Jan,
The idea is that gas-fired water heaters sometimes have a chimney that
runs from the burner up through the tank. When the burner is active then
the air/exhaust in the chimney is hot and the water in the tank gains a
little energy from the conduction/convection heat transfer from the
chimney air to the water. When the burner is not active then the air in
the chimney is not hot and there can be additional energy losses from
the tank water to that air. The amount of loss is controlled by a
parameter that asks what the u-value of the flue is and by the input
that sets the temperature of the air/exhaust in the flue. If you want to
deactivate those losses you can set the flue u-value to zero.
kind regards,
David
On 2/2/2023 5:48 AM, Böttner, Jan via TRNSYS-users wrote:
>
> Hi,
>
> I’m using the storage tank type 534.
>
> This tank has gasflue losses, which I don’t quite understand from
> reading the documentation.
>
> But the way I understand it, it doesn’t apply for the tank I am
> modelling.
>
> So I would like to deactivate these losses, as they make up for about
> 10% for my energy supply.
>
> Best regards,
>
> Jan
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
--
***************************
David BRADLEY
Principal
Thermal Energy System Specialists, LLC
3 North Pinckney Street - suite 202
Madison, WI 53703 USA
P:+1.608.274.2577
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20230202/e2b44cd3/attachment.htm>
More information about the TRNSYS-users
mailing list