<html>
<body>
DOE2.2, like DOE2.1e allows for the Electric Input Ratio for fossil
boilers.  The EIR represents boiler components such as a blower
fan.  I can't seem to locate the default for HW-BOILER in equest but
for DOE2.1e the default EIR is 0.022.  If you don't override the
default you will see Electric Heat in the results.  In the equest
Boiler Properties input screen the Electric Input Ratio is at the right
side of the dialog box.<br><br>
<br>
At 04:35 PM 4/5/2010, David Bastow wrote:<br>
<blockquote type=cite class=cite cite="">Content-Type: multipart/related;
type="multipart/alternative";<br>
<x-tab>        </x-tab>
boundary="----_=_NextPart_001_01CAD4FF.996E5818"<br>
Content-class: urn:content-classes:message<br><br>
<font size=2 color="#0000FF">Stephen,<br>
</font> <br>
<font size=2 color="#0000FF">You might check to see if you have electric
baseboard heaters set up on your air side HVAC under heating, under the
preheat/baseboard tab.  That is the main thing that I have often
seen on reviews get left mistakenly on.<br>
</font> <br>
<font size=6 color="#0000FF"><b><i>David A. Bastow <br>
</font>McClure Engineering, Inc.  <br>
</i></b><font face="Batang" size=2 color="#FF0000">507 Main Avenue
West<br>
Post Office Box 1404<br>
Twin Falls, Idaho   83303-1404<br>
</font><font size=2>Web Site: 
</font><a href="http://www.mcclure-engineering.com/">
<font size=2 color="#0000FF">www.mcclure-engineering.com</a><br>
</font><br>
<hr>
<font face="Tahoma" size=2><b>From:</b>
equest-users-bounces@lists.onebuilding.org
[<a href="mailto:equest-users-bounces@lists.onebuilding.org" eudora="autourl">
mailto:equest-users-bounces@lists.onebuilding.org</a>] <b>On Behalf Of
</b>John Aulbach<br>
<b>Sent:</b> Monday, April 05, 2010 1:25 PM<br>
<b>To:</b> Salomon, Stephen; equest-users@lists.onebuilding.org<br>
<b>Subject:</b> Re: [Equest-users] Unexplained Electric Space Heat<br>
</font><br>
.INP and .PD2 files needs to be looked at. You have SOMETHING set as
electric heat.<br>
 <br><br>
<a name="_MailAutoSig"></a>John R. Aulbach, PE, CEM<br><br>
Senior Energy Engineer<br>
<br>
<b>Partner Energy<br>
</b><br>
1990 E. Grand Avenue, El Segundo, CA 90245<br>
W: 888-826-1216, X254| D: 310-765-7295 | F: 310-817-2745<br><br>
<a href="http://www.ptrenergy.com/">www.ptrenergy.com</a>
<a href="mailto:%7C%20jaulbach@ptrenergy.com">|
jaulbach@ptrenergy.com</a><br><br>
 <br><br>
<br>
<font face="Tahoma" size=2><b>From:</b> "Salomon, Stephen"
<ssalomon@smma.com><br>
<b>To:</b> "equest-users@lists.onebuilding.org"
<equest-users@lists.onebuilding.org><br>
<b>Sent:</b> Mon, April 5, 2010 12:06:40 PM<br>
<b>Subject:</b> [Equest-users] Unexplained Electric Space Heat<br>
</font><br>
Hi,<br><br>
 <br><br>
I am modeling my design building that contains some AHUs, UHs, CUHs, and
MAUs.  All of the heating in the systems comes from 3 hot water
boilers that supply hot water coils in the air-side equipment.  The
VAV systems have VAV boxes with hot water reheat coils and there are no
electric resistance heating coils in the building.  However when I
simulate the model I get an extremely large space heating load under the
Electric Consumption.  Has anyone come across this problem?<br><br>
 <br><br>
Thank you for any ideas or help.<br><br>
 <br><br>
Stephen Salomon<br><br>
 <br><br>
__________________________________________<br><br>
<b>Stephen E Salomon<br>
</b><br>
Mechanical<br><br>
<b>Symmes Maini & McKee Associates, Inc.<br>
</b><br>
1000 Massachusetts Avenue, Cambridge, MA 02138<br><br>
t: 617.520.9238<br><br>
<img src="cid:7.1.0.9.2.20100406125017.026f7da8@enersave.ca.1" width=63 height=64 alt="http://intranet/Images/USGBC.jpg">
<br><br>
 <br><br>
f: 617.354.5758<br><br>
<a href="mailto:SSalomon@smma.com">ssalomon@smma.com</a><br><br>
<a href="http://www.smma.com/" eudora="autourl">www.smma.com</a><br><br>
 <br><br>
 <br><br>
<br><br>
_______________________________________________<br>
Equest-users mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" eudora="autourl">
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a>
<br>
To unsubscribe from this mailing list send  a blank message to
EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</blockquote>
<x-sigsep><p></x-sigsep>
<br>
Chris Jones<br>
14 Oneida Avenue<br>
Toronto, ON M5J 2E3.<br>
Tel.  416-203-7465<br>
Fax. 416-946-1005<br><br>
</body>
</html>