[Equest-users] Sizing Ratio
DongEun Kim
equested at gmail.com
Tue Jun 28 17:55:33 PDT 2011
Thank you Ncik and Brian !
Let me rephrase my question.
The building has one AHU per floor,
I thought I could put the coil capacity, fan cfm (not auto-sizing), and
everything as they are designed then just expand the capacity with sizing
ratio to fit
the expanded load by floor multiplier.
Does it make sense?
And one more thing,
when there are more than one FCUs for a zone, could I just model one FCU and
apply the number of FCU in sizing ratio?
Many thanks in advance.
DE
2011/6/28 Brian Fountain <bfountain at greensim.com>
> **
> You will find that your floor multiplier (& space multiplier if it is used)
> are carried over as zone multipliers. So, the values you put in at the
> zonal level will be multiplied by your floor multiplier. The values you put
> in at the system level will be for the overall system serving all 17 floors
> -- if capacities are not entered then the overall capacity based on the
> auto-sizing will be used. You do not need to put "17" in for the sizing
> ratio.
>
>
> On 6/28/2011 1:09 AM, DongEun Kim wrote:
>
> Hi all,
>
> Can anyone help me with this two question?
>
> As I model a high-rise building using"Floor Muliplier", I have a floor
> (middle) which actually represent the load for 17 floors.
>
> Now I want to link this floor(s) to a certain HVAC system.
>
> Can I simply put "17" in System Sizing > Sizing Ratio ?
>
> Thank you in advance !
>
> ~DE
>
> Kim, DongEun(DE) | Research Engineer, LEED AP
> Annex R&D Institute, HIMEC(Hanil Mech. & Elec. Consultants)
>
>
>
> _______________________________________________
> Equest-users mailing listhttp://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
>
> No virus found in this message.
> Checked by AVG - www.avg.com
> Version: 10.0.1388 / Virus Database: 1516/3730 - Release Date: 06/27/11
>
>
>