[Equest-users] Sizing Ratio
Brian Fountain
bfountain at greensim.com
Tue Jun 28 07:23:15 PDT 2011
You will find that your floor multiplier (& space multiplier if it is
used) are carried over as zone multipliers. So, the values you put in
at the zonal level will be multiplied by your floor multiplier. The
values you put in at the system level will be for the overall system
serving all 17 floors -- if capacities are not entered then the overall
capacity based on the auto-sizing will be used. You do not need to put
"17" in for the sizing ratio.
On 6/28/2011 1:09 AM, DongEun Kim wrote:
> Hi all,
> Can anyone help me with this two question?
> As I model a high-rise building using"Floor Muliplier", I have a floor
> (middle) which actually represent the load for 17 floors.
> Now I want to link this floor(s) to a certain HVAC system.
> Can I simply put "17" in System Sizing > Sizing Ratio ?
> Thank you in advance !
> ~DE
> Kim, DongEun(DE) | Research Engineer, LEED AP
> Annex R&D Institute, HIMEC(Hanil Mech. & Elec. Consultants)
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
> No virus found in this message.
> Checked by AVG - www.avg.com <http://www.avg.com>
> Version: 10.0.1388 / Virus Database: 1516/3730 - Release Date: 06/27/11
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110628/2056b294/attachment.htm>
More information about the Equest-users
mailing list