[Equest-users] Unexplained Electric Space Heat
David Bastow
dbastow at mcclure-engineering.com
Mon Apr 5 13:35:58 PDT 2010
Stephen,
You might check to see if you have electric baseboard heaters set up on
your air side HVAC under heating, under the preheat/baseboard tab. That
is the main thing that I have often seen on reviews get left mistakenly
on.
David A. Bastow
McClure Engineering, Inc.
507 Main Avenue West
Post Office Box 1404
Twin Falls, Idaho 83303-1404
Web Site: www.mcclure-engineering.com
<http://www.mcclure-engineering.com/>
________________________________
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of John
Aulbach
Sent: Monday, April 05, 2010 1:25 PM
To: Salomon, Stephen; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Unexplained Electric Space Heat
.INP and .PD2 files needs to be looked at. You have SOMETHING set as
electric heat.
John R. Aulbach, PE, CEM
Senior Energy Engineer
________________________________
Partner Energy
1990 E. Grand Avenue, El Segundo, CA 90245
W: 888-826-1216, X254| D: 310-765-7295 | F: 310-817-2745
www.ptrenergy.com <http://www.ptrenergy.com/> | jaulbach at ptrenergy.com
<mailto:%7C%20jaulbach at ptrenergy.com>
________________________________
From: "Salomon, Stephen" <ssalomon at smma.com>
To: "equest-users at lists.onebuilding.org"
<equest-users at lists.onebuilding.org>
Sent: Mon, April 5, 2010 12:06:40 PM
Subject: [Equest-users] Unexplained Electric Space Heat
Hi,
I am modeling my design building that contains some AHUs, UHs, CUHs, and
MAUs. All of the heating in the systems comes from 3 hot water boilers
that supply hot water coils in the air-side equipment. The VAV systems
have VAV boxes with hot water reheat coils and there are no electric
resistance heating coils in the building. However when I simulate the
model I get an extremely large space heating load under the Electric
Consumption. Has anyone come across this problem?
Thank you for any ideas or help.
Stephen Salomon
__________________________________________
Stephen E Salomon
Mechanical
Symmes Maini & McKee Associates, Inc.
1000 Massachusetts Avenue, Cambridge, MA 02138
t: 617.520.9238
f: 617.354.5758
ssalomon at smma.com <mailto:SSalomon at smma.com>
www.smma.com <http://www.smma.com/>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100405/bdec3997/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 14792 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100405/bdec3997/attachment.jpeg>
More information about the Equest-users
mailing list