You will find that your floor multiplier (& space multiplier if
it is used) are carried over as zone multipliers. So, the values
you put in at the zonal level will be multiplied by your floor
multiplier. The values you put in at the system level will be for
the overall system serving all 17 floors -- if capacities are not
entered then the overall capacity based on the auto-sizing will be
used. You do not need to put "17" in for the sizing ratio.<br>
<br>
On 6/28/2011 1:09 AM, DongEun Kim wrote:
<blockquote
cite="mid:BANLkTi=BZXH9bWE56Kh8F-ZvdTJEf3_LLw@mail.gmail.com"
type="cite">
<div>Hi all,</div>
<div> </div>
<div>Can anyone help me with this two question?</div>
<div> </div>
<div>As I model a high-rise building using"Floor Muliplier", I
have a floor (middle) which actually represent the load for 17
floors.</div>
<div> </div>
<div>Now I want to link this floor(s) to a certain HVAC system. </div>
<div> </div>
<div>Can I simply put "17" in System Sizing > Sizing Ratio ?</div>
<div> </div>
<div>Thank you in advance !</div>
<div> </div>
<div>~DE</div>
<div> </div>
<div>
<div><font size="2" color="#000080" face="Arial">Kim,
DongEun(DE) | Research Engineer, LEED AP<br>
Annex R&D Institute, HIMEC(Hanil Mech. & Elec.
Consultants)</font></div>
</div>
<div> </div>
<pre wrap="">
<fieldset class="mimeAttachmentHeader"></fieldset>
_______________________________________________
Equest-users mailing list
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a>
To unsubscribe from this mailing list send a blank message to <a class="moz-txt-link-abbreviated" href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a>
</pre>
<br>
<fieldset class="mimeAttachmentHeader"></fieldset>
<br>
<p class="avgcert" color="#000000" align="left">No virus found in
this message.<br>
Checked by AVG - <a moz-do-not-send="true"
href="http://www.avg.com">www.avg.com</a><br>
Version: 10.0.1388 / Virus Database: 1516/3730 - Release Date:
06/27/11</p>
</blockquote>
<br>
</body>
</html>