	16	19	 -     	 -     		0.62	-1.17
345.5	16.73	19.63	-6.1	 -     	1	16	19	 -     	32 046.67		0.73	0.63
345.75	16.85	18.46	-3.4	 -     	 -     	16	19	 -     	 -     		0.85	-0.54
346	17.03	20.16	-3.4	 -     	1	16	19	 -     	32 046.67		1.03	1.16
346.25	17.07	19.25	-3.4	 -     	 -     	16	19	 -     	 -     		1.07	0.25
346.5	17.08	17.09	-3.4	 -     	 -     	16	19	 -     	 -     		1.08	-1.91
346.75	17.34	21.02	0.4	 -     	1	16	19	 -     	32 046.67		1.34	2.02
347	17.56	19.64	0.4	 -     	 -     	16	19	 -     	 -     		1.56	0.64
347.25	17.59	17.85	0.4	 -     	 -     	16	19	 -     	 -     		1.59	-1.15
347.5	17.71	21.55	0.4	 -     	1	16	19	 -     	32 046.67		1.71	2.55
347.75	17.76	19.79	1.9	 -     	 -     	16	19	 -     	 -     		1.76	0.79
348	17.98	18.07	1.9	 -     	 -     	16	19	 -     	 -     		1.98	-0.93
348.25	18.17	21.86	1.9	 -     	1	16	19	 -     	32 046.67		2.17	2.86
348.5	18.14	20.03	1.9	 -     	 -     	16	19	 -     	 -     		2.14	1.03
348.75	18.17	18.17	3.7	 -     	 -     	16	19	 -     	 -     		2.17	-0.83
349	18.55	22.1	3.7	 -     	1	16	19	 -     	32 046.67		2.55	3.1
349.25	18.61	20.34	3.7	 -     	 -     	16	19	 -     	 -     		2.61	1.34
349.5	18.54	18.41	3.7	 -     	 -     	16	19	 -     	 -     		2.54	-0.59
349.75	18.68	22.23	5.9	 -     	1	16	19	 -     	32 046.67		2.68	3.23
350	18.96	20.95	5.9	 -     	 -     	16	19	 -     	 -     		2.96	1.95
350.25	22.55	19.22	5.9	1	 -     	19	16	32 046.67	 -     		3.55	3.22
350.5	20.82	19.64	5.9	 -     	 -     	19	16	 -     	 -     		1.82	3.64
350.75	18.63	19.52	7.5	 -     	 -     	19	16	 -     	 -     		-0.37	3.52
351	23.2	19.56	7.5	1	 -     	19	16	32 046.67	 -     		4.2	3.56
351.25	21.54	19.46	7.5	 -     	 -     	19	16	 -     	 -     		2.54	3.46
351.5	19.26	19.42	7.5	 -     	 -     	19	16	 -     	 -     		0.26	3.42
351.75	19.67	19.43	8	 -     	 -     	19	16	 -     	 -     		0.67	3.43
352	20	19.35	8	 -     	 -     	19	16	 -     	 -     		1	3.35
352.25	20.12	19.31	8	 -     	 -     	19	16	 -     	 -     		1.12	3.31
352.5	19.94	19.29	8	 -     	 -     	19	16	 -     	 -     		0.94	3.29
352.75	19.76	19.18	5.7	 -     	 -     	19	16	 -     	 -     		0.76	3.18
353	19.39	18.96	5.7	 -     	 -     	19	16	 -     	 -     		0.39	2.96
353.25	19.29	18.91	5.7	 -     	 -     	19	16	 -     	 -     		0.29	2.91
353.5	19.31	18.93	5.7	 -     	 -     	19	16	 -     	 -     		0.31	2.93
353.75	19.14	18.76	0.2	 -     	 -     	19	16	 -     	 -     		0.14	2.76
354	18.85	18.52	0.2	 -     	 -     	19	16	 -     	 -     		-0.15	2.52
354.25	18.75	18.49	0.2	 -     	 -     	16	16	 -     	 -     		2.75	2.49
354.5	18.74	18.5	0.2	 -     	 -     	16	16	 -     	 -     		2.74	2.5
354.75	18.74	18.49	0.2	 -     	 -     	16	16	 -     	 -     		2.74	2.49
355	18.54	18.33	0.2	 -     	 -     	16	16	 -     	 -     		2.54	2.33
355.25	18.46	18.27	0.2	 -     	 -     	16	16	 -     	 -     		2.46	2.27
355.5	18.47	18.28	0.2	 -     	 -     	16	16	 -     	 -     		2.47	2.28
355.75	18.44	18.25	-0.7	 -     	 -     	16	16	 -     	 -     		2.44	2.25
356	18.24	18.08	-0.7	 -     	 -     	16	16	 -     	 -     		2.24	2.08
356.25	18.17	18.03	-0.7	 -     	 -     	16	16	 -     	 -     		2.17	2.03
356.5	18.18	18.04	-0.7	 -     	 -     	16	16	 -     	 -     		2.18	2.04
356.75	18.15	18.01	-1.5	 -     	 -     	16	16	 -     	 -     		2.15	2.01
357	17.95	17.84	-1.5	 -     	 -     	16	16	 -     	 -     		1.95	1.84
357.25	17.89	17.79	-1.5	 -     	 -     	16	16	 -     	 -     		1.89	1.79
357.5	17.9	17.8	-1.5	 -     	 -     	16	16	 -     	 -     		1.9	1.8
357.75	17.88	17.78	-2.2	 -     	 -     	16	16	 -     	 -     		1.88	1.78
358	17.68	17.61	-2.2	 -     	 -     	16	16	 -     	 -     		1.68	1.61
358.25	17.61	17.56	-2.2	 -     	 -     	16	16	 -     	 -     		1.61	1.56
358.5	17.63	17.57	-2.2	 -     	 -     	16	16	 -     	 -     		1.63	1.57
358.75	17.6	17.54	-3	 -     	 -     	16	16	 -     	 -     		1.6	1.54
359	17.4	17.37	-3	 -     	 -     	16	16	 -     	 -     		1.4	1.37
359.25	17.34	17.32	-3	 -     	 -     	16	16	 -     	 -     		1.34	1.32
359.5	17.35	17.33	-3	 -     	 -     	16	16	 -     	 -     		1.35	1.33
359.75	17.34	17.31	-3.4	 -     	 -     	16	16	 -     	 -     		1.34	1.31
360	17.15	17.15	-3.4	 -     	 -     	16	16	 -     	 -     		1.15	1.15
360.25	17.09	17.09	-3.4	 -     	 -     	16	16	 -     	 -     		1.09	1.09
360.5	17.1	17.11	-3.4	 -     	 -     	16	16	 -     	 -     		1.1	1.11
360.75	17.08	17.09	-3.8	 -     	 -     	16	16	 -     	 -     		1.08	1.09
361	16.9	16.93	-3.8	 -     	 -     	16	16	 -     	 -     		0.9	0.93
361.25	16.83	16.87	-3.8	 -     	 -     	16	16	 -     	 -     		0.83	0.87
361.5	16.85	16.89	-3.8	 -     	 -     	16	16	 -     	 -     		0.85	0.89
361.75	16.83	16.86	-4.4	 -     	 -     	16	16	 -     	 -     		0.83	0.86
362	16.64	16.7	-4.4	 -     	 -     	16	16	 -     	 -     		0.64	0.7
362.25	16.58	16.64	-4.4	 -     	 -     	16	16	 -     	 -     		0.58	0.64
362.5	16.59	16.66	-4.4	 -     	 -     	16	16	 -     	 -     		0.59	0.66
362.75	16.58	16.64	-4.7	 -     	 -     	16	16	 -     	 -     		0.58	0.64
363	16.4	16.48	-4.7	 -     	 -     	16	16	 -     	 -     		0.4	0.48
363.25	16.33	16.42	-4.7	 -     	 -     	16	16	 -     	 -     		0.33	0.42
363.5	16.35	16.44	-4.7	 -     	 -     	16	16	 -     	 -     		0.35	0.44
363.75	16.35	16.44	-4.6	 -     	 -     	16	16	 -     	 -     		0.35	0.44
364	16.17	16.28	-4.6	 -     	 -     	16	16	 -     	 -     		0.17	0.28
364.25	16.11	16.22	-4.6	 -     	 -     	16	16	 -     	 -     		0.11	0.22
364.5	16.12	16.24	-4.6	 -     	 -     	16	16	 -     	 -     		0.12	0.24
364.75	16.12	16.24	-4.5	 -     	 -     	16	16	 -     	 -     		0.12	0.24
365	15.96	16.09	-4.5	 -     	 -     	16	16	 -     	 -     		-0.04	0.09
365.25	19.39	16.11	-4.5	1	 -     	16	16	32 046.67	 -     		3.39	0.11
365.5	17.68	16.08	-4.5	 -     	 -     	16	16	 -     	 -     		1.68	0.08
365.75	15.5	16.02	-4.9	 -     	 -     	16	16	 -     	 -     		-0.5	0.02
366	19.68	15.96	-4.9	1	 -     	16	16	32 046.67	 -     		3.68	-0.04
366.25	18.01	19.07	-4.9	 -     	1	16	16	 -     	32 046.67		2.01	3.07
366.5	15.81	17.36	-4.9	 -     	 -     	16	16	 -     	 -     		-0.19	1.36
366.75	19.73	15.47	-5.2	1	 -     	16	16	32 046.67	 -     		3.73	-0.53
367	18.49	19.39	-5.2	 -     	1	16	16	 -     	32 046.67		2.49	3.39
367.25	16.51	17.59	-5.2	 -     	 -     	16	16	 -     	 -     		0.51	1.59
367.5	16.89	15.66	-5.2	 -     	 -     	16	16	 -     	 -     		0.89	-0.34
367.75	16.88	19.41	-5.1	 -     	1	16	16	 -     	32 046.67		0.88	3.41
368	17.07	18.07	-5.1	 -     	 -     	16	16	 -     	 -     		1.07	2.07
368.25	17.15	19.58	-5.1	 -     	1	16	19	 -     	32 046.67		1.15	0.58
368.5	16.96	18.43	-5.1	 -     	 -     	16	19	 -     	 -     		0.96	-0.57
368.75	17.06	19.55	-4.5	 -     	1	16	19	 -     	32 046.67		1.06	0.55
369	17.13	18.94	-4.5	 -     	 -     	16	19	 -     	 -     		1.13	-0.06
369.25	17.24	20.18	-4.5	 -     	1	16	19	 -     	32 046.67		1.24	1.18
369.5	17.29	19.08	-4.5	 -     	 -     	16	19	 -     	 -     		1.29	0.08
369.75	17.43	17.11	-0.9	 -     	 -     	16	19	 -     	 -     		1.43	-1.89
370	17.68	21.12	-0.9	 -     	1	16	19	 -     	32 046.67		1.68	2.12
370.25	17.71	19.33	-0.9	 -     	 -     	16	19	 -     	 -     		1.71	0.33
370.5	17.71	17.41	-0.9	 -     	 -     	16	19	 -     	 -     		1.71	-1.59
370.75	17.95	21.27	2.7	 -     	1	16	19	 -     	32 046.67		1.95	2.27
371	18.2	19.98	2.7	 -     	 -     	16	19	 -     	 -     		2.2	0.98
371.25	18.24	18.2	2.7	 -     	 -     	16	19	 -     	 -     		2.24	-0.8
371.5	18.34	21.9	2.7	 -     	1	16	19	 -     	32 046.67		2.34	2.9
371.75	18.41	20.16	5.1	 -     	 -     	16	19	 -     	 -     		2.41	1.16
372	18.68	18.47	5.1	 -     	 -     	16	19	 -     	 -     		2.68	-0.53
372.25	18.87	22.28	5.1	 -     	1	16	19	 -     	32 046.67		2.87	3.28
372.5	18.84	20.44	5.1	 -     	 -     	16	19	 -     	 -     		2.84	1.44
372.75	18.88	18.59	7.2	 -     	 -     	16	19	 -     	 -     		2.88	-0.41
373	19.28	22.54	7.2	 -     	1	16	19	 -     	32 046.67		3.28	3.54
373.25	19.34	20.79	7.2	 -     	 -     	16	19	 -     	 -     		3.34	1.79
373.5	19.26	18.86	7.2	 -     	 -     	16	19	 -     	 -     		3.26	-0.14
373.75	19.36	22.63	7.8	 -     	1	16	19	 -     	32 046.67		3.36	3.63
374	19.63	21.35	7.8	 -     	 -     	16	19	 -     	 -     		3.63	2.35
374.25	19.73	19.55	7.8	 -     	 -     	19	16	 -     	 -     		0.73	3.55
374.5	19.71	20.01	7.8	 -     	 -     	19	16	 -     	 -     		0.71	4.01
374.75	19.69	19.91	8.5	 -     	 -     	19	16	 -     	 -     		0.69	3.91
375	19.89	19.84	8.5	 -     	 -     	19	16	 -     	 -     		0.89	3.84
375.25	19.91	19.78	8.5	 -     	 -     	19	16	 -     	 -     		0.91	3.78
375.5	19.81	19.79	8.5	 -     	 -     	19	16	 -     	 -     		0.81	3.79
375.75	19.72	19.77	8.2	 -     	 -     	19	16	 -     	 -     		0.72	3.77
376	19.8	19.67	8.2	 -     	 -     	19	16	 -     	 -     		0.8	3.67
376.25	19.77	19.62	8.2	 -     	 -     	19	16	 -     	 -     		0.77	3.62
376.5	19.61	19.6	8.2	 -     	 -     	19	16	 -     	 -     		0.61	3.6
376.75	19.37	19.51	7.5	 -     	 -     	19	16	 -     	 -     		0.37	3.51
377	19.17	19.35	7.5	 -     	 -     	19	16	 -     	 -     		0.17	3.35
377.25	19.13	19.3	7.5	 -     	 -     	19	16	 -     	 -     		0.13	3.3
377.5	19.13	19.31	7.5	 -     	 -     	19	16	 -     	 -     		0.13	3.31
377.75	19.02	19.2	4	 -     	 -     	19	16	 -     	 -     		0.02	3.2
378	18.76	18.96	2.6	 -     	 -     	19	16	 -     	 -     		-0.24	2.96
378.25	18.65	18.91	2.6	 -     	 -     	16	16	 -     	 -     		2.65	2.91
378.5	18.64	18.92	2.6	 -     	 -     	16	16	 -     	 -     		2.64	2.92
378.75	18.64	18.92	2.6	 -     	 -     	16	16	 -     	 -     		2.64	2.92
379	18.47	18.76	2.6	 -     	 -     	16	16	 -     	 -     		2.47	2.76
379.25	18.4	18.71	2.6	 -     	 -     	16	16	 -     	 -     		2.4	2.71
379.5	18.42	18.72	2.6	 -     	 -     	16	16	 -     	 -     		2.42	2.72
379.75	18.38	18.68	1.3	 -     	 -     	16	16	 -     	 -     		2.38	2.68
380	18.19	18.51	1.3	 -     	 -     	16	16	 -     	 -     		2.19	2.51
380.25	18.13	18.47	1.3	 -     	 -     	16	16	 -     	 -     		2.13	2.47
380.5	18.14	18.48	1.3	 -     	 -     	16	16	 -     	 -     		2.14	2.48
380.75	18.12	18.46	0.7	 -     	 -     	16	16	 -     	 -     		2.12	2.46
381	17.95	18.3	0.7	 -     	 -     	16	16	 -     	 -     		1.95	2.3
381.25	17.89	18.25	0.7	 -     	 -     	16	16	 -     	 -     		1.89	2.25
381.5	17.9	18.26	0.7	 -     	 -     	16	16	 -     	 -     		1.9	2.26
381.75	17.88	18.24	 -     	 -     	 -     	16	16	 -     	 -     		1.88	2.24
382	17.7	18.08	 -     	 -     	 -     	16	16	 -     	 -     		1.7	2.08
382.25	17.65	18.03	 -     	 -     	 -     	16	16	 -     	 -     		1.65	2.03
382.5	17.66	18.04	 -     	 -     	 -     	16	16	 -     	 -     		1.66	2.04
382.75	17.63	18.02	-0.7	 -     	 -     	16	16	 -     	 -     		1.63	2.02
383	17.46	17.86	-0.7	 -     	 -     	16	16	 -     	 -     		1.46	1.86
383.25	17.4	17.81	-0.7	 -     	 -     	16	16	 -     	 -     		1.4	1.81
383.5	17.42	17.82	-0.7	 -     	 -     	16	16	 -     	 -     		1.42	1.82
383.75	17.39	17.8	-1.4	 -     	 -     	16	16	 -     	 -     		1.39	1.8
384	17.22	17.64	-1.4	 -     	 -     	16	16	 -     	 -     		1.22	1.64
384.25	17.16	17.59	-1.4	 -     	 -     	16	16	 -     	 -     		1.16	1.59
384.5	17.17	17.6	-1.4	 -     	 -     	16	16	 -     	 -     		1.17	1.6
384.75	17.15	17.57	-2.2	 -     	 -     	16	16	 -     	 -     		1.15	1.57
385	16.97	17.41	-2.2	 -     	 -     	16	16	 -     	 -     		0.97	1.41
385.25	16.91	17.36	-2.2	 -     	 -     	16	16	 -     	 -     		0.91	1.36
385.5	16.93	17.37	-2.2	 -     	 -     	16	16	 -     	 -     		0.93	1.37
385.75	16.95	17.4	-1.4	 -     	 -     	16	16	 -     	 -     		0.95	1.4
386	16.8	17.26	-1.4	 -     	 -     	16	16	 -     	 -     		0.8	1.26
386.25	16.74	17.2	-1.4	 -     	 -     	16	16	 -     	 -     		0.74	1.2
386.5	16.75	17.22	-1.4	 -     	 -     	16	16	 -     	 -     		0.75	1.22
386.75	16.81	17.27	0.6	 -     	 -     	16	16	 -     	 -     		0.81	1.27
387	16.7	17.16	0.6	 -     	 -     	16	16	 -     	 -     		0.7	1.16
387.25	16.64	17.1	0.6	 -     	 -     	16	16	 -     	 -     		0.64	1.1
387.5	16.65	17.12	0.6	 -     	 -     	16	16	 -     	 -     		0.65	1.12
387.75	16.71	17.18	2.8	 -     	 -     	16	16	 -     	 -     		0.71	1.18
388	16.62	17.09	2.8	 -     	 -     	16	16	 -     	 -     		0.62	1.09
388.25	16.57	17.04	2.8	 -     	 -     	16	16	 -     	 -     		0.57	1.04
388.5	16.58	17.05	2.8	 -     	 -     	16	16	 -     	 -     		0.58	1.05
388.75	16.59	17.06	3.3	 -     	 -     	16	16	 -     	 -     		0.59	1.06
389	16.48	16.96	3.3	 -     	 -     	16	16	 -     	 -     		0.48	0.96
389.25	16.44	16.91	3.3	 -     	 -     	16	16	 -     	 -     		0.44	0.91
389.5	16.45	16.92	3.3	 -     	 -     	16	16	 -     	 -     		0.45	0.92
389.75	16.45	16.93	3.6	 -     	 -     	16	16	 -     	 -     		0.45	0.93
390	16.34	16.82	3.6	 -     	 -     	16	16	 -     	 -     		0.34	0.82
390.25	16.3	16.78	3.6	 -     	 -     	16	16	 -     	 -     		0.3	0.78
390.5	16.31	16.79	3.6	 -     	 -     	16	16	 -     	 -     		0.31	0.79
390.75	16.31	16.8	3.8	 -     	 -     	16	16	 -     	 -     		0.31	0.8
391	16.2	16.69	3.8	 -     	 -     	16	16	 -     	 -     		0.2	0.69
391.25	16.16	16.65	3.8	 -     	 -     	16	16	 -     	 -     		0.16	0.65
391.5	16.17	16.66	3.8	 -     	 -     	16	16	 -     	 -     		0.17	0.66
391.75	16.2	16.69	4.7	 -     	 -     	16	16	 -     	 -     		0.2	0.69
392	16.25	16.63	4.7	 -     	 -     	16	16	 -     	 -     		0.25	0.63
392.25	16.35	19.87	4.7	 -     	1	16	19	 -     	32 046.67		0.35	0.87
392.5	16.27	18.24	4.7	 -     	 -     	16	19	 -     	 -     		0.27	-0.76
392.75	16.39	19.51	5.1	 -     	1	16	19	 -     	32 046.67		0.39	0.51
393	16.46	18.98	5.1	 -     	 -     	16	19	 -     	 -     		0.46	-0.02
