hotline hotline at Transsolar.com
Wed Jan 18 02:16:50 PST 2023


Dear Ali,

the output QSENS is the sensible energy load that is met by the ideal heating/ ideal cooling in the airnode. If you bring conditioned air into your zone (through TRNFlow?) so that the set temperatures of heating/ cooling are reached, the output QSENS will be zero. Have you checked if that is the case?

Best,
Christina

__________________________________________________________________________________________________


Transsolar KlimaEngineering

Stuttgart  | München | Paris | New York


https://www.trnsys.de<https://www.trnsys.de/>
https://transsolar.com/de

<https://www.trnsys.de>


Transsolar Energietechnik GmbH | Curiestraße 2 | 70563 Stuttgart

Geschäftsführer: Matthias Schuler, Thomas Auer, Stefan Holst, Dieter Schnelle

Registered at Amtsgericht Stuttgart HRB 23347 | USt-IdNr.: DE 152272639

The simulation project you have sent will be stored on the local servers of Transsolar Energietechnik GmbH for the duration of the project support. Our employees are obliged by us to confidentiality. After this period, all project-related data is deleted.

The storage of your personal e-mail and other contact information is based on the mutual interest in the execution of this traffic and on a mutual business contact. If you have any questions, please contact our data protection officer at privacy at transsolar.com<mailto:privacy at transsolar.com>. Our privacy policy can be found here<http://www.trnsys.de/docs/userservice/userservice_dataprivacy_en.htm>.


________________________________
Von: TRNSYS-users <trnsys-users-bounces at lists.onebuilding.org> im Auftrag von Ali Shahrouzian via TRNSYS-users <trnsys-users at lists.onebuilding.org>
Gesendet: Dienstag, 10. Januar 2023 16:46
An: TRNSYS-users at lists.onebuilding.org <TRNSYS-users at lists.onebuilding.org>
Cc: Ali Shahrouzian <ALISHAHROUZIAN at cmail.carleton.ca>
Betreff: [TRNSYS-users] TrnFlow & Type 151


Dear all TRNSYS users,



I am modelling a VAV AHU system to satisfy heating and cooling loads of a residential building. I have used Type 151 in connection with Type 56. As you know, it is required to connect the NTYPE 2 (QSENS) as output from Type 56 to the “Zone sensible energy load” of Type 151 as input. However, when I turn on Trnflow button in Type56-Trnflow, the NTYPE 2(QSENS) is always zero.



Am I allowed to connect this component (Type 151) to Type 56-Trnflow component when Trnflow button is on? If I am, how can I fix the problem of zero output (NTYPE 2)?



I’d be glad if someone could help me out.



Best regards,

Ali