[TRNSYS-users] COP Type 941 Ait to water Heat Pump
miriam di matteo
dimatteo.1585179 at studenti.uniroma1.it
Mon Mar 21 05:01:56 PDT 2022
Dear all users,
About the Type 941 (Trnsys v.17):
- First: can you confirm if I understand its functioning? I use it only
for heating, at the moment.
- Second: I believe that the values of the COP it isn’t correct, or I
don’t understand it. The COP trend depends on the external files with the
heating performance data, is it? In this file I have:
Capacity increases when the entered water temperature decreases and the
air temperature increases ( <Tin,w and >Tin,a → >Capacity)
Power increases when the entered water temperature increases and the air
temperature decreases ( >Tin,w and <Tin,a → >Power)
So the COP increases when the entered water temperature decreases and
the air temperature increases ( <Tin,w and >Tin,a → >COP). But the
simulation gives opposites results. The external files are wrong? or I
misunderstand the Type functioning?
I tried to calculate the COP with excel and the results come out as per
the provision, therefore different from TRNSYS' results.
About the first question:
I know as *Parameters:*
- Specific Heat of Liquid Stream
- Blower Power (pb)
- Total Air Flowrate (Fa,d)
- Rated Heating Capacity (qh,d)
- Rated Heating Power (ph,d)
*and as Input:*
- Inlet Liquid Temperature (Tin,w)
- Inlet Liquid Flowrate (Fin,w)
- Inlet Air Temperature (Tin,a)
- Inlet Air Humidity Ratio
- Inlet Air % Relative Humidity
- Heating Control Signal
and as *external files*
- Heating and cooling catalog data for the capacity and power as a
function of entering the water and air temperature (fc=f(Tin,a;Tin,w) and
fp=f(Tin,a;Tin,w))
So when the simulation running:
1. The Type 941 reads the air and water entering temperature (Tin,w and
Tin,a)
2. Interpolates the heating performance file and multiplies this
“performance factor” by HP Rated capacity and power. (fc(Tin,a;Tin,w) and
fp(Tin,a;Tin,w))
3. So obtain Capacity and Power as a function of entering the water and
air temperature by each time step. (qh(t)=fc*qh,d and ph(t)=fp*ph,d)
4. Calculates the COPh as a ratio between qh(t)/(ph(t)+pblower) , i put
paux=0
Is it correct??
Thank you in advance,
Regards,
Miriam Di Matteo
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20220321/59cd859a/attachment-0001.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: BilancioMensile_Cap-Vol.b17
Type: application/octet-stream
Size: 478933 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20220321/59cd859a/attachment-0003.obj>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: Impianto di Riscaldamento_HP_Rad_v2.tpf
Type: application/octet-stream
Size: 837281 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20220321/59cd859a/attachment-0004.obj>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: AWHP_Type941_H.dat
Type: application/octet-stream
Size: 2882 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20220321/59cd859a/attachment-0005.obj>
More information about the TRNSYS-users
mailing list