393.25	16.56	20.27	5.1	 -     	1	16	19	 -     	32 046.67		0.56	1.27
393.5	16.59	19.16	5.1	 -     	 -     	16	19	 -     	 -     		0.59	0.16
393.75	16.73	17.16	8.5	 -     	 -     	16	19	 -     	 -     		0.73	-1.84
394	17.03	21.27	8.5	 -     	1	16	19	 -     	32 046.67		1.03	2.27
394.25	17.09	19.53	8.5	 -     	 -     	16	19	 -     	 -     		1.09	0.53
394.5	17.12	17.59	8.5	 -     	 -     	16	19	 -     	 -     		1.12	-1.41
394.75	17.31	21.38	9.8	 -     	1	16	19	 -     	32 046.67		1.31	2.38
395	17.57	20.13	9.8	 -     	 -     	16	19	 -     	 -     		1.57	1.13
395.25	17.64	18.39	9.8	 -     	 -     	16	19	 -     	 -     		1.64	-0.61
395.5	17.74	22.07	9.8	 -     	1	16	19	 -     	32 046.67		1.74	3.07
395.75	17.76	20.29	10.4	 -     	 -     	16	19	 -     	 -     		1.76	1.29
396	18.03	18.63	10.4	 -     	 -     	16	19	 -     	 -     		2.03	-0.37
396.25	18.24	22.46	10.4	 -     	1	16	19	 -     	32 046.67		2.24	3.46
396.5	18.2	20.62	10.4	 -     	 -     	16	19	 -     	 -     		2.2	1.62
396.75	18.2	18.72	11.1	 -     	 -     	16	19	 -     	 -     		2.2	-0.28
397	18.61	22.69	11.1	 -     	1	16	19	 -     	32 046.67		2.61	3.69
397.25	18.69	20.97	11.1	 -     	 -     	16	19	 -     	 -     		2.69	1.97
397.5	18.59	19.03	11.1	 -     	 -     	16	19	 -     	 -     		2.59	0.03
397.75	18.54	19.57	11	 -     	 -     	16	19	 -     	 -     		2.54	0.57
398	18.73	19.68	11	 -     	 -     	16	19	 -     	 -     		2.73	0.68
398.25	22.27	19.83	11	1	 -     	19	16	32 046.67	 -     		3.27	3.83
398.5	20.43	19.71	11	 -     	 -     	19	16	 -     	 -     		1.43	3.71
398.75	18.02	19.58	7.9	 -     	 -     	19	16	 -     	 -     		-0.98	3.58
399	22.37	19.5	7.9	1	 -     	19	16	32 046.67	 -     		3.37	3.5
399.25	20.68	19.43	7.9	 -     	 -     	19	16	 -     	 -     		1.68	3.43
399.5	18.38	19.37	7.9	 -     	 -     	19	16	 -     	 -     		-0.62	3.37
399.75	22.27	19.39	6.6	1	 -     	19	16	32 046.67	 -     		3.27	3.39
400	21.03	19.25	6.6	 -     	 -     	19	16	 -     	 -     		2.03	3.25
400.25	19.12	19.18	6.6	 -     	 -     	19	16	 -     	 -     		0.12	3.18
400.5	19.55	19.18	6.6	 -     	 -     	19	16	 -     	 -     		0.55	3.18
400.75	19.5	19.16	5.7	 -     	 -     	19	16	 -     	 -     		0.5	3.16
401	20.23	19.27	5.7	 -     	 -     	19	16	 -     	 -     		1.23	3.27
401.25	19.42	19.01	5.7	 -     	 -     	19	16	 -     	 -     		0.42	3.01
401.5	19	18.9	5.7	 -     	 -     	19	16	 -     	 -     		0	2.9
401.75	19.08	18.92	5.2	 -     	 -     	19	16	 -     	 -     		0.08	2.92
402	18.99	18.81	5.2	 -     	 -     	19	16	 -     	 -     		-0.01	2.81
402.25	18.94	18.77	5.2	 -     	 -     	16	16	 -     	 -     		2.94	2.77
402.5	18.91	18.78	5.2	 -     	 -     	16	16	 -     	 -     		2.91	2.78
402.75	18.92	18.78	5.2	 -     	 -     	16	16	 -     	 -     		2.92	2.78
403	18.74	18.65	5.2	 -     	 -     	16	16	 -     	 -     		2.74	2.65
403.25	18.68	18.6	5.2	 -     	 -     	16	16	 -     	 -     		2.68	2.6
403.5	18.69	18.62	5.2	 -     	 -     	16	16	 -     	 -     		2.69	2.62
403.75	18.7	18.62	5.5	 -     	 -     	16	16	 -     	 -     		2.7	2.62
404	18.55	18.51	5.5	 -     	 -     	16	16	 -     	 -     		2.55	2.51
404.25	18.49	18.46	5.5	 -     	 -     	16	16	 -     	 -     		2.49	2.46
404.5	18.5	18.48	5.5	 -     	 -     	16	16	 -     	 -     		2.5	2.48
404.75	18.49	18.46	5.2	 -     	 -     	16	16	 -     	 -     		2.49	2.46
405	18.35	18.35	5.2	 -     	 -     	16	16	 -     	 -     		2.35	2.35
405.25	18.29	18.31	5.2	 -     	 -     	16	16	 -     	 -     		2.29	2.31
405.5	18.31	18.32	5.2	 -     	 -     	16	16	 -     	 -     		2.31	2.32
405.75	18.29	18.3	4.6	 -     	 -     	16	16	 -     	 -     		2.29	2.3
406	18.14	18.17	4.6	 -     	 -     	16	16	 -     	 -     		2.14	2.17
406.25	18.09	18.14	4.6	 -     	 -     	16	16	 -     	 -     		2.09	2.14
406.5	18.1	18.15	4.6	 -     	 -     	16	16	 -     	 -     		2.1	2.15
406.75	18.09	18.13	4.2	 -     	 -     	16	16	 -     	 -     		2.09	2.13
407	17.95	18.01	4.2	 -     	 -     	16	16	 -     	 -     		1.95	2.01
407.25	17.9	17.97	4.2	 -     	 -     	16	16	 -     	 -     		1.9	1.97
407.5	17.91	17.98	4.2	 -     	 -     	16	16	 -     	 -     		1.91	1.98
407.75	17.91	17.98	4.2	 -     	 -     	16	16	 -     	 -     		1.91	1.98
408	17.78	17.87	4.2	 -     	 -     	16	16	 -     	 -     		1.78	1.87
408.25	17.73	17.83	4.2	 -     	 -     	16	16	 -     	 -     		1.73	1.83
408.5	17.74	17.84	4.2	 -     	 -     	16	16	 -     	 -     		1.74	1.84
408.75	17.73	17.83	3.9	 -     	 -     	16	16	 -     	 -     		1.73	1.83
409	17.59	17.71	3.9	 -     	 -     	16	16	 -     	 -     		1.59	1.71
409.25	17.55	17.67	3.9	 -     	 -     	16	16	 -     	 -     		1.55	1.67
409.5	17.56	17.68	3.9	 -     	 -     	16	16	 -     	 -     		1.56	1.68
409.75	17.53	17.66	3.2	 -     	 -     	16	16	 -     	 -     		1.53	1.66
410	17.4	17.54	3.2	 -     	 -     	16	16	 -     	 -     		1.4	1.54
410.25	17.35	17.5	3.2	 -     	 -     	16	16	 -     	 -     		1.35	1.5
410.5	17.36	17.51	3.2	 -     	 -     	16	16	 -     	 -     		1.36	1.51
410.75	17.35	17.5	3	 -     	 -     	16	16	 -     	 -     		1.35	1.5
411	17.22	17.38	3	 -     	 -     	16	16	 -     	 -     		1.22	1.38
411.25	17.18	17.34	3	 -     	 -     	16	16	 -     	 -     		1.18	1.34
411.5	17.19	17.35	3	 -     	 -     	16	16	 -     	 -     		1.19	1.35
411.75	17.18	17.34	2.7	 -     	 -     	16	16	 -     	 -     		1.18	1.34
412	17.05	17.23	2.7	 -     	 -     	16	16	 -     	 -     		1.05	1.23
412.25	17	17.19	2.7	 -     	 -     	16	16	 -     	 -     		1	1.19
412.5	17.01	17.2	2.7	 -     	 -     	16	16	 -     	 -     		1.01	1.2
412.75	17	17.19	2.5	 -     	 -     	16	16	 -     	 -     		1	1.19
413	16.88	17.07	2.5	 -     	 -     	16	16	 -     	 -     		0.88	1.07
413.25	16.83	17.03	2.5	 -     	 -     	16	16	 -     	 -     		0.83	1.03
413.5	16.84	17.04	2.5	 -     	 -     	16	16	 -     	 -     		0.84	1.04
413.75	16.84	17.04	2.6	 -     	 -     	16	16	 -     	 -     		0.84	1.04
414	16.72	16.93	2.6	 -     	 -     	16	16	 -     	 -     		0.72	0.93
414.25	16.68	16.89	2.6	 -     	 -     	16	16	 -     	 -     		0.68	0.89
414.5	16.68	16.9	2.6	 -     	 -     	16	16	 -     	 -     		0.68	0.9
414.75	16.68	16.89	2.4	 -     	 -     	16	16	 -     	 -     		0.68	0.89
415	16.55	16.78	2.4	 -     	 -     	16	16	 -     	 -     		0.55	0.78
415.25	16.51	16.74	2.4	 -     	 -     	16	16	 -     	 -     		0.51	0.74
415.5	16.52	16.75	2.4	 -     	 -     	16	16	 -     	 -     		0.52	0.75
415.75	16.52	16.75	2.5	 -     	 -     	16	16	 -     	 -     		0.52	0.75
416	16.46	16.66	2.5	 -     	 -     	16	16	 -     	 -     		0.46	0.66
416.25	16.56	19.9	2.5	 -     	1	16	19	 -     	32 046.67		0.56	0.9
416.5	16.54	18.29	2.5	 -     	 -     	16	19	 -     	 -     		0.54	-0.71
416.75	16.55	19.52	2.7	 -     	1	16	19	 -     	32 046.67		0.55	0.52
417	16.49	18.96	2.7	 -     	 -     	16	19	 -     	 -     		0.49	-0.04
417.25	16.5	20.24	2.7	 -     	1	16	19	 -     	32 046.67		0.5	1.24
417.5	16.47	19.12	2.7	 -     	 -     	16	19	 -     	 -     		0.47	0.12
417.75	16.46	17.03	3.4	 -     	 -     	16	19	 -     	 -     		0.46	-1.97
418	16.5	21.05	3.4	 -     	1	16	19	 -     	32 046.67		0.5	2.05
418.25	16.44	19.3	3.4	 -     	 -     	16	19	 -     	 -     		0.44	0.3
418.5	16.41	17.36	3.4	 -     	 -     	16	19	 -     	 -     		0.41	-1.64
418.75	16.54	21.16	4.8	 -     	1	16	19	 -     	32 046.67		0.54	2.16
419	16.5	19.85	4.8	 -     	 -     	16	19	 -     	 -     		0.5	0.85
419.25	16.43	18.09	4.8	 -     	 -     	16	19	 -     	 -     		0.43	-0.91
419.5	16.52	21.78	4.8	 -     	1	16	19	 -     	32 046.67		0.52	2.78
419.75	16.53	20.02	6	 -     	 -     	16	19	 -     	 -     		0.53	1.02
420	16.49	18.33	6	 -     	 -     	16	19	 -     	 -     		0.49	-0.67
420.25	16.59	22.15	6	 -     	1	16	19	 -     	32 046.67		0.59	3.15
420.5	16.62	20.33	6	 -     	 -     	16	19	 -     	 -     		0.62	1.33
420.75	16.63	18.43	6.4	 -     	 -     	16	19	 -     	 -     		0.63	-0.57
421	16.74	22.35	6.4	 -     	1	16	19	 -     	32 046.67		0.74	3.35
421.25	16.74	20.61	6.4	 -     	 -     	16	19	 -     	 -     		0.74	1.61
421.5	16.7	18.67	6.4	 -     	 -     	16	19	 -     	 -     		0.7	-0.33
421.75	16.8	22.44	7.3	 -     	1	16	19	 -     	32 046.67		0.8	3.44
422	16.84	21.14	7.3	 -     	 -     	16	19	 -     	 -     		0.84	2.14
422.25	20.35	19.4	7.3	1	 -     	19	16	32 046.67	 -     		1.35	3.4
422.5	18.65	19.81	7.3	 -     	 -     	19	16	 -     	 -     		-0.35	3.81
422.75	19.98	19.71	7.3	1	 -     	19	16	32 046.67	 -     		0.98	3.71
423	19.53	19.61	7.3	 -     	 -     	19	16	 -     	 -     		0.53	3.61
423.25	17.56	19.52	7.3	 -     	 -     	19	16	 -     	 -     		-1.44	3.52
423.5	21.55	19.62	7.3	1	 -     	19	16	32 046.67	 -     		2.55	3.62
423.75	19.8	19.6	7.8	 -     	 -     	19	16	 -     	 -     		0.8	3.6
424	18.06	19.46	7.8	 -     	 -     	19	16	 -     	 -     		-0.94	3.46
424.25	22.16	19.49	7.8	1	 -     	19	16	32 046.67	 -     		3.16	3.49
424.5	20.25	19.45	7.8	 -     	 -     	19	16	 -     	 -     		1.25	3.45
424.75	18.11	19.38	6.7	 -     	 -     	19	16	 -     	 -     		-0.89	3.38
425	23.2	19.59	6.7	1	 -     	19	16	32 046.67	 -     		4.2	3.59
425.25	20.67	19.29	6.7	 -     	 -     	19	16	 -     	 -     		1.67	3.29
425.5	18.03	19.12	6.7	 -     	 -     	19	16	 -     	 -     		-0.97	3.12
425.75	22.05	19.18	4.8	1	 -     	19	16	32 046.67	 -     		3.05	3.18
426	20.8	19.01	3.9	 -     	 -     	19	16	 -     	 -     		1.8	3.01
426.25	18.84	18.94	3.9	 -     	 -     	16	16	 -     	 -     		2.84	2.94
426.5	19.23	18.95	3.9	 -     	 -     	16	16	 -     	 -     		3.23	2.95
426.75	19.15	18.95	3.9	 -     	 -     	16	16	 -     	 -     		3.15	2.95
427	18.93	18.8	3.9	 -     	 -     	16	16	 -     	 -     		2.93	2.8
427.25	18.84	18.74	3.9	 -     	 -     	16	16	 -     	 -     		2.84	2.74
427.5	18.86	18.76	3.9	 -     	 -     	16	16	 -     	 -     		2.86	2.76
427.75	18.85	18.75	3.7	 -     	 -     	16	16	 -     	 -     		2.85	2.75
428	18.65	18.61	3.7	 -     	 -     	16	16	 -     	 -     		2.65	2.61
428.25	18.58	18.56	3.7	 -     	 -     	16	16	 -     	 -     		2.58	2.56
428.5	18.59	18.57	3.7	 -     	 -     	16	16	 -     	 -     		2.59	2.57
428.75	18.6	18.58	3.9	 -     	 -     	16	16	 -     	 -     		2.6	2.58
429	18.43	18.45	3.9	 -     	 -     	16	16	 -     	 -     		2.43	2.45
429.25	18.37	18.4	3.9	 -     	 -     	16	16	 -     	 -     		2.37	2.4
429.5	18.38	18.42	3.9	 -     	 -     	16	16	 -     	 -     		2.38	2.42
429.75	18.39	18.42	4.2	 -     	 -     	16	16	 -     	 -     		2.39	2.42
430	18.24	18.31	4.2	 -     	 -     	16	16	 -     	 -     		2.24	2.31
430.25	18.18	18.26	4.2	 -     	 -     	16	16	 -     	 -     		2.18	2.26
430.5	18.19	18.27	4.2	 -     	 -     	16	16	 -     	 -     		2.19	2.27
430.75	18.21	18.29	4.8	 -     	 -     	16	16	 -     	 -     		2.21	2.29
431	18.08	18.18	4.8	 -     	 -     	16	16	 -     	 -     		2.08	2.18
431.25	18.02	18.14	4.8	 -     	 -     	16	16	 -     	 -     		2.02	2.14
431.5	18.03	18.15	4.8	 -     	 -     	16	16	 -     	 -     		2.03	2.15
431.75	18.03	18.14	4.6	 -     	 -     	16	16	 -     	 -     		2.03	2.14
432	17.89	18.03	4.6	 -     	 -     	16	16	 -     	 -     		1.89	2.03
432.25	17.84	17.99	4.6	 -     	 -     	16	16	 -     	 -     		1.84	1.99
432.5	17.85	18	4.6	 -     	 -     	16	16	 -     	 -     		1.85	2
432.75	17.84	17.99	4.4	 -     	 -     	16	16	 -     	 -     		1.84	1.99
433	17.71	17.88	4.4	 -     	 -     	16	16	 -     	 -     		1.71	1.88
433.25	17.67	17.84	4.4	 -     	 -     	16	16	 -     	 -     		1.67	1.84
433.5	17.68	17.85	4.4	 -     	 -     	16	16	 -     	 -     		1.68	1.85
433.75	17.68	17.85	4.5	 -     	 -     	16	16	 -     	 -     		1.68	1.85
434	17.56	17.75	4.5	 -     	 -     	16	16	 -     	 -     		1.56	1.75
434.25	17.51	17.71	4.5	 -     	 -     	16	16	 -     	 -     		1.51	1.71
434.5	17.52	17.72	4.5	 -     	 -     	16	16	 -     	 -     		1.52	1.72
434.75	17.5	17.7	3.8	 -     	 -     	16	16	 -     	 -     		1.5	1.7
435	17.36	17.58	3.8	 -     	 -     	16	16	 -     	 -     		1.36	1.58
435.25	17.32	17.55	3.8	 -     	 -     	16	16	 -     	 -     		1.32	1.55
435.5	17.33	17.56	3.8	 -     	 -     	16	16	 -     	 -     		1.33	1.56
435.75	17.34	17.57	4.1	 -     	 -     	16	16	 -     	 -     		1.34	1.57
436	17.22	17.47	4.1	 -     	 -     	16	16	 -     	 -     		1.22	1.47
436.25	17.18	17.43	4.1	 -     	 -     	16	16	 -     	 -     		1.18	1.43
436.5	17.19	17.44	4.1	 -     	 -     	16	16	 -     	 -     		1.19	1.44
436.75	17.19	17.44	4.2	 -     	 -     	16	16	 -     	 -     		1.19	1.44
437	17.07	17.34	4.2	 -     	 -     	16	16	 -     	 -     		1.07	1.34
437.25	17.03	17.3	4.2	 -     	 -     	16	16	 -     	 -     		1.03	1.3
437.5	17.04	17.31	4.2	 -     	 -     	16	16	 -     	 -     		1.04	1.31
437.75	17.06	17.33	4.9	 -     	 -     	16	16	 -     	 -     		1.06	1.33
438	16.96	17.24	4.9	 -     	 -     	16	16	 -     	 -     		0.96	1.24
438.25	16.92	17.2	4.9	 -     	 -     	16	16	 -     	 -     		0.92	1.2
438.5	16.93	17.21	4.9	 -     	 -     	16	16	 -     	 -     		0.93	1.21
438.75	16.94	17.23	5.4	 -     	 -     	16	16	 -     	 -     		0.94	1.23
439	16.85	17.14	5.4	 -     	 -     	16	16	 -     	 -     		0.85	1.14
439.25	16.81	17.11	5.4	 -     	 -     	16	16	 -     	 -     		0.81	1.11
439.5	16.81	17.11	5.4	 -     	 -     	16	16	 -     	 -     		0.81	1.11
439.75	16.91	17.21	8.6	 -     	 -     	16	16	 -     	 -     		0.91	1.21
440	16.88	17.18	8.6	 -     	 -     	16	16	 -     	 -     		0.88	1.18
440.25	16.92	20.41	8.6	 -     	1	16	19	 -     	32 046.67		0.92	1.41
440.5	16.9	18.79	8.6	 -     	 -     	16	19	 -     	 -     		0.9	-0.21
440.75	16.94	20.02	8.6	 -     	1	16	19	 -     	32 046.67		0.94	1.02
441	16.89	19.49	8.6	 -     	 -     	16	19	 -     	 -     		0.89	0.49
441.25	16.85	17.58	8.6	 -     	 -     	16	19	 -     	 -     		0.85	-1.42
