<div>Thank you Ncik and Brian !</div>
<div> </div>
<div>Let me rephrase my question.</div>
<div>The building has one AHU per floor, </div>
<div>I thought I could put the coil capacity, fan cfm (not auto-sizing), and everything as they are designed then just expand the capacity with sizing ratio to fit</div>
<div>the expanded load by floor multiplier. <br>Does it make sense?</div>
<div> </div>
<div>And one more thing, </div>
<div>when there are more than one FCUs for a zone, could I just model one FCU and apply the number of FCU in sizing ratio?</div>
<div> </div>
<div>Many thanks in advance.</div>
<div> </div>
<div>DE</div>
<div> </div>
<div class="gmail_quote">2011/6/28 Brian Fountain <span dir="ltr"><<a href="mailto:bfountain@greensim.com">bfountain@greensim.com</a>></span><br>
<blockquote style="BORDER-LEFT: #ccc 1px solid; MARGIN: 0px 0px 0px 0.8ex; PADDING-LEFT: 1ex" class="gmail_quote"><u></u>
<div text="#000000" bgcolor="#ffffff">You will find that your floor multiplier (& space multiplier if it is used) are carried over as zone multipliers. So, the values you put in at the zonal level will be multiplied by your floor multiplier. The values you put in at the system level will be for the overall system serving all 17 floors -- if capacities are not entered then the overall capacity based on the auto-sizing will be used. You do not need to put "17" in for the sizing ratio.
<div>
<div></div>
<div class="h5"><br><br>On 6/28/2011 1:09 AM, DongEun Kim wrote: </div></div>
<blockquote type="cite">
<div>
<div></div>
<div class="h5">
<div>Hi all,</div>
<div> </div>
<div>Can anyone help me with this two question?</div>
<div> </div>
<div>As I model a high-rise building using"Floor Muliplier", I have a floor (middle) which actually represent the load for 17 floors.</div>
<div> </div>
<div>Now I want to link this floor(s) to a certain HVAC system. </div>
<div> </div>
<div>Can I simply put "17" in System Sizing > Sizing Ratio ?</div>
<div> </div>
<div>Thank you in advance !</div>
<div> </div>
<div>~DE</div>
<div> </div>
<div>
<div><font color="#000080" size="2" face="Arial">Kim, DongEun(DE) | Research Engineer, LEED AP<br>Annex R&D Institute, HIMEC(Hanil Mech. & Elec. Consultants)</font></div></div>
<div> </div></div></div><pre><fieldset></fieldset>
_______________________________________________
Equest-users mailing list
<a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a>
To unsubscribe from this mailing list send a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG" target="_blank">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a>
</pre><br>
<fieldset></fieldset> <br>
<p align="left" color="#000000">No virus found in this message.<br>Checked by AVG - <a href="http://www.avg.com/" target="_blank">www.avg.com</a><br>Version: 10.0.1388 / Virus Database: 1516/3730 - Release Date: 06/27/11</p>
</blockquote><br></div></blockquote></div><br>