Tue Jun 7 10:43:20 PDT 2022
Type941 models a heat pump that has a single speed compressor and a
single speed fan. The device's capacity (the maximum amount of energy
that it can transfer to/from the air) is a function of the inlet water
temperature and the inlet air dry bulb temperature. It is not a function
of the air flow rate. Changing the air flow rate will change the air
outlet temperature but not the energy transferred to/from the air.
As a side note, there are some models of multistage and variable speed
compressor heat pumps in which the capacity is a function of the air
flow rate as well as of the inlet temperatures.
kind regards,
David
On 06/07/2022 10:59, Jen parken via TRNSYS-users wrote:
> hello all
> I have a question about type 941
> why whenever i change the amount of inlet air flow rate, the value of
> "heat transfer to air" doesn't change?
> even though the value of output air flow rate (output6) changes when i
> change the value of the inlet flow rate
> I went through the equations in the documentation and i found that the
> heat transfer to air depends on the flow rate
> please correct me if i am wrong
> thanks
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
--
***************************
David BRADLEY
Principal
Thermal Energy System Specialists, LLC
3 North Pinckney Street - suite 202
Madison, WI 53703 USA
P:+1.608.274.2577
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20220607/3334b0d5/attachment.htm>
More information about the TRNSYS-users
mailing list