441.5	16.94	21.32	8.6	 -     	1	16	19	 -     	32 046.67		0.94	2.32
441.75	16.93	19.54	9.2	 -     	 -     	16	19	 -     	 -     		0.93	0.54
442	16.86	17.88	9.2	 -     	 -     	16	19	 -     	 -     		0.86	-1.12
442.25	16.93	21.72	9.2	 -     	1	16	19	 -     	32 046.67		0.93	2.72
442.5	16.9	19.88	9.2	 -     	 -     	16	19	 -     	 -     		0.9	0.88
442.75	16.86	17.96	9.1	 -     	 -     	16	19	 -     	 -     		0.86	-1.04
443	16.91	21.9	9.1	 -     	1	16	19	 -     	32 046.67		0.91	2.9
443.25	16.86	20.15	9.1	 -     	 -     	16	19	 -     	 -     		0.86	1.15
443.5	16.82	18.2	9.1	 -     	 -     	16	19	 -     	 -     		0.82	-0.8
443.75	16.88	21.93	8.6	 -     	1	16	19	 -     	32 046.67		0.88	2.93
444	16.81	20.61	8.6	 -     	 -     	16	19	 -     	 -     		0.81	1.61
444.25	16.76	18.85	8.6	 -     	 -     	16	19	 -     	 -     		0.76	-0.15
444.5	16.83	22.54	8.6	 -     	1	16	19	 -     	32 046.67		0.83	3.54
444.75	16.78	20.72	8.2	 -     	 -     	16	19	 -     	 -     		0.78	1.72
445	16.68	18.98	8.2	 -     	 -     	16	19	 -     	 -     		0.68	-0.02
445.25	16.75	22.79	8.2	 -     	1	16	19	 -     	32 046.67		0.75	3.79
445.5	16.71	20.96	8.2	 -     	 -     	16	19	 -     	 -     		0.71	1.96
445.75	16.66	19.02	7.9	 -     	 -     	16	19	 -     	 -     		0.66	0.02
446	16.61	19.7	7.9	 -     	 -     	16	19	 -     	 -     		0.61	0.7
446.25	20.16	19.64	7.9	1	 -     	19	16	32 046.67	 -     		1.16	3.64
446.5	18.48	19.6	7.9	 -     	 -     	19	16	 -     	 -     		-0.52	3.6
446.75	19.81	19.63	7.9	1	 -     	19	16	32 046.67	 -     		0.81	3.63
447	19.24	19.47	7.9	 -     	 -     	19	16	 -     	 -     		0.24	3.47
447.25	17.25	19.39	7.9	 -     	 -     	19	16	 -     	 -     		-1.75	3.39
447.5	21.24	19.5	7.9	1	 -     	19	16	32 046.67	 -     		2.24	3.5
447.75	19.47	19.45	7.2	 -     	 -     	19	16	 -     	 -     		0.47	3.45
448	17.7	19.3	7.2	 -     	 -     	19	16	 -     	 -     		-1.3	3.3
448.25	21.83	19.35	7.2	1	 -     	19	16	32 046.67	 -     		2.83	3.35
448.5	19.97	19.32	7.2	 -     	 -     	19	16	 -     	 -     		0.97	3.32
448.75	17.8	19.24	5.9	 -     	 -     	19	16	 -     	 -     		-1.2	3.24
449	22.53	19.34	5.9	1	 -     	19	16	32 046.67	 -     		3.53	3.34
449.25	20.28	19.12	5.9	 -     	 -     	19	16	 -     	 -     		1.28	3.12
449.5	17.8	19	5.9	 -     	 -     	19	16	 -     	 -     		-1.2	3
449.75	21.85	19.1	6	1	 -     	19	16	32 046.67	 -     		2.85	3.1
450	20.63	18.97	5.5	 -     	 -     	19	16	 -     	 -     		1.63	2.97
450.25	18.65	18.89	5.5	 -     	 -     	16	16	 -     	 -     		2.65	2.89
450.5	19.04	18.91	5.5	 -     	 -     	16	16	 -     	 -     		3.04	2.91
450.75	18.95	18.91	5.5	 -     	 -     	16	16	 -     	 -     		2.95	2.91
451	18.77	18.77	5.5	 -     	 -     	16	16	 -     	 -     		2.77	2.77
451.25	18.69	18.72	5.5	 -     	 -     	16	16	 -     	 -     		2.69	2.72
451.5	18.7	18.74	5.5	 -     	 -     	16	16	 -     	 -     		2.7	2.74
451.75	18.7	18.73	5.4	 -     	 -     	16	16	 -     	 -     		2.7	2.73
452	18.52	18.61	5.4	 -     	 -     	16	16	 -     	 -     		2.52	2.61
452.25	18.45	18.56	5.4	 -     	 -     	16	16	 -     	 -     		2.45	2.56
452.5	18.46	18.58	5.4	 -     	 -     	16	16	 -     	 -     		2.46	2.58
452.75	18.45	18.57	5.2	 -     	 -     	16	16	 -     	 -     		2.45	2.57
453	18.3	18.45	5.2	 -     	 -     	16	16	 -     	 -     		2.3	2.45
453.25	18.24	18.41	5.2	 -     	 -     	16	16	 -     	 -     		2.24	2.41
453.5	18.25	18.42	5.2	 -     	 -     	16	16	 -     	 -     		2.25	2.42
453.75	18.24	18.4	4.9	 -     	 -     	16	16	 -     	 -     		2.24	2.4
454	18.09	18.29	4.9	 -     	 -     	16	16	 -     	 -     		2.09	2.29
454.25	18.04	18.25	4.9	 -     	 -     	16	16	 -     	 -     		2.04	2.25
454.5	18.05	18.26	4.9	 -     	 -     	16	16	 -     	 -     		2.05	2.26
454.75	18.05	18.25	4.8	 -     	 -     	16	16	 -     	 -     		2.05	2.25
455	17.91	18.14	4.8	 -     	 -     	16	16	 -     	 -     		1.91	2.14
455.25	17.86	18.1	4.8	 -     	 -     	16	16	 -     	 -     		1.86	2.1
455.5	17.87	18.11	4.8	 -     	 -     	16	16	 -     	 -     		1.87	2.11
455.75	17.86	18.1	4.5	 -     	 -     	16	16	 -     	 -     		1.86	2.1
456	17.73	17.98	4.5	 -     	 -     	16	16	 -     	 -     		1.73	1.98
456.25	17.68	17.95	4.5	 -     	 -     	16	16	 -     	 -     		1.68	1.95
456.5	17.69	17.96	4.5	 -     	 -     	16	16	 -     	 -     		1.69	1.96
456.75	17.69	17.95	4.5	 -     	 -     	16	16	 -     	 -     		1.69	1.95
457	17.56	17.85	4.5	 -     	 -     	16	16	 -     	 -     		1.56	1.85
457.25	17.52	17.81	4.5	 -     	 -     	16	16	 -     	 -     		1.52	1.81
457.5	17.53	17.82	4.5	 -     	 -     	16	16	 -     	 -     		1.53	1.82
457.75	17.52	17.81	4.5	 -     	 -     	16	16	 -     	 -     		1.52	1.81
458	17.41	17.71	4.5	 -     	 -     	16	16	 -     	 -     		1.41	1.71
458.25	17.36	17.67	4.5	 -     	 -     	16	16	 -     	 -     		1.36	1.67
458.5	17.37	17.68	4.5	 -     	 -     	16	16	 -     	 -     		1.37	1.68
458.75	17.37	17.68	4.7	 -     	 -     	16	16	 -     	 -     		1.37	1.68
459	17.26	17.58	4.7	 -     	 -     	16	16	 -     	 -     		1.26	1.58
459.25	17.22	17.54	4.7	 -     	 -     	16	16	 -     	 -     		1.22	1.54
459.5	17.23	17.55	4.7	 -     	 -     	16	16	 -     	 -     		1.23	1.55
459.75	17.22	17.54	4.5	 -     	 -     	16	16	 -     	 -     		1.22	1.54
460	17.1	17.44	4.5	 -     	 -     	16	16	 -     	 -     		1.1	1.44
460.25	17.06	17.4	4.5	 -     	 -     	16	16	 -     	 -     		1.06	1.4
460.5	17.07	17.41	4.5	 -     	 -     	16	16	 -     	 -     		1.07	1.41
460.75	17.06	17.4	4.3	 -     	 -     	16	16	 -     	 -     		1.06	1.4
461	16.95	17.3	4.3	 -     	 -     	16	16	 -     	 -     		0.95	1.3
461.25	16.91	17.26	4.3	 -     	 -     	16	16	 -     	 -     		0.91	1.26
461.5	16.92	17.27	4.3	 -     	 -     	16	16	 -     	 -     		0.92	1.27
461.75	16.91	17.27	4.3	 -     	 -     	16	16	 -     	 -     		0.91	1.27
462	16.81	17.17	4.3	 -     	 -     	16	16	 -     	 -     		0.81	1.17
462.25	16.76	17.13	4.3	 -     	 -     	16	16	 -     	 -     		0.76	1.13
462.5	16.77	17.14	4.3	 -     	 -     	16	16	 -     	 -     		0.77	1.14
462.75	16.77	17.14	4.4	 -     	 -     	16	16	 -     	 -     		0.77	1.14
463	16.67	17.04	4.4	 -     	 -     	16	16	 -     	 -     		0.67	1.04
463.25	16.63	17.01	4.4	 -     	 -     	16	16	 -     	 -     		0.63	1.01
463.5	16.64	17.02	4.4	 -     	 -     	16	16	 -     	 -     		0.64	1.02
463.75	16.64	17.02	4.5	 -     	 -     	16	16	 -     	 -     		0.64	1.02
464	16.54	16.92	4.5	 -     	 -     	16	16	 -     	 -     		0.54	0.92
464.25	16.5	16.89	4.5	 -     	 -     	16	16	 -     	 -     		0.5	0.89
464.5	16.51	16.9	4.5	 -     	 -     	16	16	 -     	 -     		0.51	0.9
464.75	16.5	16.89	4.3	 -     	 -     	16	16	 -     	 -     		0.5	0.89
465	16.41	16.8	4.3	 -     	 -     	16	16	 -     	 -     		0.41	0.8
465.25	16.38	16.77	4.3	 -     	 -     	16	16	 -     	 -     		0.38	0.77
465.5	16.39	16.79	4.3	 -     	 -     	16	16	 -     	 -     		0.39	0.79
465.75	16.41	16.81	4.9	 -     	 -     	16	16	 -     	 -     		0.41	0.81
466	16.33	16.73	4.9	 -     	 -     	16	16	 -     	 -     		0.33	0.73
466.25	16.31	16.71	4.9	 -     	 -     	16	16	 -     	 -     		0.31	0.71
466.5	16.33	16.72	4.9	 -     	 -     	16	16	 -     	 -     		0.33	0.72
466.75	16.35	16.74	5.2	 -     	 -     	16	16	 -     	 -     		0.35	0.74
467	16.34	16.69	5.2	 -     	 -     	16	16	 -     	 -     		0.34	0.69
467.25	16.37	16.69	5.2	 -     	 -     	16	16	 -     	 -     		0.37	0.69
467.5	16.41	16.71	5.2	 -     	 -     	16	16	 -     	 -     		0.41	0.71
467.75	16.38	16.71	5	 -     	 -     	16	16	 -     	 -     		0.38	0.71
468	16.33	16.65	5	 -     	 -     	16	16	 -     	 -     		0.33	0.65
468.25	16.31	16.63	5	 -     	 -     	16	16	 -     	 -     		0.31	0.63
468.5	16.3	16.63	5	 -     	 -     	16	16	 -     	 -     		0.3	0.63
468.75	16.29	16.63	5	 -     	 -     	16	16	 -     	 -     		0.29	0.63
469	16.24	16.57	5	 -     	 -     	16	16	 -     	 -     		0.24	0.57
469.25	16.22	16.55	5	 -     	 -     	16	16	 -     	 -     		0.22	0.55
469.5	16.22	16.55	5	 -     	 -     	16	16	 -     	 -     		0.22	0.55
469.75	16.22	16.56	5.2	 -     	 -     	16	16	 -     	 -     		0.22	0.56
470	16.17	16.5	5.2	 -     	 -     	16	16	 -     	 -     		0.17	0.5
470.25	16.15	16.48	5.2	 -     	 -     	16	16	 -     	 -     		0.15	0.48
470.5	16.16	16.48	5.2	 -     	 -     	16	16	 -     	 -     		0.16	0.48
470.75	16.14	16.47	5	 -     	 -     	16	16	 -     	 -     		0.14	0.47
471	16.07	16.4	5	 -     	 -     	16	16	 -     	 -     		0.07	0.4
471.25	16.03	16.37	5	 -     	 -     	16	16	 -     	 -     		0.03	0.37
471.5	16.02	16.36	5	 -     	 -     	16	16	 -     	 -     		0.02	0.36
471.75	16.01	16.35	5	 -     	 -     	16	16	 -     	 -     		0.01	0.35
472	15.93	16.27	5	 -     	 -     	16	16	 -     	 -     		-0.07	0.27
472.25	19.41	16.31	5	1	 -     	16	16	32 046.67	 -     		3.41	0.31
472.5	17.68	16.27	5	 -     	 -     	16	16	 -     	 -     		1.68	0.27
472.75	15.47	16.21	4.6	 -     	 -     	16	16	 -     	 -     		-0.53	0.21
473	19.74	16.21	4.6	1	 -     	16	16	32 046.67	 -     		3.74	0.21
473.25	18.03	16.16	4.6	 -     	 -     	16	16	 -     	 -     		2.03	0.16
473.5	15.85	16.11	4.6	 -     	 -     	16	16	 -     	 -     		-0.15	0.11
473.75	19.81	16.17	3.9	1	 -     	16	16	32 046.67	 -     		3.81	0.17
474	18.54	16.06	3.6	 -     	 -     	16	16	 -     	 -     		2.54	0.06
474.25	16.58	15.99	3.6	 -     	 -     	16	16	 -     	 -     		0.58	-0.01
474.5	17.08	19.21	3.6	 -     	1	16	16	 -     	32 046.67		1.08	3.21
474.75	16.96	17.55	3.6	 -     	 -     	16	16	 -     	 -     		0.96	1.55
475	16.78	15.82	3.6	 -     	 -     	16	16	 -     	 -     		0.78	-0.18
475.25	16.8	19.66	3.6	 -     	1	16	16	 -     	32 046.67		0.8	3.66
475.5	16.78	17.82	3.6	 -     	 -     	16	16	 -     	 -     		0.78	1.82
475.75	16.73	15.9	3.7	 -     	 -     	16	16	 -     	 -     		0.73	-0.1
476	16.67	19.81	3.7	 -     	1	16	16	 -     	32 046.67		0.67	3.81
476.25	16.59	18.06	3.7	 -     	 -     	16	16	 -     	 -     		0.59	2.06
476.5	16.55	16.12	3.7	 -     	 -     	16	16	 -     	 -     		0.55	0.12
476.75	16.56	16.66	3.8	 -     	 -     	16	16	 -     	 -     		0.56	0.66
477	16.44	16.69	3.8	 -     	 -     	16	16	 -     	 -     		0.44	0.69
477.25	16.4	16.79	3.8	 -     	 -     	16	16	 -     	 -     		0.4	0.79
477.5	16.41	16.76	3.8	 -     	 -     	16	16	 -     	 -     		0.41	0.76
477.75	16.4	16.76	3.6	 -     	 -     	16	16	 -     	 -     		0.4	0.76
478	16.27	16.59	3.6	 -     	 -     	16	16	 -     	 -     		0.27	0.59
478.25	16.22	16.53	3.6	 -     	 -     	16	16	 -     	 -     		0.22	0.53
478.5	16.23	16.55	3.6	 -     	 -     	16	16	 -     	 -     		0.23	0.55
478.75	16.23	16.54	3.6	 -     	 -     	16	16	 -     	 -     		0.23	0.54
479	16.11	16.42	3.6	 -     	 -     	16	16	 -     	 -     		0.11	0.42
479.25	16.06	16.37	3.6	 -     	 -     	16	16	 -     	 -     		0.06	0.37
479.5	16.07	16.38	3.6	 -     	 -     	16	16	 -     	 -     		0.07	0.38
479.75	16.07	16.38	3.6	 -     	 -     	16	16	 -     	 -     		0.07	0.38
480	15.96	16.27	3.6	 -     	 -     	16	16	 -     	 -     		-0.04	0.27
480.25	19.43	16.3	3.6	1	 -     	16	16	32 046.67	 -     		3.43	0.3
480.5	17.72	16.28	3.6	 -     	 -     	16	16	 -     	 -     		1.72	0.28
480.75	15.54	16.23	3.8	 -     	 -     	16	16	 -     	 -     		-0.46	0.23
481	19.8	16.23	3.8	1	 -     	16	16	32 046.67	 -     		3.8	0.23
481.25	18.09	16.16	3.8	 -     	 -     	16	16	 -     	 -     		2.09	0.16
481.5	15.9	16.13	3.8	 -     	 -     	16	16	 -     	 -     		-0.1	0.13
481.75	19.89	16.21	3.8	1	 -     	16	16	32 046.67	 -     		3.89	0.21
482	18.63	16.1	3.8	 -     	 -     	16	16	 -     	 -     		2.63	0.1
482.25	16.68	16.03	3.8	 -     	 -     	16	16	 -     	 -     		0.68	0.03
482.5	17.1	16.05	3.8	 -     	 -     	16	16	 -     	 -     		1.1	0.05
482.75	17.01	16.05	3.9	 -     	 -     	16	16	 -     	 -     		1.01	0.05
483	16.86	15.95	3.9	 -     	 -     	16	16	 -     	 -     		0.86	-0.05
483.25	16.86	19.11	3.9	 -     	1	16	16	 -     	32 046.67		0.86	3.11
483.5	16.84	17.46	3.9	 -     	 -     	16	16	 -     	 -     		0.84	1.46
483.75	16.79	15.48	3.8	 -     	 -     	16	16	 -     	 -     		0.79	-0.52
484	16.73	19.47	3.8	 -     	1	16	16	 -     	32 046.67		0.73	3.47
484.25	16.65	17.73	3.8	 -     	 -     	16	16	 -     	 -     		0.65	1.73
484.5	16.61	15.78	3.8	 -     	 -     	16	16	 -     	 -     		0.61	-0.22
484.75	16.69	19.53	3.8	 -     	1	16	16	 -     	32 046.67		0.69	3.53
485	16.55	18.19	3.8	 -     	 -     	16	16	 -     	 -     		0.55	2.19
485.25	16.47	16.44	3.8	 -     	 -     	16	16	 -     	 -     		0.47	0.44
485.5	16.48	16.92	3.8	 -     	 -     	16	16	 -     	 -     		0.48	0.92
485.75	16.49	16.79	3.9	 -     	 -     	16	16	 -     	 -     		0.49	0.79
486	16.36	16.67	3.9	 -     	 -     	16	16	 -     	 -     		0.36	0.67
486.25	16.31	16.6	3.9	 -     	 -     	16	16	 -     	 -     		0.31	0.6
486.5	16.32	16.62	3.9	 -     	 -     	16	16	 -     	 -     		0.32	0.62
486.75	16.31	16.61	3.8	 -     	 -     	16	16	 -     	 -     		0.31	0.61
487	16.19	16.47	3.8	 -     	 -     	16	16	 -     	 -     		0.19	0.47
487.25	16.14	16.42	3.8	 -     	 -     	16	16	 -     	 -     		0.14	0.42
487.5	16.15	16.43	3.8	 -     	 -     	16	16	 -     	 -     		0.15	0.43
487.75	16.15	16.43	3.7	 -     	 -     	16	16	 -     	 -     		0.15	0.43
488	16.08	16.32	3.7	 -     	 -     	16	16	 -     	 -     		0.08	0.32
488.25	16.1	16.3	3.7	 -     	 -     	16	16	 -     	 -     		0.1	0.3
488.5	16.11	16.32	3.7	 -     	 -     	16	16	 -     	 -     		0.11	0.32
488.75	16.1	16.32	3.8	 -     	 -     	16	16	 -     	 -     		0.1	0.32
489	16.02	16.23	3.8	 -     	 -     	16	16	 -     	 -     		0.02	0.23
489.25	15.99	16.2	3.8	 -     	 -     	16	16	 -     	 -     		-0.01	0.2
489.5	19.52	16.3	3.8	1	 -     	16	16	32 046.67	 -     		3.52	0.3
