Usually you have to use some combination of thermostat models (which
compare a temperature to a set point), differential controllers (which
operate based on a temperature difference instead of on absolute
values), and equations, which combine the outputs of the individual
thermostats together. You'll probably need to use some of the boolean
functions such as GT(:,:). It returns a 1 if the first argument is
greater than the second. There are also functions such as AND(:,:),
which will return a 1 only if both of the arguments are 1. I would start
out by creating a truth table using your input variables (house
temperature, tank temperature, collector temperature) and fully define
how the valve should be set for all sensed temperatures. From there the
truth table can be turned into one or more equations.
kind regards,
David
On 05/14/2022 03:57, berkane ahlem via TRNSYS-users wrote:
> Dear Users,
> in GSHP systems, the diverting Valve- will generally send all of its
> input flow to house but if the house is warm enough and the tank is
> cold while the collector is cold too, this valve will send all of its
> input to tank. how can i wright a control function gor this diveting
> valve
> Regards
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
--
***************************
David BRADLEY
Principal
Thermal Energy System Specialists, LLC
3 North Pinckney Street - suite 202
Madison, WI 53703 USA
P:+1.608.274.2577
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20220516/ddb372f4/attachment.htm>
More information about the TRNSYS-users
mailing list