[Equest-users] Unexplained Electric Space Heat

Chris Jones cj at enersave.ca
Tue Apr 6 09:54:50 PDT 2010


DOE2.2, like DOE2.1e allows for the Electric Input Ratio for fossil 
boilers.  The EIR represents boiler components such as a blower 
fan.  I can't seem to locate the default for HW-BOILER in equest but 
for DOE2.1e the default EIR is 0.022.  If you don't override the 
default you will see Electric Heat in the results.  In the equest 
Boiler Properties input screen the Electric Input Ratio is at the 
right side of the dialog box.


At 04:35 PM 4/5/2010, David Bastow wrote:
>Content-Type: multipart/related; type="multipart/alternative";
>         boundary="----_=_NextPart_001_01CAD4FF.996E5818"
>Content-class: urn:content-classes:message
>
>Stephen,
>
>You might check to see if you have electric baseboard heaters set up 
>on your air side HVAC under heating, under the preheat/baseboard 
>tab.  That is the main thing that I have often seen on reviews get 
>left mistakenly on.
>
>David A. Bastow
>McClure Engineering, Inc.
>507 Main Avenue West
>Post Office Box 1404
>Twin Falls, Idaho   83303-1404
>Web Site:  <http://www.mcclure-engineering.com/>www.mcclure-engineering.com
>
>
>----------
>From: equest-users-bounces at lists.onebuilding.org 
>[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of John Aulbach
>Sent: Monday, April 05, 2010 1:25 PM
>To: Salomon, Stephen; equest-users at lists.onebuilding.org
>Subject: Re: [Equest-users] Unexplained Electric Space Heat
>
>.INP and .PD2 files needs to be looked at. You have SOMETHING set as 
>electric heat.
>
>
>John R. Aulbach, PE, CEM
>
>Senior Energy Engineer
>
>Partner Energy
>
>1990 E. Grand Avenue, El Segundo, CA 90245
>W: 888-826-1216, X254| D: 310-765-7295 | F: 310-817-2745
>
><http://www.ptrenergy.com/>www.ptrenergy.com 
><mailto:%7C%20jaulbach at ptrenergy.com>| jaulbach at ptrenergy.com
>
>
>
>
>From: "Salomon, Stephen" <ssalomon at smma.com>
>To: "equest-users at lists.onebuilding.org" <equest-users at lists.onebuilding.org>
>Sent: Mon, April 5, 2010 12:06:40 PM
>Subject: [Equest-users] Unexplained Electric Space Heat
>
>Hi,
>
>
>
>I am modeling my design building that contains some AHUs, UHs, CUHs, 
>and MAUs.  All of the heating in the systems comes from 3 hot water 
>boilers that supply hot water coils in the air-side equipment.  The 
>VAV systems have VAV boxes with hot water reheat coils and there are 
>no electric resistance heating coils in the building.  However when 
>I simulate the model I get an extremely large space heating load 
>under the Electric Consumption.  Has anyone come across this problem?
>
>
>
>Thank you for any ideas or help.
>
>
>
>Stephen Salomon
>
>
>
>__________________________________________
>
>Stephen E Salomon
>
>Mechanical
>
>Symmes Maini & McKee Associates, Inc.
>
>1000 Massachusetts Avenue, Cambridge, MA 02138
>
>t: 617.520.9238
>
>http://intranet/Images/USGBC.jpg
>
>
>
>
>f: 617.354.5758
>
><mailto:SSalomon at smma.com>ssalomon at smma.com
>
>www.smma.com
>
>
>
>
>
>
>
>_______________________________________________
>Equest-users mailing list
>http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
>To unsubscribe from this mailing list send  a blank message to 
>EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG


Chris Jones
14 Oneida Avenue
Toronto, ON M5J 2E3.
Tel.  416-203-7465
Fax. 416-946-1005

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100406/c39fd348/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: 47232a59.jpg
Type: image/jpeg
Size: 14792 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100406/c39fd348/attachment.jpg>


More information about the Equest-users mailing list