489.75	17.83	16.28	4.1	 -     	 -     	16	16	 -     	 -     		1.83	0.28
490	16	16.19	4.1	 -     	 -     	16	16	 -     	 -     		0	0.19
490.25	16.63	16.19	4.1	 -     	 -     	16	16	 -     	 -     		0.63	0.19
490.5	16.56	16.21	4.1	 -     	 -     	16	16	 -     	 -     		0.56	0.21
490.75	16.65	16.24	4.6	 -     	 -     	16	16	 -     	 -     		0.65	0.24
491	16.6	16.19	4.6	 -     	 -     	16	16	 -     	 -     		0.6	0.19
491.25	16.62	16.18	4.6	 -     	 -     	16	16	 -     	 -     		0.62	0.18
491.5	16.73	16.2	4.6	 -     	 -     	16	16	 -     	 -     		0.73	0.2
491.75	16.85	16.23	5.6	 -     	 -     	16	16	 -     	 -     		0.85	0.23
492	17.05	16.21	5.6	 -     	 -     	16	16	 -     	 -     		1.05	0.21
492.25	17.22	16.2	5.6	 -     	 -     	16	16	 -     	 -     		1.22	0.2
492.5	17.37	16.2	5.6	 -     	 -     	16	16	 -     	 -     		1.37	0.2
492.75	17.53	16.22	6.4	 -     	 -     	16	16	 -     	 -     		1.53	0.22
493	17.89	16.22	6.4	 -     	 -     	16	16	 -     	 -     		1.89	0.22
493.25	18.07	16.22	6.4	 -     	 -     	16	16	 -     	 -     		2.07	0.22
493.5	18.1	16.23	6.4	 -     	 -     	16	16	 -     	 -     		2.1	0.23
493.75	18.12	16.27	7.5	 -     	 -     	16	16	 -     	 -     		2.12	0.27
494	18.47	16.3	7.5	 -     	 -     	16	16	 -     	 -     		2.47	0.3
494.25	18.53	16.3	7.5	 -     	 -     	16	16	 -     	 -     		2.53	0.3
494.5	18.4	16.31	7.5	 -     	 -     	16	16	 -     	 -     		2.4	0.31
494.75	18.36	16.35	9.2	 -     	 -     	16	16	 -     	 -     		2.36	0.35
495	18.57	16.39	9.2	 -     	 -     	16	16	 -     	 -     		2.57	0.39
495.25	18.54	16.37	9.2	 -     	 -     	16	16	 -     	 -     		2.54	0.37
495.5	18.38	16.35	9.2	 -     	 -     	16	16	 -     	 -     		2.38	0.35
495.75	18.23	16.31	8.5	 -     	 -     	16	16	 -     	 -     		2.23	0.31
496	18.21	16.28	8.5	 -     	 -     	16	16	 -     	 -     		2.21	0.28
496.25	18.15	16.25	8.5	 -     	 -     	16	16	 -     	 -     		2.15	0.25
496.5	18.03	16.22	8.5	 -     	 -     	16	16	 -     	 -     		2.03	0.22
496.75	17.91	16.17	8	 -     	 -     	16	16	 -     	 -     		1.91	0.17
497	17.76	16.09	8	 -     	 -     	16	16	 -     	 -     		1.76	0.09
497.25	17.71	16.07	8	 -     	 -     	16	16	 -     	 -     		1.71	0.07
497.5	17.71	16.07	8	 -     	 -     	16	16	 -     	 -     		1.71	0.07
497.75	17.68	16.04	6.9	 -     	 -     	16	16	 -     	 -     		1.68	0.04
498	17.51	15.93	6.3	 -     	 -     	16	16	 -     	 -     		1.51	-0.07
498.25	17.52	19.11	6.3	 -     	1	16	16	 -     	32 046.67		1.52	3.11
498.5	17.5	17.45	6.3	 -     	 -     	16	16	 -     	 -     		1.5	1.45
498.75	17.45	15.48	6.3	 -     	 -     	16	16	 -     	 -     		1.45	-0.52
499	17.42	19.48	6.3	 -     	1	16	16	 -     	32 046.67		1.42	3.48
499.25	17.35	17.75	6.3	 -     	 -     	16	16	 -     	 -     		1.35	1.75
499.5	17.31	15.8	6.3	 -     	 -     	16	16	 -     	 -     		1.31	-0.2
499.75	17.4	19.56	6.5	 -     	1	16	16	 -     	32 046.67		1.4	3.56
500	17.28	18.24	6.5	 -     	 -     	16	16	 -     	 -     		1.28	2.24
500.25	17.2	16.49	6.5	 -     	 -     	16	16	 -     	 -     		1.2	0.49
500.5	17.21	16.98	6.5	 -     	 -     	16	16	 -     	 -     		1.21	0.98
500.75	17.21	16.84	6.5	 -     	 -     	16	16	 -     	 -     		1.21	0.84
501	17.09	16.74	6.5	 -     	 -     	16	16	 -     	 -     		1.09	0.74
501.25	17.05	16.68	6.5	 -     	 -     	16	16	 -     	 -     		1.05	0.68
501.5	17.06	16.69	6.5	 -     	 -     	16	16	 -     	 -     		1.06	0.69
501.75	17.03	16.67	5.7	 -     	 -     	16	16	 -     	 -     		1.03	0.67
502	16.9	16.53	5.7	 -     	 -     	16	16	 -     	 -     		0.9	0.53
502.25	16.87	16.49	5.7	 -     	 -     	16	16	 -     	 -     		0.87	0.49
502.5	16.87	16.5	5.7	 -     	 -     	16	16	 -     	 -     		0.87	0.5
502.75	16.84	16.47	4.6	 -     	 -     	16	16	 -     	 -     		0.84	0.47
503	16.71	16.34	4.6	 -     	 -     	16	16	 -     	 -     		0.71	0.34
503.25	16.67	16.31	4.6	 -     	 -     	16	16	 -     	 -     		0.67	0.31
503.5	16.68	16.31	4.6	 -     	 -     	16	16	 -     	 -     		0.68	0.31
503.75	16.66	16.29	4	 -     	 -     	16	16	 -     	 -     		0.66	0.29
504	16.53	16.18	4	 -     	 -     	16	16	 -     	 -     		0.53	0.18
504.25	16.49	16.14	4	 -     	 -     	16	16	 -     	 -     		0.49	0.14
504.5	16.5	16.15	4	 -     	 -     	16	16	 -     	 -     		0.5	0.15
504.75	16.55	16.2	5.7	 -     	 -     	16	16	 -     	 -     		0.55	0.2
505	16.47	16.12	5.7	 -     	 -     	16	16	 -     	 -     		0.47	0.12
505.25	16.42	16.08	5.7	 -     	 -     	16	16	 -     	 -     		0.42	0.08
505.5	16.43	16.09	5.7	 -     	 -     	16	16	 -     	 -     		0.43	0.09
505.75	16.41	16.07	5.2	 -     	 -     	16	16	 -     	 -     		0.41	0.07
506	16.3	15.98	5.2	 -     	 -     	16	16	 -     	 -     		0.3	-0.02
506.25	16.34	19.15	5.2	 -     	1	16	16	 -     	32 046.67		0.34	3.15
506.5	16.32	17.5	5.2	 -     	 -     	16	16	 -     	 -     		0.32	1.5
506.75	16.3	15.56	6.4	 -     	 -     	16	16	 -     	 -     		0.3	-0.44
507	16.33	19.57	6.4	 -     	1	16	16	 -     	32 046.67		0.33	3.57
507.25	16.26	17.83	6.4	 -     	 -     	16	16	 -     	 -     		0.26	1.83
507.5	16.22	15.88	6.4	 -     	 -     	16	16	 -     	 -     		0.22	-0.12
507.75	16.28	19.61	5.8	 -     	1	16	16	 -     	32 046.67		0.28	3.61
508	16.18	18.28	5.8	 -     	 -     	16	16	 -     	 -     		0.18	2.28
508.25	16.11	16.53	5.8	 -     	 -     	16	16	 -     	 -     		0.11	0.53
508.5	16.12	17.02	5.8	 -     	 -     	16	16	 -     	 -     		0.12	1.02
508.75	16.13	16.89	5.9	 -     	 -     	16	16	 -     	 -     		0.13	0.89
509	16.03	16.77	5.9	 -     	 -     	16	16	 -     	 -     		0.03	0.77
509.25	15.99	16.71	5.9	 -     	 -     	16	16	 -     	 -     		-0.01	0.71
509.5	19.51	16.8	5.9	1	 -     	16	16	32 046.67	 -     		3.51	0.8
509.75	17.78	16.75	5.5	 -     	 -     	16	16	 -     	 -     		1.78	0.75
510	15.9	16.59	5.5	 -     	 -     	16	16	 -     	 -     		-0.1	0.59
510.25	20	16.63	5.5	1	 -     	16	16	32 046.67	 -     		4	0.63
510.5	18.15	16.61	5.5	 -     	 -     	16	16	 -     	 -     		2.15	0.61
510.75	15.98	16.54	5.1	 -     	 -     	16	16	 -     	 -     		-0.02	0.54
511	20.18	16.52	5.1	1	 -     	16	16	32 046.67	 -     		4.18	0.52
511.25	18.44	16.45	5.1	 -     	 -     	16	16	 -     	 -     		2.44	0.45
511.5	16.26	16.42	5.1	 -     	 -     	16	16	 -     	 -     		0.26	0.42
511.75	16.72	16.41	4.8	 -     	 -     	16	16	 -     	 -     		0.72	0.41
512	16.89	16.33	4.8	 -     	 -     	16	16	 -     	 -     		0.89	0.33
512.25	17.1	19.58	4.8	 -     	1	16	19	 -     	32 046.67		1.1	0.58
512.5	17.04	17.96	4.8	 -     	 -     	16	19	 -     	 -     		1.04	-1.04
512.75	17.04	19.17	4.3	 -     	1	16	19	 -     	32 046.67		1.04	0.17
513	16.89	18.6	4.3	 -     	 -     	16	19	 -     	 -     		0.89	-0.4
513.25	16.89	19.89	4.3	 -     	1	16	19	 -     	32 046.67		0.89	0.89
513.5	16.88	18.76	4.3	 -     	 -     	16	19	 -     	 -     		0.88	-0.24
513.75	17	19.95	7.2	 -     	1	16	19	 -     	32 046.67		1	0.95
514	16.96	19.43	7.2	 -     	 -     	16	19	 -     	 -     		0.96	0.43
514.25	16.88	17.47	7.2	 -     	 -     	16	19	 -     	 -     		0.88	-1.53
514.5	16.97	21.23	7.2	 -     	1	16	19	 -     	32 046.67		0.97	2.23
514.75	16.98	19.46	8.3	 -     	 -     	16	19	 -     	 -     		0.98	0.46
515	16.91	17.78	8.3	 -     	 -     	16	19	 -     	 -     		0.91	-1.22
515.25	16.97	21.59	8.3	 -     	1	16	19	 -     	32 046.67		0.97	2.59
515.5	16.93	19.76	8.3	 -     	 -     	16	19	 -     	 -     		0.93	0.76
515.75	16.89	17.84	9.2	 -     	 -     	16	19	 -     	 -     		0.89	-1.16
516	16.94	21.77	9.2	 -     	1	16	19	 -     	32 046.67		0.94	2.77
516.25	16.88	20.01	9.2	 -     	 -     	16	19	 -     	 -     		0.88	1.01
516.5	16.83	18.06	9.2	 -     	 -     	16	19	 -     	 -     		0.83	-0.94
516.75	16.94	21.83	10.1	 -     	1	16	19	 -     	32 046.67		0.94	2.83
517	16.9	20.51	10.1	 -     	 -     	16	19	 -     	 -     		0.9	1.51
517.25	16.84	18.76	10.1	 -     	 -     	16	19	 -     	 -     		0.84	-0.24
517.5	16.92	22.45	10.1	 -     	1	16	19	 -     	32 046.67		0.92	3.45
517.75	16.97	20.73	12.6	 -     	 -     	16	19	 -     	 -     		0.97	1.73
518	16.94	19.05	12.6	 -     	 -     	16	19	 -     	 -     		0.94	0.05
518.25	20.49	19.68	12.6	1	 -     	19	16	32 046.67	 -     		1.49	3.68
518.5	18.8	19.44	12.6	 -     	 -     	19	16	 -     	 -     		-0.2	3.44
518.75	20.13	19.54	13.1	1	 -     	19	16	32 046.67	 -     		1.13	3.54
519	19.59	19.37	13.1	 -     	 -     	19	16	 -     	 -     		0.59	3.37
519.25	17.55	19.28	13.1	 -     	 -     	19	16	 -     	 -     		-1.45	3.28
519.5	21.49	19.36	13.1	1	 -     	19	16	32 046.67	 -     		2.49	3.36
519.75	19.68	19.32	13.3	 -     	 -     	19	16	 -     	 -     		0.68	3.32
520	17.85	19.19	13.3	 -     	 -     	19	16	 -     	 -     		-1.15	3.19
520.25	21.95	19.24	13.3	1	 -     	19	16	32 046.67	 -     		2.95	3.24
520.5	20.09	19.2	13.3	 -     	 -     	19	16	 -     	 -     		1.09	3.2
520.75	17.92	19.14	13	 -     	 -     	19	16	 -     	 -     		-1.08	3.14
521	22.14	19.14	13	1	 -     	19	16	32 046.67	 -     		3.14	3.14
521.25	20.41	19.07	13	 -     	 -     	19	16	 -     	 -     		1.41	3.07
521.5	18.22	19.03	13	 -     	 -     	19	16	 -     	 -     		-0.78	3.03
521.75	22.16	19.07	11.7	1	 -     	19	16	32 046.67	 -     		3.16	3.07
522	20.92	18.97	12	 -     	 -     	19	16	 -     	 -     		1.92	2.97
522.25	18.94	18.91	12	 -     	 -     	16	16	 -     	 -     		2.94	2.91
522.5	19.33	18.92	12	 -     	 -     	16	16	 -     	 -     		3.33	2.92
522.75	19.25	18.92	12	 -     	 -     	16	16	 -     	 -     		3.25	2.92
523	19.11	18.83	12	 -     	 -     	16	16	 -     	 -     		3.11	2.83
523.25	19.05	18.8	12	 -     	 -     	16	16	 -     	 -     		3.05	2.8
523.5	19.07	18.81	12	 -     	 -     	16	16	 -     	 -     		3.07	2.81
523.75	19.05	18.79	11.6	 -     	 -     	16	16	 -     	 -     		3.05	2.79
524	18.91	18.71	11.6	 -     	 -     	16	16	 -     	 -     		2.91	2.71
524.25	18.86	18.68	11.6	 -     	 -     	16	16	 -     	 -     		2.86	2.68
524.5	18.87	18.69	11.6	 -     	 -     	16	16	 -     	 -     		2.87	2.69
524.75	18.86	18.67	11.2	 -     	 -     	16	16	 -     	 -     		2.86	2.67
525	18.74	18.59	11.2	 -     	 -     	16	16	 -     	 -     		2.74	2.59
525.25	18.7	18.56	11.2	 -     	 -     	16	16	 -     	 -     		2.7	2.56
525.5	18.71	18.57	11.2	 -     	 -     	16	16	 -     	 -     		2.71	2.57
525.75	18.75	18.61	12.7	 -     	 -     	16	16	 -     	 -     		2.75	2.61
526	18.68	18.57	12.7	 -     	 -     	16	16	 -     	 -     		2.68	2.57
526.25	18.63	18.53	12.7	 -     	 -     	16	16	 -     	 -     		2.63	2.53
526.5	18.64	18.54	12.7	 -     	 -     	16	16	 -     	 -     		2.64	2.54
526.75	18.63	18.52	12.2	 -     	 -     	16	16	 -     	 -     		2.63	2.52
527	18.54	18.45	12.2	 -     	 -     	16	16	 -     	 -     		2.54	2.45
527.25	18.51	18.43	12.2	 -     	 -     	16	16	 -     	 -     		2.51	2.43
527.5	18.51	18.44	12.2	 -     	 -     	16	16	 -     	 -     		2.51	2.44
527.75	18.47	18.4	10.8	 -     	 -     	16	16	 -     	 -     		2.47	2.4
528	18.36	18.31	10.8	 -     	 -     	16	16	 -     	 -     		2.36	2.31
528.25	18.33	18.29	10.8	 -     	 -     	16	16	 -     	 -     		2.33	2.29
528.5	18.34	18.3	10.8	 -     	 -     	16	16	 -     	 -     		2.34	2.3
528.75	18.35	18.31	11.2	 -     	 -     	16	16	 -     	 -     		2.35	2.31
529	18.27	18.24	11.2	 -     	 -     	16	16	 -     	 -     		2.27	2.24
529.25	18.24	18.22	11.2	 -     	 -     	16	16	 -     	 -     		2.24	2.22
529.5	18.24	18.22	11.2	 -     	 -     	16	16	 -     	 -     		2.24	2.22
529.75	18.24	18.22	11	 -     	 -     	16	16	 -     	 -     		2.24	2.22
530	18.15	18.15	11	 -     	 -     	16	16	 -     	 -     		2.15	2.15
530.25	18.12	18.12	11	 -     	 -     	16	16	 -     	 -     		2.12	2.12
530.5	18.13	18.13	11	 -     	 -     	16	16	 -     	 -     		2.13	2.13
530.75	18.13	18.13	10.9	 -     	 -     	16	16	 -     	 -     		2.13	2.13
531	18.05	18.06	10.9	 -     	 -     	16	16	 -     	 -     		2.05	2.06
531.25	18.02	18.04	10.9	 -     	 -     	16	16	 -     	 -     		2.02	2.04
531.5	18.02	18.04	10.9	 -     	 -     	16	16	 -     	 -     		2.02	2.04
531.75	18	18.02	10.1	 -     	 -     	16	16	 -     	 -     		2	2.02
532	17.91	17.94	10.1	 -     	 -     	16	16	 -     	 -     		1.91	1.94
532.25	17.88	17.92	10.1	 -     	 -     	16	16	 -     	 -     		1.88	1.92
532.5	17.89	17.92	10.1	 -     	 -     	16	16	 -     	 -     		1.89	1.92
532.75	17.86	17.9	9.4	 -     	 -     	16	16	 -     	 -     		1.86	1.9
533	17.77	17.82	9.4	 -     	 -     	16	16	 -     	 -     		1.77	1.82
533.25	17.74	17.8	9.4	 -     	 -     	16	16	 -     	 -     		1.74	1.8
533.5	17.75	17.8	9.4	 -     	 -     	16	16	 -     	 -     		1.75	1.8
533.75	17.75	17.8	9.4	 -     	 -     	16	16	 -     	 -     		1.75	1.8
534	17.66	17.73	9.4	 -     	 -     	16	16	 -     	 -     		1.66	1.73
534.25	17.63	17.7	9.4	 -     	 -     	16	16	 -     	 -     		1.63	1.7
534.5	17.64	17.71	9.4	 -     	 -     	16	16	 -     	 -     		1.64	1.71
534.75	17.62	17.69	8.7	 -     	 -     	16	16	 -     	 -     		1.62	1.69
535	17.52	17.6	8.7	 -     	 -     	16	16	 -     	 -     		1.52	1.6
535.25	17.5	17.58	8.7	 -     	 -     	16	16	 -     	 -     		1.5	1.58
535.5	17.5	17.59	8.7	 -     	 -     	16	16	 -     	 -     		1.5	1.59
535.75	17.52	17.6	9.3	 -     	 -     	16	16	 -     	 -     		1.52	1.6
536	17.48	17.55	9.3	 -     	 -     	16	16	 -     	 -     		1.48	1.55
536.25	17.53	20.79	9.3	 -     	1	16	19	 -     	32 046.67		1.53	1.79
536.5	17.49	19.17	9.3	 -     	 -     	16	19	 -     	 -     		1.49	0.17
536.75	17.47	17.22	9.9	 -     	 -     	16	19	 -     	 -     		1.47	-1.78
537	17.53	21.28	9.9	 -     	1	16	19	 -     	32 046.67		1.53	2.28
537.25	17.49	19.57	9.9	 -     	 -     	16	19	 -     	 -     		1.49	0.57
537.5	17.46	17.63	9.9	 -     	 -     	16	19	 -     	 -     		1.46	-1.37
