On 2022-11-21 11:21, Alex Cheng via TRNSYS-users wrote:
> Is it more accurate to model a large body of containerized water
> within a room by:
> * Increasing the thermal capacitance in Type56 or,
> * Using storage tanks like Type 158 with Top, Edge, Bottom Loss
> coefficients?
If it's a large tank of water in a room that you are trying to simulate
then model it as a large tank of water within a room! Artificially
increasing the zone capacitance and modeling it that way means that the
water and air are always effectively the same temperature - which is
very unlikely during periods of transient behavior.
Jeff
--
----