537.75	17.54	21.36	9.6	 -     	1	16	19	 -     	32 046.67		1.54	2.36
538	17.49	20.09	9.6	 -     	 -     	16	19	 -     	 -     		1.49	1.09
538.25	17.45	18.37	9.6	 -     	 -     	16	19	 -     	 -     		1.45	-0.63
538.5	17.54	22.06	9.6	 -     	1	16	19	 -     	32 046.67		1.54	3.06
538.75	17.55	20.3	10.5	 -     	 -     	16	19	 -     	 -     		1.55	1.3
539	17.53	18.64	10.5	 -     	 -     	16	19	 -     	 -     		1.53	-0.36
539.25	17.68	22.48	10.5	 -     	1	16	19	 -     	32 046.67		1.68	3.48
539.5	17.71	20.66	10.5	 -     	 -     	16	19	 -     	 -     		1.71	1.66
539.75	17.8	18.79	12.1	 -     	 -     	16	19	 -     	 -     		1.8	-0.21
540	18.08	22.78	12.1	 -     	1	16	19	 -     	32 046.67		2.08	3.78
540.25	18.22	21.05	12.1	 -     	 -     	16	19	 -     	 -     		2.22	2.05
540.5	18.28	19.12	12.1	 -     	 -     	16	19	 -     	 -     		2.28	0.12
540.75	18.33	19.69	12.8	 -     	 -     	16	19	 -     	 -     		2.33	0.69
541	18.45	19.81	12.8	 -     	 -     	16	19	 -     	 -     		2.45	0.81
541.25	18.4	19.94	12.8	 -     	 -     	16	19	 -     	 -     		2.4	0.94
541.5	18.23	19.89	12.8	 -     	 -     	16	19	 -     	 -     		2.23	0.89
541.75	18.18	19.91	13.1	 -     	 -     	16	19	 -     	 -     		2.18	0.91
542	18.27	19.83	13.1	 -     	 -     	16	19	 -     	 -     		2.27	0.83
542.25	21.85	19.82	13.1	1	 -     	19	16	32 046.67	 -     		2.85	3.82
542.5	20.14	19.75	13.1	 -     	 -     	19	16	 -     	 -     		1.14	3.75
542.75	17.92	19.69	12.5	 -     	 -     	19	16	 -     	 -     		-1.08	3.69
543	22.31	19.72	12.5	1	 -     	19	16	32 046.67	 -     		3.31	3.72
543.25	20.65	19.67	12.5	 -     	 -     	19	16	 -     	 -     		1.65	3.67
543.5	18.45	19.62	12.5	 -     	 -     	19	16	 -     	 -     		-0.55	3.62
543.75	22.45	19.69	12.3	1	 -     	19	16	32 046.67	 -     		3.45	3.69
544	21.32	19.62	12.3	 -     	 -     	19	16	 -     	 -     		2.32	3.62
544.25	19.38	19.56	12.3	 -     	 -     	19	16	 -     	 -     		0.38	3.56
544.5	19.76	19.55	12.3	 -     	 -     	19	16	 -     	 -     		0.76	3.55
544.75	19.63	19.52	11.7	 -     	 -     	19	16	 -     	 -     		0.63	3.52
545	19.63	19.45	11.7	 -     	 -     	19	16	 -     	 -     		0.63	3.45
545.25	19.43	19.37	11.7	 -     	 -     	19	16	 -     	 -     		0.43	3.37
545.5	19.36	19.36	11.7	 -     	 -     	19	16	 -     	 -     		0.36	3.36
545.75	19.35	19.33	10.8	 -     	 -     	19	16	 -     	 -     		0.35	3.33
546	19.2	19.21	9.9	 -     	 -     	19	16	 -     	 -     		0.2	3.21
546.25	19.11	19.17	9.9	 -     	 -     	16	16	 -     	 -     		3.11	3.17
546.5	19.09	19.18	9.9	 -     	 -     	16	16	 -     	 -     		3.09	3.18
546.75	19.1	19.17	9.9	 -     	 -     	16	16	 -     	 -     		3.1	3.17
547	18.97	19.08	9.9	 -     	 -     	16	16	 -     	 -     		2.97	3.08
547.25	18.93	19.05	9.9	 -     	 -     	16	16	 -     	 -     		2.93	3.05
547.5	18.94	19.06	9.9	 -     	 -     	16	16	 -     	 -     		2.94	3.06
547.75	18.94	19.06	10.1	 -     	 -     	16	16	 -     	 -     		2.94	3.06
548	18.84	18.98	10.1	 -     	 -     	16	16	 -     	 -     		2.84	2.98
548.25	18.79	18.94	10.1	 -     	 -     	16	16	 -     	 -     		2.79	2.94
548.5	18.8	18.95	10.1	 -     	 -     	16	16	 -     	 -     		2.8	2.95
548.75	18.77	18.92	9.1	 -     	 -     	16	16	 -     	 -     		2.77	2.92
549	18.65	18.82	9.1	 -     	 -     	16	16	 -     	 -     		2.65	2.82
549.25	18.62	18.79	9.1	 -     	 -     	16	16	 -     	 -     		2.62	2.79
549.5	18.62	18.8	9.1	 -     	 -     	16	16	 -     	 -     		2.62	2.8
549.75	18.67	18.85	10.7	 -     	 -     	16	16	 -     	 -     		2.67	2.85
550	18.6	18.79	10.7	 -     	 -     	16	16	 -     	 -     		2.6	2.79
550.25	18.56	18.75	10.7	 -     	 -     	16	16	 -     	 -     		2.56	2.75
550.5	18.57	18.76	10.7	 -     	 -     	16	16	 -     	 -     		2.57	2.76
550.75	18.56	18.75	10.5	 -     	 -     	16	16	 -     	 -     		2.56	2.75
551	18.47	18.68	10.5	 -     	 -     	16	16	 -     	 -     		2.47	2.68
551.25	18.44	18.65	10.5	 -     	 -     	16	16	 -     	 -     		2.44	2.65
551.5	18.45	18.66	10.5	 -     	 -     	16	16	 -     	 -     		2.45	2.66
551.75	18.39	18.61	8.8	 -     	 -     	16	16	 -     	 -     		2.39	2.61
552	18.28	18.5	8.8	 -     	 -     	16	16	 -     	 -     		2.28	2.5
552.25	18.25	18.48	8.8	 -     	 -     	16	16	 -     	 -     		2.25	2.48
552.5	18.26	18.49	8.8	 -     	 -     	16	16	 -     	 -     		2.26	2.49
552.75	18.27	18.5	9.1	 -     	 -     	16	16	 -     	 -     		2.27	2.5
553	18.18	18.42	9.1	 -     	 -     	16	16	 -     	 -     		2.18	2.42
553.25	18.14	18.39	9.1	 -     	 -     	16	16	 -     	 -     		2.14	2.39
553.5	18.15	18.4	9.1	 -     	 -     	16	16	 -     	 -     		2.15	2.4
553.75	18.11	18.36	7.9	 -     	 -     	16	16	 -     	 -     		2.11	2.36
554	18	18.26	7.9	 -     	 -     	16	16	 -     	 -     		2	2.26
554.25	17.97	18.24	7.9	 -     	 -     	16	16	 -     	 -     		1.97	2.24
554.5	17.98	18.24	7.9	 -     	 -     	16	16	 -     	 -     		1.98	2.24
554.75	17.96	18.22	7.2	 -     	 -     	16	16	 -     	 -     		1.96	2.22
555	17.85	18.12	7.2	 -     	 -     	16	16	 -     	 -     		1.85	2.12
555.25	17.82	18.1	7.2	 -     	 -     	16	16	 -     	 -     		1.82	2.1
555.5	17.83	18.1	7.2	 -     	 -     	16	16	 -     	 -     		1.83	2.1
555.75	17.79	18.07	6.2	 -     	 -     	16	16	 -     	 -     		1.79	2.07
556	17.68	17.97	6.2	 -     	 -     	16	16	 -     	 -     		1.68	1.97
556.25	17.65	17.94	6.2	 -     	 -     	16	16	 -     	 -     		1.65	1.94
556.5	17.65	17.95	6.2	 -     	 -     	16	16	 -     	 -     		1.65	1.95
556.75	17.64	17.94	5.9	 -     	 -     	16	16	 -     	 -     		1.64	1.94
557	17.54	17.84	5.9	 -     	 -     	16	16	 -     	 -     		1.54	1.84
557.25	17.5	17.81	5.9	 -     	 -     	16	16	 -     	 -     		1.5	1.81
557.5	17.51	17.82	5.9	 -     	 -     	16	16	 -     	 -     		1.51	1.82
557.75	17.5	17.81	5.7	 -     	 -     	16	16	 -     	 -     		1.5	1.81
558	17.4	17.71	5.7	 -     	 -     	16	16	 -     	 -     		1.4	1.71
558.25	17.36	17.68	5.7	 -     	 -     	16	16	 -     	 -     		1.36	1.68
558.5	17.37	17.69	5.7	 -     	 -     	16	16	 -     	 -     		1.37	1.69
558.75	17.37	17.69	5.8	 -     	 -     	16	16	 -     	 -     		1.37	1.69
559	17.27	17.6	5.8	 -     	 -     	16	16	 -     	 -     		1.27	1.6
559.25	17.24	17.56	5.8	 -     	 -     	16	16	 -     	 -     		1.24	1.56
559.5	17.25	17.57	5.8	 -     	 -     	16	16	 -     	 -     		1.25	1.57
559.75	17.26	17.59	6.4	 -     	 -     	16	16	 -     	 -     		1.26	1.59
560	17.99	17.68	6.4	 -     	 -     	16	16	 -     	 -     		1.99	1.68
560.25	17.99	20.9	6.4	 -     	1	16	19	 -     	32 046.67		1.99	1.9
560.5	17.67	19.22	6.4	 -     	 -     	16	19	 -     	 -     		1.67	0.22
560.75	17.71	17.25	6.2	 -     	 -     	16	19	 -     	 -     		1.71	-1.75
561	18.08	21.34	6.2	 -     	1	16	19	 -     	32 046.67		2.08	2.34
561.25	18.22	19.64	6.2	 -     	 -     	16	19	 -     	 -     		2.22	0.64
561.5	18.24	17.7	6.2	 -     	 -     	16	19	 -     	 -     		2.24	-1.3
561.75	18.42	21.46	6.5	 -     	1	16	19	 -     	32 046.67		2.42	2.46
562	18.69	20.22	6.5	 -     	 -     	16	19	 -     	 -     		2.69	1.22
562.25	18.8	18.5	6.5	 -     	 -     	16	19	 -     	 -     		2.8	-0.5
562.5	18.94	22.18	6.5	 -     	1	16	19	 -     	32 046.67		2.94	3.18
562.75	19.03	20.44	8.4	 -     	 -     	16	19	 -     	 -     		3.03	1.44
563	19.39	18.82	8.4	 -     	 -     	16	19	 -     	 -     		3.39	-0.18
563.25	19.63	22.65	8.4	 -     	1	16	19	 -     	32 046.67		3.63	3.65
563.5	19.6	20.8	8.4	 -     	 -     	16	19	 -     	 -     		3.6	1.8
563.75	19.61	18.96	11.5	 -     	 -     	16	19	 -     	 -     		3.61	-0.04
564	20.03	22.98	11.5	 -     	1	16	19	 -     	32 046.67		4.03	3.98
564.25	20.03	21.24	11.5	 -     	 -     	16	19	 -     	 -     		4.03	2.24
564.5	19.85	19.3	11.5	 -     	 -     	16	19	 -     	 -     		3.85	0.3
564.75	19.8	19.86	12	 -     	 -     	16	19	 -     	 -     		3.8	0.86
565	20.03	19.99	12	 -     	 -     	16	19	 -     	 -     		4.03	0.99
565.25	20.08	20.13	12	 -     	 -     	16	19	 -     	 -     		4.08	1.13
565.5	20.01	20.1	12	 -     	 -     	16	19	 -     	 -     		4.01	1.1
565.75	19.98	20.12	12.3	 -     	 -     	16	19	 -     	 -     		3.98	1.12
566	20.08	20.04	12.3	 -     	 -     	16	19	 -     	 -     		4.08	1.04
566.25	20.08	19.95	12.3	 -     	 -     	19	16	 -     	 -     		1.08	3.95
566.5	20.01	19.91	12.3	 -     	 -     	19	16	 -     	 -     		1.01	3.91
566.75	19.96	19.91	12.2	 -     	 -     	19	16	 -     	 -     		0.96	3.91
567	20	19.85	12.2	 -     	 -     	19	16	 -     	 -     		1	3.85
567.25	20	19.83	12.2	 -     	 -     	19	16	 -     	 -     		1	3.83
567.5	19.96	19.82	12.2	 -     	 -     	19	16	 -     	 -     		0.96	3.82
567.75	19.93	19.82	12.4	 -     	 -     	19	16	 -     	 -     		0.93	3.82
568	19.91	19.76	12.4	 -     	 -     	19	16	 -     	 -     		0.91	3.76
568.25	19.87	19.72	12.4	 -     	 -     	19	16	 -     	 -     		0.87	3.72
568.5	19.81	19.7	12.4	 -     	 -     	19	16	 -     	 -     		0.81	3.7
568.75	19.71	19.65	12	 -     	 -     	19	16	 -     	 -     		0.71	3.65
569	19.6	19.56	12	 -     	 -     	19	16	 -     	 -     		0.6	3.56
569.25	19.57	19.53	12	 -     	 -     	19	16	 -     	 -     		0.57	3.53
569.5	19.57	19.53	12	 -     	 -     	19	16	 -     	 -     		0.57	3.53
569.75	19.54	19.5	11.1	 -     	 -     	19	16	 -     	 -     		0.54	3.5
570	19.37	19.34	9.1	 -     	 -     	19	16	 -     	 -     		0.37	3.34
570.25	19.26	19.28	9.1	 -     	 -     	16	16	 -     	 -     		3.26	3.28
570.5	19.24	19.3	9.1	 -     	 -     	16	16	 -     	 -     		3.24	3.3
570.75	19.25	19.29	9.1	 -     	 -     	16	16	 -     	 -     		3.25	3.29
571	19.13	19.19	9.1	 -     	 -     	16	16	 -     	 -     		3.13	3.19
571.25	19.09	19.16	9.1	 -     	 -     	16	16	 -     	 -     		3.09	3.16
571.5	19.1	19.17	9.1	 -     	 -     	16	16	 -     	 -     		3.1	3.17
571.75	19.08	19.15	8.5	 -     	 -     	16	16	 -     	 -     		3.08	3.15
572	18.96	19.04	8.5	 -     	 -     	16	16	 -     	 -     		2.96	3.04
572.25	18.92	19.01	8.5	 -     	 -     	16	16	 -     	 -     		2.92	3.01
572.5	18.92	19.02	8.5	 -     	 -     	16	16	 -     	 -     		2.92	3.02
572.75	18.89	18.98	7.3	 -     	 -     	16	16	 -     	 -     		2.89	2.98
573	18.75	18.87	7.3	 -     	 -     	16	16	 -     	 -     		2.75	2.87
573.25	18.72	18.84	7.3	 -     	 -     	16	16	 -     	 -     		2.72	2.84
573.5	18.72	18.85	7.3	 -     	 -     	16	16	 -     	 -     		2.72	2.85
573.75	18.69	18.81	6.3	 -     	 -     	16	16	 -     	 -     		2.69	2.81
574	18.56	18.7	6.3	 -     	 -     	16	16	 -     	 -     		2.56	2.7
574.25	18.52	18.67	6.3	 -     	 -     	16	16	 -     	 -     		2.52	2.67
574.5	18.53	18.67	6.3	 -     	 -     	16	16	 -     	 -     		2.53	2.67
574.75	18.5	18.64	5.3	 -     	 -     	16	16	 -     	 -     		2.5	2.64
575	18.36	18.52	5.3	 -     	 -     	16	16	 -     	 -     		2.36	2.52
575.25	18.32	18.49	5.3	 -     	 -     	16	16	 -     	 -     		2.32	2.49
575.5	18.33	18.5	5.3	 -     	 -     	16	16	 -     	 -     		2.33	2.5
575.75	18.3	18.47	4.5	 -     	 -     	16	16	 -     	 -     		2.3	2.47
576	18.17	18.35	4.5	 -     	 -     	16	16	 -     	 -     		2.17	2.35
576.25	18.13	18.31	4.5	 -     	 -     	16	16	 -     	 -     		2.13	2.31
576.5	18.13	18.32	4.5	 -     	 -     	16	16	 -     	 -     		2.13	2.32
576.75	18.12	18.31	4.1	 -     	 -     	16	16	 -     	 -     		2.12	2.31
577	17.99	18.19	4.1	 -     	 -     	16	16	 -     	 -     		1.99	2.19
577.25	17.95	18.15	4.1	 -     	 -     	16	16	 -     	 -     		1.95	2.15
577.5	17.96	18.16	4.1	 -     	 -     	16	16	 -     	 -     		1.96	2.16
577.75	17.93	18.13	3.2	 -     	 -     	16	16	 -     	 -     		1.93	2.13
578	17.79	18.01	3.2	 -     	 -     	16	16	 -     	 -     		1.79	2.01
578.25	17.74	17.97	3.2	 -     	 -     	16	16	 -     	 -     		1.74	1.97
578.5	17.75	17.98	3.2	 -     	 -     	16	16	 -     	 -     		1.75	1.98
578.75	17.74	17.96	2.7	 -     	 -     	16	16	 -     	 -     		1.74	1.96
579	17.6	17.84	2.7	 -     	 -     	16	16	 -     	 -     		1.6	1.84
579.25	17.56	17.8	2.7	 -     	 -     	16	16	 -     	 -     		1.56	1.8
579.5	17.57	17.81	2.7	 -     	 -     	16	16	 -     	 -     		1.57	1.81
579.75	17.55	17.79	2.2	 -     	 -     	16	16	 -     	 -     		1.55	1.79
580	17.41	17.67	2.2	 -     	 -     	16	16	 -     	 -     		1.41	1.67
580.25	17.37	17.63	2.2	 -     	 -     	16	16	 -     	 -     		1.37	1.63
580.5	17.38	17.64	2.2	 -     	 -     	16	16	 -     	 -     		1.38	1.64
580.75	17.36	17.63	1.9	 -     	 -     	16	16	 -     	 -     		1.36	1.63
581	17.23	17.5	1.9	 -     	 -     	16	16	 -     	 -     		1.23	1.5
581.25	17.18	17.46	1.9	 -     	 -     	16	16	 -     	 -     		1.18	1.46
581.5	17.19	17.47	1.9	 -     	 -     	16	16	 -     	 -     		1.19	1.47
581.75	17.23	17.5	3.1	 -     	 -     	16	16	 -     	 -     		1.23	1.5
582	17.13	17.41	3.1	 -     	 -     	16	16	 -     	 -     		1.13	1.41
582.25	17.07	17.36	3.1	 -     	 -     	16	16	 -     	 -     		1.07	1.36
582.5	17.08	17.37	3.1	 -     	 -     	16	16	 -     	 -     		1.08	1.37
582.75	17.11	17.4	4	 -     	 -     	16	16	 -     	 -     		1.11	1.4
583	17.01	17.3	4	 -     	 -     	16	16	 -     	 -     		1.01	1.3
583.25	16.96	17.26	4	 -     	 -     	16	16	 -     	 -     		0.96	1.26
583.5	16.97	17.27	4	 -     	 -     	16	16	 -     	 -     		0.97	1.27
583.75	16.95	17.25	3.4	 -     	 -     	16	16	 -     	 -     		0.95	1.25
584	16.97	17.17	3.4	 -     	 -     	16	16	 -     	 -     		0.97	1.17
584.25	17.05	20.42	3.4	 -     	1	16	19	 -     	32 046.67		1.05	1.42
584.5	17.03	18.81	3.4	 -     	 -     	16	19	 -     	 -     		1.03	-0.19
584.75	17.1	20.06	3.8	 -     	1	16	19	 -     	32 046.67		1.1	1.06
585	17.1	19.51	3.8	 -     	 -     	16	19	 -     	 -     		1.1	0.51
585.25	17.09	17.6	3.8	 -     	 -     	16	19	 -     	 -     		1.09	-1.4
585.5	17.21	21.35	3.8	 -     	1	16	19	 -     	32 046.67		1.21	2.35
585.75	17.23	19.57	4.3	 -     	 -     	16	19	 -     	 -     		1.23	0.57
586	17.24	17.91	4.3	 -     	 -     	16	19	 -     	 -     		1.24	-1.09
586.25	17.36	21.75	4.3	 -     	1	16	19	 -     	32 046.67		1.36	2.75
586.5	17.36	19.92	4.3	 -     	 -     	16	19	 -     	 -     		1.36	0.92
586.75	17.3	18.01	4.5	 -     	 -     	16	19	 -     	 -     		1.3	-0.99
587	17.43	21.95	4.5	 -     	1	16	19	 -     	32 046.67		1.43	2.95
587.25	17.42	20.21	4.5	 -     	 -     	16	19	 -     	 -     		1.42	1.21
587.5	17.37	18.27	4.5	 -     	 -     	16	19	 -     	 -     		1.37	-0.73
587.75	17.45	22.01	4.3	 -     	1	16	19	 -     	32 046.67		1.45	3.01
588	17.51	20.71	4.3	 -     	 -     	16	19	 -     	 -     		1.51	1.71
588.25	17.56	18.97	4.3	 -     	 -     	16	19	 -     	 -     		1.56	-0.03
588.5	17.69	22.65	4.3	 -     	1	16	19	 -     	32 046.67		1.69	3.65
588.75	17.72	20.86	4.6	 -     	 -     	16	19	 -     	 -     		1.72	1.86
589	17.9	19.16	4.6	 -     	 -     	16	19	 -     	 -     		1.9	0.16
589.25	18.06	19.78	4.6	 -     	 -     	16	19	 -     	 -     		2.06	0.78
589.5	18.17	19.62	4.6	 -     	 -     	16	19	 -     	 -     		2.17	0.62
589.75	18.29	19.71	5.4	 -     	 -     	16	19	 -     	 -     		2.29	0.71
590	18.59	19.57	5.4	 -     	 -     	16	19	 -     	 -     		2.59	0.57
590.25	22.26	19.55	5.4	1	 -     	19	16	32 046.67	 -     		3.26	3.55
590.5	20.56	19.5	5.4	 -     	 -     	19	16	 -     	 -     		1.56	3.5
590.75	18.37	19.5	6.6	 -     	 -     	19	16	 -     	 -     		-0.63	3.5
591	23	19.55	6.6	1	 -     	19	16	32 046.67	 -     		4	3.55
591.25	21.36	19.49	6.6	 -     	 -     	19	16	 -     	 -     		2.36	3.49
591.5	19.06	19.44	6.6	 -     	 -     	19	16	 -     	 -     		0.06	3.44
591.75	19.45	19.43	6.3	 -     	 -     	19	16	 -     	 -     		0.45	3.43
592	19.81	19.38	6.3	 -     	 -     	19	16	 -     	 -     		0.81	3.38
592.25	19.94	19.35	6.3	 -     	 -     	19	16	 -     	 -     		0.94	3.35
592.5	19.77	19.33	6.3	 -     	 -     	19	16	 -     	 -     		0.77	3.33
592.75	19.58	19.27	5.9	 -     	 -     	19	16	 -     	 -     		0.58	3.27
593	19.37	19.13	5.9	 -     	 -     	19	16	 -     	 -     		0.37	3.13
593.25	19.21	19.05	5.9	 -     	 -     	19	16	 -     	 -     		0.21	3.05
593.5	19.17	19.04	5.9	 -     	 -     	19	16	 -     	 -     		0.17	3.04
593.75	19.16	19.03	5.4	 -     	 -     	19	16	 -     	 -     		0.16	3.03
594	18.99	18.89	5.2	 -     	 -     	19	16	 -     	 -     		-0.01	2.89
594.25	18.88	18.84	5.2	 -     	 -     	16	16	 -     	 -     		2.88	2.84
594.5	18.87	18.86	5.2	 -     	 -     	16	16	 -     	 -     		2.87	2.86
594.75	18.87	18.85	5.2	 -     	 -     	16	16	 -     	 -     		2.87	2.85
595	18.71	18.73	5.2	 -     	 -     	16	16	 -     	 -     		2.71	2.73
595.25	18.65	18.68	5.2	 -     	 -     	16	16	 -     	 -     		2.65	2.68
595.5	18.67	18.7	5.2	 -     	 -     	16	16	 -     	 -     		2.67	2.7
595.75	18.66	18.69	5	 -     	 -     	16	16	 -     	 -     		2.66	2.69
596	18.51	18.57	5	 -     	 -     	16	16	 -     	 -     		2.51	2.57
596.25	18.45	18.52	5	 -     	 -     	16	16	 -     	 -     		2.45	2.52
596.5	18.46	18.54	5	 -     	 -     	16	16	 -     	 -     		2.46	2.54
596.75	18.45	18.53	4.8	 -     	 -     	16	16	 -     	 -     		2.45	2.53
597	18.31	18.41	4.8	 -     	 -     	16	16	 -     	 -     		2.31	2.41
597.25	18.26	18.37	4.8	 -     	 -     	16	16	 -     	 -     		2.26	2.37
597.5	18.27	18.38	4.8	 -     	 -     	16	16	 -     	 -     		2.27	2.38
597.75	18.27	18.38	4.8	 -     	 -     	16	16	 -     	 -     		2.27	2.38
598	18.14	18.26	4.8	 -     	 -     	16	16	 -     	 -     		2.14	2.26
598.25	18.09	18.22	4.8	 -     	 -     	16	16	 -     	 -     		2.09	2.22
598.5	18.1	18.23	4.8	 -     	 -     	16	16	 -     	 -     		2.1	2.23
598.75	18.06	18.2	3.8	 -     	 -     	16	16	 -     	 -     		2.06	2.2
599	17.92	18.07	3.8	 -     	 -     	16	16	 -     	 -     		1.92	2.07
599.25	17.87	18.04	3.8	 -     	 -     	16	16	 -     	 -     		1.87	2.04
599.5	17.88	18.05	3.8	 -     	 -     	16	16	 -     	 -     		1.88	2.05
599.75	17.87	18.03	3.4	 -     	 -     	16	16	 -     	 -     		1.87	2.03
600	17.73	17.91	3.4	 -     	 -     	16	16	 -     	 -     		1.73	1.91
600.25	17.68	17.87	3.4	 -     	 -     	16	16	 -     	 -     		1.68	1.87
600.5	17.69	17.88	3.4	 -     	 -     	16	16	 -     	 -     		1.69	1.88
600.75	17.69	17.88	3.5	 -     	 -     	16	16	 -     	 -     		1.69	1.88
601	17.57	17.77	3.5	 -     	 -     	16	16	 -     	 -     		1.57	1.77
601.25	17.52	17.73	3.5	 -     	 -     	16	16	 -     	 -     		1.52	1.73
601.5	17.53	17.74	3.5	 -     	 -     	16	16	 -     	 -     		1.53	1.74
601.75	17.53	17.74	3.5	 -     	 -     	16	16	 -     	 -     		1.53	1.74
602	17.41	17.63	3.5	 -     	 -     	16	16	 -     	 -     		1.41	1.63
602.25	17.36	17.59	3.5	 -     	 -     	16	16	 -     	 -     		1.36	1.59
602.5	17.37	17.6	3.5	 -     	 -     	16	16	 -     	 -     		1.37	1.6
602.75	17.37	17.6	3.5	 -     	 -     	16	16	 -     	 -     		1.37	1.6
603	17.25	17.49	3.5	 -     	 -     	16	16	 -     	 -     		1.25	1.49
603.25	17.2	17.45	3.5	 -     	 -     	16	16	 -     	 -     		1.2	1.45
603.5	17.21	17.46	3.5	 -     	 -     	16	16	 -     	 -     		1.21	1.46
603.75	17.21	17.45	3.5	 -     	 -     	16	16	 -     	 -     		1.21	1.45
604	17.09	17.35	3.5	 -     	 -     	16	16	 -     	 -     		1.09	1.35
604.25	17.05	17.31	3.5	 -     	 -     	16	16	 -     	 -     		1.05	1.31
604.5	17.06	17.32	3.5	 -     	 -     	16	16	 -     	 -     		1.06	1.32
604.75	17.06	17.32	3.6	 -     	 -     	16	16	 -     	 -     		1.06	1.32
605	16.94	17.21	3.6	 -     	 -     	16	16	 -     	 -     		0.94	1.21
605.25	16.9	17.17	3.6	 -     	 -     	16	16	 -     	 -     		0.9	1.17
605.5	16.91	17.18	3.6	 -     	 -     	16	16	 -     	 -     		0.91	1.18
605.75	16.91	17.18	3.6	 -     	 -     	16	16	 -     	 -     		0.91	1.18
606	16.8	17.08	3.6	 -     	 -     	16	16	 -     	 -     		0.8	1.08
606.25	16.75	17.04	3.6	 -     	 -     	16	16	 -     	 -     		0.75	1.04
606.5	16.76	17.05	3.6	 -     	 -     	16	16	 -     	 -     		0.76	1.05
606.75	16.76	17.05	3.7	 -     	 -     	16	16	 -     	 -     		0.76	1.05
607	16.66	16.95	3.7	 -     	 -     	16	16	 -     	 -     		0.66	0.95
607.25	16.61	16.91	3.7	 -     	 -     	16	16	 -     	 -     		0.61	0.91
607.5	16.62	16.92	3.7	 -     	 -     	16	16	 -     	 -     		0.62	0.92
607.75	16.62	16.92	3.7	 -     	 -     	16	16	 -     	 -     		0.62	0.92
608	16.59	16.84	3.7	 -     	 -     	16	16	 -     	 -     		0.59	0.84
608.25	16.64	20.08	3.7	 -     	1	16	19	 -     	32 046.67		0.64	1.08
608.5	16.58	18.45	3.7	 -     	 -     	16	19	 -     	 -     		0.58	-0.55
608.75	16.62	19.69	3.8	 -     	1	16	19	 -     	32 046.67		0.62	0.69
609	16.56	19.13	3.8	 -     	 -     	16	19	 -     	 -     		0.56	0.13
609.25	16.52	17.21	3.8	 -     	 -     	16	19	 -     	 -     		0.52	-1.79
609.5	16.61	20.97	3.8	 -     	1	16	19	 -     	32 046.67		0.61	1.97
609.75	16.58	19.16	3.8	 -     	 -     	16	19	 -     	 -     		0.58	0.16
610	16.48	17.47	3.8	 -     	 -     	16	19	 -     	 -     		0.48	-1.53
610.25	16.55	21.3	3.8	 -     	1	16	19	 -     	32 046.67		0.55	2.3
610.5	16.52	19.47	3.8	 -     	 -     	16	19	 -     	 -     		0.52	0.47
610.75	16.48	17.55	3.9	 -     	 -     	16	19	 -     	 -     		0.48	-1.45
611	16.5	21.47	3.9	 -     	1	16	19	 -     	32 046.67		0.5	2.47
611.25	16.45	19.72	3.9	 -     	 -     	16	19	 -     	 -     		0.45	0.72
611.5	16.43	17.79	3.9	 -     	 -     	16	19	 -     	 -     		0.43	-1.21
611.75	16.52	21.55	4.1	 -     	1	16	19	 -     	32 046.67		0.52	2.55
612	16.46	20.21	4.1	 -     	 -     	16	19	 -     	 -     		0.46	1.21
612.25	16.41	18.46	4.1	 -     	 -     	16	19	 -     	 -     		0.41	-0.54
612.5	16.51	22.16	4.1	 -     	1	16	19	 -     	32 046.67		0.51	3.16
612.75	16.48	20.36	4.2	 -     	 -     	16	19	 -     	 -     		0.48	1.36
613	16.39	18.63	4.2	 -     	 -     	16	19	 -     	 -     		0.39	-0.37
613.25	16.44	22.44	4.2	 -     	1	16	19	 -     	32 046.67		0.44	3.44
613.5	16.4	20.6	4.2	 -     	 -     	16	19	 -     	 -     		0.4	1.6
613.75	16.35	18.67	4.2	 -     	 -     	16	19	 -     	 -     		0.35	-0.33
614	16.38	22.55	4.2	 -     	1	16	19	 -     	32 046.67		0.38	3.55
614.25	19.88	20.81	4.2	1	 -     	19	16	32 046.67	 -     		0.88	4.81
614.5	18.15	18.8	4.2	 -     	 -     	19	16	 -     	 -     		-0.85	2.8
614.75	19.5	19.39	4.7	1	 -     	19	16	32 046.67	 -     		0.5	3.39
615	18.96	19.41	4.7	 -     	 -     	19	16	 -     	 -     		-0.04	3.41
615.25	20.48	19.56	4.7	1	 -     	19	16	32 046.67	 -     		1.48	3.56
615.5	19.23	19.5	4.7	 -     	 -     	19	16	 -     	 -     		0.23	3.5
615.75	16.95	19.45	4.5	 -     	 -     	19	16	 -     	 -     		-2.05	3.45
616	21.26	19.36	4.5	1	 -     	19	16	32 046.67	 -     		2.26	3.36
616.25	19.57	19.26	4.5	 -     	 -     	19	16	 -     	 -     		0.57	3.26
616.5	17.37	19.23	4.5	 -     	 -     	19	16	 -     	 -     		-1.63	3.23
616.75	21.34	19.29	4.3	1	 -     	19	16	32 046.67	 -     		2.34	3.29
617	20.14	19.15	4.3	 -     	 -     	19	16	 -     	 -     		1.14	3.15
617.25	18.04	19.01	4.3	 -     	 -     	19	16	 -     	 -     		-0.96	3.01
617.5	21.92	19.08	4.3	1	 -     	19	16	32 046.67	 -     		2.92	3.08
617.75	20.12	19.05	4.2	 -     	 -     	19	16	 -     	 -     		1.12	3.05
618	18.18	18.88	4.3	 -     	 -     	19	16	 -     	 -     		-0.82	2.88
618.25	18.7	18.84	4.3	 -     	 -     	16	16	 -     	 -     		2.7	2.84
618.5	18.55	18.85	4.3	 -     	 -     	16	16	 -     	 -     		2.55	2.85
618.75	18.58	18.85	4.3	 -     	 -     	16	16	 -     	 -     		2.58	2.85
619	18.33	18.7	4.3	 -     	 -     	16	16	 -     	 -     		2.33	2.7
619.25	18.24	18.65	4.3	 -     	 -     	16	16	 -     	 -     		2.24	2.65
619.5	18.26	18.66	4.3	 -     	 -     	16	16	 -     	 -     		2.26	2.66
619.75	18.25	18.65	4.2	 -     	 -     	16	16	 -     	 -     		2.25	2.65
620	18.09	18.52	4.2	 -     	 -     	16	16	 -     	 -     		2.09	2.52
620.25	18.02	18.47	4.2	 -     	 -     	16	16	 -     	 -     		2.02	2.47
620.5	18.03	18.49	4.2	 -     	 -     	16	16	 -     	 -     		2.03	2.49
620.75	18.02	18.47	3.9	 -     	 -     	16	16	 -     	 -     		2.02	2.47
621	17.87	18.34	3.9	 -     	 -     	16	16	 -     	 -     		1.87	2.34
621.25	17.81	18.3	3.9	 -     	 -     	16	16	 -     	 -     		1.81	2.3
621.5	17.82	18.31	3.9	 -     	 -     	16	16	 -     	 -     		1.82	2.31
621.75	17.81	18.3	3.7	 -     	 -     	16	16	 -     	 -     		1.81	2.3
622	17.67	18.18	3.7	 -     	 -     	16	16	 -     	 -     		1.67	2.18
622.25	17.62	18.13	3.7	 -     	 -     	16	16	 -     	 -     		1.62	2.13
622.5	17.63	18.14	3.7	 -     	 -     	16	16	 -     	 -     		1.63	2.14
622.75	17.63	18.14	3.8	 -     	 -     	16	16	 -     	 -     		1.63	2.14
623	17.49	18.03	3.8	 -     	 -     	16	16	 -     	 -     		1.49	2.03
623.25	17.44	17.98	3.8	 -     	 -     	16	16	 -     	 -     		1.44	1.98
623.5	17.45	17.99	3.8	 -     	 -     	16	16	 -     	 -     		1.45	1.99
623.75	17.45	17.99	3.8	 -     	 -     	16	16	 -     	 -     		1.45	1.99
624	17.32	17.87	3.8	 -     	 -     	16	16	 -     	 -     		1.32	1.87
624.25	17.27	17.83	3.8	 -     	 -     	16	16	 -     	 -     		1.27	1.83
624.5	17.29	17.84	3.8	 -     	 -     	16	16	 -     	 -     		1.29	1.84
624.75	17.28	17.84	3.8	 -     	 -     	16	16	 -     	 -     		1.28	1.84
625	17.16	17.73	3.8	 -     	 -     	16	16	 -     	 -     		1.16	1.73
625.25	17.11	17.69	3.8	 -     	 -     	16	16	 -     	 -     		1.11	1.69
625.5	17.12	17.7	3.8	 -     	 -     	16	16	 -     	 -     		1.12	1.7
625.75	17.12	17.69	3.8	 -     	 -     	16	16	 -     	 -     		1.12	1.69
626	17	17.58	3.8	 -     	 -     	16	16	 -     	 -     		1	1.58
626.25	16.96	17.54	3.8	 -     	 -     	16	16	 -     	 -     		0.96	1.54
626.5	16.97	17.55	3.8	 -     	 -     	16	16	 -     	 -     		0.97	1.55
626.75	16.96	17.55	3.8	 -     	 -     	16	16	 -     	 -     		0.96	1.55
627	16.85	17.44	3.8	 -     	 -     	16	16	 -     	 -     		0.85	1.44
627.25	16.81	17.4	3.8	 -     	 -     	16	16	 -     	 -     		0.81	1.4
627.5	16.81	17.41	3.8	 -     	 -     	16	16	 -     	 -     		0.81	1.41
627.75	16.81	17.41	3.7	 -     	 -     	16	16	 -     	 -     		0.81	1.41
628	16.69	17.3	3.7	 -     	 -     	16	16	 -     	 -     		0.69	1.3
628.25	16.65	17.26	3.7	 -     	 -     	16	16	 -     	 -     		0.65	1.26
628.5	16.66	17.27	3.7	 -     	 -     	16	16	 -     	 -     		0.66	1.27
628.75	16.66	17.27	3.7	 -     	 -     	16	16	 -     	 -     		0.66	1.27
629	16.55	17.16	3.7	 -     	 -     	16	16	 -     	 -     		0.55	1.16
629.25	16.51	17.12	3.7	 -     	 -     	16	16	 -     	 -     		0.51	1.12
629.5	16.52	17.13	3.7	 -     	 -     	16	16	 -     	 -     		0.52	1.13
629.75	16.51	17.13	3.7	 -     	 -     	16	16	 -     	 -     		0.51	1.13
630	16.4	17.02	3.7	 -     	 -     	16	16	 -     	 -     		0.4	1.02
630.25	16.36	16.98	3.7	 -     	 -     	16	16	 -     	 -     		0.36	0.98
630.5	16.37	17	3.7	 -     	 -     	16	16	 -     	 -     		0.37	1
630.75	16.37	16.99	3.7	 -     	 -     	16	16	 -     	 -     		0.37	0.99
631	16.26	16.89	3.7	 -     	 -     	16	16	 -     	 -     		0.26	0.89
631.25	16.22	16.85	3.7	 -     	 -     	16	16	 -     	 -     		0.22	0.85
631.5	16.23	16.86	3.7	 -     	 -     	16	16	 -     	 -     		0.23	0.86
631.75	16.23	16.86	3.8	 -     	 -     	16	16	 -     	 -     		0.23	0.86
632	16.19	16.78	3.8	 -     	 -     	16	16	 -     	 -     		0.19	0.78
632.25	16.2	16.76	3.8	 -     	 -     	16	16	 -     	 -     		0.2	0.76
632.5	16.2	16.78	3.8	 -     	 -     	16	16	 -     	 -     		0.2	0.78
632.75	16.2	16.78	3.9	 -     	 -     	16	16	 -     	 -     		0.2	0.78
633	16.13	16.71	3.9	 -     	 -     	16	16	 -     	 -     		0.13	0.71
633.25	16.11	16.68	3.9	 -     	 -     	16	16	 -     	 -     		0.11	0.68
633.5	16.12	16.7	3.9	 -     	 -     	16	16	 -     	 -     		0.12	0.7
633.75	16.13	16.71	3.9	 -     	 -     	16	16	 -     	 -     		0.13	0.71
634	16.07	16.64	3.9	 -     	 -     	16	16	 -     	 -     		0.07	0.64
634.25	16.05	16.61	3.9	 -     	 -     	16	16	 -     	 -     		0.05	0.61
634.5	16.05	16.63	3.9	 -     	 -     	16	16	 -     	 -     		0.05	0.63
634.75	16.07	16.64	4.1	 -     	 -     	16	16	 -     	 -     		0.07	0.64
635	16.03	16.58	4.1	 -     	 -     	16	16	 -     	 -     		0.03	0.58
635.25	16.02	16.57	4.1	 -     	 -     	16	16	 -     	 -     		0.02	0.57
635.5	16.04	16.58	4.1	 -     	 -     	16	16	 -     	 -     		0.04	0.58
635.75	16.06	16.59	4.3	 -     	 -     	16	16	 -     	 -     		0.06	0.59
636	16.03	16.54	4.3	 -     	 -     	16	16	 -     	 -     		0.03	0.54
636.25	16.02	16.53	4.3	 -     	 -     	16	16	 -     	 -     		0.02	0.53
636.5	16.02	16.53	4.3	 -     	 -     	16	16	 -     	 -     		0.02	0.53
636.75	16.03	16.55	4.8	 -     	 -     	16	16	 -     	 -     		0.03	0.55
637	16.01	16.51	4.8	 -     	 -     	16	16	 -     	 -     		0.01	0.51
637.25	16	16.48	4.8	 -     	 -     	16	16	 -     	 -     		0	0.48
637.5	19.51	16.56	4.8	1	 -     	16	16	32 046.67	 -     		3.51	0.56
637.75	17.8	16.53	5	 -     	 -     	16	16	 -     	 -     		1.8	0.53
638	15.99	16.46	5	 -     	 -     	16	16	 -     	 -     		-0.01	0.46
638.25	20.11	16.53	5	1	 -     	16	16	32 046.67	 -     		4.11	0.53
638.5	18.26	16.49	5	 -     	 -     	16	16	 -     	 -     		2.26	0.49
638.75	16.09	16.44	5.1	 -     	 -     	16	16	 -     	 -     		0.09	0.44
639	16.82	16.4	5.1	 -     	 -     	16	16	 -     	 -     		0.82	0.4
639.25	16.81	16.38	5.1	 -     	 -     	16	16	 -     	 -     		0.81	0.38
639.5	16.79	16.37	5.1	 -     	 -     	16	16	 -     	 -     		0.79	0.37
639.75	16.78	16.37	5.2	 -     	 -     	16	16	 -     	 -     		0.78	0.37
640	16.65	16.29	5.2	 -     	 -     	16	16	 -     	 -     		0.65	0.29
640.25	16.59	16.26	5.2	 -     	 -     	16	16	 -     	 -     		0.59	0.26
640.5	16.59	16.26	5.2	 -     	 -     	16	16	 -     	 -     		0.59	0.26
640.75	16.58	16.24	5	 -     	 -     	16	16	 -     	 -     		0.58	0.24
641	16.48	16.16	5	 -     	 -     	16	16	 -     	 -     		0.48	0.16
641.25	16.57	16.17	5	 -     	 -     	16	16	 -     	 -     		0.57	0.17
641.5	16.44	16.13	5	 -     	 -     	16	16	 -     	 -     		0.44	0.13
641.75	16.36	16.1	4.9	 -     	 -     	16	16	 -     	 -     		0.36	0.1
642	16.29	16.03	4.9	 -     	 -     	16	16	 -     	 -     		0.29	0.03
642.25	16.25	16	4.9	 -     	 -     	16	16	 -     	 -     		0.25	0
642.5	16.33	19.21	4.9	 -     	1	16	16	 -     	32 046.67		0.33	3.21
642.75	16.3	17.55	4.9	 -     	 -     	16	16	 -     	 -     		0.3	1.55
643	16.16	15.83	4.9	 -     	 -     	16	16	 -     	 -     		0.16	-0.17
643.25	16.21	19.68	4.9	 -     	1	16	16	 -     	32 046.67		0.21	3.68
643.5	16.18	17.84	4.9	 -     	 -     	16	16	 -     	 -     		0.18	1.84
643.75	16.13	15.91	4.7	 -     	 -     	16	16	 -     	 -     		0.13	-0.09
644	16.11	19.82	4.7	 -     	1	16	16	 -     	32 046.67		0.11	3.82
644.25	16.04	18.08	4.7	 -     	 -     	16	16	 -     	 -     		0.04	2.08
644.5	16.01	16.13	4.7	 -     	 -     	16	16	 -     	 -     		0.01	0.13
644.75	16	16.66	4.5	 -     	 -     	16	16	 -     	 -     		0	0.66
645	15.91	16.69	4.5	 -     	 -     	16	16	 -     	 -     		-0.09	0.69
645.25	19.39	16.88	4.5	1	 -     	16	16	32 046.67	 -     		3.39	0.88
645.5	17.68	16.81	4.5	 -     	 -     	16	16	 -     	 -     		1.68	0.81
645.75	15.5	16.77	4.4	 -     	 -     	16	16	 -     	 -     		-0.5	0.77
646	19.76	16.7	4.4	1	 -     	16	16	32 046.67	 -     		3.76	0.7
646.25	18.04	16.62	4.4	 -     	 -     	16	16	 -     	 -     		2.04	0.62
646.5	15.86	16.58	4.4	 -     	 -     	16	16	 -     	 -     		-0.14	0.58
646.75	19.85	16.67	4.6	1	 -     	16	16	32 046.67	 -     		3.85	0.67
647	18.6	16.55	4.6	 -     	 -     	16	16	 -     	 -     		2.6	0.55
647.25	16.64	16.47	4.6	 -     	 -     	16	16	 -     	 -     		0.64	0.47
647.5	17.06	16.49	4.6	 -     	 -     	16	16	 -     	 -     		1.06	0.49
647.75	16.97	16.48	4.4	 -     	 -     	16	16	 -     	 -     		0.97	0.48
648	16.82	16.36	4.4	 -     	 -     	16	16	 -     	 -     		0.82	0.36
648.25	16.75	16.32	4.4	 -     	 -     	16	16	 -     	 -     		0.75	0.32
648.5	16.77	16.33	4.4	 -     	 -     	16	16	 -     	 -     		0.77	0.33
648.75	16.76	16.32	4.2	 -     	 -     	16	16	 -     	 -     		0.76	0.32
649	16.6	16.21	4.2	 -     	 -     	16	16	 -     	 -     		0.6	0.21
649.25	16.54	16.18	4.2	 -     	 -     	16	16	 -     	 -     		0.54	0.18
649.5	16.55	16.19	4.2	 -     	 -     	16	16	 -     	 -     		0.55	0.19
649.75	16.54	16.18	3.9	 -     	 -     	16	16	 -     	 -     		0.54	0.18
650	16.41	16.07	3.9	 -     	 -     	16	16	 -     	 -     		0.41	0.07
650.25	16.36	16.03	3.9	 -     	 -     	16	16	 -     	 -     		0.36	0.03
650.5	16.37	16.04	3.9	 -     	 -     	16	16	 -     	 -     		0.37	0.04
650.75	16.34	16.01	3	 -     	 -     	16	16	 -     	 -     		0.34	0.01
651	16.2	15.9	3	 -     	 -     	16	16	 -     	 -     		0.2	-0.1
651.25	16.23	19.07	3	 -     	1	16	16	 -     	32 046.67		0.23	3.07
651.5	16.2	17.42	3	 -     	 -     	16	16	 -     	 -     		0.2	1.42
651.75	16.13	15.42	2.1	 -     	 -     	16	16	 -     	 -     		0.13	-0.58
652	16.08	19.38	2.1	 -     	1	16	16	 -     	32 046.67		0.08	3.38
652.25	16.01	17.65	2.1	 -     	 -     	16	16	 -     	 -     		0.01	1.65
652.5	15.98	15.7	2.1	 -     	 -     	16	16	 -     	 -     		-0.02	-0.3
652.75	19.55	19.5	1.4	1	1	16	16	32 046.67	32 046.67		3.55	3.5
653	18.02	18.12	1.4	 -     	 -     	16	16	 -     	 -     		2.02	2.12
653.25	15.88	16.33	1.4	 -     	 -     	16	16	 -     	 -     		-0.12	0.33
653.5	19.85	16.89	1.4	1	 -     	16	16	32 046.67	 -     		3.85	0.89
653.75	18.02	16.71	0.8	 -     	 -     	16	16	 -     	 -     		2.02	0.71
654	16.12	16.53	0.8	 -     	 -     	16	16	 -     	 -     		0.12	0.53
654.25	16.69	16.47	0.8	 -     	 -     	16	16	 -     	 -     		0.69	0.47
654.5	16.57	16.49	0.8	 -     	 -     	16	16	 -     	 -     		0.57	0.49
654.75	16.59	16.48	0.5	 -     	 -     	16	16	 -     	 -     		0.59	0.48
655	16.35	16.31	0.5	 -     	 -     	16	16	 -     	 -     		0.35	0.31
655.25	16.27	16.25	0.5	 -     	 -     	16	16	 -     	 -     		0.27	0.25
655.5	16.29	16.27	0.5	 -     	 -     	16	16	 -     	 -     		0.29	0.27
655.75	16.28	16.25	0.3	 -     	 -     	16	16	 -     	 -     		0.28	0.25
656	16.22	16.14	0.3	 -     	 -     	16	16	 -     	 -     		0.22	0.14
656.25	16.17	16.1	0.3	 -     	 -     	16	16	 -     	 -     		0.17	0.1
656.5	16.16	16.12	0.3	 -     	 -     	16	16	 -     	 -     		0.16	0.12
656.75	16.15	16.12	0.3	 -     	 -     	16	16	 -     	 -     		0.15	0.12
657	16.03	16.01	0.3	 -     	 -     	16	16	 -     	 -     		0.03	0.01
657.25	16	15.97	0.3	 -     	 -     	16	16	 -     	 -     		0	-0.03
657.5	19.6	19.27	0.3	1	1	16	16	32 046.67	32 046.67		3.6	3.27
657.75	17.85	17.57	0.2	 -     	 -     	16	16	 -     	 -     		1.85	1.57
658	15.92	15.82	0.2	 -     	 -     	16	16	 -     	 -     		-0.08	-0.18
658.25	20.09	19.75	0.2	1	1	16	16	32 046.67	32 046.67		4.09	3.75
658.5	18.21	17.87	0.2	 -     	 -     	16	16	 -     	 -     		2.21	1.87
658.75	16.03	15.92	0.7	 -     	 -     	16	16	 -     	 -     		0.03	-0.08
659	16.81	19.86	0.7	 -     	1	16	16	 -     	32 046.67		0.81	3.86
659.25	16.77	18.11	0.7	 -     	 -     	16	16	 -     	 -     		0.77	2.11
659.5	16.73	16.18	0.7	 -     	 -     	16	16	 -     	 -     		0.73	0.18
659.75	16.75	16.72	0.7	 -     	 -     	16	16	 -     	 -     		0.75	0.72
660	16.63	16.77	0.7	 -     	 -     	16	16	 -     	 -     		0.63	0.77
660.25	16.61	16.89	0.7	 -     	 -     	16	16	 -     	 -     		0.61	0.89
660.5	16.65	16.87	0.7	 -     	 -     	16	16	 -     	 -     		0.65	0.87
660.75	16.68	16.89	1.1	 -     	 -     	16	16	 -     	 -     		0.68	0.89
661	16.6	16.75	1.1	 -     	 -     	16	16	 -     	 -     		0.6	0.75
661.25	16.56	16.7	1.1	 -     	 -     	16	16	 -     	 -     		0.56	0.7
661.5	16.57	16.71	1.1	 -     	 -     	16	16	 -     	 -     		0.57	0.71
661.75	16.57	16.71	1.4	 -     	 -     	16	16	 -     	 -     		0.57	0.71
662	16.52	16.62	1.4	 -     	 -     	16	16	 -     	 -     		0.52	0.62
662.25	16.49	16.58	1.4	 -     	 -     	16	16	 -     	 -     		0.49	0.58
662.5	16.5	16.59	1.4	 -     	 -     	16	16	 -     	 -     		0.5	0.59
662.75	16.49	16.58	1.6	 -     	 -     	16	16	 -     	 -     		0.49	0.58
663	16.42	16.49	1.6	 -     	 -     	16	16	 -     	 -     		0.42	0.49
663.25	16.4	16.45	1.6	 -     	 -     	16	16	 -     	 -     		0.4	0.45
663.5	16.4	16.45	1.6	 -     	 -     	16	16	 -     	 -     		0.4	0.45
663.75	16.38	16.44	1.7	 -     	 -     	16	16	 -     	 -     		0.38	0.44
664	16.31	16.35	1.7	 -     	 -     	16	16	 -     	 -     		0.31	0.35
664.25	16.27	16.31	1.7	 -     	 -     	16	16	 -     	 -     		0.27	0.31
664.5	16.29	16.31	1.7	 -     	 -     	16	16	 -     	 -     		0.29	0.31
664.75	16.3	16.31	2	 -     	 -     	16	16	 -     	 -     		0.3	0.31
665	16.2	16.21	2	 -     	 -     	16	16	 -     	 -     		0.2	0.21
665.25	16.2	16.18	2	 -     	 -     	16	16	 -     	 -     		0.2	0.18
665.5	16.08	16.14	2	 -     	 -     	16	16	 -     	 -     		0.08	0.14
665.75	16.02	16.12	1.8	 -     	 -     	16	16	 -     	 -     		0.02	0.12
666	15.93	16.01	1.8	 -     	 -     	16	16	 -     	 -     		-0.07	0.01
666.25	19.4	16.05	1.8	1	 -     	16	16	32 046.67	 -     		3.4	0.05
666.5	17.69	16.03	1.8	 -     	 -     	16	16	 -     	 -     		1.69	0.03
666.75	15.51	15.98	1.8	 -     	 -     	16	16	 -     	 -     		-0.49	-0.02
667	19.82	19.17	1.8	1	1	16	16	32 046.67	32 046.67		3.82	3.17
667.25	18.07	17.44	1.8	 -     	 -     	16	16	 -     	 -     		2.07	1.44
667.5	15.84	15.43	1.8	 -     	 -     	16	16	 -     	 -     		-0.16	-0.57
667.75	19.9	19.26	1.7	1	1	16	16	32 046.67	32 046.67		3.9	3.26
668	18.63	17.95	1.7	 -     	 -     	16	16	 -     	 -     		2.63	1.95
668.25	16.64	16.18	1.7	 -     	 -     	16	16	 -     	 -     		0.64	0.18
668.5	17.06	16.66	1.7	 -     	 -     	16	16	 -     	 -     		1.06	0.66
668.75	16.98	16.54	2	 -     	 -     	16	16	 -     	 -     		0.98	0.54
669	16.81	16.41	2	 -     	 -     	16	16	 -     	 -     		0.81	0.41
669.25	16.74	16.34	2	 -     	 -     	16	16	 -     	 -     		0.74	0.34
669.5	16.75	16.36	2	 -     	 -     	16	16	 -     	 -     		0.75	0.36
669.75	16.75	16.36	2.1	 -     	 -     	16	16	 -     	 -     		0.75	0.36
670	16.58	16.22	2.1	 -     	 -     	16	16	 -     	 -     		0.58	0.22
670.25	16.52	16.17	2.1	 -     	 -     	16	16	 -     	 -     		0.52	0.17
670.5	16.53	16.18	2.1	 -     	 -     	16	16	 -     	 -     		0.53	0.18
670.75	16.52	16.17	1.9	 -     	 -     	16	16	 -     	 -     		0.52	0.17
671	16.37	16.04	1.9	 -     	 -     	16	16	 -     	 -     		0.37	0.04
671.25	16.31	16	1.9	 -     	 -     	16	16	 -     	 -     		0.31	0
671.5	16.4	19.22	1.9	 -     	1	16	16	 -     	32 046.67		0.4	3.22
671.75	16.35	17.54	1.5	 -     	 -     	16	16	 -     	 -     		0.35	1.54
672	16.18	15.79	1.5	 -     	 -     	16	16	 -     	 -     		0.18	-0.21
672.25	16.22	19.62	1.5	 -     	1	16	16	 -     	32 046.67		0.22	3.62
672.5	16.19	17.78	1.5	 -     	 -     	16	16	 -     	 -     		0.19	1.78
672.75	16.11	15.83	0.5	 -     	 -     	16	16	 -     	 -     		0.11	-0.17
673	16.06	19.7	0.5	 -     	1	16	16	 -     	32 046.67		0.06	3.7
673.25	15.98	17.95	0.5	 -     	 -     	16	16	 -     	 -     		-0.02	1.95
673.5	19.46	16.08	0.5	1	 -     	16	16	32 046.67	 -     		3.46	0.08
673.75	17.71	16.55	-0.5	 -     	 -     	16	16	 -     	 -     		1.71	0.55
674	15.79	16.51	-0.5	 -     	 -     	16	16	 -     	 -     		-0.21	0.51
674.25	19.87	16.7	-0.5	1	 -     	16	16	32 046.67	 -     		3.87	0.7
674.5	18.04	16.64	-0.5	 -     	 -     	16	16	 -     	 -     		2.04	0.64
674.75	15.86	16.58	-1	 -     	 -     	16	16	 -     	 -     		-0.14	0.58
675	20	16.47	-1	1	 -     	16	16	32 046.67	 -     		4	0.47
675.25	18.25	16.37	-1	 -     	 -     	16	16	 -     	 -     		2.25	0.37
675.5	16.07	16.34	-1	 -     	 -     	16	16	 -     	 -     		0.07	0.34
675.75	16.53	16.33	-1.5	 -     	 -     	16	16	 -     	 -     		0.53	0.33
676	16.59	16.18	-1.5	 -     	 -     	16	16	 -     	 -     		0.59	0.18
676.25	16.68	16.13	-1.5	 -     	 -     	16	16	 -     	 -     		0.68	0.13
676.5	16.66	16.14	-1.5	 -     	 -     	16	16	 -     	 -     		0.66	0.14
676.75	16.66	16.13	-1.7	 -     	 -     	16	16	 -     	 -     		0.66	0.13
677	16.43	15.98	-1.7	 -     	 -     	16	16	 -     	 -     		0.43	-0.02
677.25	16.42	19.12	-1.7	 -     	1	16	16	 -     	32 046.67		0.42	3.12
677.5	16.4	17.47	-1.7	 -     	 -     	16	16	 -     	 -     		0.4	1.47
677.75	16.37	15.52	-1.2	 -     	 -     	16	16	 -     	 -     		0.37	-0.48
678	16.3	19.46	-1.2	 -     	1	16	16	 -     	32 046.67		0.3	3.46
678.25	16.2	17.71	-1.2	 -     	 -     	16	16	 -     	 -     		0.2	1.71
678.5	16.17	15.77	-1.2	 -     	 -     	16	16	 -     	 -     		0.17	-0.23
678.75	16.26	19.53	-0.7	 -     	1	16	16	 -     	32 046.67		0.26	3.53
679	16.11	18.16	-0.7	 -     	 -     	16	16	 -     	 -     		0.11	2.16
679.25	16.02	16.39	-0.7	 -     	 -     	16	16	 -     	 -     		0.02	0.39
679.5	16.03	16.88	-0.7	 -     	 -     	16	16	 -     	 -     		0.03	0.88
679.75	16.04	16.76	-0.3	 -     	 -     	16	16	 -     	 -     		0.04	0.76
680	16.06	16.65	-0.3	 -     	 -     	16	16	 -     	 -     		0.06	0.65
680.25	16.12	19.84	-0.3	 -     	1	16	19	 -     	32 046.67		0.12	0.84
680.5	16.09	18.24	-0.3	 -     	 -     	16	19	 -     	 -     		0.09	-0.76
680.75	16.14	19.49	0.4	 -     	1	16	19	 -     	32 046.67		0.14	0.49
681	16.07	18.87	0.4	 -     	 -     	16	19	 -     	 -     		0.07	-0.13
681.25	16.08	20.13	0.4	 -     	1	16	19	 -     	32 046.67		0.08	1.13
681.5	16.06	19.02	0.4	 -     	 -     	16	19	 -     	 -     		0.06	0.02
681.75	16.03	16.93	1.2	 -     	 -     	16	19	 -     	 -     		0.03	-2.07
682	16.06	20.92	1.2	 -     	1	16	19	 -     	32 046.67		0.06	1.92
682.25	16	19.16	1.2	 -     	 -     	16	19	 -     	 -     		0	0.16
682.5	19.46	17.3	1.2	1	 -     	16	19	32 046.67	 -     		3.46	-1.7
682.75	17.84	21.03	1.9	 -     	1	16	19	 -     	32 046.67		1.84	2.03
683	15.99	19.66	1.9	 -     	 -     	16	19	 -     	 -     		-0.01	0.66
683.25	20.06	17.98	1.9	1	 -     	16	19	32 046.67	 -     		4.06	-1.02
683.5	18.29	21.64	1.9	 -     	1	16	19	 -     	32 046.67		2.29	2.64
683.75	16.11	19.81	2.3	 -     	 -     	16	19	 -     	 -     		0.11	0.81
684	16.8	18.09	2.3	 -     	 -     	16	19	 -     	 -     		0.8	-0.91
684.25	16.87	21.9	2.3	 -     	1	16	19	 -     	32 046.67		0.87	2.9
684.5	16.84	20.06	2.3	 -     	 -     	16	19	 -     	 -     		0.84	1.06
684.75	16.79	18.14	2.3	 -     	 -     	16	19	 -     	 -     		0.79	-0.86
685	16.75	22.01	2.3	 -     	1	16	19	 -     	32 046.67		0.75	3.01
685.25	16.67	20.24	2.3	 -     	 -     	16	19	 -     	 -     		0.67	1.24
685.5	16.64	18.31	2.3	 -     	 -     	16	19	 -     	 -     		0.64	-0.69
685.75	16.72	22.05	2.3	 -     	1	16	19	 -     	32 046.67		0.72	3.05
686	16.63	20.69	2.3	 -     	 -     	16	19	 -     	 -     		0.63	1.69
686.25	20.11	18.94	2.3	1	 -     	19	16	32 046.67	 -     		1.11	2.94
686.5	18.43	19.36	2.3	 -     	 -     	19	16	 -     	 -     		-0.57	3.36
686.75	19.75	19.26	2.3	1	 -     	19	16	32 046.67	 -     		0.75	3.26
687	19.15	19.11	2.3	 -     	 -     	19	16	 -     	 -     		0.15	3.11
687.25	17.1	18.99	2.3	 -     	 -     	19	16	 -     	 -     		-1.9	2.99
687.5	21.05	19.09	2.3	1	 -     	19	16	32 046.67	 -     		2.05	3.09
687.75	19.22	19.03	1.9	 -     	 -     	19	16	 -     	 -     		0.22	3.03
688	17.33	18.82	1.9	 -     	 -     	19	16	 -     	 -     		-1.67	2.82
688.25	21.41	18.84	1.9	1	 -     	19	16	32 046.67	 -     		2.41	2.84
688.5	19.56	18.81	1.9	 -     	 -     	19	16	 -     	 -     		0.56	2.81
688.75	17.38	18.74	1.5	 -     	 -     	19	16	 -     	 -     		-1.62	2.74
689	21.55	18.67	1.5	1	 -     	19	16	32 046.67	 -     		2.55	2.67
689.25	19.82	18.58	1.5	 -     	 -     	19	16	 -     	 -     		0.82	2.58
689.5	17.55	18.52	1.5	 -     	 -     	19	16	 -     	 -     		-1.45	2.52
689.75	21.48	18.57	1	1	 -     	19	16	32 046.67	 -     		2.48	2.57
690	20.19	18.41	1	 -     	 -     	19	16	 -     	 -     		1.19	2.41
690.25	18.17	18.31	0.8	 -     	 -     	16	16	 -     	 -     		2.17	2.31
690.5	18.57	18.33	0.8	 -     	 -     	16	16	 -     	 -     		2.57	2.33
690.75	18.48	18.33	0.8	 -     	 -     	16	16	 -     	 -     		2.48	2.33
691	18.27	18.17	0.8	 -     	 -     	16	16	 -     	 -     		2.27	2.17
691.25	18.18	18.11	0.8	 -     	 -     	16	16	 -     	 -     		2.18	2.11
691.5	18.2	18.12	0.8	 -     	 -     	16	16	 -     	 -     		2.2	2.12
691.75	18.18	18.11	0.4	 -     	 -     	16	16	 -     	 -     		2.18	2.11
692	17.97	17.95	0.4	 -     	 -     	16	16	 -     	 -     		1.97	1.95
692.25	17.89	17.9	0.4	 -     	 -     	16	16	 -     	 -     		1.89	1.9
692.5	17.91	17.91	0.4	 -     	 -     	16	16	 -     	 -     		1.91	1.91
692.75	17.9	17.9	0.2	 -     	 -     	16	16	 -     	 -     		1.9	1.9
693	17.71	17.75	0.2	 -     	 -     	16	16	 -     	 -     		1.71	1.75
693.25	17.64	17.7	0.2	 -     	 -     	16	16	 -     	 -     		1.64	1.7
693.5	17.66	17.72	0.2	 -     	 -     	16	16	 -     	 -     		1.66	1.72
693.75	17.66	17.72	0.3	 -     	 -     	16	16	 -     	 -     		1.66	1.72
694	17.49	17.58	0.3	 -     	 -     	16	16	 -     	 -     		1.49	1.58
694.25	17.43	17.53	0.3	 -     	 -     	16	16	 -     	 -     		1.43	1.53
694.5	17.44	17.54	0.3	 -     	 -     	16	16	 -     	 -     		1.44	1.54
694.75	17.44	17.54	0.5	 -     	 -     	16	16	 -     	 -     		1.44	1.54
695	17.29	17.41	0.5	 -     	 -     	16	16	 -     	 -     		1.29	1.41
695.25	17.23	17.36	0.5	 -     	 -     	16	16	 -     	 -     		1.23	1.36
695.5	17.24	17.37	0.5	 -     	 -     	16	16	 -     	 -     		1.24	1.37
695.75	17.24	17.37	0.6	 -     	 -     	16	16	 -     	 -     		1.24	1.37
696	17.09	17.24	0.6	 -     	 -     	16	16	 -     	 -     		1.09	1.24
696.25	17.04	17.2	0.6	 -     	 -     	16	16	 -     	 -     		1.04	1.2
696.5	17.05	17.21	0.6	 -     	 -     	16	16	 -     	 -     		1.05	1.21
696.75	17.05	17.21	0.6	 -     	 -     	16	16	 -     	 -     		1.05	1.21
697	16.9	17.08	0.6	 -     	 -     	16	16	 -     	 -     		0.9	1.08
697.25	16.85	17.03	0.6	 -     	 -     	16	16	 -     	 -     		0.85	1.03
697.5	16.86	17.04	0.6	 -     	 -     	16	16	 -     	 -     		0.86	1.04
697.75	16.86	17.04	0.6	 -     	 -     	16	16	 -     	 -     		0.86	1.04
698	16.72	16.91	0.6	 -     	 -     	16	16	 -     	 -     		0.72	0.91
698.25	16.67	16.87	0.6	 -     	 -     	16	16	 -     	 -     		0.67	0.87
698.5	16.68	16.88	0.6	 -     	 -     	16	16	 -     	 -     		0.68	0.88
698.75	16.68	16.88	0.7	 -     	 -     	16	16	 -     	 -     		0.68	0.88
699	16.55	16.76	0.7	 -     	 -     	16	16	 -     	 -     		0.55	0.76
699.25	16.5	16.71	0.7	 -     	 -     	16	16	 -     	 -     		0.5	0.71
699.5	16.51	16.73	0.7	 -     	 -     	16	16	 -     	 -     		0.51	0.73
699.75	16.51	16.73	0.8	 -     	 -     	16	16	 -     	 -     		0.51	0.73
700	16.38	16.61	0.8	 -     	 -     	16	16	 -     	 -     		0.38	0.61
700.25	16.33	16.56	0.8	 -     	 -     	16	16	 -     	 -     		0.33	0.56
700.5	16.34	16.57	0.8	 -     	 -     	16	16	 -     	 -     		0.34	0.57
700.75	16.33	16.56	0.6	 -     	 -     	16	16	 -     	 -     		0.33	0.56
701	16.2	16.44	0.6	 -     	 -     	16	16	 -     	 -     		0.2	0.44
701.25	16.16	16.4	0.6	 -     	 -     	16	16	 -     	 -     		0.16	0.4
701.5	16.17	16.41	0.6	 -     	 -     	16	16	 -     	 -     		0.17	0.41
701.75	16.16	16.41	0.6	 -     	 -     	16	16	 -     	 -     		0.16	0.41
702	16.04	16.29	0.6	 -     	 -     	16	16	 -     	 -     		0.04	0.29
702.25	15.99	16.25	0.6	 -     	 -     	16	16	 -     	 -     		-0.01	0.25
702.5	19.51	16.33	0.6	1	 -     	16	16	32 046.67	 -     		3.51	0.33
702.75	17.79	16.29	0.4	 -     	 -     	16	16	 -     	 -     		1.79	0.29
703	15.88	16.14	0.4	 -     	 -     	16	16	 -     	 -     		-0.12	0.14
703.25	19.96	16.19	0.4	1	 -     	16	16	32 046.67	 -     		3.96	0.19
703.5	18.12	16.17	0.4	 -     	 -     	16	16	 -     	 -     		2.12	0.17
703.75	15.97	16.12	0.3	 -     	 -     	16	16	 -     	 -     		-0.03	0.12
704	20.22	16.13	0.3	1	 -     	16	16	32 046.67	 -     		4.22	0.13
704.25	18.62	19.34	0.3	 -     	1	16	19	 -     	32 046.67		2.62	0.34
704.5	16.39	17.67	0.3	 -     	 -     	16	19	 -     	 -     		0.39	-1.33
704.75	16.88	18.91	0.3	 -     	1	16	19	 -     	32 046.67		0.88	-0.09
705	17.12	21.55	0.3	 -     	1	16	19	 -     	32 046.67		1.12	2.55
705.25	17.17	17.97	0.3	 -     	 -     	16	19	 -     	 -     		1.17	-1.03
705.5	17.18	19.75	0.3	 -     	1	16	19	 -     	32 046.67		1.18	0.75
705.75	17.16	18.5	0.4	 -     	 -     	16	19	 -     	 -     		1.16	-0.5
706	17.08	20.18	0.4	 -     	1	16	19	 -     	32 046.67		1.08	1.18
706.25	17	19.3	0.4	 -     	 -     	16	19	 -     	 -     		1	0.3
706.5	16.97	17.13	0.4	 -     	 -     	16	19	 -     	 -     		0.97	-1.87
706.75	17.07	20.95	0.6	 -     	1	16	19	 -     	32 046.67		1.07	1.95
707	16.97	19.53	0.6	 -     	 -     	16	19	 -     	 -     		0.97	0.53
707.25	16.9	17.76	0.6	 -     	 -     	16	19	 -     	 -     		0.9	-1.24
707.5	17	21.46	0.6	 -     	1	16	19	 -     	32 046.67		1	2.46
707.75	17	19.69	1.3	 -     	 -     	16	19	 -     	 -     		1	0.69
708	16.92	17.96	1.3	 -     	 -     	16	19	 -     	 -     		0.92	-1.04
708.25	16.98	21.77	1.3	 -     	1	16	19	 -     	32 046.67		0.98	2.77
708.5	16.97	19.94	1.3	 -     	 -     	16	19	 -     	 -     		0.97	0.94
708.75	16.95	18.04	1.7	 -     	 -     	16	19	 -     	 -     		0.95	-0.96
709	17.06	21.94	1.7	 -     	1	16	19	 -     	32 046.67		1.06	2.94
709.25	17.06	20.18	1.7	 -     	 -     	16	19	 -     	 -     		1.06	1.18
709.5	17.07	18.25	1.7	 -     	 -     	16	19	 -     	 -     		1.07	-0.75
709.75	17.24	21.99	1.6	 -     	1	16	19	 -     	32 046.67		1.24	2.99
710	17.34	20.66	1.6	 -     	 -     	16	19	 -     	 -     		1.34	1.66
710.25	20.96	18.94	1.6	1	 -     	19	16	32 046.67	 -     		1.96	2.94
710.5	19.36	19.37	1.6	 -     	 -     	19	16	 -     	 -     		0.36	3.37
710.75	17.26	19.24	2.9	 -     	 -     	19	16	 -     	 -     		-1.74	3.24
711	21.79	19.25	2.9	1	 -     	19	16	32 046.67	 -     		2.79	3.25
711.25	20.14	19.15	2.9	 -     	 -     	19	16	 -     	 -     		1.14	3.15
711.5	17.88	19.11	2.9	 -     	 -     	19	16	 -     	 -     		-1.12	3.11
711.75	21.78	19.15	2.1	1	 -     	19	16	32 046.67	 -     		2.78	3.15
712	20.68	19.01	2.1	 -     	 -     	19	16	 -     	 -     		1.68	3.01
712.25	18.72	18.92	2.1	 -     	 -     	19	16	 -     	 -     		-0.28	2.92
712.5	22.5	18.97	2.1	1	 -     	19	16	32 046.67	 -     		3.5	2.97
712.75	20.57	18.9	2	 -     	 -     	19	16	 -     	 -     		1.57	2.9
713	18.7	18.74	2	 -     	 -     	19	16	 -     	 -     		-0.3	2.74
713.25	22.84	18.78	2	1	 -     	19	16	32 046.67	 -     		3.84	2.78
713.5	20.8	18.69	2	 -     	 -     	19	16	 -     	 -     		1.8	2.69
713.75	18.55	18.6	1.4	 -     	 -     	19	16	 -     	 -     		-0.45	2.6
714	22.69	18.55	1.4	1	 -     	19	16	32 046.67	 -     		3.69	2.55
714.25	20.89	18.46	1.3	 -     	 -     	16	16	 -     	 -     		4.89	2.46
714.5	18.69	18.43	1.3	 -     	 -     	16	16	 -     	 -     		2.69	2.43
714.75	19.16	18.43	1.3	 -     	 -     	16	16	 -     	 -     		3.16	2.43
715	19.19	18.29	1.3	 -     	 -     	16	16	 -     	 -     		3.19	2.29
715.25	19.26	18.24	1.3	 -     	 -     	16	16	 -     	 -     		3.26	2.24
715.5	19.25	18.26	1.3	 -     	 -     	16	16	 -     	 -     		3.25	2.26
715.75	19.23	18.24	0.7	 -     	 -     	16	16	 -     	 -     		3.23	2.24
716	18.96	18.08	0.7	 -     	 -     	16	16	 -     	 -     		2.96	2.08
716.25	18.87	18.03	0.7	 -     	 -     	16	16	 -     	 -     		2.87	2.03
716.5	18.89	18.04	0.7	 -     	 -     	16	16	 -     	 -     		2.89	2.04
716.75	18.87	18.03	0.4	 -     	 -     	16	16	 -     	 -     		2.87	2.03
717	18.67	17.88	0.4	 -     	 -     	16	16	 -     	 -     		2.67	1.88
717.25	18.59	17.83	0.4	 -     	 -     	16	16	 -     	 -     		2.59	1.83
717.5	18.6	17.84	0.4	 -     	 -     	16	16	 -     	 -     		2.6	1.84
717.75	18.59	17.83	0.2	 -     	 -     	16	16	 -     	 -     		2.59	1.83
718	18.41	17.69	0.2	 -     	 -     	16	16	 -     	 -     		2.41	1.69
718.25	18.34	17.64	0.2	 -     	 -     	16	16	 -     	 -     		2.34	1.64
718.5	18.35	17.66	0.2	 -     	 -     	16	16	 -     	 -     		2.35	1.66
718.75	18.34	17.65	-0.1	 -     	 -     	16	16	 -     	 -     		2.34	1.65
719	18.16	17.51	-0.1	 -     	 -     	16	16	 -     	 -     		2.16	1.51
719.25	18.09	17.46	-0.1	 -     	 -     	16	16	 -     	 -     		2.09	1.46
719.5	18.11	17.47	-0.1	 -     	 -     	16	16	 -     	 -     		2.11	1.47
719.75	18.09	17.46	-0.4	 -     	 -     	16	16	 -     	 -     		2.09	1.46
720	17.92	17.32	-0.4	 -     	 -     	16	16	 -     	 -     		1.92	1.32
720.25	17.86	17.28	-0.4	 -     	 -     	16	16	 -     	 -     		1.86	1.28
720.5	17.87	17.29	-0.4	 -     	 -     	16	16	 -     	 -     		1.87	1.29
720.75	17.86	17.28	-0.5	 -     	 -     	16	16	 -     	 -     		1.86	1.28
721	17.7	17.15	-0.5	 -     	 -     	16	16	 -     	 -     		1.7	1.15
721.25	17.64	17.1	-0.5	 -     	 -     	16	16	 -     	 -     		1.64	1.1
721.5	17.65	17.11	-0.5	 -     	 -     	16	16	 -     	 -     		1.65	1.11
721.75	17.64	17.11	-0.6	 -     	 -     	16	16	 -     	 -     		1.64	1.11
722	17.48	16.98	-0.6	 -     	 -     	16	16	 -     	 -     		1.48	0.98
722.25	17.43	16.93	-0.6	 -     	 -     	16	16	 -     	 -     		1.43	0.93
722.5	17.44	16.94	-0.6	 -     	 -     	16	16	 -     	 -     		1.44	0.94
722.75	17.43	16.93	-0.8	 -     	 -     	16	16	 -     	 -     		1.43	0.93
723	17.27	16.8	-0.8	 -     	 -     	16	16	 -     	 -     		1.27	0.8
723.25	17.21	16.76	-0.8	 -     	 -     	16	16	 -     	 -     		1.21	0.76
723.5	17.23	16.77	-0.8	 -     	 -     	16	16	 -     	 -     		1.23	0.77
723.75	17.22	16.76	-1	 -     	 -     	16	16	 -     	 -     		1.22	0.76
724	17.06	16.63	-1	 -     	 -     	16	16	 -     	 -     		1.06	0.63
724.25	17.01	16.58	-1	 -     	 -     	16	16	 -     	 -     		1.01	0.58
724.5	17.02	16.6	-1	 -     	 -     	16	16	 -     	 -     		1.02	0.6
724.75	17.02	16.59	-1	 -     	 -     	16	16	 -     	 -     		1.02	0.59
725	16.87	16.47	-1	 -     	 -     	16	16	 -     	 -     		0.87	0.47
725.25	16.81	16.42	-1	 -     	 -     	16	16	 -     	 -     		0.81	0.42
725.5	16.82	16.43	-1	 -     	 -     	16	16	 -     	 -     		0.82	0.43
725.75	16.82	16.43	-1.1	 -     	 -     	16	16	 -     	 -     		0.82	0.43
726	16.67	16.3	-1.1	 -     	 -     	16	16	 -     	 -     		0.67	0.3
726.25	16.62	16.26	-1.1	 -     	 -     	16	16	 -     	 -     		0.62	0.26
726.5	16.63	16.27	-1.1	 -     	 -     	16	16	 -     	 -     		0.63	0.27
726.75	16.62	16.26	-1.1	 -     	 -     	16	16	 -     	 -     		0.62	0.26
727	16.48	16.14	-1.1	 -     	 -     	16	16	 -     	 -     		0.48	0.14
727.25	16.43	16.1	-1.1	 -     	 -     	16	16	 -     	 -     		0.43	0.1
727.5	16.44	16.11	-1.1	 -     	 -     	16	16	 -     	 -     		0.44	0.11
727.75	16.44	16.11	-1.1	 -     	 -     	16	16	 -     	 -     		0.44	0.11
728	16.5	16.04	-1.1	 -     	 -     	16	16	 -     	 -     		0.5	0.04
728.25	16.62	19.28	-1.1	 -     	1	16	19	 -     	32 046.67		0.62	0.28
728.5	16.54	17.66	-1.1	 -     	 -     	16	19	 -     	 -     		0.54	-1.34
728.75	16.53	18.88	-1.3	 -     	1	16	19	 -     	32 046.67		0.53	-0.12
729	16.56	21.5	-1.3	 -     	1	16	19	 -     	32 046.67		0.56	2.5
729.25	16.49	17.91	-1.3	 -     	 -     	16	19	 -     	 -     		0.49	-1.09
729.5	16.4	19.66	-1.3	 -     	1	16	19	 -     	32 046.67		0.4	0.66
729.75	16.29	18.34	-1.1	 -     	 -     	16	19	 -     	 -     		0.29	-0.66
730	16.25	20	-1.1	 -     	1	16	19	 -     	32 046.67		0.25	1


More information about the TRNSYS-users mailing list